Owain wrote:
At 30m you will have to do proper calculations to prove the cable size is
suitable taking into accoutn voltage drop and fault impedance etc
This will get you started:-
http://www.tlc-direct.co.uk/Technica...ltageDrop.html
(SWA is typically XLPE these days)
At thirty meters I would be more inclined to not export the house earth
(i.e. use it to earth the screen of a two core cable, but terminate that
in a insulated consumer unit at the far end. Then use a local earth rod
with local 30mA trip RCD to provide a TT setup. You will also need to
consider protection for the cable at the source end in the event of a
catastrophic L to N or L to E fault in the cable.
--
Cheers,
John.
/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/