  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default Can a TRV fail with its sprung pin 'out'?

One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of
the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?

David
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,023
Default Can a TRV fail with its sprung pin 'out'?

Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of the
valve, suspecting that its pin might be stuck down; however it definitely
isn't, and it's currently in the fully 'out' position with the valve head
removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at a
blockage (or, unlikely, an airlock) somewhere?

David


The jumper (that the pin pushes down) can stick to the valve seat. There's
no solid link between pin and jumper. I usually give the valve body a sharp
tap with a hammer/spanner/whatever comes to hand and that seems to free it
up.

Tim
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,010
Default Can a TRV fail with its sprung pin 'out'?

Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of
the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking
at a blockage (or, unlikely, an airlock) somewhere?


currently working on 4 new builds and had this problem with one rad in each
house - the same one in each house for some reason - all the rest were
glowing and this one wouldn't get warm.
Left heating on and turned all other rads off and it got hot, then went
around and turned all other rads back on and now they all work fine, we did
get a bit of air out of the one on the third floor so it was probably an
airlock.

The cold rad was on the ground floor only 5m from the boiler, yet the 'loft'
one got heated up fairly quickly


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Can a TRV fail with its sprung pin 'out'?

On Thu, 8 Nov 2012 20:28:38 -0000, Phil L wrote:

The cold rad was on the ground floor only 5m from the boiler, yet the
'loft' one got heated up fairly quickly


Sounds as if gravity is making the circulation happen as much if nor more
so than the pump... Was the ground floor rad on long (FSVO long) from the
main flow and return pipe work?

--
Cheers
Dave.



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,010
Default Can a TRV fail with its sprung pin 'out'?

Dave Liquorice wrote:
On Thu, 8 Nov 2012 20:28:38 -0000, Phil L wrote:

The cold rad was on the ground floor only 5m from the boiler, yet the
'loft' one got heated up fairly quickly


Sounds as if gravity is making the circulation happen as much if nor
more so than the pump... Was the ground floor rad on long (FSVO long)
from the main flow and return pipe work?


No, the pipe run was a metre up from boiler, about 3m across a ceiling and
2.5m down a wall, not much different from the other two downstairs ones,
then there's 3 on the middle floor and one in the loft room.

Boilers are glow worms, 26k I think.

They all seem to be fine now, I've a feeling there was a 'U' in the pipe to
this rad - it's all done in plastic and it was coiled, so it could be an
undulation where they were drilled through the joists




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,713
Default Can a TRV fail with its sprung pin 'out'?

Lobster wrote:

One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of
the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?

This is what I wrote a long time ago:

I have attacked mine several times in the following way, without
draining the system, and no more than a dribble of leakage.

Having unscrewed the dome, prod the pin which protrudes from the
valve a few times. Mild jams can be cleared this way.

If it is still stuck, first get some old cloths or towels to
catch any spillage. Remove the circlip and lift out the plate
through which the pin passes. Beneath is a rubber diaphragm,
which may or may not come with it. Remove it, taking care not to
tear it. Water may start to well up in the valve body. Insert a
screwdriver into the body, of a suitable size so that it is a
fairly tight fit. A mixture of jabs and twists with the
screwdriver should result in it freeing the mechanism. You will
feel the spring release, and the valve will be free to move
vertically.

Now you have to get things back together. Replace the rubber
diaphragm, replace the plate with pin protruding through. Now
comes the hard part - get the circlip back. Some of my valves
have had this done so many times that I really don't want to
disturb them again.

If this still does not work, then you will have to drain down,
and get right into the valve to persuade the parts to move
freely.

I had all the valves replaced a few years ago, when I had a new
boiler, fresh inhibitor was added, and they haven't needed any
attention.

Chris
--
Chris J Dixon Nottingham UK


Have dancing shoes, will ceilidh.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 726
Default Can a TRV fail with its sprung pin 'out'?

Chris J Dixon wrote:
Lobster wrote:

One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of
the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?

This is what I wrote a long time ago:

I have attacked mine several times in the following way, without
draining the system, and no more than a dribble of leakage.

Having unscrewed the dome, prod the pin which protrudes from the
valve a few times. Mild jams can be cleared this way.

If it is still stuck, first get some old cloths or towels to
catch any spillage. Remove the circlip and lift out the plate
through which the pin passes. Beneath is a rubber diaphragm,
which may or may not come with it. Remove it, taking care not to
tear it. Water may start to well up in the valve body. Insert a
screwdriver into the body, of a suitable size so that it is a
fairly tight fit. A mixture of jabs and twists with the
screwdriver should result in it freeing the mechanism. You will
feel the spring release, and the valve will be free to move
vertically.

Now you have to get things back together. Replace the rubber
diaphragm, replace the plate with pin protruding through. Now
comes the hard part - get the circlip back. Some of my valves
have had this done so many times that I really don't want to
disturb them again.

If this still does not work, then you will have to drain down,
and get right into the valve to persuade the parts to move
freely.

I had all the valves replaced a few years ago, when I had a new
boiler, fresh inhibitor was added, and they haven't needed any
attention.

Chris


Or, gie it a dunt wi' a hammer. ;-)

Tim
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Can a TRV fail with its sprung pin 'out'?

On Thu, 8 Nov 2012 21:12:17 -0000, Phil L wrote:

No, the pipe run was a metre up from boiler, about 3m across a ceiling
and 2.5m down a wall, ...


They all seem to be fine now, I've a feeling there was a 'U' in the
pipe to this rad -


What you describe is quite a large inverted U. Plenty of scope to trap
air, particulary if the pipe work runs ever so slightly up from the main
flow return runs.

--
Cheers
Dave.



  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default Can a TRV fail with its sprung pin 'out'?

On 09/11/2012 09:19, Tim+ wrote:
Chris J Dixon wrote:
Lobster wrote:

One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of
the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?

This is what I wrote a long time ago:

I have attacked mine several times in the following way, without
draining the system, and no more than a dribble of leakage.

Having unscrewed the dome, prod the pin which protrudes from the
valve a few times. Mild jams can be cleared this way.

If it is still stuck, first get some old cloths or towels to
catch any spillage. Remove the circlip and lift out the plate
through which the pin passes. Beneath is a rubber diaphragm,
which may or may not come with it. Remove it, taking care not to
tear it. Water may start to well up in the valve body. Insert a
screwdriver into the body, of a suitable size so that it is a
fairly tight fit. A mixture of jabs and twists with the
screwdriver should result in it freeing the mechanism. You will
feel the spring release, and the valve will be free to move
vertically.


Thanks for this. Don't you at least have to depressurise the system to
do this? As in, when this circlip comes out won't the system otherwise
'self-depressurise' rather rapidly at that point?

Or, gie it a dunt wi' a hammer. ;-)


Thanks for the tip - I attempted a good old 'dunt'ing yesterday, but
alas to no avail.

(At least this is the spare room rad - normally set to 'off' anyway;
which is probably the root of the problem...)

David

  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,713
Default Can a TRV fail with its sprung pin 'out'?

rLobster wrote:

On 09/11/2012 09:19, Tim+ wrote:
Chris J Dixon wrote:
Lobster wrote:

One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of
the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?

This is what I wrote a long time ago:

I have attacked mine several times in the following way, without
draining the system, and no more than a dribble of leakage.

Having unscrewed the dome, prod the pin which protrudes from the
valve a few times. Mild jams can be cleared this way.

If it is still stuck, first get some old cloths or towels to
catch any spillage. Remove the circlip and lift out the plate
through which the pin passes. Beneath is a rubber diaphragm,
which may or may not come with it. Remove it, taking care not to
tear it. Water may start to well up in the valve body. Insert a
screwdriver into the body, of a suitable size so that it is a
fairly tight fit. A mixture of jabs and twists with the
screwdriver should result in it freeing the mechanism. You will
feel the spring release, and the valve will be free to move
vertically.


Thanks for this. Don't you at least have to depressurise the system to
do this? As in, when this circlip comes out won't the system otherwise
'self-depressurise' rather rapidly at that point?

At the time my system was vented, so just the static head to cope
with. Although there was some water seepage, very little actually
escaped.

For a pressurised system, you may well be right.

Chris
--
Chris J Dixon Nottingham UK


Have dancing shoes, will ceilidh.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default Can a TRV fail with its sprung pin 'out'?

On 08/11/2012 19:40, Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of the
valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?

David


If the pin springs back up when you push it down and then release it,
the valve is probably ok. You can check that it's passing water by fully
shutting[1] the lockshield valve and then opening the bleed screw. If
water squirts out, water must be flowing through the valve (unless the
lockshield is duff and not shutting fully - but let's assume that the
lockshield is ok). If air comes out, keep it coming until water starts
to come out (and then top up the system to the correct pressure). For
completeness, close the TRV fully (preferably with a decorating cap),
open the lockshield and re-bleed - to ensure that that side of the
circuit is working.

Having proved that water is flowing through *both* valves, if the rad
still doesn't get hot, you've probably got an air lock. The usual trick
here is to turn off all the other rads, turn the pump up to max speed -
if adjustable - and run the system for a bit. That should clear any air
lock, and the rad should get hot. After that, it should continue to work ok.

[1] Count how many turns are needed to close it, so that you can restore
it to the same position (assuming that the system has ever been balanced!
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,023
Default Can a TRV fail with its sprung pin 'out'?

Roger Mills wrote:
On 08/11/2012 19:40, Lobster wrote:
One of our radiators has stopped working completely; ie not a trace
of warmth when the CH is on. First port of call was an investigation
of the valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking
at a blockage (or, unlikely, an airlock) somewhere?

David


If the pin springs back up when you push it down and then release it,
the valve is probably ok.


Um, no. I've had the jumper stick in one of my radiator valves many times
when it's been turned off over summer. A good dunt to the valve side with a
hammer has always freed it off.

Tim

  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default Can a TRV fail with its sprung pin 'out'?

On 09/11/2012 14:24, Roger Mills wrote:
On 08/11/2012 19:40, Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of the
valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?


If the pin springs back up when you push it down and then release it,
the valve is probably ok. You can check that it's passing water by fully
shutting[1] the lockshield valve and then opening the bleed screw. If
water squirts out, water must be flowing through the valve (unless the
lockshield is duff and not shutting fully - but let's assume that the
lockshield is ok). If air comes out, keep it coming until water starts
to come out (and then top up the system to the correct pressure). For
completeness, close the TRV fully (preferably with a decorating cap),
open the lockshield and re-bleed - to ensure that that side of the
circuit is working.

Having proved that water is flowing through *both* valves, if the rad
still doesn't get hot, you've probably got an air lock. The usual trick
here is to turn off all the other rads, turn the pump up to max speed -
if adjustable - and run the system for a bit. That should clear any air
lock, and the rad should get hot. After that, it should continue to work
ok.


As I finally got round to sorting the above out at the weekend (during a
system drain-down necessitated by installing a new rad elsewhere in the
house) i thought I'd just report back (always good to hear the outcome,
innit?). Thanks Roger for the sensible how-to-do-it.

Upon investigation I found the lockshield valve was completely shut off,
which would of course account for the completely cold radiator. WTF?
Then - lightbulb moment - I suddenly remembered that *last* winter I had
a problem with this rad (which is in a little-used spare room) not being
possible to turn *off*: ie with the TRV set to minimum the rad was
still warming up and keeping the empty spare room warm all winter. So I
shut down the lockshield valve and made a mental note to sort it out
come the summer. HTF did I just completely forget that? Well scary.

Fortunately the grey cells are still up to swapping out a failed TRV,
which I duly sorted out...

David


  #14   Report Post  
Posted to uk.d-i-y
MM MM is offline
external usenet poster
 
Posts: 2,172
Default Can a TRV fail with its sprung pin 'out'?

On Thu, 13 Dec 2012 08:08:25 +0000, Lobster
wrote:

On 09/11/2012 14:24, Roger Mills wrote:
On 08/11/2012 19:40, Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of the
valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?


If the pin springs back up when you push it down and then release it,
the valve is probably ok. You can check that it's passing water by fully
shutting[1] the lockshield valve and then opening the bleed screw. If
water squirts out, water must be flowing through the valve (unless the
lockshield is duff and not shutting fully - but let's assume that the
lockshield is ok). If air comes out, keep it coming until water starts
to come out (and then top up the system to the correct pressure). For
completeness, close the TRV fully (preferably with a decorating cap),
open the lockshield and re-bleed - to ensure that that side of the
circuit is working.

Having proved that water is flowing through *both* valves, if the rad
still doesn't get hot, you've probably got an air lock. The usual trick
here is to turn off all the other rads, turn the pump up to max speed -
if adjustable - and run the system for a bit. That should clear any air
lock, and the rad should get hot. After that, it should continue to work
ok.


As I finally got round to sorting the above out at the weekend (during a
system drain-down necessitated by installing a new rad elsewhere in the
house) i thought I'd just report back (always good to hear the outcome,
innit?). Thanks Roger for the sensible how-to-do-it.

Upon investigation I found the lockshield valve was completely shut off,
which would of course account for the completely cold radiator. WTF?
Then - lightbulb moment - I suddenly remembered that *last* winter I had
a problem with this rad (which is in a little-used spare room) not being
possible to turn *off*: ie with the TRV set to minimum the rad was
still warming up and keeping the empty spare room warm all winter. So I
shut down the lockshield valve and made a mental note to sort it out
come the summer. HTF did I just completely forget that? Well scary.

Fortunately the grey cells are still up to swapping out a failed TRV,
which I duly sorted out...

David


"Mental note", yep, been there, too! I'm 66 and now have to make
written notes if I want to remember anything important. Pi**es me off,
but if I try to remember important stuff, I just forget. And yet I can
cast my mind back to age eight in Hastings in the 1950s and remember
loads of details of my everyday life.

By the way, if you start jotting down "reminders", always make a
mental note to where those reminders are, else you'll never find 'em
again!

MM
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,093
Default Can a TRV fail with its sprung pin 'out'?

On 14/12/2012 07:03, MM wrote:
On Thu, 13 Dec 2012 08:08:25 +0000, Lobster
wrote:

On 09/11/2012 14:24, Roger Mills wrote:
On 08/11/2012 19:40, Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation of the
valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I looking at
a blockage (or, unlikely, an airlock) somewhere?


If the pin springs back up when you push it down and then release it,
the valve is probably ok. You can check that it's passing water by fully
shutting[1] the lockshield valve and then opening the bleed screw. If
water squirts out, water must be flowing through the valve (unless the
lockshield is duff and not shutting fully - but let's assume that the
lockshield is ok). If air comes out, keep it coming until water starts
to come out (and then top up the system to the correct pressure). For
completeness, close the TRV fully (preferably with a decorating cap),
open the lockshield and re-bleed - to ensure that that side of the
circuit is working.

Having proved that water is flowing through *both* valves, if the rad
still doesn't get hot, you've probably got an air lock. The usual trick
here is to turn off all the other rads, turn the pump up to max speed -
if adjustable - and run the system for a bit. That should clear any air
lock, and the rad should get hot. After that, it should continue to work
ok.


As I finally got round to sorting the above out at the weekend (during a
system drain-down necessitated by installing a new rad elsewhere in the
house) i thought I'd just report back (always good to hear the outcome,
innit?). Thanks Roger for the sensible how-to-do-it.

Upon investigation I found the lockshield valve was completely shut off,
which would of course account for the completely cold radiator. WTF?
Then - lightbulb moment - I suddenly remembered that *last* winter I had
a problem with this rad (which is in a little-used spare room) not being
possible to turn *off*: ie with the TRV set to minimum the rad was
still warming up and keeping the empty spare room warm all winter. So I
shut down the lockshield valve and made a mental note to sort it out
come the summer. HTF did I just completely forget that? Well scary.

Fortunately the grey cells are still up to swapping out a failed TRV,
which I duly sorted out...

David


"Mental note", yep, been there, too! I'm 66 and now have to make
written notes if I want to remember anything important. Pi**es me off,
but if I try to remember important stuff, I just forget. And yet I can
cast my mind back to age eight in Hastings in the 1950s and remember
loads of details of my everyday life.


Do you ever watch that Foyles War?

By the way, if you start jotting down "reminders", always make a
mental note to where those reminders are, else you'll never find 'em
again!

MM



--
Dave - The Medway Handyman www.medwayhandyman.co.uk


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default Can a TRV fail with its sprung pin 'out'?

Fortunately the grey cells are still up to swapping out a failed TRV,
which I duly sorted out...


Had three of they recently differing properties. All the same a gentle
tapping and tweak and they work OK again ...


David


"Mental note", yep, been there, too! I'm 66 and now have to make
written notes if I want to remember anything important. Pi**es me off,
but if I try to remember important stuff, I just forget. And yet I can
cast my mind back to age eight in Hastings in the 1950s and remember
loads of details of my everyday life.


Yep thats ageing;(..

Ought to be a law 'agin it;!//


By the way, if you start jotting down "reminders", always make a
mental note to where those reminders are, else you'll never find 'em
again!


Like all those bloody passwords U have to remember..

Still I've now simplified doG.............

Which they say is rather good one..


MM


--
Tony Sayer

  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default Can a TRV fail with its sprung pin 'out'?

On 14/12/2012 08:22, The Medway Handyman wrote:
On 14/12/2012 07:03, MM wrote:
On Thu, 13 Dec 2012 08:08:25 +0000, Lobster
wrote:

On 09/11/2012 14:24, Roger Mills wrote:
On 08/11/2012 19:40, Lobster wrote:
One of our radiators has stopped working completely; ie not a trace of
warmth when the CH is on. First port of call was an investigation
of the
valve, suspecting that its pin might be stuck down; however it
definitely isn't, and it's currently in the fully 'out' position with
the valve head removed, and the rad's still in Witches' Tit mode.

So - is it possible the valve still needs replacing? Or am I
looking at
a blockage (or, unlikely, an airlock) somewhere?

If the pin springs back up when you push it down and then release it,
the valve is probably ok. You can check that it's passing water by
fully
shutting[1] the lockshield valve and then opening the bleed screw. If
water squirts out, water must be flowing through the valve (unless the
lockshield is duff and not shutting fully - but let's assume that the
lockshield is ok). If air comes out, keep it coming until water starts
to come out (and then top up the system to the correct pressure). For
completeness, close the TRV fully (preferably with a decorating cap),
open the lockshield and re-bleed - to ensure that that side of the
circuit is working.

Having proved that water is flowing through *both* valves, if the rad
still doesn't get hot, you've probably got an air lock. The usual trick
here is to turn off all the other rads, turn the pump up to max speed -
if adjustable - and run the system for a bit. That should clear any air
lock, and the rad should get hot. After that, it should continue to
work
ok.

As I finally got round to sorting the above out at the weekend (during a
system drain-down necessitated by installing a new rad elsewhere in the
house) i thought I'd just report back (always good to hear the outcome,
innit?). Thanks Roger for the sensible how-to-do-it.

Upon investigation I found the lockshield valve was completely shut off,
which would of course account for the completely cold radiator. WTF?
Then - lightbulb moment - I suddenly remembered that *last* winter I had
a problem with this rad (which is in a little-used spare room) not being
possible to turn *off*: ie with the TRV set to minimum the rad was
still warming up and keeping the empty spare room warm all winter. So I
shut down the lockshield valve and made a mental note to sort it out
come the summer. HTF did I just completely forget that? Well scary.


Fortunately the grey cells are still up to swapping out a failed TRV,
which I duly sorted out...

David


"Mental note", yep, been there, too! I'm 66 and now have to make
written notes if I want to remember anything important. Pi**es me off,
but if I try to remember important stuff, I just forget. And yet I can
cast my mind back to age eight in Hastings in the 1950s and remember
loads of details of my everyday life.


Do you ever watch that Foyles War?


Possibly. Can't remember...

David



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
My well tank sprung a leak [email protected] Home Repair 7 December 19th 07 10:02 PM
Sprung Pole bradsalmon UK diy 9 May 23rd 06 06:08 PM
OT? I need a PC soundcard with 'line-out' .. T i m UK diy 26 April 21st 05 02:27 PM
boiler woes- goes 'out' on its own..... Zax UK diy 8 March 22nd 05 07:29 PM
'Drying out' oil on cutting blade? Jim Witte Metalworking 1 April 10th 04 06:30 AM