Every other email from Screwfix tries to sell me a Nest or Hive system,
so I thought I'd have another look at them with my holiday flat in mind.

I currently have an S-Plan system with an unvented HW cylinder. There is
an electronic (manual) timer for both HW and CH. The HW circuit has a
tank stat which controls the HW 2-port valve. The CH heating valve (both
timing and temperature) is controlled by a wireless programmable
thermostat (with the CH side of the manual timer being set to
permanently on). There are TRVs on most radiators.

The current system provides *most* of what I need, but it doesn't allow
the heating to be switched on and off remotely not does it allow the
temperature to be monitored remotely. The flat gets pretty cold when
unoccupied in the winter months and it would be nice to be able to turn
the heating on a few hours before we plan to arrive each time so that
it's warm when we get there. In theory we could do this by using the
'holiday' mode on the programmable stat, but that requires us to know
when our next visit will be - and we don't always know that.

I'm not interested in a system which is too clever by half by trying to
second guess when we're in or out nor in anything with any more zonal
granularity than a single heating zone with a few TRVs. On that basis, a
Hive 2 system appears to be a pretty good match. Although there's no
real need to have remote control of the HW, this is included with most
of the Hive 2's on offer, so I may as well use it - and get get rid of
all the current timing devices.

I've read past threads on the subject and the Hive 2 Installation
Manual, and I have a few queries to which I haven't been able to find
answers.

How does it do HW control? There's no mention of a HW temperature sensor
so I assume that it is used in conjunction with the existing cylinder
stat, and just provides timing. Is that correct? What does HW boost do?
I assume that it simply turns the HW circuit on at a time when it would
otherwise be off - leaving the cylinder stat to control the temperature.
Is that correct?

What does CH boost do?

It appears that the heating can be remotely controlled by SMS messages
for the benefit of people who have tradition mobile phones rather than
smartphones. How does that work? Is there a SIM card in the unit, or
does the SMS message go to a Hive server which then communicates with
the unit over the internet? If the former, do you have to pay for a
mobile service of some sort?

Some people have expressed concerns about being reliant on an external
server - which could be withdrawn at any time. Since Hive is a British
Gas system, I doubt that BG will cease to exist any time soon, but have
they made any public pronouncements about long-term support for Hive?
AIUI, once you have bought the hardware you can access the Hive servers
for free without having to pay any subscription charges (unlike trueCall
junk call blockers, for example). Is this correct?

Answers to the above questions from those knowledgeable in the subject
will be much appreciated.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #2   Report Post  
Posted to uk.d-i-y
NY NY is offline
external usenet poster
 
Posts: 1,863
Default Hive CH Automation (again)

"Roger Mills" wrote in message
...
Every other email from Screwfix tries to sell me a Nest or Hive system, so
I thought I'd have another look at them with my holiday flat in mind.

I currently have an S-Plan system with an unvented HW cylinder. There is
an electronic (manual) timer for both HW and CH. The HW circuit has a tank
stat which controls the HW 2-port valve. The CH heating valve (both timing
and temperature) is controlled by a wireless programmable thermostat (with
the CH side of the manual timer being set to permanently on). There are
TRVs on most radiators.

The current system provides *most* of what I need, but it doesn't allow
the heating to be switched on and off remotely not does it allow the
temperature to be monitored remotely. The flat gets pretty cold when
unoccupied in the winter months and it would be nice to be able to turn
the heating on a few hours before we plan to arrive each time so that it's
warm when we get there. In theory we could do this by using the 'holiday'
mode on the programmable stat, but that requires us to know when our next
visit will be - and we don't always know that.

I'm not interested in a system which is too clever by half by trying to
second guess when we're in or out nor in anything with any more zonal
granularity than a single heating zone with a few TRVs. On that basis, a
Hive 2 system appears to be a pretty good match. Although there's no real
need to have remote control of the HW, this is included with most of the
Hive 2's on offer, so I may as well use it - and get get rid of all the
current timing devices.

I've read past threads on the subject and the Hive 2 Installation Manual,
and I have a few queries to which I haven't been able to find answers.

How does it do HW control? There's no mention of a HW temperature sensor
so I assume that it is used in conjunction with the existing cylinder
stat, and just provides timing. Is that correct? What does HW boost do? I
assume that it simply turns the HW circuit on at a time when it would
otherwise be off - leaving the cylinder stat to control the temperature.
Is that correct?

What does CH boost do?

It appears that the heating can be remotely controlled by SMS messages for
the benefit of people who have tradition mobile phones rather than
smartphones. How does that work? Is there a SIM card in the unit, or does
the SMS message go to a Hive server which then communicates with the unit
over the internet? If the former, do you have to pay for a mobile service
of some sort?

Some people have expressed concerns about being reliant on an external
server - which could be withdrawn at any time. Since Hive is a British Gas
system, I doubt that BG will cease to exist any time soon, but have they
made any public pronouncements about long-term support for Hive? AIUI,
once you have bought the hardware you can access the Hive servers for free
without having to pay any subscription charges (unlike trueCall junk call
blockers, for example). Is this correct?

Answers to the above questions from those knowledgeable in the subject
will be much appreciated.


I installed a Hive on our boiler and it works great.

Hive consists of three boxes: a controller (simple on/off switches that are
connected to the boiler); a wireless thermostat; an internet hub. The three
units talk by a private wireless link - private in the sense that they are
not part of your internet wifi. The hub connects by Ethernet to your
internet router; I don't think it has the option to use wifi instead.

We have a combi boiler which pre-heats a reservoir of hot water and keeps
that up to temperature, and then feeds that initially when a hot tap is
turned on, to cover the time lag until the boiler can heat the incoming cold
feed. Because of this, and the fact that we only want the pre-heat during
waking hours, we needed to get a two-channel Hive: one for the hot water
which is simply a timer, and one for the CH which sets the desired
temperature at different times of day.

If your present time controller allows you to schedule times of hot water as
well as CH, you too probably need dual-channel Hive.

The Hive takes the place of the timers for HW and CH and of the CH
thermostat.

HW is simple: your controller will have a "HW on" wire which is connected to
live when the HW system is on; any thermostatic control of HW temperature
will be done by a thermostat in the boiler and/or the hot water cylinder
which will remain unchanged (I think).

For CH I think you would replace your current wireless thermostat with the
one provided as part of Hive. The CH section of Hive has two wires: "CH on"
and "CH off". For simple systems "CH on" goes live when the boiler needs to
be turned on. Some systems may also use "CH off" to close any valves after
the boiler has been turned off; ours didn't so that wire is unused.

The Hive turns on the CH whenever its wireless thermostat notices that the
room temp is below the desired temp. You can define desired temp as a
function of time - eg you can set it to 15 degrees between 22:00 and 07:00,
20 degrees between 07:00-09:00 and 18:00-2200, and 18 degrees at all other
times.

If you had a wired thermostat, you'd bypass that so it is permanently in the
"calling for heat" position (as if room temp was permanently less than
desired temp). Your present wireless stat may have a switch which is turned
on and off by the wireless stat; if so, connect to be permanently on.

CH is normally wired as two switches in series: timer controller and stat.
Hive becomes a single switch that does both time and temperature control.

As well as being able to control the temp by turning the dial on its
wireless stat, you can also do the same using either a web page or an
Android/iPad app - these allow you to control the temp manually (as if you'd
turned the knob on the stat) or to alter the schedule of temperatures. There
is a Boost button which keeps the temp at its present setting for an hour
longer than the schedule (eg it would keep temp at 20 until 2300 and then 15
from then until 0700, in my example above).

I suggest you get a central heating engineer to look at your system and make
sure that Hive's settings (HW on, CH on, CH off) can control your system,
but unless it is very unusual it should be fine.

Hive is marketed for use with gas boilers but it works perfectly well with
oil (ours is oil) even though this isn't mentioned very prominently in the
literature.

I installed everything myself because our CH engineer didn't feel confident
to do the internet side of things. I checked the wires at the timer
controller and thermostat and OK'd what I was planning to do with him and
with my father-in-law who is an electrician. The longest task was the most
trivial: working out how I was going to attach the controller unit in place
of the current timer, because our timer had an old-style backing plate. Most
modern controllers have a standard plate with the pins in a standard order
so you just unhook the old controller and put the Hive one in its place.


One thing we've noticed. With the old system, we found that the interior
temperature varied by about 3 degrees in a cycle during the day - the boiler
didn't turn off until the temp was about 1.5 deg about the desired and then
didn't turn back on until the temp had fallen to 1.5 below desired. With
Hive, it's more tightly controlled and temp varies by only about 0.5
degrees - assuming you don't open doors/windows and that the sun doesn't
heat the house!

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default Hive CH Automation (again)

On 26/01/2017 12:21, NY wrote:


I installed a Hive on our boiler and it works great.

Thanks for your feedback.



For CH I think you would replace your current wireless thermostat with
the one provided as part of Hive. The CH section of Hive has two wires:
"CH on" and "CH off". For simple systems "CH on" goes live when the
boiler needs to be turned on. Some systems may also use "CH off" to
close any valves after the boiler has been turned off; ours didn't so
that wire is unused.

That puzzles me. Are you saying that the CH switch is a changeover
switch with permanent live effectively connected to COM (although there
isn't a COM terminal as such) so that CH ON is live when there is a call
for heat and CH OFF is live when there isn't? I had assumed that CH OFF
and CH ON were connected to a pair of volt-free contacts - independent
of the mains - so that boilers which used low voltage switching could
use them.

Anyone else care to comment on that?


The Hive turns on the CH whenever its wireless thermostat notices that
the room temp is below the desired temp. You can define desired temp as
a function of time - eg you can set it to 15 degrees between 22:00 and
07:00, 20 degrees between 07:00-09:00 and 18:00-2200, and 18 degrees at
all other times.


That's what my programmable stat currently does, so it would replace that.


As well as being able to control the temp by turning the dial on its
wireless stat, you can also do the same using either a web page or an
Android/iPad app - these allow you to control the temp manually (as if
you'd turned the knob on the stat) or to alter the schedule of
temperatures. There is a Boost button which keeps the temp at its
present setting for an hour longer than the schedule (eg it would keep
temp at 20 until 2300 and then 15 from then until 0700, in my example
above).

Thanks for the explanation of 'boost'.

I suggest you get a central heating engineer to look at your system and
make sure that Hive's settings (HW on, CH on, CH off) can control your
system, but unless it is very unusual it should be fine.


I'm my own CH engineer! I have reasonably intimate knowledge of my
system having fitted the wireless programmable stat when there
previously wasn't a room stat in the system.


One thing we've noticed. With the old system, we found that the interior
temperature varied by about 3 degrees in a cycle during the day - the
boiler didn't turn off until the temp was about 1.5 deg about the
desired and then didn't turn back on until the temp had fallen to 1.5
below desired. With Hive, it's more tightly controlled and temp varies
by only about 0.5 degrees - assuming you don't open doors/windows and
that the sun doesn't heat the house!


I assume that you previously had a mechanical stat. They have quite a
lot of hysteresis compared with electronic stats.

Anyone care to comment on the other questions which I raised in my
previous post - how SMS control works, and the implications of relying
on an external server?

Oh, and one other thing I meant to ask: the Hive thermostat seems to be
designed for wall mounting only. My current wireless stat can be wall
mounted but is also provided with a stand. I sometimes find it useful to
move it from room to room. Is there any reason why I shouldn't make a
simple stand for a Hive stat, and do the same with that?
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Hive CH Automation (again)

I don't have to pay true call, I can manage the list on the device after the
free internet sub is over with.
I found the internet a bit fiddly in any case. I see these remote heating
things nowhave a skill for the Amazon Echo.
Brian

--
----- -
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please!
"Roger Mills" wrote in message
...
Every other email from Screwfix tries to sell me a Nest or Hive system, so
I thought I'd have another look at them with my holiday flat in mind.

I currently have an S-Plan system with an unvented HW cylinder. There is
an electronic (manual) timer for both HW and CH. The HW circuit has a tank
stat which controls the HW 2-port valve. The CH heating valve (both timing
and temperature) is controlled by a wireless programmable thermostat (with
the CH side of the manual timer being set to permanently on). There are
TRVs on most radiators.

The current system provides *most* of what I need, but it doesn't allow
the heating to be switched on and off remotely not does it allow the
temperature to be monitored remotely. The flat gets pretty cold when
unoccupied in the winter months and it would be nice to be able to turn
the heating on a few hours before we plan to arrive each time so that it's
warm when we get there. In theory we could do this by using the 'holiday'
mode on the programmable stat, but that requires us to know when our next
visit will be - and we don't always know that.

I'm not interested in a system which is too clever by half by trying to
second guess when we're in or out nor in anything with any more zonal
granularity than a single heating zone with a few TRVs. On that basis, a
Hive 2 system appears to be a pretty good match. Although there's no real
need to have remote control of the HW, this is included with most of the
Hive 2's on offer, so I may as well use it - and get get rid of all the
current timing devices.

I've read past threads on the subject and the Hive 2 Installation Manual,
and I have a few queries to which I haven't been able to find answers.

How does it do HW control? There's no mention of a HW temperature sensor
so I assume that it is used in conjunction with the existing cylinder
stat, and just provides timing. Is that correct? What does HW boost do? I
assume that it simply turns the HW circuit on at a time when it would
otherwise be off - leaving the cylinder stat to control the temperature.
Is that correct?

What does CH boost do?

It appears that the heating can be remotely controlled by SMS messages for
the benefit of people who have tradition mobile phones rather than
smartphones. How does that work? Is there a SIM card in the unit, or does
the SMS message go to a Hive server which then communicates with the unit
over the internet? If the former, do you have to pay for a mobile service
of some sort?

Some people have expressed concerns about being reliant on an external
server - which could be withdrawn at any time. Since Hive is a British Gas
system, I doubt that BG will cease to exist any time soon, but have they
made any public pronouncements about long-term support for Hive? AIUI,
once you have bought the hardware you can access the Hive servers for free
without having to pay any subscription charges (unlike trueCall junk call
blockers, for example). Is this correct?

Answers to the above questions from those knowledgeable in the subject
will be much appreciated.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.



  #5   Report Post  
Posted to uk.d-i-y
NY NY is offline
external usenet poster
 
Posts: 1,863
Default Hive CH Automation (again)

"Roger Mills" wrote in message
...
On 26/01/2017 12:21, NY wrote:


I installed a Hive on our boiler and it works great.

Thanks for your feedback.



For CH I think you would replace your current wireless thermostat with
the one provided as part of Hive. The CH section of Hive has two wires:
"CH on" and "CH off". For simple systems "CH on" goes live when the
boiler needs to be turned on. Some systems may also use "CH off" to
close any valves after the boiler has been turned off; ours didn't so
that wire is unused.

That puzzles me. Are you saying that the CH switch is a changeover switch
with permanent live effectively connected to COM (although there isn't a
COM terminal as such) so that CH ON is live when there is a call for heat
and CH OFF is live when there isn't? I had assumed that CH OFF and CH ON
were connected to a pair of volt-free contacts - independent of the
mains - so that boilers which used low voltage switching could use them.

Anyone else care to comment on that?


Since CH OFF wasn't relevant for me, I didn't actually test this, but I
imagine you're right: CH ON is live when Hive is "calling" (ie actual temp
is below required temp) and CH OFF is live when Hive is "not calling".

Certainly when it's installed in my system, CH ON is live when Hive turns
on, thereby supplying power to the boiler to activate the burner and the
pump for the CH.



  #6   Report Post  
Posted to uk.d-i-y
NY NY is offline
external usenet poster
 
Posts: 1,863
Default Hive CH Automation (again)

"Brian Gaff" wrote in message
news
I see these remote heating things now have a skill for the Amazon Echo.


They do indeed. My wife likes being able to lie in bed and say "Alexa, turn
up the heating by one degree" or "Alexa, boost the heating for one hour".
She thinks Alexa is great: we've also got a remote-controlled mains socket
with a standard lamp plugged in, with an Echo "skill" so she can say "Alexa,
turn spot on" (or off) - when we configured the name of the plug as "spot"
(light). It means that when she goes downstairs early in the morning she can
turn the light on in the lounge before she is goes downstairs.

As a bit of a gimmick I was demonstrating all this to my parents when we saw
them at Christmas, looking at the lounge an my mobile phone through the
security camera and then turning on the light - all from several hundred
miles away :-)

We're not *really* obsessed with gadgets :-)

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,774
Default Hive CH Automation (again)

On 26/01/2017 10:49, Roger Mills wrote:

Some people have expressed concerns about being reliant on an external
server - which could be withdrawn at any time. Since Hive is a British
Gas system, I doubt that BG will cease to exist any time soon, but have
they made any public pronouncements about long-term support for Hive?


They will just withdraw the service when they have something different
to sell.

Its much like them ceasing to support a boiler in order to sell a new
one when spares etc. are still readily available from the manufacturer.


--
mailto: news {at} admac {dot] myzen {dot} co {dot} uk
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,115
Default Hive CH Automation (again)

On Thu, 26 Jan 2017 19:51:47 +0000, alan_m wrote:

On 26/01/2017 10:49, Roger Mills wrote:

Some people have expressed concerns about being reliant on an external
server - which could be withdrawn at any time. Since Hive is a British
Gas system, I doubt that BG will cease to exist any time soon, but have
they made any public pronouncements about long-term support for Hive?


They will just withdraw the service when they have something different
to sell.

Its much like them ceasing to support a boiler in order to sell a new
one when spares etc. are still readily available from the manufacturer.


Hear hear. They tried that on me. Only they destroyed part of the boiler
too.

--
My posts are my copyright and if @diy_forums or Home Owners' Hub
wish to copy them they can pay me £1 a message.
Use the BIG mirror service in the UK: http://www.mirrorservice.org
*lightning surge protection* - a w_tom conductor
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Beekeeping and hive building [email protected] UK diy 6 March 7th 16 11:51 AM
OT (ish?): British Gas Hive Hub Allan UK diy 8 January 15th 15 01:04 AM
Fininshing a bee hive Phil Hansen Woodworking 5 January 5th 07 05:26 PM
OBSERVATION BEE HIVE J T Woodworking 4 September 21st 06 01:15 AM
OBSERVATION HIVE J T Woodworking 0 August 17th 05 09:19 PM


All times are GMT +1. The time now is 03:12 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"