Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
I have to fit a room thermostat into a building where there is already
an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max |
#2
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max With all the electricy off at the MCBs, but on at the main switch, find which wire is less than a couple of ohms to neutral in any handy socket. (Possibly one of the others will only be few tens or hundreds of ohms if there is something inductive connected, but ignore this.) That wire is probably neutral. With the electricity on check which wire is live. That is the live wire. The third wire is switched live. Alternatively, look at the other end and note the colour code. -- Roger Hayter |
#3
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On Sunday, 15 October 2017 09:44:49 UTC+1, Maxwell Boltzmann wrote:
I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R. NT |
#4
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
|
#6
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
posted On Sunday, 15 October 2017 09:44:49 UTC+1, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R. Thanks to you and Roger. One of the problems is that there *is* no handy socket nearby to which I can measure the voltage/resistance to earth and live; but no doubt I can get round that. Neutral, not earth for the resistance measurement. They may not be sufficiently similar if you don't have the right sort of house earthing. -- Roger Hayter |
#7
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 15/10/2017 14:25, Maxwell Boltzmann wrote:
posted On Sunday, 15 October 2017 09:44:49 UTC+1, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R. Thanks to you and Roger. One of the problems is that there *is* no handy socket nearby to which I can measure the voltage/resistance to earth and live; but no doubt I can get round that. Extension lead may be your friend then... -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#8
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On Sunday, 15 October 2017 14:26:15 UTC+1, Maxwell Boltzmann wrote:
tabbypurr posted On Sunday, 15 October 2017 09:44:49 UTC+1, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R. Thanks to you and Roger. One of the problems is that there *is* no handy socket nearby to which I can measure the voltage/resistance to earth and live; but no doubt I can get round that. socket, metal light fitting, radiator, water tap or drain, most of those are earthed, but not all. The other option to identify live is to measure the 3 voltages between the 3 wires, live to N and live to swL will both give 240v, N to swL should give 0v. (Y plans do complicate this.) Obviously safe practice is required. NT |
#9
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 15/10/2017 09:40, Maxwell Boltzmann wrote:
I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existingÂ* thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Finding the other end of the cable and finding out what is connected to what. -- Michael Chare |
#10
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
wrote:
On Sunday, 15 October 2017 14:26:15 UTC+1, Maxwell Boltzmann wrote: tabbypurr posted On Sunday, 15 October 2017 09:44:49 UTC+1, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R. Thanks to you and Roger. One of the problems is that there *is* no handy socket nearby to which I can measure the voltage/resistance to earth and live; but no doubt I can get round that. socket, metal light fitting, radiator, water tap or drain, most of those are earthed, but not all. The other option to identify live is to measure the 3 voltages between the 3 wires, live to N and live to swL will both give 240v, N to swL should give 0v. (Y plans do complicate this.) Obviously safe practice is required. NT Live to swL can give you Ov either because it is open circuit or because (as you say) some other control has connected ti to live. If N to L and N to swL are both 240v then further measures are necessary. Probably, as you say, something to do with motorised valves and their switches. If N to swL is Ov, which is which, if live to either gives 240V? I think your scheme only works if you know exactly what is connected at the other end and even then ambiguities are left. Another possibility if you use a high impedance meter and swL is open circuit is that N to swL will give you 5 or 10V AC. What do you conclude from this? -- Roger Hayter |
#11
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On Monday, 16 October 2017 00:10:25 UTC+1, Roger Hayter wrote:
tabbypurr wrote: On Sunday, 15 October 2017 14:26:15 UTC+1, Maxwell Boltzmann wrote: tabbypurr posted On Sunday, 15 October 2017 09:44:49 UTC+1, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R. Thanks to you and Roger. One of the problems is that there *is* no handy socket nearby to which I can measure the voltage/resistance to earth and live; but no doubt I can get round that. socket, metal light fitting, radiator, water tap or drain, most of those are earthed, but not all. The other option to identify live is to measure the 3 voltages between the 3 wires, live to N and live to swL will both give 240v, N to swL should give 0v. (Y plans do complicate this.) Obviously safe practice is required. Live to swL can give you Ov either because it is open circuit if so the system is broken or because (as you say) some other control has connected ti to live. is it too hard to switch the programmer to off? If N to L and N to swL are both 240v then further measures are necessary. but they aren't Probably, as you say, something to do with motorised valves and their switches. If N to swL is Ov, which is which, if live to either gives 240V? I think your scheme only works if you know exactly what is connected at the other end and even then ambiguities are left. I'm pretty sure I addressed that question Another possibility if you use a high impedance meter and swL is open circuit is that N to swL will give you 5 or 10V AC. What do you conclude from this? 3 readings are required to reach any conclusions, not 1. Enjoy trolling. NT |
#12
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 15/10/2017 23:49, Michael Chare wrote:
On 15/10/2017 09:40, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existingÂ* thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Finding the other end of the cable and finding out what is connected to what. That's called stating the bleeding obvious:-). Although I would want to know why there is no earth connection. -- Adam |
#13
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
ARW wrote:
Michael Chare wrote: Finding the other end of the cable and finding out what is connected to what. That's called stating the bleeding obvious:-). Although I would want to know why there is no earth connection. It's been 'promoted' to switched live for maximum surprise? |
#14
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
ARW posted
On 15/10/2017 23:49, Michael Chare wrote: On 15/10/2017 09:40, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing* thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Finding the other end of the cable and finding out what is connected to what. That's called stating the bleeding obvious:-). Although I would want to know why there is no earth connection. Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. -- Jack |
#15
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 16/10/2017 22:02, Andy Burns wrote:
ARW wrote: Michael Chare wrote: Finding the other end of the cable and finding out what is connected to what. That's called stating the bleeding obvious:-). Although I would want to know why there is no earth connection. It's been 'promoted' to switched live for maximum surprise? vbg The further question also needs to be asked. Does the boiler actually work without the missing roomstat? -- Adam |
#16
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
ARW posted On 15/10/2017 23:49, Michael Chare wrote: On 15/10/2017 09:40, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which. There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire? Max Finding the other end of the cable and finding out what is connected to what. That's called stating the bleeding obvious:-). Although I would want to know why there is no earth connection. Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. -- Roger Hayter |
#17
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 16/10/2017 22:34, Maxwell Boltzmann wrote:
ARW posted On 15/10/2017 23:49, Michael Chare wrote: On 15/10/2017 09:40, Maxwell Boltzmann wrote: I have to fit a room thermostat into a building where there is alreadyÂ* an old three-wire connection for a (mechanical) thermostat, but noÂ* existingÂ* thermostat. So it is not immediately obvious which wire isÂ* which. There is no earth connection. Using a multimeter, what is the simplestÂ* and safest way of identifying each wire? Max Â*Finding the other end of the cable and finding out what is connected toÂ* what. That's called stating the bleeding obvious:-). Although I would want to know why there is no earth connection. Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. I think you might be "reading" the diagram incorrectly fella. Your diagram should look something like this http://www.montel-css.co.uk/SupOther...llt6360wi.jpeg possibly without the earth terminal shown. There would or should be an earth cable there even if the stat does not require one. -- Adam |
#18
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Roger Hayter posted
Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth. I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. -- Jack |
#19
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. No, the neutral is permanently connected to the heating system (and the anticipator) with the permanent live Pin1 switched to Pin2 when heating is on. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth. I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. I agree the diagram looks grossly misleading. But we must assume that the wire marked 'live' is indeed a direct connection to live. The yellow wire to terminal three does not connect to anything else in the thermostat box (although terminal three also connects to one end of the heater in the thermostat which heats the bimetal strip and is used to reduce hysteriesis), but wanders off down the cable to the boiler controls, described hear as 'heating system'. When the thermostat is demanding heat the switch from terminal one connects to the contact on terminal three and supplies live voltage to the boiler control. The boiler control certainly will have its own neutral, but this is connected directly at the boiler end and does not rely on the neutral wire in the thermostat. Although electrically the boiler control neutral is connected to the terminal two neutral at the boiler end, there is no wire doing this connecting in the thermostat box despite the junction shown, and just one neutral wire comes to the thermostat purely for the purpose of supplying a current return for the anti-hysteresis heater (called anticipator in the diagram). If you imagine the orange 'heating system' box dragged off the page, still connnected to its blue and yellow wires, and down the corridor and connected by a yellow blue and red ( and also earth!) cable to the thermostat then things fall into place. In theory the red and earth cable do not need to come from the boiler control, as they are just live and earth, but in practice this is the correct way to wire it. The live incoming to the thermostat is connected to the switched live yellow wire and activates the boiler control. -- Roger Hayter |
#21
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 17/10/2017 19:33, Maxwell Boltzmann wrote:
Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. Not a problem if it's a class II appliance. -- Adam |
#22
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 17/10/2017 20:04, Roger Hayter wrote:
If you imagine the orange 'heating system' box dragged off the page, still connnected to its blue and yellow wires, and down the corridor and connected by a yellow blue and red ( and also earth!) cable to the thermostat then things fall into place. I like that. -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
In article ,
Maxwell Boltzmann wrote: Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth. I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. There should be a switched live to the thermostat, It's the thermostat that does the switching and it gives a switched live on pin 3. Pin 2 is the neutral INPUT going to the heater element which gets its live from pin 3. If you can't read a very simple circuit diagram, should you be doing this work yourself? -- from KT24 in Surrey, England |
#24
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
In article , charles
wrote: In article , Maxwell Boltzmann wrote: Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth. I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. CORRECTION There should NOT be a switched live to the thermostat, It's the thermostat that does the switching and it gives a switched live on pin 3. Pin 2 is the neutral INPUT going to the heater element which gets its live from pin 3. If you can't read a very simple circuit diagram, should you be doing this work yourself? -- from KT24 in Surrey, England |
#25
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
charles Wrote in message:
In article , charles wrote: In article , Maxwell Boltzmann wrote: Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth. I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. CORRECTION There should NOT be a switched live to the thermostat, It's the thermostat that does the switching and it gives a switched live on pin 3. Pin 2 is the neutral INPUT going to the heater element which gets its live from pin 3. If you can't read a very simple circuit diagram, should you be doing this work yourself? If you can't read a very simple circuit diagram, should you be proffering "advice"? -- Jim K ----Android NewsGroup Reader---- http://usenet.sinaapp.com/ |
#26
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Andy Burns posted
Maxwell Boltzmann wrote: I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P OK, then. In the diagram, the wires coming out of the wall are represented by the coloured lines. Which is the switched live? The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. No, the neutral is permanently connected to the heating system Which is switched. (and the anticipator) with the permanent live Pin1 switched to Pin2 when heating is on. You don't say. -- Max |
#27
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
Andy Burns posted: Maxwell Boltzmann wrote: I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P OK, then. In the diagram, the wires coming out of the wall are represented by the coloured lines. Which is the switched live? In the diagram Adam supplied - the yellow wire is switched live. |
#28
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 17/10/2017 22:38, charles wrote:
If you can't read a very simple circuit diagram, should you be doing this work yourself? Everyone started off a virgin! And the fact the OP had the nous to ask before making the connections is a better start than some. -- Robin reply-to address is (intended to be) valid |
#29
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
In article ,
Maxwell Boltzmann wrote: Andy Burns posted Maxwell Boltzmann wrote: I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P OK, then. In the diagram, the wires coming out of the wall are represented by the coloured lines. Which is the switched live? The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. No, the neutral is permanently connected to the heating system Which is switched. No it isn't. The switch in question feeds the outgoing switched live and also live to the other end of the heater (represented by a zigzag line). (and the anticipator) with the permanent live Pin1 switched to Pin2 when heating is on. You don't say. -- from KT24 in Surrey, England |
#30
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
In article , Robin
wrote: On 17/10/2017 22:38, charles wrote: If you can't read a very simple circuit diagram, should you be doing this work yourself? Everyone started off a virgin! And the fact the OP had the nous to ask before making the connections is a better start than some. True. But he seems to keep insisting on "switched neutral" - evena fter he is ntold it isn't switched. But it reminds me of a letter the BBC once reeceived " I think there should be a book written about how Ceefax works. Please tell me so that I can write the book." -- from KT24 in Surrey, England |
#31
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 18/10/2017 11:09, Andy Burns wrote:
Maxwell Boltzmann wrote: Andy Burns posted: Maxwell Boltzmann wrote: I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P OK, then. In the diagram, the wires coming out of the wall are represented by the coloured lines. Which is the switched live? In the diagram Adam supplied - the yellow wire is switched live. Do you think that there might be a misunderstanding here and that he is talking about the live *TO* the thermostat being switched by a timer? SteveW |
#32
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Andy Burns posted
Maxwell Boltzmann wrote: Andy Burns posted: Maxwell Boltzmann wrote: I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P OK, then. In the diagram, the wires coming out of the wall are represented by the coloured lines. Which is the switched live? In the diagram Adam supplied - the yellow wire is switched live. There is no thermostat. Where is the switched live? -- Max |
#33
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
Maxwell Boltzmann wrote:
Andy Burns posted Maxwell Boltzmann wrote: Which is the switched live? In the diagram Adam supplied - the yellow wire is switched live. There is no thermostat. What do you think a Honeywell T 6303 is? Where is the switched live? At this point I'm going to slow back away and leave you to it ... |
#34
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
In article ,
Andy Burns wrote: Maxwell Boltzmann wrote: Andy Burns posted Maxwell Boltzmann wrote: Which is the switched live? In the diagram Adam supplied - the yellow wire is switched live. There is no thermostat. What do you think a Honeywell T 6303 is? Where is the switched live? At this point I'm going to slow back away and leave you to it ... +1 -- from KT24 in Surrey, England |
#35
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 17/10/2017 19:33, Maxwell Boltzmann wrote:
Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. If its marked with a double insulated logo (square within a square) then it does not mater if it is made of metal. Incidentally, the wiring diagram printed inside the new thermostat doesn't show a switched live connection but a switched neutral. Any chance of hosting a scan somewhere? That seems a bit surprising for something on sale in the UK. It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth. What model number? I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat. Are you sure its not just a set of "no volt" contacts? (i.e. a switch that closes, but is not connected to either live or neutral itself). -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#36
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 17/10/2017 22:38, charles wrote:
There should NOT be a switched live to the thermostat, How would you describe the CH on connection from a programmer then? e.g. pin 4 on the junction strip: http://wiki.diyfaq.org.uk/images/6/6c/C-Plan-Wiring.gif -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#37
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On Thursday, 19 October 2017 16:07:56 UTC+1, John Rumm wrote:
On 17/10/2017 19:33, Maxwell Boltzmann wrote: Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. If its marked with a double insulated logo (square within a square) then it does not mater if it is made of metal. Years ago I saw some of those marked [[]] but in reality they did not take the relevant precaustions and the live connection was very close to the metal case. I don't remember the brand. NT |
#38
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 19/10/2017 18:10, wrote:
On Thursday, 19 October 2017 16:07:56 UTC+1, John Rumm wrote: On 17/10/2017 19:33, Maxwell Boltzmann wrote: Roger Hayter posted Maxwell Boltzmann wrote: Aren't most thermostats made of plastic with no accessible metal parts? The one I'm proposing to install certainly is. There are advantages in having an earth wire available and I believe it is considered good practice to install one. No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands. If its marked with a double insulated logo (square within a square) then it does not mater if it is made of metal. Years ago I saw some of those marked [[]] but in reality they did not take the relevant precaustions and the live connection was very close to the metal case. I don't remember the brand. In much the same vein, you can get lots of LED lamps from China that "must be earthed" and provide a wire for you to do so. Only problem is there is no continuity between said wire and the metal case. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#39
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
John Rumm wrote:
In much the same vein, you can get lots of LED lamps from China that "must be earthed" and provide a wire for you to do so. Only problem is there is no continuity between said wire and the metal case. My cheap chinese "20" watt LED floodlamp was like that, but it's died now. I have an iSpot 30W to replace it with, it is surprisingly large and basically all heatsink ... not fitted yet. https://screwfix.com/p/ispot-30w-LED/5514h |
#40
Posted to uk.d-i-y
|
|||
|
|||
Room thermostat wiring
On 18/10/2017 17:04, Maxwell Boltzmann wrote:
Andy Burns posted Maxwell Boltzmann wrote: Andy Burns posted: Maxwell Boltzmann wrote: I'm not sure what ARW means by me misunderstanding the diagram. I'd say he's right :-P Â*OK, then. In the diagram, the wires coming out of the wall are represented by the coloured lines. Which is the switched live? In the diagram Adam supplied - the yellow wire is switched live. There is no thermostat. Where is the switched live? Which comes back to the question I asked earlier that everyone missed. Does the boiler actually work without the missing roomstat? It makes a massive difference to how you do the job. -- Adam |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Wiring a room thermostat to a combi boiler | UK diy | |||
Wiring A Programmable Room Thermostat | UK diy | |||
Central Heating Room Thermostat - wiring problem | UK diy | |||
Replacing room thermostat wiring | UK diy | |||
Changing a room thermostat / wiring | UK diy |