  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 92
Default New (outdoor) boiler

I have bought a Grant external boiler for the renovation.

I have a couple of questions re the electrical connection.

As regards supplementary bonding to the oil feed pipe, is this required
if the boiler is outside? The internal plumbing will be all plastic
after the first metre.

The manual states that "The electrical supply to the boiler and control
system should be fed from a single separate 5 Amp circuit breaker with
earth leakage protection providing complete electrical isolation". Also
a fused double pole switch should be used. I was planning to just use a
FCU on the downstairs ring to provide power. Is the separate circuit
breaker (MCB?) really necessary?

Cheers

Martin

--
Martin Carroll
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default New (outdoor) boiler

Martin Carroll wrote:

I have bought a Grant external boiler for the renovation.

I have a couple of questions re the electrical connection.

As regards supplementary bonding to the oil feed pipe, is this required
if the boiler is outside? The internal plumbing will be all plastic
after the first metre.


If its all plastic in the house, then I can't see the need.

The manual states that "The electrical supply to the boiler and control
system should be fed from a single separate 5 Amp circuit breaker with
earth leakage protection providing complete electrical isolation". Also
a fused double pole switch should be used. I was planning to just use a
FCU on the downstairs ring to provide power. Is the separate circuit
breaker (MCB?) really necessary?


Not required, but perhaps desirable. Boilers and appliances outside are
good candidates for nuisance trip problems, so not sharing a RCD with
your socket circuit could have advantages.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default New (outdoor) boiler

On 31 Jan, 15:34, John Rumm wrote:
Martin Carroll wrote:
I have bought a Grant external boiler for the renovation.


I have a couple of questions re the electrical connection.


As regards supplementary bonding to the oil feed pipe, is this required
if the boiler is outside? *The internal plumbing will be all plastic
after the first metre.


If its all plastic in the house, then I can't see the need.

The manual states that "The electrical supply to the boiler and control
system should be fed from a single separate 5 Amp circuit breaker with
earth leakage protection providing complete electrical isolation". Also
a fused double pole switch should be used. *I was planning to just use a
FCU on the downstairs ring to provide power. *Is the separate circuit
breaker (MCB?) really necessary?


Not required, but perhaps desirable. Boilers and appliances outside are
good candidates for nuisance trip problems, so not sharing a RCD with
your socket circuit could have advantages.

--
Cheers,

John.

/================================================== ===============\
| * * * * *Internode Ltd - *http://www.internode.co.uk* * * * * *|
|-----------------------------------------------------------------|
| * * * *John Rumm - john(at)internode(dot)co(dot)uk * * * * * * *|
\================================================= ================/


"good candidates for nuisance trip" Hmm - interesting. I've three
external circuits - outside boiler, outside workshop and outside
garage/greenhouse/storage shed and in 25 years I've never had a
problem. Perhaps as an amateur I do a good job of wiring !!!

Of course having just said that, they will now all give me hell!

Rob
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,092
Default New (outdoor) boiler

We were somewhere around Barstow, on the edge of the desert, when the
drugs began to take hold. I remember Martin Carroll
saying something like:

The manual states that "The electrical supply to the boiler and control
system should be fed from a single separate 5 Amp circuit breaker with
earth leakage protection providing complete electrical isolation". Also
a fused double pole switch should be used. I was planning to just use a
FCU on the downstairs ring to provide power. Is the separate circuit
breaker (MCB?) really necessary?


Do like 99% of installers do and take a spur from the protected ring to
a switched double socket at the boiler with the boiler and pump plugged
in with 5A fuses in the plugs. Does all you need and safely, too, for
servicing.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default New (outdoor) boiler

robgraham wrote:

"good candidates for nuisance trip" Hmm - interesting. I've three
external circuits - outside boiler, outside workshop and outside
garage/greenhouse/storage shed and in 25 years I've never had a
problem. Perhaps as an amateur I do a good job of wiring !!!

Of course having just said that, they will now all give me hell!


As with all these things, you can only go with probabilities. There is
no guarantee that any setup will cause a problem and none that it won't.
So its just a case of working out what is possible or likely, and
deciding on how important the implications of it are. Circuits that
potentially involve dampness, water, high humidity etc are more likely
to cause problems (as are ones with copious mains IF filters or mineral
insulated heating elements). Then again in reality they may work
faultlessly.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default New (outdoor) boiler


"robgraham" wrote in message
...
On 31 Jan, 15:34, John Rumm wrote:
Martin Carroll wrote:
I have bought a Grant external boiler for the renovation.


I have a couple of questions re the electrical connection.


As regards supplementary bonding to the oil feed pipe, is this required
if the boiler is outside? The internal plumbing will be all plastic
after the first metre.


If its all plastic in the house, then I can't see the need.

The manual states that "The electrical supply to the boiler and control
system should be fed from a single separate 5 Amp circuit breaker with
earth leakage protection providing complete electrical isolation". Also
a fused double pole switch should be used. I was planning to just use a
FCU on the downstairs ring to provide power. Is the separate circuit
breaker (MCB?) really necessary?


Not required, but perhaps desirable. Boilers and appliances outside are
good candidates for nuisance trip problems, so not sharing a RCD with
your socket circuit could have advantages.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


"good candidates for nuisance trip" Hmm - interesting. I've three
external circuits - outside boiler, outside workshop and outside
garage/greenhouse/storage shed and in 25 years I've never had a
problem. Perhaps as an amateur I do a good job of wiring !!!

Of course having just said that, they will now all give me hell!

Rob


This is not a comment on any of your work Rob but a serious question, but
have you tested the RCD in the last 25 years?

I have come across several RCDs that will not trip when they are supposed
to.

Adam


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default New (outdoor) boiler

On Sat, 31 Jan 2009 15:08:56 +0000 someone who may be Martin Carroll
wrote this:-

The manual states that "The electrical supply to the boiler and control
system should be fed from a single separate 5 Amp circuit breaker with
earth leakage protection providing complete electrical isolation".


They appear to be confused, or need to introduce some commas. Earth
leakage protection is not designed to provide complete electrical
isolation, although a suitable double-pole RCD will do so.

There is something to be said for a dedicated radial circuit to a
boiler, with a fuse or MCB in the consumer unit. What else is
desirable or necessary depends on where the boiler is located. An
outbuilding, a separate boiler house, a separate building, outdoors
(unlikely, but possible) and so on. Then there is a similar question
with regard to the oil tank. The answers to the questions will help
with answers to questions on things like bonding.



--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 92
Default New (outdoor) boiler

In article , David Hansen
writes
There is something to be said for a dedicated radial circuit to a
boiler, with a fuse or MCB in the consumer unit. What else is
desirable or necessary depends on where the boiler is located. An
outbuilding, a separate boiler house, a separate building, outdoors
(unlikely, but possible) and so on.


The boiler is indeed an outdoor model, http://www.grantuk.com/product/29

Cheers

Martin

--
Martin Carroll
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outdoor boiler Martin Carroll UK diy 6 September 27th 07 12:33 AM
Running outdoor Christmas lights without an outdoor outlet PM Home Repair 5 December 17th 06 04:12 AM
Running outdoor Christmas lights without an outdoor outlet PM Home Ownership 2 December 16th 06 11:56 PM
Connecting a boiler outdoor sensor Matt UK diy 0 August 16th 06 01:08 PM
Does anybody have an outdoor kerosene boiler? Wes UK diy 9 November 2nd 04 12:05 AM


All times are GMT +1. The time now is 03:30 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"