  #1   Report Post  
Andy Lewis
 
Posts: n/a
Default Electrical cable outside

I wish to lay an outside electrical cable to my garden shed 30 metres from
house, what is the best sort of cable? Cheap but safe and can I bury the
cable?
Thanks......


  #2   Report Post  
Harry Bloomfield
 
Posts: n/a
Default

Andy Lewis expressed precisely :
I wish to lay an outside electrical cable to my garden shed 30 metres from
house, what is the best sort of cable? Cheap but safe and can I bury the
cable?
Thanks......


SWA (steel wire armoured) cable and yes it can be buried. Depth depends
upon where it is to be buried or rather what is along the intended
route.

--


--

Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.org

  #3   Report Post  
:::Jerry::::
 
Posts: n/a
Default


"Andy Lewis" wrote in message
...
I wish to lay an outside electrical cable to my garden shed 30 metres from
house, what is the best sort of cable? Cheap but safe and can I bury the
cable?


And just what are you going to use this cable for, a 5w bulb or a sub main
for your 300amp stand-by generator ?....

I other words, more info is required.


  #4   Report Post  
Tim S
 
Posts: n/a
Default

On Mon, 07 Feb 2005 19:16:34 +0000, Andy Lewis wrote:

I wish to lay an outside electrical cable to my garden shed 30 metres
from house, what is the best sort of cable? Cheap but safe and can I
bury the cable?
Thanks......


Armoured (SWA) is an option (there are others). I'm not qualified BTW -
but there are a few things that need to be considered. It's not
necessarily as simple as lob cable in ground and connect (it might be, but
not necessarily).

Cable needs to be routed suitably - including burying in correctly
prepared trench of certain minimum depth with warning tape above by a
specified amount (so far, still cheap, but much hard work involved).
Surround cable with sieved soil as stones can damage it. Cable can be
clipped to solid structures for some of its run - but not to a fence,
deemed too likely to fall over.

Also, there is a serious need to consider the earthing arrangements - I'm
studying this myself and am so far not totally clear - but it is *not*
necessarily the case that you export the supply earth from the house. It's
worth first finding out what type of earth the supply presents to your
house as this makes a difference to the design. You can end up in certain
cases with having to supply a local earth via rods and these should be
tested. That's going to cost but I can't stress enough that it's important
and is money well spent.

SWA is not particularly difficult to work with, but you need to have the
correct brass termination glands and know how to deal with the earths at
each end. It's best (to the best of my knowledge) to use 3 core for this
type of job, using one core as an earth rather than rely on the steel wire
armouring (which *must* also be earthed solidly or the cable is
potentially dangerous if you stick a fork through it).

I'm being cautious here as regulations applying to outside wiring are
quite onerous. I would recommend seeking an engineer's advice (or a
seasoned sparky) on the earthing requirements in particular,
which is what I am expecting to do myself.

Sorry to make it sound painful, but outside power really needs to be done
right.

HTH

Tim
  #5   Report Post  
Andy Lewis
 
Posts: n/a
Default

Many thanks to those who have taken time to respond..
The cable will only be used to supply lighting to the shed and power to a
submersible water pump
Thanks


"Tim S" wrote in message
news
On Mon, 07 Feb 2005 19:16:34 +0000, Andy Lewis wrote:

I wish to lay an outside electrical cable to my garden shed 30 metres
from house, what is the best sort of cable? Cheap but safe and can I
bury the cable?
Thanks......


Armoured (SWA) is an option (there are others). I'm not qualified BTW -
but there are a few things that need to be considered. It's not
necessarily as simple as lob cable in ground and connect (it might be, but
not necessarily).

Cable needs to be routed suitably - including burying in correctly
prepared trench of certain minimum depth with warning tape above by a
specified amount (so far, still cheap, but much hard work involved).
Surround cable with sieved soil as stones can damage it. Cable can be
clipped to solid structures for some of its run - but not to a fence,
deemed too likely to fall over.

Also, there is a serious need to consider the earthing arrangements - I'm
studying this myself and am so far not totally clear - but it is *not*
necessarily the case that you export the supply earth from the house. It's
worth first finding out what type of earth the supply presents to your
house as this makes a difference to the design. You can end up in certain
cases with having to supply a local earth via rods and these should be
tested. That's going to cost but I can't stress enough that it's important
and is money well spent.

SWA is not particularly difficult to work with, but you need to have the
correct brass termination glands and know how to deal with the earths at
each end. It's best (to the best of my knowledge) to use 3 core for this
type of job, using one core as an earth rather than rely on the steel wire
armouring (which *must* also be earthed solidly or the cable is
potentially dangerous if you stick a fork through it).

I'm being cautious here as regulations applying to outside wiring are
quite onerous. I would recommend seeking an engineer's advice (or a
seasoned sparky) on the earthing requirements in particular,
which is what I am expecting to do myself.

Sorry to make it sound painful, but outside power really needs to be done
right.

HTH

Tim





  #6   Report Post  
Owain
 
Posts: n/a
Default

"Andy Lewis" wrote
| I wish to lay an outside electrical cable to my garden shed 30 metres
| from house, what is the best sort of cable? Cheap but safe and can I
| bury the cable?

Steel wire armoured (SWA) cable is suitable for burial. It must be buried
deep enough it will not be disturbed/damaged, which usually means two forks
deep on lawn and deeper on beds with will be double-dug. You can get buried
cable warning tape to bury in the trench just below the surface.

http://www.tlc-direct.co.uk/Main_Ind...SWA/index.html

At 30m you will have to do proper calculations to prove the cable size is
suitable taking into accoutn voltage drop and fault impedance etc

Owain




  #7   Report Post  
Tim S
 
Posts: n/a
Default

On Mon, 07 Feb 2005 21:08:15 +0000, Andy Lewis wrote:

Many thanks to those who have taken time to respond.. The cable will only
be used to supply lighting to the shed and power to a submersible water
pump
Thanks



I was wondering myself about a lights only supply (sealed lights on gate
posts specifically). Does anyone know definitively if exporting the house
earth is generically OK in this case?

I think in your case, as a pond pump is involved, you should go the whole
hog and seek professional advice. Running and connecting
the cable is quite within the abilities of a competent DIYer but the
planning is not cut and dried.

Don't forget the RCD(s) too

Tim
  #8   Report Post  
John Rumm
 
Posts: n/a
Default

Owain wrote:

At 30m you will have to do proper calculations to prove the cable size is
suitable taking into accoutn voltage drop and fault impedance etc


This will get you started:-

http://www.tlc-direct.co.uk/Technica...ltageDrop.html

(SWA is typically XLPE these days)

At thirty meters I would be more inclined to not export the house earth
(i.e. use it to earth the screen of a two core cable, but terminate that
in a insulated consumer unit at the far end. Then use a local earth rod
with local 30mA trip RCD to provide a TT setup. You will also need to
consider protection for the cable at the source end in the event of a
catastrophic L to N or L to E fault in the cable.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Ian Stirling
 
Posts: n/a
Default

Owain wrote:
"Andy Lewis" wrote
| I wish to lay an outside electrical cable to my garden shed 30 metres
| from house, what is the best sort of cable? Cheap but safe and can I
| bury the cable?

Steel wire armoured (SWA) cable is suitable for burial. It must be buried
deep enough it will not be disturbed/damaged, which usually means two forks
deep on lawn and deeper on beds with will be double-dug. You can get buried
cable warning tape to bury in the trench just below the surface.


Does it have to be cable warning marking tape?
I used yellow painted dexian (steel angle) 5cm over the conduit.
  #10   Report Post  
Rick
 
Posts: n/a
Default

On 08 Feb 2005 15:00:02 GMT, Ian Stirling
wrote:

Owain wrote:
"Andy Lewis" wrote
| I wish to lay an outside electrical cable to my garden shed 30 metres
| from house, what is the best sort of cable? Cheap but safe and can I
| bury the cable?

Steel wire armoured (SWA) cable is suitable for burial. It must be buried
deep enough it will not be disturbed/damaged, which usually means two forks
deep on lawn and deeper on beds with will be double-dug. You can get buried
cable warning tape to bury in the trench just below the surface.


Does it have to be cable warning marking tape?
I used yellow painted dexian (steel angle) 5cm over the conduit.


The idea of the warning tape, is so that somebody who digs, finds the
tape long before the cable. For the reason the tapes is put somewhere
neer the surface. An excavator bucket (small machine) can take out 2
foot deep in one bite .......

Rick




  #11   Report Post  
s--p--o--n--i--x
 
Posts: n/a
Default

On 08 Feb 2005 15:00:02 GMT, Ian Stirling
wrote:


"Andy Lewis" wrote
| I wish to lay an outside electrical cable


Anyone know if a cable supported by a catenary wire is still allowed?

sPoNiX

  #12   Report Post  
Stefek Zaba
 
Posts: n/a
Default

s--p--o--n--i--x wrote:

Anyone know if a cable supported by a catenary wire is still allowed?

Yes; but to be Regs-compliant, the catenary wire needs to be earthed,
and the suspended cable needs to be flown pretty damn high: 3.5m above
ground when "inaccessible to vehicular traffic", or 5.2m otherwise (and
5.8m at road crossings - presumably because double-deckers mount Minis
preferentially at road crossings ;-). There are even prescribed - and
quite tight - intervals at which the cables are to be supported, if not
"continually bound up with" the catenary - roughly every foot (300 of
your earth millimiters) for non-armoured, increasing a little for
thicker cables and for armoured - but not by much, with SWA-over-20mm
needing support every 450mm.

It's also Permitted to fly a short (no more than 3m) span of T&E, HiTuf,
or similar - at the same heights, without a catenary, and with sensible
supports (well-rounded, strain-relieving, non-chafing).
  #13   Report Post  
Bob Eager
 
Posts: n/a
Default

On Tue, 8 Feb 2005 17:07:13 UTC, Stefek Zaba
wrote:

Yes; but to be Regs-compliant, the catenary wire needs to be earthed,
and the suspended cable needs to be flown pretty damn high: 3.5m above
ground when "inaccessible to vehicular traffic", or 5.2m otherwise (and
5.8m at road crossings - presumably because double-deckers mount Minis
preferentially at road crossings ;-). There are even prescribed - and


The errata/update to the OSG makes it 5.8m pretty well everywhere - 5.2m
only appears in one place now.

--
Bob Eager
begin a new life...dump Windows!
  #14   Report Post  
Andy Wade
 
Posts: n/a
Default

Ian Stirling wrote:

Does it have to be cable warning marking tape?
I used yellow painted dexian (steel angle) 5cm over the conduit.


Reg. 522-06-03 of BS 7671 allows cable covers or marking tape. Cable
covers are usually pre-cast concrete things, not bits of old scrap iron.

Oh, hang on, you said conduit. The above is for a directly buried
cable. All it says for buried conduits is that they shall be "suitably
identified."

Also: "buried cables, conduits and ducts shall be at a sufficient depth
to avoid being damaged by any reasonably foreseeable disturbance of the
ground." This is usually considered to mean a minimum depth of 450 mm.

--
Andy
  #15   Report Post  
Ian Stirling
 
Posts: n/a
Default

Andy Wade wrote:
Ian Stirling wrote:

Does it have to be cable warning marking tape?
I used yellow painted dexian (steel angle) 5cm over the conduit.


Reg. 522-06-03 of BS 7671 allows cable covers or marking tape. Cable
covers are usually pre-cast concrete things, not bits of old scrap iron.


Fairly substatial, you're not going through it with a spade.
(buried 15 years stuff was recovered more or less intact, unpainted.)

Oh, hang on, you said conduit. The above is for a directly buried
cable. All it says for buried conduits is that they shall be "suitably
identified."

Also: "buried cables, conduits and ducts shall be at a sufficient depth
to avoid being damaged by any reasonably foreseeable disturbance of the
ground." This is usually considered to mean a minimum depth of 450 mm.


Good, it's about that down.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Running Electrical Cable [email protected] Kill the 2 trees in e Home Repair 4 October 15th 04 07:02 AM
slightly OT NTL/Telewest cable descrambler ntldescrambler UK diy 10 August 26th 04 03:25 PM
Electrical cable - how cold? Anna Kettle UK diy 6 August 22nd 04 07:39 AM
Shower electrical cable Jeff UK diy 1 August 13th 03 04:44 PM
Routeing Electrical FTE cable pickerel UK diy 3 July 24th 03 12:43 AM


All times are GMT +1. The time now is 04:56 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"