The instructions with the loft insulation say that electric cables should go
above the insulation - presumably in case there's any build up of heat.

Is this an absolute because in places there's not enough slack in the wiring
and there are connection boxes which are screwed to the joists.

Alan

--
email =~ s/nospam/fudokai/
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 197
Default Loft insulation and wiring

ajp wrote:
The instructions with the loft insulation say that electric cables
should go above the insulation - presumably in case there's any build
up of heat.

Is this an absolute because in places there's not enough slack in the
wiring and there are connection boxes which are screwed to the joists.

Alan


Not answering your question, just adding to it...

I was also wondering this, I plan to board my loft, so when I rewire I was
planning on clipping all the cables to the sides of the joists, is this
going to be an issue when I then insulate it?

Toby...

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default Loft insulation and wiring

On Fri, 28 Nov 2008 15:00:27 +0000 someone who may be ajp
wrote this:-

The instructions with the loft insulation say that electric cables should go
above the insulation - presumably in case there's any build up of heat.


Because the heat can't get away from the electric cables so easily
when they are covered in insulation. If the heat can't get away then
the cables may at best just melt and at worst set the house on fire.

Is this an absolute


Mostly, yes.

Lighting cables are probably alright if covered with insulation, but
you need to do the calculations to check this. Other cables are
probably not alright, though you need to check this in the same way.

You don't say what sort of house you have or what sort of cables are
in the loft, so there is almost nothing else which can usefully be
said other than in a "typical" two storey house the only circuits in
the loft tend to be lighting circuits. We are not remote viewers and
so we cannot see what is in your loft.



--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #4   Report Post  
Posted to uk.d-i-y
jal jal is offline
external usenet poster
 
Posts: 67
Default Loft insulation and wiring

In article ,
ajp wrote:

The instructions with the loft insulation say that electric cables should go
above the insulation - presumably in case there's any build up of heat.

Is this an absolute because in places there's not enough slack in the wiring
and there are connection boxes which are screwed to the joists.


Ditto. I put my cables over the insulation when I rewired my house 12
or so years ago. This summer we had the (now-advised extra 6" of
insulation put in, and the cables are all too tight to go over that.

I am figuring:

(1) I'll keep a weather eye out for fires starting in the loft (don't
ask me how).

and

(2) All legislation and "advisories" are based not so much upon
practical risks, as upon protecting insurance companies from claims by
tradesmen / contractors / householders, i.e. a 1 in a million chance[1].
In other words, one in a million lofts may catch fire -- so make all
1,000,000 of them install things "properly".

dons fireproof clothing - not because of loft fires but because of the
expected heat of responses to this sacrilegious post

--
[1] It's still a chance, of course.
  #5   Report Post  
Posted to uk.d-i-y
ajp ajp is offline
external usenet poster
 
Posts: 17
Default Loft insulation and wiring

David Hansen wrote:

On Fri, 28 Nov 2008 15:00:27 +0000 someone who may be ajp
wrote this:-

The instructions with the loft insulation say that electric cables should
go above the insulation - presumably in case there's any build up of heat.


Because the heat can't get away from the electric cables so easily
when they are covered in insulation. If the heat can't get away then
the cables may at best just melt and at worst set the house on fire.

Is this an absolute


Mostly, yes.

Lighting cables are probably alright if covered with insulation, but
you need to do the calculations to check this. Other cables are
probably not alright, though you need to check this in the same way.

You don't say what sort of house you have or what sort of cables are
in the loft, so there is almost nothing else which can usefully be
said other than in a "typical" two storey house the only circuits in
the loft tend to be lighting circuits. We are not remote viewers and
so we cannot see what is in your loft.




We're in a bungalow so there is power circuitry in the loft.

If I'm not allowed to cover them then fitting insulation is going to be a
problem. So far I've managed to fit the insulation under the wiring but I'm
reaching an area where this may not be possible - or at least not without
some tugging on the cables :-)

Alan

--
email =~ s/nospam/fudokai/


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Loft insulation and wiring

Toby wrote:
ajp wrote:
The instructions with the loft insulation say that electric cables
should go above the insulation - presumably in case there's any build
up of heat.

Is this an absolute because in places there's not enough slack in the
wiring and there are connection boxes which are screwed to the joists.

Alan


Not answering your question, just adding to it...

I was also wondering this, I plan to board my loft, so when I rewire I
was planning on clipping all the cables to the sides of the joists, is
this going to be an issue when I then insulate it?


With lighting circuits this is mostly a non issue if they are protected
at 5 or 6A as is normal. The smallest cable typically used is 1.0mm^2
T&E and this is good for 11A when clipped direct to a surface or in free
air. So even if you do cover it with insulation you are unlikely to
de-rate it enough to be a problem unless there are other factors to take
into account (high ambient temperatures, cable grouping etc).

Clipping them to a joist is worthwhile, since the wood will conduct heat
away more heat from a cable when compared to one completely surrounded
by insulation.

Power circuits (sockets etc) however are another issue. These you will
need to take far more care with since you probably don't have the spare
capacity to play with.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 197
Default Loft insulation and wiring

John Rumm wrote:
Toby wrote:
ajp wrote:
The instructions with the loft insulation say that electric cables
should go above the insulation - presumably in case there's any
build up of heat.

Is this an absolute because in places there's not enough slack in
the wiring and there are connection boxes which are screwed to the
joists. Alan


Not answering your question, just adding to it...

I was also wondering this, I plan to board my loft, so when I rewire
I was planning on clipping all the cables to the sides of the
joists, is this going to be an issue when I then insulate it?


With lighting circuits this is mostly a non issue if they are
protected at 5 or 6A as is normal. The smallest cable typically used
is 1.0mm^2 T&E and this is good for 11A when clipped direct to a
surface or in free air. So even if you do cover it with insulation
you are unlikely to de-rate it enough to be a problem unless there
are other factors to take into account (high ambient temperatures,
cable grouping etc).
Clipping them to a joist is worthwhile, since the wood will conduct
heat away more heat from a cable when compared to one completely
surrounded by insulation.

Power circuits (sockets etc) however are another issue. These you will
need to take far more care with since you probably don't have the
spare capacity to play with.


Thanks John,

I will use 1.5mm cable to give a little more headroom.

I will have an outside lighting circuit, connected to a 10A RCBO, but I
think this will be all in the 1st floor floor, so that shouldn't be an
issue.

In the bedroom, on the 1st floor (top floor) there are already a load of
GU10 down lighters installed, I will be keeping them (mainly to save having
to fill the plasterboard!) and will also install some wall lights, so they
won't be used much, I assume I need to install fire-hoods over them - if so,
is it OK to put insulation over this, or would it be better to leave holes
over each one?

The same with the boarding I will then put down, can I just board over them,
or do I need to cut vent holes in!?

Thanks!

Toby...

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Loft insulation and wiring

jal wrote:

Is this an absolute because in places there's not enough slack in the wiring
and there are connection boxes which are screwed to the joists.


Ditto. I put my cables over the insulation when I rewired my house 12
or so years ago. This summer we had the (now-advised extra 6" of
insulation put in, and the cables are all too tight to go over that.

I am figuring:

(1) I'll keep a weather eye out for fires starting in the loft (don't
ask me how).


Not really practical is it? You need to make sure it is not going to be
a problem by taking the required action when insulating. That may
require rerouting, or extending cables, it may even require you
substitute larger cables in some cases (e.g. upgrading 2.5mm^2 T&E on a
ring circuit to 4mm^2).

and

(2) All legislation and "advisories" are based not so much upon
practical risks, as upon protecting insurance companies from claims by
tradesmen / contractors / householders, i.e. a 1 in a million chance[1].
In other words, one in a million lofts may catch fire -- so make all
1,000,000 of them install things "properly".


No offence, but this is ********. The reason they warn you of the risks
may well come down to disclaiming responsibility etc, however the actual
risks themselves just come down to basic physics.

dons fireproof clothing - not because of loft fires but because of the
expected heat of responses to this sacrilegious post


well you did ask ;-)

Remember that the current carrying capacity of cables is dictated by the
maximum sustained temperature that they can endure without suffering
damage. Most PVC cables with be rated for operation at upto 70 deg C.
Hence if you live in a single story property, and your kitchen ring
circuit is fairly fully loaded (not uncommon), then you will routinely
be running the cables quite hot and close to their design limit. If you
now cover those with insulation you are likely to get cable damage as a
result. You will also de-rate the cable to a point where its current
carrying capacity is unacceptably low for a ring circuit. In a modern
installation this is unlikely to result in a fire directly, but it may
well result in nuisance trips, failed insulation, and the need to
replace cables before you can restore power to the effected circuits.

(2.5mm^2 T&E can carry 27A clipped to a surface, but that can fall to
17A when sat on a plasterboard ceiling and the covered with more than
100mm of loft insulation)

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,538
Default Loft insulation and wiring

John Rumm coughed up some electrons that declared:


(2.5mm^2 T&E can carry 27A clipped to a surface, but that can fall to
17A when sat on a plasterboard ceiling and the covered with more than
100mm of loft insulation)


And if I might add to John's excellent post, the correct design for any leg
on a 32A ring final circuit such that the current carrying capacity of the
cable be 20A or greater, after all derating and grouping corrections are
applied (17th, regulation 433.1.5).

So 20A is the magic number to aim for. Obviously with any other type of
circuit, the cable must be capable of carrying at least what the
breaker/fuse is rated at irrespective of the anticipated actual load on the
cable. So a 7.6kW shower fed by a 40A breaker needs a 40A cable, not a 33A
one.

Taken from the OnSite guide, I've copied out some key numbers for 1.5mm2,
2.5mm2 and 4mm2 T+E cable which may prove useful:

But you should check these again before actually using, typos etc..

Method C, "Clipped Direct"

1.5mm2 19.5A
2.5mm2 27A
4mm2 36A

Method B, "Conduit in/on non insulating wall"
1.5mm2 16.5A
2.5mm2 23A
4mm2 30A

Method 100, "Above plasterboard ceiling covered by no more than 100mm
thickness of insulation"
1.5mm2 16A
2.5mm2 21A
4mm2 27A

Method 101, "Above plasterboard ceiling covered by more than 100mm thickness
of insulation"
1.5mm2 13A
2.5mm2 17A
4mm2 22A

As you can see, Method 101 kills 2.5mm2 as a 32A ring cable, but Method 100
is OK, just, as long as you don't further derate the cables due to grouping
factors etc.

Going up to 4mm2 is a pain, as you are only allowed 2 4mm2 wires in the back
of a BS standard 13A socket terminal, so no spurs.

Cheers

Tim
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Loft insulation and wiring

Tim S wrote:

(2.5mm^2 T&E can carry 27A clipped to a surface, but that can fall to
17A when sat on a plasterboard ceiling and the covered with more than
100mm of loft insulation)


And if I might add to John's excellent post, the correct design for any leg
on a 32A ring final circuit such that the current carrying capacity of the
cable be 20A or greater, after all derating and grouping corrections are
applied (17th, regulation 433.1.5).


Indeed...

So 20A is the magic number to aim for. Obviously with any other type of
circuit, the cable must be capable of carrying at least what the
breaker/fuse is rated at irrespective of the anticipated actual load on the
cable. So a 7.6kW shower fed by a 40A breaker needs a 40A cable, not a 33A
one.


I will add a slight complication to that one...

The cable needs to match or exceed the overcurrent protection. While
that is traditionally provided by the circuits main fuse/breaker, it
does not *have* to be at the head end (as might be assumed by some
reading the "breaker/fuse" bit). The obvious example is a socket on an
unfused spur. The single run of 2.5mm^2 T&E is given adequate fault
protection by the 32A breaker, but overcurrent protection is down to the
fusing in the plugs.

Taken from the OnSite guide, I've copied out some key numbers for 1.5mm2,
2.5mm2 and 4mm2 T+E cable which may prove useful:

But you should check these again before actually using, typos etc..


snip handy list

There is also a table here if needed:

http://wiki.diyfaq.org.uk/index.php?title=Cable#T.26E


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Loft insulation and wiring

Toby wrote:

With lighting circuits this is mostly a non issue if they are
protected at 5 or 6A as is normal. The smallest cable typically used
is 1.0mm^2 T&E and this is good for 11A when clipped direct to a
surface or in free air. So even if you do cover it with insulation


Oops, better correct that. That should read 16A clipped direct. The 11A
(well 10.5) is actually the case when covered in =100mm insulation.

I will use 1.5mm cable to give a little more headroom.


From the PoV of current carrying capacity there is no need on a
standard circuit really - you are still well clear in most cases. If you
were protecting them at 10A and wanted to bury them in insulation, and
apply other de-ratings, *then* it might be worth using 1.5mm^2.

The time 1.5mm^2 becomes handy is for dealing with voltage drop. The
17th edition limit is now 3% (so 6.9V) on a lighting circuit. With a 6A
MCB and 1.0mm cable, with a full load distributed around the circuit,
that results in a maximum cable length of 59m (Table 17.1 in the OSG).
Falling to 35m for a 10A protected circuit. Using 1.5mm^2 raises these
limits to 90m and 52m respectively.

In the bedroom, on the 1st floor (top floor) there are already a load of
GU10 down lighters installed, I will be keeping them (mainly to save
having to fill the plasterboard!) and will also install some wall
lights, so they won't be used much, I assume I need to install
fire-hoods over them - if so, is it OK to put insulation over this, or
would it be better to leave holes over each one?


The main problem with downlights is if you let them get too hot, bulb
life suffers even more (especially with GU10s). Sometimes a flower pot
(real one, not plastic!) is suggested as a way of keeping some air space
round them. Fire hoods are handy if you need to maintain the fire
integrity of the ceiling.

The same with the boarding I will then put down, can I just board over
them, or do I need to cut vent holes in!?


Much depends on the joist depth. On slim loft joists you may even find
the boards are prevented from seating correctly by the upstanding lights.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Loft insulation. Warm loft, colder bedrooms? [email protected] UK diy 2 October 27th 07 07:52 PM
Loft Insulation ? the_constructor UK diy 1 January 8th 07 08:07 AM
Insulation on loft roof - insulation blankets...? Simon Hawthorne UK diy 10 April 18th 05 09:55 PM
Loft insulation Broadback UK diy 3 October 24th 04 02:07 PM
Loft insulation Conrad Edwards UK diy 0 August 25th 03 09:57 PM


All times are GMT +1. The time now is 08:05 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"