UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
jacob
 
Posts: n/a
Default 3 phase electrics

What size flex 3 metres long for a 2.2kw 3 phase combi woodwork
machine?
What size cable to workshop (about 6 metres) to supply say max at one
time 6kw 3 phase machines?
Would this need to be armoured or just conduited or what?
Separate single phase elsewhere, but could I run a spur from a 3phase
wall socket to a single phase socket (same phase as other single
phase?) or is this against the rules?
I've got some sheathed and armoured 3 core cable. Does this need a
separate earth for 3 phase use, or do you earth the sheathing, or
both, or neither?

thanks

Jacob
  #3   Report Post  
BigWallop
 
Posts: n/a
Default 3 phase electrics


"jacob" wrote in message
om...
What size flex 3 metres long for a 2.2kw 3 phase combi woodwork
machine?
What size cable to workshop (about 6 metres) to supply say max at one
time 6kw 3 phase machines?
Would this need to be armoured or just conduited or what?
Separate single phase elsewhere, but could I run a spur from a 3phase
wall socket to a single phase socket (same phase as other single
phase?) or is this against the rules?
I've got some sheathed and armoured 3 core cable. Does this need a
separate earth for 3 phase use, or do you earth the sheathing, or
both, or neither?

thanks

Jacob


Is this 3-phase installation at home ? Do you already have a 3-phase supply to the
property ? If you don't already have 3-phase, are you thinking of using a converter
from the single phase domestic supply ?

If you already have the right supply at the property, then it is best to make the
outbuildings a totally separate sub-mains supply from an isolator switch at the head
end. You will need to have the supply split to take this but it is will be worth it
for your own safety and convenience.

If you think you're only going to run up to 6 kW running ampage, then you'll need to
treble that amount to take the start up ampage of the motors on the machines all
running together. This will also allow for any strain on the working motors under
their normal use.

Taking all that into account, you're talking about a supply of 16 mm on each conductor
for the lengths you're talking about, and you may also have to double the neutral to
take the start up load until the motors are all running to speed.

With that supply it will allow you to run lighting and a few sockets from it as well.


---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.687 / Virus Database: 448 - Release Date: 16/05/04


  #4   Report Post  
John Rumm
 
Posts: n/a
Default 3 phase electrics

BigWallop wrote:

If you think you're only going to run up to 6 kW running ampage, then you'll need to
treble that amount to take the start up ampage of the motors on the machines all
running together. This will also allow for any strain on the working motors under
their normal use.


Not any expert on 3 ph setups, but I was under the impression that you
designed cable sizes for the working load and not the startup current
since it is only a short duration transient?

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #5   Report Post  
Lurch
 
Posts: n/a
Default 3 phase electrics

On Mon, 17 May 2004 21:30:39 +0100, in uk.d-i-y John Rumm
strung together this:

Not any expert on 3 ph setups, but I was under the impression that you
designed cable sizes for the working load and not the startup current
since it is only a short duration transient?

Quite right, any motor and most inductive loads will take a large
surge at startup. The continuous circuit current is the one that
determines the cable size. You would also provide motor rated MCB's or
fuses to cope with the startup current.
--

SJW
A.C.S. Ltd.


  #6   Report Post  
BigWallop
 
Posts: n/a
Default 3 phase electrics


"John Rumm" wrote in message
...
BigWallop wrote:

If you think you're only going to run up to 6 kW running ampage, then you'll need

to
treble that amount to take the start up ampage of the motors on the machines all
running together. This will also allow for any strain on the working motors under
their normal use.


Not any expert on 3 ph setups, but I was under the impression that you
designed cable sizes for the working load and not the startup current
since it is only a short duration transient?

Cheers,

John.


Generally you would only allow for the motor start up surge but these motors will be
under strained load conditions while they work and not just start up and run at a
constant rate. Three phase gives you a motor that can keep torque even though it is
slowing under tension loading. As an example, a lift motor can reach the same load
rating while lifting a heavy bin as it does when it first starts dry. So you don't
just rate loading on three phase commercial tooling machinery as you would with a
static motor on say a ventilation system or the like.


---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.687 / Virus Database: 448 - Release Date: 16/05/04


  #7   Report Post  
Owain
 
Posts: n/a
Default 3 phase electrics

"Lurch" wrote
| John Rumm strung together this:
| Not any expert on 3 ph setups, but I was under the impression
| that you designed cable sizes for the working load and not
| the startup current since it is only a short duration transient?
| Quite right, any motor and most inductive loads will take a large
| surge at startup. The continuous circuit current is the one that
| determines the cable size. You would also provide motor rated MCB's or
| fuses to cope with the startup current.

Wouldn't you need to check voltage drop at the start current though, to
ensure there's enough voltage to get the thing started (or does a starter
controller take care of that)?

Owain


  #8   Report Post  
Lurch
 
Posts: n/a
Default 3 phase electrics

On Mon, 17 May 2004 23:07:33 +0100, in uk.d-i-y "Owain"
strung together this:

Wouldn't you need to check voltage drop at the start current though, to
ensure there's enough voltage to get the thing started (or does a starter
controller take care of that)?

Bit of both, a decent starter will drop out if the voltage is too low
but if you've sized up the cable properly with all the correct volt
drop calcs and the like then it shouldn't drop!
--

SJW
A.C.S. Ltd.
  #9   Report Post  
nightjar
 
Posts: n/a
Default 3 phase electrics


"BigWallop" wrote in message
...
.....
Taking all that into account, you're talking about a supply of 16 mm on

each conductor
for the lengths you're talking about, and you may also have to double the

neutral to
take the start up load until the motors are all running to speed.

With that supply it will allow you to run lighting and a few sockets from

it as well.

Personally, I would run it in 25mm, on the principle that it is easier to
build in spare capacity at the beginning than it is to add it later. One of
Murphy's Laws must be that you always want more power in a workshop than you
first designed for.

Colin Bignell


  #10   Report Post  
jacob
 
Posts: n/a
Default 3 phase electrics

What size flex 3 metres long for a 2.2kw 3 phase combi woodwork
machine?
What size cable to workshop (about 6 metres) to supply say max at one
time 6kw 3 phase machines?
Would this need to be armoured or just conduited or what?
Separate single phase elsewhere, but could I run a spur from a 3phase
wall socket to a single phase socket (same phase as other single
phase?) or is this against the rules?
I've got some sheathed and armoured 3 core cable. Does this need a
separate earth for 3 phase use, or do you earth the sheathing, or
both, or neither?

thanks

Jacob


Is this 3-phase installation at home ? Do you already have a 3-phase supply to the
property ?

Is chapel conversion with existing 3 phase supply. Will be single
phase throughout except for connection to basement workshop. This is
how it was before - the 3 phase only powering the organ blower.

If you think you're only going to run up to 6 kW running ampage, then you'll need to
treble that amount to take the start up ampage of the motors on the machines all
running together. This will also allow for any strain on the working motors under
their normal use.

Taking all that into account, you're talking about a supply of 16 mm on each conductor
for the lengths you're talking about, and you may also have to double the neutral to
take the start up load until the motors are all running to speed.

With that supply it will allow you to run lighting and a few sockets from it as well.

6kw only occasionally likely, and simultaneous start-up of all
machines very unlikely. Separate single phase circuit for lights and
sockets. So 16mm sounds excessive to me. 10mm perhaps?


thanks for info

Jacob


  #11   Report Post  
BigWallop
 
Posts: n/a
Default 3 phase electrics


"jacob" wrote in message
m...
What size flex 3 metres long for a 2.2kw 3 phase combi woodwork

snipped
Taking all that into account, you're talking about a supply of 16 mm on each

conductor
for the lengths you're talking about, and you may also have to double the neutral

to
take the start up load until the motors are all running to speed.

With that supply it will allow you to run lighting and a few sockets from it as

well.
6kw only occasionally likely, and simultaneous start-up of all
machines very unlikely. Separate single phase circuit for lights and
sockets. So 16mm sounds excessive to me. 10mm perhaps?


thanks for info

Jacob


If you can be sure that the machines are going to be running individually from each
other, then you might be able to run the supply in 10 mm csa' but if you are going to
have one machine running on its own, then start another machine, then turn a heater
on. Your talking about un-plugging one machine before you plug another one in to be
sure that you're not going to overload the supply. Three phase has an awful
reputation of kicking you in the ass if you don't get it right first time, remember.

Any imbalance on the loadings of the three phase conductors causes heat, this heat
creates further imbalance, this further imbalance creates more heat, and so the cycle
continues. The start-up ampage of some three phase quick start motors can jump to
nearly five or six time the running ampage, so if one machine is under strain loading
taking a slightly higher ampage to do its work, then you start another machine with a
quick start motor, the ampage across the supply is huge.

Even if the load is for a few seconds at a time, it causes improperly sized conductors
to degrade very quickly, so it's best to err on the safe side of caution when you're
dealing with phased supplies. Believe me on this, I've been through it many times
with industrial installations.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 phase armoured used for single phase supply? T i m UK diy 13 February 26th 04 03:25 PM
three phase separation drifter UK diy 8 February 6th 04 09:20 PM
12 KVA Fisher Panda genset and 10kw 3 phase electric motor Rob UK diy 6 October 6th 03 10:57 PM
Upgrade to a three phase domestic supply? Pandora UK diy 32 October 5th 03 02:33 AM
Three phase installation ....? Nicholas UK diy 3 September 1st 03 09:44 AM


All times are GMT +1. The time now is 04:40 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"