After lots of helpful comments on my plight to redesign my Dad's
CH using a thermal store system, I was wondering if anyone could comment
on this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump
assembly by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents
70+C water at the inflow end of the underfloor pipework.

So parts of the floor are presumably going to get rather hot???

Would you say my instincts are correct or would this type of regulation
actually work?

Ta muchly,

Timbo
--
Tim Southerwood

  #2   Report Post  
Tim
 
Posts: n/a
Default

On Thu, 04 Nov 2004 13:25:33 +0000, Tim wrote:

After lots of helpful comments on my plight to redesign my Dad's CH
using a thermal store system, I was wondering if anyone could comment on
this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump assembly
by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents 70+C
water at the inflow end of the underfloor pipework.

So parts of the floor are presumably going to get rather hot???


OK - one adittional thing... I just found the installation manual on their
website and it does mention that the heating pipe must be run in a
double-spiral config, so a flow and return pipe are alway adjacent.

Wonder if that's how they make such a simple system work? ie they are
relying on the thermal conductivity of the screed to reduce the
inflow/outflow differential and also using the return flow to indrectly
cool the inflow... Sounds didgey - but it *could* just work?

Timbo
  #3   Report Post  
Christian McArdle
 
Posts: n/a
Default

OK - one adittional thing... I just found the installation manual on their
website and it does mention that the heating pipe must be run in a
double-spiral config, so a flow and return pipe are alway adjacent.


Ah. That makes more sense. It controls the power by varying flow speed. As
this will produce a large temperature difference, you need to have the hot
entrance pipes next to the cold exit pipe to ensure average heat transfer
over the whole area.

However, the system would lead to localised hot spots, unless the floor is
sufficiently conductive to ensure that the hot and cold parts produce an
average.

At one end of the spiral, you get a 70C and a 20C pipe. In the middle of the
room, you both pipes finally meet at around 45C. The approach gives an
average 45C anywhere in the room, with some variation, however, depending on
the exact flow rate chosen.

I'd probably still want a proper TMV and pump, though, even for a solid
floor. I like the idea of a simple thermostat setting to set the floor
temperature.

Christian.


  #4   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Tim wrote:

On Thu, 04 Nov 2004 13:25:33 +0000, Tim wrote:


After lots of helpful comments on my plight to redesign my Dad's CH
using a thermal store system, I was wondering if anyone could comment on
this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump assembly
by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents 70+C
water at the inflow end of the underfloor pipework.

So parts of the floor are presumably going to get rather hot???



OK - one adittional thing... I just found the installation manual on their
website and it does mention that the heating pipe must be run in a
double-spiral config, so a flow and return pipe are alway adjacent.

Wonder if that's how they make such a simple system work? ie they are
relying on the thermal conductivity of the screed to reduce the
inflow/outflow differential and also using the return flow to indrectly
cool the inflow... Sounds didgey - but it *could* just work?


Dream on Tim.

When I levelled my U/F heated floor prior to laying laminate, you could
see the wet bits betweenteh double spiral, and the dry bits above it.

The doble sopral simply spreads teh overall heating effect more or less
eenly across teh total floor area.

It does not stop localised hot spots on the floor surface, still less
inside it.

I think you are asking for a cracked screed.




Timbo

  #5   Report Post  
Tim S
 
Posts: n/a
Default

On Fri, 05 Nov 2004 14:40:11 +0000, The Natural Philosopher wrote:

When I levelled my U/F heated floor prior to laying laminate, you could
see the wet bits betweenteh double spiral, and the dry bits above it.


That's certainly very interesting...

The doble sopral simply spreads teh overall heating effect more or less
eenly across teh total floor area.

It does not stop localised hot spots on the floor surface, still less
inside it.

I think you are asking for a cracked screed.


I guess it's one of those things - it either works OK forever or it
buggers your floor. I suspect that in many cases the Danfoss would work,
but I'm one of those unlucky sods that if it's going to pear up, it will
do it to me!


  #6   Report Post  
G&M
 
Posts: n/a
Default


"Tim" wrote in message
news
On Thu, 04 Nov 2004 13:25:33 +0000, Tim wrote:

After lots of helpful comments on my plight to redesign my Dad's CH
using a thermal store system, I was wondering if anyone could comment on
this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump assembly
by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents 70+C
water at the inflow end of the underfloor pipework.


And so parts of the floor would overheat. This would be especially damaging
for a wooden floor.


  #7   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

G&M wrote:

"Tim" wrote in message
news
On Thu, 04 Nov 2004 13:25:33 +0000, Tim wrote:


After lots of helpful comments on my plight to redesign my Dad's CH
using a thermal store system, I was wondering if anyone could comment on
this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump assembly
by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents 70+C
water at the inflow end of the underfloor pipework.



And so parts of the floor would overheat. This would be especially damaging
for a wooden floor.


Yes. I have a bit of a 'cold bridge' near one door threshold - no way to
avoid it really, and you can walk across teh floor in bare tootsies, and
know exactly where it is.

Screed is not a massicvely good heat conductor at all.

Iadeally you want zillions of tiny pipes all at 40C or so in it.
Practically a double helix or two with regulated flow temps is the best
solution.

Apart from the now sticking motorised valve, my system was dead easy to
install, and has after all the calcs and pressure tests etc, performed
exactly as it was supposed to.




  #8   Report Post  
pjdesign
 
Posts: n/a
Default


"Tim" wrote in message
news
After lots of helpful comments on my plight to redesign my Dad's
CH using a thermal store system, I was wondering if anyone could comment
on this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump
assembly by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents
70+C water at the inflow end of the underfloor pipework.

So parts of the floor are presumably going to get rather hot???

Would you say my instincts are correct or would this type of regulation
actually work?

Ta muchly,

Timbo
--
Tim Southerwood


Hi Tim
The valve is a Danfoss http://tinyurl.com/4blyr
I used them in my conservatory.
No mixers, works a treat.
We use the room all the year round. It is super I wish I could do the whole
house like it.
Baz



  #9   Report Post  
IMM
 
Posts: n/a
Default


"pjdesign" wrote in message
...

"Tim" wrote in message
news
After lots of helpful comments on my plight to redesign my Dad's
CH using a thermal store system, I was wondering if anyone could comment
on this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump
assembly by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents
70+C water at the inflow end of the underfloor pipework.

So parts of the floor are presumably going to get rather hot???

Would you say my instincts are correct or would this type of regulation
actually work?

Ta muchly,

Timbo
--
Tim Southerwood


Hi Tim
The valve is a Danfoss http://tinyurl.com/4blyr
I used them in my conservatory.
No mixers, works a treat.
We use the room all the year round. It is super I wish I could do the

whole
house like it.
Baz


Make sure the flow temp is no more than 50-55C. A mixer should be used to
ensure this, or a condensing boiler set to 50Cish and a priority system for
DHW where the boiler temp is ramped right up. ECO-Hometec do boiler just
for this.


  #10   Report Post  
Tim
 
Posts: n/a
Default

On Thu, 04 Nov 2004 13:40:36 +0000, pjdesign wrote:


Hi Tim
The valve is a Danfoss http://tinyurl.com/4blyr
I used them in my conservatory.
No mixers, works a treat.
We use the room all the year round. It is super I wish I could do the whole
house like it.
Baz


Hi Baz. Thanks for the feedback. I'm still weighing it up :?

Timbo


  #11   Report Post  
Christian McArdle
 
Posts: n/a
Default

Would you say my instincts are correct or would this type of regulation
actually work?


It didn't give me a warm fuzzy feeling reading the specs. The "solid floor
only" restriction is probably about the inability to limit temperatures to
sensible values. There's probably an item in the instruction manual saying
to run the boiler at 50C or something.

You really need to go the pump/TMV route.

Christian.


  #12   Report Post  
Tim
 
Posts: n/a
Default

On Thu, 04 Nov 2004 13:41:26 +0000, Christian McArdle wrote:

Would you say my instincts are correct or would this type of regulation
actually work?


It didn't give me a warm fuzzy feeling reading the specs. The "solid
floor only" restriction is probably about the inability to limit
temperatures to sensible values. There's probably an item in the
instruction manual saying to run the boiler at 50C or something.


Hi Christian,

The only fuzzy feeling I got was "ooh, that's simple to install and small
and neat".

They do claim the boiler can run at a standard 81/70C.

You really need to go the pump/TMV route.


I'm completely sure your instinct is well founded - I'm just being cheap
and was wondering whether it is too good to be true or not. I notice that
Baz found his Danfoss works in practise, so I'm still weighing it up...

'twoud be neat and simple though for one single little circuit - it seemed
a lot of effort to install a 4port mixer and an extra pump for one room.


Christian.


Thanks as ever for your expert opinion.

Cheers

Timbo
  #13   Report Post  
Christian McArdle
 
Posts: n/a
Default

'twoud be neat and simple though for one single little circuit - it seemed
a lot of effort to install a 4port mixer and an extra pump for one room.


Is a pump and TMV that much work to install? I suppose as time goes on, I
forget that these things could be a little intimidating if you haven't done
much plumbing before. I presume someone has packaged the lot into one box,
so you just connect the room up to 2 holes and the CH circuit up to the
others and apply electricity.

Christian.


  #14   Report Post  
Tim
 
Posts: n/a
Default

On Thu, 04 Nov 2004 14:35:43 +0000, Christian McArdle wrote:

'twoud be neat and simple though for one single little circuit - it seemed
a lot of effort to install a 4port mixer and an extra pump for one room.


Is a pump and TMV that much work to install? I suppose as time goes on, I
forget that these things could be a little intimidating if you haven't done
much plumbing before. I presume someone has packaged the lot into one box,
so you just connect the room up to 2 holes and the CH circuit up to the
others and apply electricity.

Christian.


I suppose not. It was mostly the extra pump that put me off, what with
standard CH pumps being bulky. Unless they do little pumps for this sort
of thing?

Tim
  #15   Report Post  
IMM
 
Posts: n/a
Default


"Tim" wrote in message
news
On Thu, 04 Nov 2004 14:35:43 +0000, Christian McArdle wrote:

'twoud be neat and simple though for one single little circuit - it

seemed
a lot of effort to install a 4port mixer and an extra pump for one

room.

Is a pump and TMV that much work to install? I suppose as time goes on,

I
forget that these things could be a little intimidating if you haven't

done
much plumbing before. I presume someone has packaged the lot into one

box,
so you just connect the room up to 2 holes and the CH circuit up to the
others and apply electricity.

Christian.


I suppose not. It was mostly the extra pump that put me off, what with
standard CH pumps being bulky. Unless they do little pumps for this sort
of thing?


UFH is going to take up space with manifolds etc. If it is not designed and
controlled properly they are perform terribly badly.




  #16   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Christian McArdle wrote:
'twoud be neat and simple though for one single little circuit - it seemed
a lot of effort to install a 4port mixer and an extra pump for one room.



Is a pump and TMV that much work to install? I suppose as time goes on, I
forget that these things could be a little intimidating if you haven't done
much plumbing before. I presume someone has packaged the lot into one box,
so you just connect the room up to 2 holes and the CH circuit up to the
others and apply electricity.


Thats what I bought - polyplumb 8 way manifold,aux pump, two way valve
amd loads of isoaltaion and drain taps and balancing flow meters for
each circuit and a temp reduction valve. All for about £250 IIRC, and it
was a piece of **** to install. The manifold handles all the polypipe
underfloor circuits, and the two main connections simly go to flow and
return on the boiler.

The only tricky bit was to put in a relay so that the boiler pump could
be called up for ordinary CH without forcing the UFH pump on as well.




Christian.


  #17   Report Post  
IMM
 
Posts: n/a
Default


"Tim" wrote in message
news
On Thu, 04 Nov 2004 13:41:26 +0000, Christian McArdle wrote:

Would you say my instincts are correct or would this type of regulation
actually work?


It didn't give me a warm fuzzy feeling reading the specs. The "solid
floor only" restriction is probably about the inability to limit
temperatures to sensible values. There's probably an item in the
instruction manual saying to run the boiler at 50C or something.


Hi Christian,

The only fuzzy feeling I got was "ooh, that's simple to install and small
and neat".

They do claim the boiler can run at a standard 81/70C.

You really need to go the pump/TMV route.


I'm completely sure your instinct is well founded - I'm just being cheap
and was wondering whether it is too good to be true or not. I notice that
Baz found his Danfoss works in practise, so I'm still weighing it up...


Having 80C water through UFH pipes is ridiculous. It makes the floor far
too, hot. Then there is expansion contraction, etc. The Danfoss system is
assuming that the supply water is less than 55C.

'twoud be neat and simple though for one single little circuit - it seemed
a lot of effort to install a 4port mixer and an extra pump for one room.


No need for a 4 port mixer. A normal cheap 3-port will do.



  #18   Report Post  
pjdesign
 
Posts: n/a
Default


"IMM" wrote in message
...
SNIP
Having 80C water through UFH pipes is ridiculous. It makes the floor far
too, hot. Then there is expansion contraction, etc. The Danfoss system

is
assuming that the supply water is less than 55C.

SNIP

IMM.
Read the link http://tinyurl.com/4blyr.

"Maximum flow temperature 90°C "

" Used in systems which are predominately heated by radiators (normal system
design temperatures 82/71°C) and where Underfloor Heating represents only a
minor part of the system, for example a single room or small extension "

The water will not flow through the pipes at 82/71 because the water is only
let out of the system after it has given up some of it's heat, so it is only
topping up.

Baz


  #19   Report Post  
IMM
 
Posts: n/a
Default


"pjdesign" wrote in message
...

"IMM" wrote in message
...
SNIP
Having 80C water through UFH pipes is ridiculous. It makes the floor

far
too, hot. Then there is expansion contraction, etc. The Danfoss system

is
assuming that the supply water is less than 55C.

SNIP

IMM.
Read the link http://tinyurl.com/4blyr.

"Maximum flow temperature 90°C "

" Used in systems which are predominately heated by radiators (normal

system
design temperatures 82/71°C) and where Underfloor Heating represents only

a
minor part of the system, for example a single room or small extension "

The water will not flow through the pipes at 82/71 because the water is

only
let out of the system after it has given up some of it's heat, so it is

only
topping up.


That is nonsense. A 90C floor is very uncomfortable to walk on.



  #20   Report Post  
Tim
 
Posts: n/a
Default

On Thu, 04 Nov 2004 14:47:30 +0000, IMM wrote:

No need for a 4 port mixer. A normal cheap 3-port will do.


What's the practical difference between 3 and 4 port? I know roughly what
they look like, so I presume the 3 port just short circuits the pipework
under the floor when less heat is needed?

Would you use a 4 port if you needed more than one circuit off it?

Thanks

Tim


  #21   Report Post  
IMM
 
Posts: n/a
Default

From: "Tim"
Subject: Underfloor wet heating - alternative to mixer?
Date: 04 November 2004 15:15

On Thu, 04 Nov 2004 14:47:30 +0000, IMM wrote:

No need for a 4 port mixer. A normal cheap 3-port will do.


What's the practical difference between 3 and 4 port? I know roughly what
they look like, so I presume the 3 port just short circuits the pipework
under the floor when less heat is needed?


Would you use a 4 port if you needed more than one circuit off it?


A 4-port proportioanlly reduces one loop in favour of another. If mid way
50-50 to each. If open 25% then 25% to one and 75% to the other.

The simplest systems are from the likes of Polyplumb. Go to their web site.
their equipment is expensive, but you can buy the component parts and do it
yourself.


  #22   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Tim wrote:

After lots of helpful comments on my plight to redesign my Dad's
CH using a thermal store system, I was wondering if anyone could comment
on this underfloor heating component:

http://www.plumbworld.co.uk/186-0000

specifically: the "Return Temperature Controller"

It claims to be a way of avoiding a 4 port mixer + local pump
assembly by regulating the water return temperature.

The only thing I can see wrong is that it of course still presents
70+C water at the inflow end of the underfloor pipework.

So parts of the floor are presumably going to get rather hot???

Would you say my instincts are correct or would this type of regulation
actually work?


I think yiou have it right,.

Bite the bullet and use the proper system.

Ta muchly,

Timbo

  #23   Report Post  
Tim S
 
Posts: n/a
Default

On Fri, 05 Nov 2004 14:17:49 +0000, The Natural Philosopher wrote:

Would you say my instincts are correct or would this type of regulation
actually work?


I think yiou have it right,.

Bite the bullet and use the proper system.

Ta muchly,

Timbo


Yeah, I think that considering I'm going to blow a wad on the conservatory
(have 2 bods in today to quote) I'll put the better system in just to be
safe.

Tim
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Old "Electric" House, wanting new heating system bschott Home Repair 7 October 29th 04 04:30 AM
Central Heating and Hot Water not working properly together [email protected] UK diy 2 October 19th 04 10:31 AM
Condenser Dryer heating element problem Mark H UK diy 2 September 16th 04 08:57 AM
Heating and hot water failure Alex UK diy 3 September 12th 04 09:28 PM


All times are GMT +1. The time now is 02:33 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"