Hi,
I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco |
#2
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
Mirco Simoni wrote:
Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? I would actually. In this case I would actually go for a raised timber floor. Less messy than screeding and you wont get away with 10cm with screed plus necessary isluation either. I reckon 2.2m is the minimum room height..beware friends who are 6'8" tall though ;-) If you want more than half the heat to go into your flat, not the one downstairs, use about 50mm of celotex as a minimum, or one of these proprietary foam mouldings to carry the pipes, and follow manufacturers recommendations. Here is a typical, but by no means the only, product http://download.polypipe.com/bp/brochures/overlay.pdf I reckon that fits your bill pretty much. Tile your bathrooms and kitchens, and hardwood your living areas...and laminate the bedrooms! Also, despite heatloss calcs, go for at least 100W/sq meter. UFH is great if you have large empty rooms that are tiled: Its a loss less effective under sofas and rugs. With a thin floor and with wood, you don't want too much local heat, so LOTS of pipes..cram them in. Its easy enough to turn UFH down, Its very hard to turn it up. Another point: you cannot and should not go for more than about 50C outflow temps on the CH circuit. Normally this means a temp reducing valve which costs. HOWEVER consider running the whole boiler at lower temps - it will be more efficient, and if hot water needs to be hotter, use am immersion heater in the tank as well. IF its a small flat, one thermostat is enough, and then balance individual rooms for desired result. If its large or has areas you dont use, consider zoning it. Be prepared for very long warm-up times. Although a timber floor is vastly better than screed in this rep sect , and set any timer accordingly. This is another reason to have high pipe density..things te warmer faster. Thank you, Mirco |
#3
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Thu, 11 Jun 2009 16:16:35 +0100, The Natural Philosopher wrote:
Another point: you cannot and should not go for more than about 50C outflow temps on the CH circuit. Normally this means a temp reducing valve which costs. HOWEVER consider running the whole boiler at lower temps - it will be more efficient, and if hot water needs to be hotter, use am immersion heater in the tank as well. You can roll your own proper themostatic mixing system for approx £100 with a UFH mixing valve (from Toolstation) pump and cylinder stat (or two: one as overheat cutout) and handful of fittings. Well worth the efort for a smaller installation. -- John Stumbles -- http://yaph.co.uk Just because you're paranoid doesn't mean they're not out to get you. |
#4
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On 11 June, 15:17, Mirco Simoni wrote:
Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco DEFINETLY NOT DONT FORGET THAT DOORS WILL ALSO BE 10cm SMALLER. |
#5
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"YAPH" wrote in message ... On Thu, 11 Jun 2009 16:16:35 +0100, The Natural Philosopher wrote: Another point: you cannot and should not go for more than about 50C outflow temps on the CH circuit. Normally this means a temp reducing valve which costs. HOWEVER consider running the whole boiler at lower temps - it will be more efficient, and if hot water needs to be hotter, use am immersion heater in the tank as well. You can roll your own proper themostatic mixing system for approx £100 with a UFH mixing valve (from Toolstation) pump and cylinder stat (or two: one as overheat cutout) and handful of fittings. Well worth the efort for a smaller installation. Cylinder stata? Prey tell. |
#6
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On 11 June, 15:17, Mirco Simoni wrote:
Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco No, ceiling will be too low, nobody will want to live there. Says, I, having just returned from staying at a house with 10 foot ceilings. Sadly, my house only has 8 foot ceilings, and it seems slightly oppressive to me now. I'm a shade under 6 feet tall. At 225cm, you'd be walking into light fittings. Simon. |
#7
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Fri, 12 Jun 2009 13:36:08 +0100, Doctor Drivel wrote:
Cylinder stata? Prey tell. You mean "stats" and "pray"? One to switch the UFH pump on when the flow from the boiler is hot enough to be worthwhile, another as an overheat to cut out the pump if the flow temperature is too high. This is of course for a set-up where the UFH is not being run as a separate zone. Yes I know UFH takes longer to warm up so it should be a separate zone with its own time & temp controls: this is the budget system. If it is a separate zone then you just have the overheat stat, wired to close the zone valve. -- John Stumbles -- http://yaph.co.uk I used to be forgetful but now I ... um .... |
#8
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
Simon wrote:
On 11 June, 15:17, Mirco Simoni wrote: Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco No, ceiling will be too low, nobody will want to live there. Says, I, having just returned from staying at a house with 10 foot ceilings. Sadly, my house only has 8 foot ceilings, and it seems slightly oppressive to me now. I'm a shade under 6 feet tall. At 225cm, you'd be walking into light fittings. Simon. So use uplighters on the walls. |
#9
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"YAPH" wrote in message ... One to switch the UFH pump on when the flow from the boiler is hot enough to be worthwhile, another as an overheat to cut out the pump if the flow temperature is too high. This is of course for a set-up where the UFH is not being run as a separate zone. Yes I know UFH takes longer to warm up so it should be a separate zone with its own time & temp controls: this is the budget system. If it is a separate zone then you just have the overheat stat, wired to close the zone valve. Ah!! you mean pipe stats, not cylinder stats. The overheat is a backup in case the TMV fails. It still needs a room stat in case the room overheats. It needs a non-returnvalve in front of the pump to trpevent any circuoation frommthe systems primary pump. So, three stat in all, a TMV, non-return valve and a pump. .and a coil of plastic pipe and some fittings. I would say more than £100. Best, is a heat bank using giving cheap and effective UFH using a dual temperature boiler, like the Broag, Keston and others (avoid Keston though). With dual temperature boilers with internal weather compensation, using a boiler controlled 3-way diverter valve, they can reheat the DHW store top section ASAP under full boiler heat, when heated the valve closes and it heats the lower CH section under low temperature weather compensation control - duel temperature boiler output. The rads or UFH pumps, pump this water, which is the right temperature to the heating loop(s) (zones). Using rads a Smart pump with TRVs all around can be used and no central room stat screwing up the CH air temperature control. Then no UFH TMVs as the water in store is the correct temperature set by the boilers integral weather compensator. Of couse have a high limir pipe stats on the UFH loop(s). |
#10
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"Simon" wrote in message ... On 11 June, 15:17, Mirco Simoni wrote: Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco No, ceiling will be too low, nobody will want to live there. Says, I, having just returned from staying at a house with 10 foot ceilings. Sadly, my house only has 8 foot ceilings, and it seems slightly oppressive to me now. I'm a shade under 6 feet tall. At 225cm, you'd be walking into light fittings. Simon. With low ceilings wall lights have to be used to five the impression of height. Also a smooth very white ceiling. |
#11
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
Tommy coughed up some electrons that declared:
DEFINETLY NOT DONT FORGET THAT DOORS WILL ALSO BE 10cm SMALLER. Arrgh my ears! Don't shout, mate... |
#12
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
Mirco Simoni coughed up some electrons that declared:
Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco My rooms are 2.47m floor screed to ceiling. I am installing a layer of insulation (Marmox) leaving the finished floor about 35-40mm higher than the screed level, so about 20-30mm higher than previous floor finishes. This is right at the limit of my door frames, having nailed a batten across the door to simulate the new opening height. Any lower and it felt claustrophobic. Don't forget that people bounce as they walk, so standing head height clearance is not a good indicator alone. Now, I don't know what you plan to do with your doors, but I think 10cm off a 2.35m height is going to make the ceilings horrible. I presume you are looking at 40mm insulation and 60mm screed or variations. Some variant solutions: 1) You can run sand/cement screed down to 10mm thick if you use an SBR modified mix. I've done this - my only problem was getting it tamped level (had to finish with some self leveller) - but my rooms were weird shapes making the use of several tamping bars necessary and the errors occurred generall where the walls changed direction. 2) You can get UFH (wet) panels in polystyrene which can be glued to a subfloor (bad from heat loss POV) or glued to marmox (better) which itself can be glued to the subfloor if that's reasonably flat. www.floorheater.co.uk and google this group for my previous assessment of it. That setup is not as rigid, requiring larger format tiles, but allegedly will also take a floating wood floor. Cheers, Tim |
#13
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Sat, 13 Jun 2009 10:53:11 +0100, Doctor Drivel wrote:
"YAPH" wrote in message ... One to switch the UFH pump on when the flow from the boiler is hot enough to be worthwhile, another as an overheat to cut out the pump if the flow temperature is too high. This is of course for a set-up where the UFH is not being run as a separate zone. Yes I know UFH takes longer to warm up so it should be a separate zone with its own time & temp controls: this is the budget system. If it is a separate zone then you just have the overheat stat, wired to close the zone valve. Ah!! you mean pipe stats, not cylinder stats. Sorry, yes. Though many cyl stats can be used as pipe stats also, and that's what I've been using. Really need a bit of pipelag with an appropriate cutout to ensure the stat is really sensing the pipe temp and not ambient. The overheat is a backup in case the TMV fails. Wot I said :-) It still needs a room stat in case the room overheats. If you're not using the UFH as a separate zone then you'd want a room stat, in the same way you'd want a TRV on a rad. It needs a non-returnvalve in front of the pump to trpevent any circuoation frommthe systems primary pump. How would you fit this valve to allow circulation from the UFH pump but prevent circulation caused by the system pump? Of course if the UFH is a separate zone its 2-port zone valve carries out this function. So, three stat in all, a TMV, non-return valve and a pump. .and a coil of plastic pipe and some fittings. I would say more than £100. I wasn't including the pipe in the price since you'd need this whether you were rolling your own UFH mixer or buying a £300+ proprietary mixer/manifold assembly. Best, is a heat bank using giving cheap and effective UFH using a dual temperature boiler, like the Broag, Keston and others (avoid Keston though). With dual temperature boilers with internal weather compensation, using a boiler controlled 3-way diverter valve, they can reheat the DHW store top section ASAP under full boiler heat, when heated the valve closes and it heats the lower CH section under low temperature weather compensation control - duel temperature boiler output. The rads or UFH pumps, pump this water, which is the right temperature to the heating loop(s) (zones). Using rads a Smart pump with TRVs all around can be used and no central room stat screwing up the CH air temperature control. Then no UFH TMVs as the water in store is the correct temperature set by the boilers integral weather compensator. Of couse have a high limir pipe stats on the UFH loop(s). And that would be less than £100? -- John Stumbles -- http://yaph.co.uk Pessimists are never disappointed |
#14
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"Tim S" wrote in message ... Mirco Simoni coughed up some electrons that declared: Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco My rooms are 2.47m floor screed to ceiling. Thanks Tim for spoiling my day I have measured the heights of my ceilings. 2.32m upstairs on every ceiling. But downstairs they are 2.30m for the rooms at the front of the house and 2.38m for the rooms at back of the house. A quick check with two neighbours show they that have identical ceiling heights to my house. Adam |
#15
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Thu, 11 Jun 2009 07:17:00 -0700, Mirco Simoni wrote:
Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm why? even without insulation underneath you're not going to lose a lot of heat to the flat below, since that will probably have something like an air gap and plasterboard on its side of the slab (unless you're in some Eastern European cell, or perhaps Peckham :-)). Look up the uk.d-i-y wiki's article on UFH and there are links to some thin wet UFH systems. One is just 15mm thick. -- John Stumbles -- http://yaph.co.uk This sig intentionally left blank |
#16
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
YAPH coughed up some electrons that declared:
Look up the uk.d-i-y wiki's article on UFH and there are links to some thin wet UFH systems. One is just 15mm thick. You can get 12mm now... |
#17
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"YAPH" wrote in message ... It needs a non-returnvalve in front of the pump to trpevent any circuoation frommthe systems primary pump. How would you fit this valve to allow circulation from the UFH pump but prevent circulation caused by the system pump? With no NRV the TMV may be open and circulation into the UFH zone. It needs a positive stop to circulation. The room stat switches the pump. Of course if the UFH is a separate zone its 2-port zone valve carries out this function. Yep. So, three stat in all, a TMV, non-return valve and a pump. .and a coil of plastic pipe and some fittings. I would say more than £100. I wasn't including the pipe in the price since you'd need this whether you were rolling your own UFH mixer or buying a £300+ proprietary mixer/manifold assembly. Best, is a heat bank using giving cheap and effective UFH using a dual temperature boiler, like the Broag, Keston and others (avoid Keston though). With dual temperature boilers with internal weather compensation, using a boiler controlled 3-way diverter valve, they can reheat the DHW store top section ASAP under full boiler heat, when heated the valve closes and it heats the lower CH section under low temperature weather compensation control - duel temperature boiler output. The rads or UFH pumps, pump this water, which is the right temperature to the heating loop(s) (zones). Using rads a Smart pump with TRVs all around can be used and no central room stat screwing up the CH air temperature control. Then no UFH TMVs as the water in store is the correct temperature set by the boilers integral weather compensator. Of couse have a high limir pipe stats on the UFH loop(s). And that would be less than £100? No. But a "cheap to install", fully pro, efficient, cheap to run system. Use the dual temperature boiler's controls to maximum advantage. This saves a hell of a lot on expensive, bulky UFH control, and gives mains pressure DHW that will not blow up. The boiler maintains the UFH temp to the weather - set slope of compensator. One UFH pump can be used off the store and each UFH zone uses a cheap 2 port zone valve and room stat - simple and cheap. Or a pump for each zone from a small manifold off the store, at the store. No TMVs on zones or whatever. And the boiler is operating at a very low, highly efficient return temp all the it reheats the UFH section of the store. Even when reheating DHW is will be condensing about 80-90% of the time. |
#18
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Sat, 13 Jun 2009 22:46:24 +0100
Tim S wrote: YAPH coughed up some electrons that declared: Look up the uk.d-i-y wiki's article on UFH and there are links to some thin wet UFH systems. One is just 15mm thick. You can get 12mm now... Where? |
#19
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Sun, 14 Jun 2009 09:39:36 +0100, Doctor Drivel wrote:
With no NRV the TMV may be open and circulation into the UFH zone. It needs a positive stop to circulation. The room stat switches the pump. I agree with the desirability of preventing the system pump pushing water through the UFH even when the UFH pump is off. I just don't see how you can arrange a NRV to prevent the first without also preventing flow through the UFH from the UFH pump itself. Assuming we have an arragement like this: CH FLOW --------- | ------ UFH | TMV |-----( )------ UFH FLOW ------ PUMP | CH RETURN -------+-------------------- UFH RETURN where do you propose putting a NRV? -- John Stumbles -- http://yaph.co.uk Things don't like being anthropomorphised. |
#20
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
We were somewhere around Barstow, on the edge of the desert, when the
drugs began to take hold. I remember Mirco Simoni saying something like: Hi, I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating. I know that I have to raise floors around 10 cm but the height between floor and ceiling is just 235 cm. Has anyone had the same problem ? Would you suggest to go on with the project ? Thank you, Mirco Use the alloy plate heat-spreader system and you lose no height. Under the alloy plates is packed with fibreglass or rockwool insulation. |
#21
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
TheOldFellow coughed up some electrons that declared:
On Sat, 13 Jun 2009 22:46:24 +0100 Tim S wrote: YAPH coughed up some electrons that declared: Look up the uk.d-i-y wiki's article on UFH and there are links to some thin wet UFH systems. One is just 15mm thick. You can get 12mm now... Where? http://www.floorheater.co.uk/the_box.php |
#22
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
Grimly Curmudgeon coughed up some electrons that declared:
Use the alloy plate heat-spreader system and you lose no height. Under the alloy plates is packed with fibreglass or rockwool insulation. It's really about time someone did that sort of system based with PIR foam (aka Celotex). The extra efficiency would be a winner. Cheers Tim |
#23
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Sun, 14 Jun 2009 15:15:53 +0100, Grimly Curmudgeon wrote:
Use the alloy plate heat-spreader system and you lose no height. Under the alloy plates is packed with fibreglass or rockwool insulation. The OP said he's got screed floors :-) -- John Stumbles -- http://yaph.co.uk This sig intentionally left blank |
#24
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"YAPH" wrote in message ... On Sun, 14 Jun 2009 09:39:36 +0100, Doctor Drivel wrote: With no NRV the TMV may be open and circulation into the UFH zone. It needs a positive stop to circulation. The room stat switches the pump. I agree with the desirability of preventing the system pump pushing water through the UFH even when the UFH pump is off. I just don't see how you can arrange a NRV to prevent the first without also preventing flow through the UFH from the UFH pump itself. Assuming we have an arragement like this: CH FLOW --------- | ------ UFH | TMV |-----( )------ UFH FLOW ------ PUMP | CH RETURN -------+-------------------- UFH RETURN where do you propose putting a NRV? The system pump can pump past the TMV and into the loop, although at reduced pressure/flow. Ideally a positive stop is needed such as a zone valve. Then no circulation. When using a spring loaded NRV best after the pump. However if the system pump has a high pressure, some zones may have closed down, it may be best to have one on the UFH return as well and the UFH pump turned up to open both NRVs. You don't need to be a God to see that. |
#25
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Sun, 14 Jun 2009 23:36:20 +0100, Doctor Drivel wrote:
The system pump can pump past the TMV and into the loop, although at reduced pressure/flow. Ideally a positive stop is needed such as a zone valve. Then no circulation. When using a spring loaded NRV best after the pump. However if the system pump has a high pressure, some zones may have closed down, it may be best to have one on the UFH return as well and the UFH pump turned up to open both NRVs. You don't need to be a God to see that. So basically using NRVs to add resistance to the UFH loop to help prevent flow driven by the system pump? I think you could acheive the same effect by using your ordinary balancing valves to increase the UFH loop resistance. But basically a non-zoned UFH loop is a bit of a kludge (as is much of conventional CH practice, to put it in context). Zoned with a motorised valve is preferable. -- John Stumbles -- http://yaph.co.uk I can't stand intolerance |
#26
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"YAPH" wrote in message ... On Sun, 14 Jun 2009 23:36:20 +0100, Doctor Drivel wrote: The system pump can pump past the TMV and into the loop, although at reduced pressure/flow. Ideally a positive stop is needed such as a zone valve. Then no circulation. When using a spring loaded NRV best after the pump. However if the system pump has a high pressure, some zones may have closed down, it may be best to have one on the UFH return as well and the UFH pump turned up to open both NRVs. You don't need to be a God to see that. So basically using NRVs to add resistance to the UFH loop to help prevent flow driven by the system pump? I think you could acheive the same effect by using your ordinary balancing valves to increase the UFH loop resistance. You will still need a NRV after the pump and balance it down at the return end. Without the NRV heat will work its way into the UFH loop by force (pump) or convection. But basically a non-zoned UFH loop is a bit of a kludge (as is much of conventional CH practice, to put it in context). Zoned with a motorised valve is preferable. Yep, a spur of the rad circuit is a kludge, as they operate at different temperatures, and operate very differently to each other. In a well insulated house, as say in a bedroom, it can work very well. It needs a quicker heat up than in a screed. Having it in soft copper at rad temperature and not touching the wooden floor above with masses of rockwool beneath (acts as sound insulation as well) with cheap cooking foil over the rockwool to reflect upwards (available cheap in commercial rolls) with thermostat control can do it. Of course no carpet on the floor as in all UFH. You get sound insulation and no rads - so probably well worth it. Yep most CH system are a kludge as they are just cheap, designed by rule of thumb, retrofit systems. |
#27
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Mon, 15 Jun 2009 13:22:31 +0100, Doctor Drivel wrote:
Yep, a spur of the rad circuit is a kludge, as they operate at different temperatures, and operate very differently to each other. Well that's even more of a kludge. I did it once with a very small area of UFH in the return of the radiator in a shower room. The area was so small it wasn't worth even bothering with a pump and TMV (it was as much to warm the tiled floor as to actually heat the room). But I meant that a pump+TMV off the main heating loop, but not zoned, is a bit of a kludge. -- John Stumbles -- http://yaph.co.uk 87.5% of statistics are made up |
#28
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
We were somewhere around Barstow, on the edge of the desert, when the
drugs began to take hold. I remember YAPH saying something like: On Sun, 14 Jun 2009 15:15:53 +0100, Grimly Curmudgeon wrote: Use the alloy plate heat-spreader system and you lose no height. Under the alloy plates is packed with fibreglass or rockwool insulation. The OP said he's got screed floors :-) From the OP: "I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating." Now, I took that to mean he's putting in screed floors in order to install UFH. Disambiguation needed, to quote a horrible phrase beloved of wikipedia. |
#29
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Mon, 15 Jun 2009 13:54:42 +0100, Grimly Curmudgeon wrote:
From the OP: "I am thinking to refurbish a first floor flat with screed floors and install water underfloor heating." Now, I took that to mean he's putting in screed floors in order to install UFH. Disambiguation needed, to quote a horrible phrase beloved of wikipedia. Fairy Nuff, though if the OP's thinking of installing screed floors in a first floor flat that doesn't already have them he needs more than disambiguation ;-) -- John Stumbles -- http://yaph.co.uk The clairvoyants' meeting has been cancelled due to unforseen circumstances. |
#30
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
On Wed, 17 Jun 2009 13:08:30 +0100, Doctor Drivel wrote:
If the floor is wood and suspended and the UFH circuit is spur off the rad circuit, I would use 12mm soft copper clipped to the side of the joists and running through the joists in 22mm holes, so the copper does not touch any wood. The UFH circuit then runs at rad system temperatures and heats the space between the floor boards and the insulation beneath. I did something like that in my kitchen, years ago. Rockwool suspended on netting slung between the joists, 15mm polybutylene run up and down the gaps between the joists, suspended close to the floor surface, plywood and ceramic tiles on top. All connected into the regular CH via a TRV under the floor set to open when ambient temp under the floor falls below about 18C, IIRC. It generally keeps the room nicely warm and pleasant to walk on, though a bit patchy - some hot and some cool patches. -- John Stumbles -- http://yaph.co.uk The astronomer married a star |
#31
Posted to uk.d-i-y
|
|||
|
|||
water underfloor heating installation
"YAPH" wrote in message ... I did something like that in my kitchen, years ago. Rockwool suspended on netting slung between the joists, 15mm polybutylene run up and down the gaps between the joists, suspended close to the floor surface, plywood and ceramic tiles on top. All connected into the regular CH via a TRV under the floor set to open when ambient temp under the floor falls below about 18C, IIRC. It generally keeps the room nicely warm and pleasant to walk on, though a bit patchy - some hot and some cool patches. I assume the TRV had a remote temperature sensor. It should work well enough, as the water/heat will be restitcted through the UFH loop when approach setpoint. As I mentioned, Danfoss have dedicated mechanical UFH valves for the task. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Underfloor heating as primary heating | UK diy | |||
controlling hot water underfloor heating | UK diy | |||
Electric Underfloor Heating - AHT Heating | UK diy | |||
hot water underfloor heating | UK diy | |||
Water Temperature for underfloor heating | UK diy |