Mainsflow Thermal Store problem - coil failed?
Hi,
I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works: http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On Nov 6, 12:23*pm, Antony Jones wrote:
Hi, I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works:http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. A pressure test can give a false reading if one of the isloating valves is passing. It best to do the test with the pipework completely disconnected. The other way is to disconnect the coil and see if you get drips coming out of it that don't go away after a while, ie water leaking out of the storage tank into the coil. It does sound like the coil has failed. It might not be corrosion, sometimes they crack if there is a stress concentration point due to thermal movement. If you can get the coil out it may be repairable or replaceable if there are spares to be had. Even make one if it's just a bit of pipe. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On Nov 6, 4:37*pm, harry wrote:
On Nov 6, 12:23*pm, Antony Jones wrote: Hi, I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works:http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. A pressure test can give a false reading if one of the isloating valves is passing. *It best to do the test with the pipework completely disconnected. The other way is to disconnect the coil and see if you get drips coming out of it that don't go away after a while, ie water leaking out of the storage tank into the coil. It does sound like the coil has failed. *It might not be corrosion, sometimes they crack if there is a stress concentration point due to thermal movement. If you can get the coil out it may be repairable or replaceable if there are spares to be had. Even make one if it's just a bit of pipe.- Hide quoted text - - Show quoted text - Just another thought. I once saw a similar problem caused by a fauly mixer tap. Cold water was transfering into the hot system due to a fault on this mixer tap. Also check out if water is running into your header tank for the heating system. If what you suspect is true, it would have to be. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On Nov 6, 4:37*pm, harry wrote:
On Nov 6, 12:23*pm, Antony Jones wrote: Hi, I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works:http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. A pressure test can give a false reading if one of the isloating valves is passing. *It best to do the test with the pipework completely disconnected. The other way is to disconnect the coil and see if you get drips coming out of it that don't go away after a while, ie water leaking out of the storage tank into the coil. It does sound like the coil has failed. *It might not be corrosion, sometimes they crack if there is a stress concentration point due to thermal movement. If you can get the coil out it may be repairable or replaceable if there are spares to be had. Even make one if it's just a bit of pipe.- Hide quoted text - - Show quoted text - Or, a faulty mixer valve on a shower. Seen that one too. |
#5
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On Nov 6, 4:37*pm, harry wrote:
On Nov 6, 12:23*pm, Antony Jones wrote: Hi, I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works:http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. A pressure test can give a false reading if one of the isloating valves is passing. *It best to do the test with the pipework completely disconnected. The other way is to disconnect the coil and see if you get drips coming out of it that don't go away after a while, ie water leaking out of the storage tank into the coil. It does sound like the coil has failed. *It might not be corrosion, sometimes they crack if there is a stress concentration point due to thermal movement. If you can get the coil out it may be repairable or replaceable if there are spares to be had. Even make one if it's just a bit of pipe.- Hide quoted text - - Show quoted text - Or a faulty mixer valve on a shower. Some have non-return valves that can jam open. Seen that one too. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On 06/11/2010 16:37, harry wrote:
On Nov 6, 12:23 pm, Antony wrote: Hi, I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works:http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. A pressure test can give a false reading if one of the isloating valves is passing. It best to do the test with the pipework completely disconnected. The other way is to disconnect the coil and see if you get drips coming out of it that don't go away after a while, ie water leaking out of the storage tank into the coil. It does sound like the coil has failed. It might not be corrosion, sometimes they crack if there is a stress concentration point due to thermal movement. If you can get the coil out it may be repairable or replaceable if there are spares to be had. Even make one if it's just a bit of pipe. I disconnected the pipework both sides of the coil, so that just left the blending valve and expansion vessel in the circuit I was testing. The expansion vessel could be confusing things, of course. The internal coil is made of 4 10mm pipes bunched together, so the pipes could have cracked or pin-holed. Or the soldered joints into the 22mm feed pipes could be failing. I'd prefer a crack to corrosion as that would give me more confidence in keeping the store. (see http://img709.imageshack.us/img709/2900/p1130267.jpg and http://img3.imageshack.us/img3/1084/p1130262k.jpg which I took last time I drained the store down). But I have had other problems with 2 radiators pin holing despite inhibitor. Which makes me worried about my water being more aggressive than normal. It doesn't help having the leak as that is slowly diluting the inhibitor, of course. Cheers, Antony. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On Nov 6, 5:36*pm, Antony Jones wrote:
On 06/11/2010 16:37, harry wrote: On Nov 6, 12:23 pm, Antony *wrote: Hi, I installed an Albion Mainsflow thermal store about 5 years ago. It's this type here to save explaining how it works:http://www.albionwaterheaters.com/pd.../mainsflow.pdf It's the direct contractor version on page 3 where the store has a float valve at the top and acts as the feed and expansion tank for the boiler/radiators as well as providing hot water. The problem is its been overflowing (about half a bucket per day). It's not the float valve as I've cut and capped the pipe going to it, so that only leaves the DHW coil. I connected a pressure tester to the coil and didn't get any bubbles or noticeable drop in pressure, but there's no other way for water to get into the store. So I'm left with two options. Either replace the coil with an external plate heat exchanger, pump and flow switch. This'll cost about £250 in parts to do. The downside is if the copper coil is failing, will the cylinder itself go in time? If so, it might be better to replace the whole thing, maybe going for a more conventional unvented cylinder, which are pretty cheap (e.g. Vaillant Unistor 155 is less than £600 + fitting). I could also switch to a sealed system for the boiler/rads. But unvented cylinders aren't DIY (how much would a pro charge do you think to put one in?). Any advice appreciated. Cheers, Antony. A pressure test can give a false reading if one of the isloating valves is passing. *It best to do the test with the pipework completely disconnected. The other way is to disconnect the coil and see if you get drips coming out of it that don't go away after a while, ie water leaking out of the storage tank into the coil. It does sound like the coil has failed. * It might not be corrosion, sometimes they crack if there is a stress concentration point due to thermal movement. If you can get the coil out it may be repairable or replaceable if there are spares to be had. Even make one if it's just a bit of pipe. I disconnected the pipework both sides of the coil, so that just left the blending valve and expansion vessel in the circuit I was testing. The expansion vessel could be confusing things, of course. The internal coil is made of 4 10mm pipes bunched together, so the pipes could have cracked or pin-holed. Or the soldered joints into the 22mm feed pipes could be failing. I'd prefer a crack to corrosion as that would give me more confidence in keeping the store. (seehttp://img709.imageshack.us/img709/2900/p1130267.jpgandhttp://img3.imageshack.us/img3/1084/p1130262k.jpgwhich I took last time I drained the store down). But I have had other problems with 2 radiators pin holing despite inhibitor. Which makes me worried about my water being more aggressive than normal. It doesn't help having the leak as that is slowly diluting the inhibitor, of course. Cheers, Antony. There's always a Yorkshire sidewinder. NT |
#8
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On 06/11/2010 20:34, Tabby wrote:
Yorkshire sidewinder I had to look that up (I actually thought you were winding me up at first....) Interesting. It seems Yorkshire don't make them anymore, but it's the sort of thing that could be made on a bench. Were you thinking of this to make my thermal store indirect so I could convert to sealed system, or as a replacement for the DHW coil? One way of replacing the existing DHW coil would be to drop it in through the lid, so to speak, as I think one commercial product does (or did). Googling around it appears NuHeat do a store where the brazed plate heat exchanger is immersed in the store rather than sitting outside it, which does make some sense (no heat loss to air). Cheers, Antony |
#9
Posted to uk.d-i-y
|
|||
|
|||
Mainsflow Thermal Store problem - coil failed?
On 06/11/2010 21:48, Antony Jones wrote:
On 06/11/2010 20:34, Tabby wrote: Yorkshire sidewinder I had to look that up (I actually thought you were winding me up at first....) Interesting. It seems Yorkshire don't make them anymore, but it's the sort of thing that could be made on a bench. Were you thinking of this to make my thermal store indirect so I could convert to sealed system, or as a replacement for the DHW coil? One way of replacing the existing DHW coil would be to drop it in through the lid, so to speak, as I think one commercial product does (or did). Googling around it appears NuHeat do a store where the brazed plate heat exchanger is immersed in the store rather than sitting outside it, which does make some sense (no heat loss to air). Cheers, Antony Just to follow up my own post, it occurs to me another option to convert my store to sealed operation would be a small plate heat exchanger (the boiler is only 18kw). It means adding another pump, controlled by the zone valve on the boiler-cylinder side... But the first problem is the leaky DHW coil. Another half bucket filled over night... |