I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.

Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.

There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ? Thanks
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,713
Default OT - New boiler been fitted

Andy Cap wrote:

I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.

Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.

There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ?


Are you saying that each time you bleed you are getting lots of
air, not that it is simply working its way out from where it has
been trapped?

Is the pump speed significantly greater than the old one?

Has the flow direction changed?

If air is being sucked in, then the possibility is that the
system is incorrectly configured, since it should mostly be
positively pressurised. If that is the case, you probably won't
see a leak, the displaced water ending up back in the header
tank.

If you bleed with the pump running, is air leaking out or in?

Maybe a joint disturbed or renewed during the work is the
culprit.

Chris
--
Chris J Dixon Nottingham UK


Plant amazing Acers.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 313
Default OT - New boiler been fitted

On 09/10/15 08:34, Chris J Dixon wrote:

into the system ?


Are you saying that each time you bleed you are getting lots of
air, not that it is simply working its way out from where it has
been trapped?

Is the pump speed significantly greater than the old one?

Has the flow direction changed?

If air is being sucked in, then the possibility is that the
system is incorrectly configured, since it should mostly be
positively pressurised. If that is the case, you probably won't
see a leak, the displaced water ending up back in the header
tank.

If you bleed with the pump running, is air leaking out or in?

Maybe a joint disturbed or renewed during the work is the
culprit.

Chris


I have removed significant amounts of air on about half a dozen
occasions spread over the eight weeks. I appreciate that in the early
days, the heating had not been on to any degree but by now I would have
thought most of the system has been used.

I've just had a look at the header tank and though the level hasn't
risen significantly, it definitely looks as if it's been pumping over by
the froth on the surface, also there was heavy condensation on the
plastic cover which makes me think the water is warm. I'm guessing
pumping-over would add a considerable amount or air !

This replacement pump has speed settings 1,2 & 3 and was set to 2. I've
altered it to 1 and will see how it goes, otherwise I can always get the
guy back but I just wanted a better understanding of why it might be
happening.

Thanks Andy C
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,094
Default OT - New boiler been fitted

On 09/10/2015 07:09, Andy Cap wrote:

I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.

Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.

There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ? Thanks


The last time I gravity flushed my closed system it went from quite
noisy to virtually silent. Only material change I made was the use of
Sentinel inhibitor in place of a Wickes own brand, and a couple of new
radiators with 10mm plastic pipe feeds.

--
Cheers, Rob
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default OT - New boiler been fitted

On 09/10/2015 09:58, Andy Cap wrote:
On 09/10/15 08:34, Chris J Dixon wrote:

into the system ?


Are you saying that each time you bleed you are getting lots of
air, not that it is simply working its way out from where it has
been trapped?

Is the pump speed significantly greater than the old one?

Has the flow direction changed?

If air is being sucked in, then the possibility is that the
system is incorrectly configured, since it should mostly be
positively pressurised. If that is the case, you probably won't
see a leak, the displaced water ending up back in the header
tank.

If you bleed with the pump running, is air leaking out or in?

Maybe a joint disturbed or renewed during the work is the
culprit.

Chris


I have removed significant amounts of air on about half a dozen
occasions spread over the eight weeks. I appreciate that in the early
days, the heating had not been on to any degree but by now I would have
thought most of the system has been used.

I've just had a look at the header tank and though the level hasn't
risen significantly, it definitely looks as if it's been pumping over by
the froth on the surface, also there was heavy condensation on the
plastic cover which makes me think the water is warm. I'm guessing
pumping-over would add a considerable amount or air !

This replacement pump has speed settings 1,2 & 3 and was set to 2. I've
altered it to 1 and will see how it goes, otherwise I can always get the
guy back but I just wanted a better understanding of why it might be
happening.

Thanks Andy C


Definitely sounds as if it has been pumping over - that fits all the
symptoms.

If reducing the pump speed doesn't fix it, make sure that the pump has
been installed the right way round!
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default OT - New boiler been fitted

In article ,
Andy Cap wrote:
I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.


Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.


There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ? Thanks


Most likely cause is it's pumping over. Too much head from the pump.

--
*The severity of the itch is proportional to the reach *

Dave Plowman London SW
To e-mail, change noise into sound.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default OT - New boiler been fitted

On 09/10/2015 09:58, Andy Cap wrote:
On 09/10/15 08:34, Chris J Dixon wrote:

into the system ?


Are you saying that each time you bleed you are getting lots of
air, not that it is simply working its way out from where it has
been trapped?

Is the pump speed significantly greater than the old one?

Has the flow direction changed?

If air is being sucked in, then the possibility is that the
system is incorrectly configured, since it should mostly be
positively pressurised. If that is the case, you probably won't
see a leak, the displaced water ending up back in the header
tank.

If you bleed with the pump running, is air leaking out or in?

Maybe a joint disturbed or renewed during the work is the
culprit.

Chris


I have removed significant amounts of air on about half a dozen
occasions spread over the eight weeks. I appreciate that in the early
days, the heating had not been on to any degree but by now I would have
thought most of the system has been used.

I've just had a look at the header tank and though the level hasn't
risen significantly, it definitely looks as if it's been pumping over by
the froth on the surface, also there was heavy condensation on the
plastic cover which makes me think the water is warm. I'm guessing
pumping-over would add a considerable amount or air !

This replacement pump has speed settings 1,2 & 3 and was set to 2. I've
altered it to 1 and will see how it goes, otherwise I can always get the
guy back but I just wanted a better understanding of why it might be
happening.


As an aside, did he do a proper system flush before installing the new
boiler?


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 313
Default OT - New boiler been fitted

On 09/10/15 12:13, John Rumm wrote:

I have removed significant amounts of air on about half a dozen
occasions spread over the eight weeks. I appreciate that in the early
days, the heating had not been on to any degree but by now I would have
thought most of the system has been used.

I've just had a look at the header tank and though the level hasn't
risen significantly, it definitely looks as if it's been pumping over by
the froth on the surface, also there was heavy condensation on the
plastic cover which makes me think the water is warm. I'm guessing
pumping-over would add a considerable amount or air !

This replacement pump has speed settings 1,2 & 3 and was set to 2. I've
altered it to 1 and will see how it goes, otherwise I can always get the
guy back but I just wanted a better understanding of why it might be
happening.


As an aside, did he do a proper system flush before installing the new
boiler?



Yes he did do that.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default OT - New boiler been fitted

On 09/10/2015 11:58, Dave Plowman (News) wrote:
In article ,
Andy Cap wrote:
I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.


Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.


There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ? Thanks


Most likely cause is it's pumping over. Too much head from the pump.

A possible quick check for this, if it still pumps over on speed setting
1, would be to partially close one of the pump isolating valves (ideally
the "output" one). Also, you should be able to see pumping over by
looking in the tank when the heating is running.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 313
Default OT - New boiler been fitted

On 09/10/15 11:58, Dave Plowman (News) wrote:
In article ,
Andy Cap wrote:
I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.


Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.


There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ? Thanks


Most likely cause is it's pumping over. Too much head from the pump.


I've turned the pump down a notch and fingers-crossed, you're right.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,034
Default OT - New boiler been fitted

On 09/10/2015 07:09, Andy Cap wrote:

I had my old reliable but ageing Spacesaver replace by a Vaillant 428
about 8 weeks ago. It's a straight-swap on an open-vented system, the
only changes being a replacement bypass valve, a new pump and a
Magnaclean !! device.

Since day 1, first thing in the morning it sounds like a waterfall !
I have bled various radiators numerous times and last night, the one
on the landing, where what little air used to collect was I guess, half
empty. The one in the hall, where I never had any air from, I estimate
was a 1/4 air.

There has been no leaks as far as I can tell - there is nothing below
the ground floor level - so how might this huge amount of air getting
into the system ? Thanks


You mention that the bypass valve has been replaced.

What happens if you turn off all the radiators and start the boiler?


--
Michael Chare
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 313
Default OT - New boiler been fitted

On 09/10/15 12:58, Michael Chare wrote:


You mention that the bypass valve has been replaced.

What happens if you turn off all the radiators and start the boiler?



I'll give it a few days, now I've reduced the pump setting and if
there's no change, I'll give that a try. Cheers.
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 313
Default OT - New boiler been fitted

On 09/10/15 10:56, Roger Mills wrote:

I have removed significant amounts of air on about half a dozen
occasions spread over the eight weeks. I appreciate that in the early
days, the heating had not been on to any degree but by now I would have
thought most of the system has been used.

I've just had a look at the header tank and though the level hasn't
risen significantly, it definitely looks as if it's been pumping over by
the froth on the surface, also there was heavy condensation on the
plastic cover which makes me think the water is warm. I'm guessing
pumping-over would add a considerable amount or air !

This replacement pump has speed settings 1,2 & 3 and was set to 2. I've
altered it to 1 and will see how it goes, otherwise I can always get the
guy back but I just wanted a better understanding of why it might be
happening.

Thanks Andy C


Definitely sounds as if it has been pumping over - that fits all the
symptoms.

If reducing the pump speed doesn't fix it, make sure that the pump has
been installed the right way round!


The system's been nice and quiet now for three morning and everything
appears to be functioning OK. Nice easy fix ! Thanks for the pointers.

Andy C


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combi boiler fitted Simon Finnigan UK diy 22 October 14th 07 08:23 PM
Getting a new boiler fitted (quickly)? . UK diy 35 January 19th 07 10:13 PM
Help - I have a back boiler and want a combi boiler fitted but have plastic pipes! Vikki Home Repair 1 November 22nd 05 11:51 PM
Getting a new Combi Boiler Fitted Tony Walker UK diy 4 February 1st 05 10:21 AM
Can I tell if my boiler has a bypass fitted? Michael D UK diy 7 October 31st 04 07:08 PM


All times are GMT +1. The time now is 08:45 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"