Hoping someone can help with this one. SWMBO ordered a new built-in
double oven to replace a 15 year old existing one. No problems getting
the old one out and the new oven in and the mains cable was in excellent
condition. It is a 3 core, 4mm, Butyl multistrand fitted during a
kitchen refit 3 - 4 years ago. The old oven had a maximum rating of 5.5
KW with everything on.

So far so good until we used the new grill for the first time and saw
the energy meter showing 6 KW. The manual says to use 6mm T&E cable and
I just thought this was being overcautious but I'm not so sure now.

The RCD is 32 Amp and the whole circuit up to the cooker terminals is
4mm T&E so, do I have a major problem rearing its head?
--
James
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,532
Default Problem spotted after oven install

On Jan 23, 7:13*am, John Rumm wrote:
On 23/01/2011 06:27, James Noble wrote:

Hoping someone can help with this one. SWMBO ordered a new built-in
double oven to replace a 15 year old existing one. No problems getting
the old one out and the new oven in and the mains cable was in excellent
condition. It is a 3 core, 4mm, Butyl multistrand fitted during a
kitchen refit 3 - 4 years ago. The old oven had a maximum rating of 5.5
KW with everything on.


So far so good until we used the new grill for the first time and saw
the energy meter showing 6 KW. The manual says to use 6mm T&E cable and
I just thought this was being overcautious but I'm not so sure now.


The RCD is 32 Amp and the whole circuit up to the cooker terminals is
4mm T&E so, do I have a major problem rearing its head?


The short answer is no, not a problem.

The OSG says, a 32A circuit is usually adequate for household cookers of
a rating of up to 15kW (65A). This is because diversity plays a
significant part in reducing the average load. So the diverse load for a
6kW (26A) cooker is taken as 10A + 30% of the remaining actual load. So
in this case 10 + 30% of 16A = 14.8A. Add another 5A if your cooker
point has a socket.



http://wiki.diyfaq.org.uk/index.php?...le#Cable_Sizes


NT
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 24
Default Problem spotted after oven install

In message
,
Tabby writes
On Jan 23, 7:13*am, John Rumm wrote:
On 23/01/2011 06:27, James Noble wrote:

Hoping someone can help with this one. SWMBO ordered a new built-in
double oven to replace a 15 year old existing one. No problems getting
the old one out and the new oven in and the mains cable was in excellent
condition. It is a 3 core, 4mm, Butyl multistrand fitted during a
kitchen refit 3 - 4 years ago. The old oven had a maximum rating of 5.5
KW with everything on.


So far so good until we used the new grill for the first time and saw
the energy meter showing 6 KW. The manual says to use 6mm T&E cable and
I just thought this was being overcautious but I'm not so sure now.


The RCD is 32 Amp and the whole circuit up to the cooker terminals is
4mm T&E so, do I have a major problem rearing its head?


The short answer is no, not a problem.

The OSG says, a 32A circuit is usually adequate for household cookers of
a rating of up to 15kW (65A). This is because diversity plays a
significant part in reducing the average load. So the diverse load for a
6kW (26A) cooker is taken as 10A + 30% of the remaining actual load. So
in this case 10 + 30% of 16A = 14.8A. Add another 5A if your cooker
point has a socket.



http://wiki.diyfaq.org.uk/index.php?...le#Cable_Sizes


My thanks to you and John Rumm for the very useful information. My
original measurement of the grill power was far too high due, as I now
know, to failing batteries on my power meter, I found the rating plate
this morning and it says that the maximum load is 6.2 KW so using the
formula this would mean approximately 18 Amps if I have done the maths
correctly.

As it happens the oven is being replaced tomorrow as it has 4 faults on
it, sticky light switch on main oven door, scratched inner door glass,
rumbling fan and a grill that is wired up incorrectly. Considering it
retails at over GBP 800, I'm not impressed!

Thanks again!
--
James Noble
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,532
Default Problem spotted after oven install

On Jan 25, 8:20*am, James Noble wrote:
In message
,
Tabby writes



On Jan 23, 7:13*am, John Rumm wrote:
On 23/01/2011 06:27, James Noble wrote:


Hoping someone can help with this one. SWMBO ordered a new built-in
double oven to replace a 15 year old existing one. No problems getting
the old one out and the new oven in and the mains cable was in excellent
condition. It is a 3 core, 4mm, Butyl multistrand fitted during a
kitchen refit 3 - 4 years ago. The old oven had a maximum rating of 5.5
KW with everything on.


So far so good until we used the new grill for the first time and saw
the energy meter showing 6 KW. The manual says to use 6mm T&E cable and
I just thought this was being overcautious but I'm not so sure now.


The RCD is 32 Amp and the whole circuit up to the cooker terminals is
4mm T&E so, do I have a major problem rearing its head?


The short answer is no, not a problem.


The OSG says, a 32A circuit is usually adequate for household cookers of
a rating of up to 15kW (65A). This is because diversity plays a
significant part in reducing the average load. So the diverse load for a
6kW (26A) cooker is taken as 10A + 30% of the remaining actual load. So
in this case 10 + 30% of 16A = 14.8A. Add another 5A if your cooker
point has a socket.


http://wiki.diyfaq.org.uk/index.php?...le#Cable_Sizes


My thanks to you and John Rumm for the very useful information. My
original measurement of the grill power was far too high due, as I now
know, to failing batteries on my power meter, I found the rating plate
this morning and it says that the maximum load is 6.2 KW so using the
formula this would mean approximately 18 Amps if I have done the maths
correctly.

As it happens the oven is being replaced tomorrow as it has 4 faults on
it, sticky light switch on main oven door, scratched inner door glass,
rumbling fan and a grill that is wired up incorrectly. Considering it
retails at over GBP 800, I'm not impressed!

Thanks again!


6.2kW = 26A
I'm not sure you'll gain much by changing it.


NT
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Problem spotted after oven install

James Noble wrote:
In message
,
Tabby writes
On Jan 23, 7:13 am, John Rumm wrote:
On 23/01/2011 06:27, James Noble wrote:

Hoping someone can help with this one. SWMBO ordered a new built-in
double oven to replace a 15 year old existing one. No problems
getting the old one out and the new oven in and the mains cable
was in excellent condition. It is a 3 core, 4mm, Butyl multistrand
fitted during a kitchen refit 3 - 4 years ago. The old oven had a
maximum rating of 5.5 KW with everything on.

So far so good until we used the new grill for the first time and
saw the energy meter showing 6 KW. The manual says to use 6mm T&E
cable and I just thought this was being overcautious but I'm not
so sure now.

The RCD is 32 Amp and the whole circuit up to the cooker terminals
is 4mm T&E so, do I have a major problem rearing its head?

The short answer is no, not a problem.

The OSG says, a 32A circuit is usually adequate for household
cookers of a rating of up to 15kW (65A). This is because diversity
plays a significant part in reducing the average load. So the
diverse load for a 6kW (26A) cooker is taken as 10A + 30% of the
remaining actual load. So in this case 10 + 30% of 16A = 14.8A. Add
another 5A if your cooker point has a socket.



http://wiki.diyfaq.org.uk/index.php?...le#Cable_Sizes


My thanks to you and John Rumm for the very useful information. My
original measurement of the grill power was far too high due, as I now
know, to failing batteries on my power meter, I found the rating plate
this morning and it says that the maximum load is 6.2 KW so using the
formula this would mean approximately 18 Amps if I have done the maths
correctly.


Yes 18A is the value that applies for diversity. However you need not worry
about that in this case as even without diversity you would be running at
27A which is below your 32A supply. Quite often the manuals are written to
cover the manufactures arse and overengineer things.

Cheers
--
Adam


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
DIY Vent bodge spotted! [email protected] UK diy 4 November 13th 10 07:54 AM
spotted this bandsaw in the parking lot Bob Woodworking Plans and Photos 4 May 29th 07 04:27 PM
spotted this bandsaw in the parking lot Say What? Woodworking Plans and Photos 0 May 17th 07 02:55 AM
oven gas line install - questions Phil Schuman Home Repair 6 October 10th 05 02:19 AM
double oven install Gary and Karla Home Repair 1 July 14th 05 11:06 PM


All times are GMT +1. The time now is 09:33 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"