I've got a Vokera Synergy 29. It trips more or less daily with error
code 8, which indicates (from the manual)

====
Fault code 08 appears if the burner thermostat has been activated.
Check gas pressures
Check burner thermostat
Check wiring continuity
====

I am suspicious of the gas pressures, because it typically trips early
evening (when I might expect gas usage to be higher). The feed to the
boiler is 22mm followed by a 1m length of 15mm. The 15mm includes two
s-bends to get past some other pipes. There is also a tee (from the
22mm section) for a hob.

When the boiler trips, I turn it off and on, and it always starts up
again. It has never tripped immediately afterwards.

The boiler tripped two or three times in the first year of its life
(2006) but now trips nearly every day. It's being used a lot more too,
as the house is now occupied during the day.

As for wiring continuity, I see no reason why this would cause an
intermittent problem with this regularity, but stranger things have
happened. However, I also don't know which wires I should be checking
for continuity. There are a lot of them....

Are there any tests I can run to narrow the problem down?






  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 886
Default Boiler tripping frequently

On Tue, 09 Feb 2010 06:58:55 -0800, Nutkey wrote:

I am suspicious of the gas pressures, because it typically trips early
evening (when I might expect gas usage to be higher). The feed to the
boiler is 22mm followed by a 1m length of 15mm. The 15mm includes two
s-bends to get past some other pipes. There is also a tee (from the
22mm section) for a hob.


Not familiar with this boiler but if it's a combi the gas pipework is
definitely undersized. Even with no drop in the 22mm pipework a 1m length
of 15mm will drop the permissible 1mbar. Add two elbows in 15mm and you've
got the equivalent of 2m of 15mm pipework.

Whether that's causing the problem is another matter.

Your gas usage in the evening theory is not likely to be correct unless
the supply to your (and other) houses is such that the incoming gas
pressure is too low for your meter regulator to put out the required
21mbar.

Without a manometer and the know-how to use one correctly and safely (not
rocket science but I'm not going into it here) there's not much you can do
to test it yourself. If your regulator is one of the dodgy types that the
gas emergency service people routinely replace when they come across them
then they might come out and do that: you could phone and ask nicely (0800
111 999). Be prepared to describe the regulator to them.


--
John Stumbles -- http://yaph.co.uk

If we'd known how much fun grandchildren are
we'd have had them first
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 37
Default Boiler tripping frequently

On 9 Feb, 20:10, YAPH wrote:
On Tue, 09 Feb 2010 06:58:55 -0800, Nutkey wrote:
I am suspicious of the gas pressures, because it typically trips early
evening (when I might expect gas usage to be higher). The feed to the
boiler is 22mm followed by a 1m length of 15mm. The 15mm includes two
s-bends to get past some other pipes. There is also a tee (from the
22mm section) for a hob.


Not familiar with this boiler but if it's a combi the gas pipework is
definitely undersized. Even with no drop in the 22mm pipework a 1m length
of 15mm will drop the permissible 1mbar. Add two elbows in 15mm and you've
got the equivalent of 2m of 15mm pipework.


System boiler - but isn't it the power that matters rather than the
type? Anyway, according to the datasheet, max gas rate is 2.64m3/h.
Every table I've seen says for a flow of 2.9m3/h, up to 3m of 15mm
pipe is allowable. In my case, the s-bends are swept 30 degrees (and
that makes 4 bends, not 2), so call that 1.3 90 degree bends, plus an
elbow further up. I make that the equivalent of 2m of 15mm pipe.
That's 2/3rd of my pressure loss right there - the rest is in 22mm,
and looking at the tables again, I'd normally be allowed 8.7m of that,
so 1/3rd gives me nearly 3m. In practice I've got more than that -
more like 4m, with a couple of elbows and bends.....

So I'm under specced on the pipework. Interesting. Considering the guy
who put it in replaced all the gas pipework because it was underspec,
I think he might have brought it up to a real spec at the same
time.... Mind you, he clearly didn't test the release valves on the
pressurised cylinder, because when I did water came out of the
compression joints he'd forgotten to tighten up....



Whether that's causing the problem is another matter.

Your gas usage in the evening theory is not likely to be correct unless
the supply to your (and other) houses is such that the incoming gas
pressure is too low for your meter regulator to put out the required
21mbar.

Without a manometer and the know-how to use one correctly and safely (not
rocket science but I'm not going into it here) there's not much you can do


As it happens, I do own a manometer...

Ben
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas boiler tripping out electrics when igniting Francis[_4_] UK diy 5 July 23rd 09 11:21 PM
Drain frequently blocked [email protected] UK diy 4 May 13th 09 08:16 AM
Lights blowing out frequently TC Home Repair 24 March 11th 07 06:26 AM
Boiler tripping rcd paddy UK diy 14 July 10th 05 10:57 PM
Boiler tripping out Bob Smith UK diy 16 January 16th 04 10:49 PM


All times are GMT +1. The time now is 09:39 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"