In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.
--
bert
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 516
Default How Can This Happen (Electrical)?

On 28/02/2019 12:21, bert wrote:
In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Possibly a suppressor in the motor has failed and the resulting
inductive spike is coupling into an adjacent circuit. Makes sense as
you say it doesn't always happen, probably only when the voltage happens
to be on a high part of the AC cycle.

Cheers
--
Clive
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,556
Default How Can This Happen (Electrical)?

In article , Clive Arthur
writes
On 28/02/2019 12:21, bert wrote:
In one bedroom we have a ceiling fan supplied from the lighting
circuit. It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the
RCD protecting the ring mains has tripped. But the lighting circuits
don't go through it and the lights are still on including the one
which is part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Possibly a suppressor in the motor has failed and the resulting
inductive spike is coupling into an adjacent circuit. Makes sense as
you say it doesn't always happen, probably only when the voltage
happens to be on a high part of the AC cycle.

Cheers

Now that is a possibility. Would explain why it has just started to
happen.
--
bert
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 147
Default How Can This Happen (Electrical)?

On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Earthed via a the ring-main circuit?



--
Regards, Paul Herber
http://www.paulherber.co.uk/



  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,554
Default How Can This Happen (Electrical)?

On 28/02/2019 14:15, Paul Herber wrote:
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Earthed via a the ring-main circuit?




Probably not, RCDs don't just detect earth leakage but any current
imbalance between live and neutral.

It wouldn't actually matter where it was earthed if there was leakage to
earth and it wouldn't affect other circuit unless they also had an earth
leakage problem as RCDs aren't connect to earth.

  #7   Report Post  
Posted to uk.d-i-y
GB GB is offline
external usenet poster
 
Posts: 4,768
Default How Can This Happen (Electrical)?

On 28/02/2019 14:38, dennis@home wrote:
On 28/02/2019 14:15, Paul Herber wrote:
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Earthed via a the ring-main circuit?




Probably not, RCDs don't just detect earth leakage but any current
imbalance between live and neutral.

It wouldn't actually matter where it was earthed if there was leakage to
earth and it wouldn't affect other circuit unless they also had an earth
leakage problem as RCDs aren't connect to earth.



Quite agree. I think Clive is probably right as to the cause. Within the
consumer unit, all the lives and all the neutrals are connected
together, so there's scope for some coupling between circuits. The only
thing that's really surprising (to me) is that the RCD protecting the
lighting circuit does not trip.

(I may be making a fool of myself here. Hope not!)




  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,681
Default How Can This Happen (Electrical)?

On 28/02/2019 15:00, GB wrote:
On 28/02/2019 14:38, dennis@home wrote:
On 28/02/2019 14:15, Paul Herber wrote:
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting
circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.

Earthed via a the ring-main circuit?




Probably not, RCDs don't just detect earth leakage but any current
imbalance between live and neutral.

It wouldn't actually matter where it was earthed if there was leakage
to earth and it wouldn't affect other circuit unless they also had an
earth leakage problem as RCDs aren't connect to earth.



Quite agree. I think Clive is probably right as to the cause. Within the
consumer unit, all the lives and all the neutrals are connected
together, so there's scope for some coupling between circuits. The only
thing that's really surprising (to me) is that the RCD protecting the
lighting circuit does not trip.


I wouldn't assume there there is an RCD protecting the lighting circuit.
Very many homes don't have them.

(I may be making a fool of myself here. Hope not!)






--
Robin
reply-to address is (intended to be) valid
  #9   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default How Can This Happen (Electrical)?

On 28/02/2019 16:44, Robin wrote:
On 28/02/2019 15:00, GB wrote:
On 28/02/2019 14:38, dennis@home wrote:
On 28/02/2019 14:15, Paul Herber wrote:
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting
circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.

Earthed via a the ring-main circuit?




Probably not, RCDs don't just detect earth leakage but any current
imbalance between live and neutral.

It wouldn't actually matter where it was earthed if there was leakage
to earth and it wouldn't affect other circuit unless they also had an
earth leakage problem as RCDs aren't connect to earth.



Quite agree. I think Clive is probably right as to the cause. Within
the consumer unit, all the lives and all the neutrals are connected
together, so there's scope for some coupling between circuits. The
only thing that's really surprising (to me) is that the RCD protecting
the lighting circuit does not trip.


I wouldn't assume there there is an RCD protecting the lighting circuit.
Â*Very many homes don't have them.


Of course the 18th edition has altered that for future installs (I think
you are correct about the OPs lights)

Just for info and not related to the OPs question. Domestic properties
are now required to have RCD protection on the lighting circuits even if
the cables are run in a manner or of the type that would not require RCD
protection (eg in trunking or SWA)


--


Adam
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,556
Default How Can This Happen (Electrical)?

In article , GB
writes
On 28/02/2019 14:38, dennis@home wrote:
On 28/02/2019 14:15, Paul Herber wrote:
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.

Earthed via a the ring-main circuit?



Probably not, RCDs don't just detect earth leakage but any current
imbalance between live and neutral.
It wouldn't actually matter where it was earthed if there was
leakage to earth and it wouldn't affect other circuit unless they
also had an earth leakage problem as RCDs aren't connect to earth.



Quite agree. I think Clive is probably right as to the cause. Within
the consumer unit, all the lives and all the neutrals are connected
together, so there's scope for some coupling between circuits. The only
thing that's really surprising (to me) is that the RCD protecting the
lighting circuit does not trip.

There's no rcd on the lighting circuits.
(I may be making a fool of myself here. Hope not!)





--
bert


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,556
Default How Can This Happen (Electrical)?

In article
, Paul
Herber writes
On Thu, 28 Feb 2019 12:21:12 +0000, bert wrote:

In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.


Earthed via a the ring-main circuit?



Are you suggesting that the qualified certified to whatever professional
electrician who did this has screwed up? Well actually his dozy
apprentice did most of the actual work 'til he fired him so yes quite
possible.
--
bert
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default How Can This Happen (Electrical)?

On Thursday, 28 February 2019 12:26:10 UTC, bert wrote:
In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.
In the past few nights a couple of times when switching it off the RCD
protecting the ring mains has tripped. But the lighting circuits don't
go through it and the lights are still on including the one which is
part of the fan and the fan itself can be switched back on.
Puzzled as to how this can happen - and where to start looking.
--
bert


Neutral-Earth faults can trip the RCD.
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,556
Default How Can This Happen (Electrical)?

One on the fan unit and one at the wall. I've checked the wall switch
and tightened up the neutral connection by a turn or two. I've
"instructed" (AKA pleaded with) swmbo to only use that switch for the
time being.
For reason best known to himself the electrician wired the extension
circuits live to the switches whereas the rest of the house is wired
live to the ceiling rose.
In article , Brian Gaff
writes
Where is the switch for the fan, in the fan/light itself?
I'd start there.
Brian


--
bert
  #15   Report Post  
Posted to uk.d-i-y
NY NY is offline
external usenet poster
 
Posts: 1,863
Default How Can This Happen (Electrical)?

"Tim+" wrote in message
...
bert Wrote in message:
In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.In the past few nights a
couple of times when switching it off the RCD protecting the ring mains
has tripped. But the lighting circuits don't go through it and the lights
are still on including the one which is part of the fan and the fan
itself can be switched back on.Puzzled as to how this can happen - and
where to start looking.-- bert


It would suggest that it's not supplied by the lighting circuit...


Are you sure that your RCD *only* protects the ring mains and not *all*
circuits such as cooker, lighting in addition to ring mains?

My understanding is that an RCD in the "fuse box" is usually upstream of the
ring main MCBs (over-current sensors, equivalent to wire fuses) and protects
the whole house. Our previous house had two RCDs: one was a separate unit
that was between the meter and the fuse box, and the other was within the
fuse box. Even if the RCD within the fuse box was tripped, all power went
off, including to non-ring-main circuits such as lighting and cooker.


What happens if you manually turn off the RCD? Does the lighting still
continue working?



  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 172
Default How Can This Happen (Electrical)?



"Tim+" wrote in message
...
bert Wrote in message:
In one bedroom we have a ceiling fan supplied from the lighting circuit.
It's been there for over 10 years no problems.In the past few nights a
couple of times when switching it off the RCD protecting the ring mains
has tripped. But the lighting circuits don't go through it and the lights
are still on including the one which is part of the fan and the fan
itself can be switched back on.Puzzled as to how this can happen - and
where to start looking.-- bert


It would suggest that it's not supplied by the lighting circuit...


Doesn't explain why it can be switched on again when the RCD trips.

  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,157
Default How Can This Happen (Electrical)?

On 28/02/2019 18:27, Brian Gaff wrote:
I was thinking of back EMF.
That could make it back through the lights to the other circuits as a
spike of some kind.
Brian


  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,556
Default How Can This Happen (Electrical)?

In article , Tim+
writes
bert Wrote in message:
In one bedroom we have a ceiling fan supplied from the lighting
circuit. It's been there for over 10 years no problems.In the past few
nights a couple of times when switching it off the RCD protecting the
ring mains has tripped. But the lighting circuits don't go through it
and the lights are still on including the one which is part of the fan
and the fan itself can be switched back on.Puzzled as to how this can
happen - and where to start looking.-- bert


It would suggest that it's not supplied by the lighting circuit...

Tim

But its definitely not supplied by any circuit protected by the RCD.
--
bert
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mostly OT but some nasties can happen in the home Frank[_24_] Home Repair 1 June 15th 17 08:31 PM
How some accidents can happen whisky-dave[_2_] UK diy 3 February 26th 16 09:42 AM
Anything happen to/with the Woodhaven site? Hoyt Weathers Woodworking 6 July 3rd 04 05:12 PM
Why did 9-11 happen? Gunner Metalworking 7 April 2nd 04 08:01 AM
Don't worry, it'll never happen to you BUB 209 Woodworking 3 July 27th 03 02:35 AM


All times are GMT +1. The time now is 08:15 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"