Hi,

A corgi registered plumber recently changed the fan in my glow worm
combination boiler, because the old one was making a noise. This is
now fine, but since the plumber left the hot water doesn't work
properly, the boiler fires up when you turn the hot tap on, then shuts
down after a few seconds, then starts up again for a few seconds etc.
The water pressure seems fine, and I don't think the boiler is
shutting down because it's overheating.

If I turn the heating on for a while, then turn on the hot tap, the
boiler sometimes stays on heating the water.

Any ideas what this could be, I assume it's some sort of bad contact
that should be simple to fix?

The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...

Thanks

Ryan
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 109
Default Combination boiler hot water

On 15/09/2008 09:31, Ryan wrote:

The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...


So long as you're sure the new problem started at the time the fan was
replaced (rather than being a coincidental issue that started shortly
afterwards) make it clear in writing to the original plumber that if
they don't fix the new problem within a reasonable period of time (7
days?) you will engage someone else to repair it and then pursue the
original plumber for the cost of the remedial work.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7
Default Combination boiler hot water

On 15 Sep, 09:39, Andy Burns wrote:
On 15/09/2008 09:31, Ryan wrote:

The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...


So long as you're sure the new problem started at the time the fan was
replaced (rather than being a coincidental issue that started shortly
afterwards) make it clear in writing to the original plumber that if
they don't fix the new problem within a reasonable period of time (7
days?) you will engage someone else to repair it and then pursue the
original plumber for the cost of the remedial work.



Thanks for your post.

The guy fixed the fan in the afternoon, and when I got home in the
evening the hot water wasn't working. I only had the fan replaced
because it was making a high pitch squeek when warming up, there was
nothing actually wrong with the boiler. Wish I hadn't bothered....

I'm not sure writing will do much good, but I'll give it a try. I
haven't had hot water now for 4 days and I needed it sorted asap...

Anyone got any ideas to exactly what the problem could be?

Thanks
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,231
Default Combination boiler hot water

On Mon, 15 Sep 2008 02:14:50 -0700, Ryan wrote:

On 15 Sep, 09:39, Andy Burns wrote:
On 15/09/2008 09:31, Ryan wrote:

The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...


So long as you're sure the new problem started at the time the fan was
replaced (rather than being a coincidental issue that started shortly
afterwards) make it clear in writing to the original plumber that if
they don't fix the new problem within a reasonable period of time (7
days?) you will engage someone else to repair it and then pursue the
original plumber for the cost of the remedial work.



Thanks for your post.

The guy fixed the fan in the afternoon, and when I got home in the
evening the hot water wasn't working. I only had the fan replaced
because it was making a high pitch squeek when warming up, there was
nothing actually wrong with the boiler. Wish I hadn't bothered....

I'm not sure writing will do much good, but I'll give it a try. I
haven't had hot water now for 4 days and I needed it sorted asap...

Anyone got any ideas to exactly what the problem could be?

Sounds like a new fault tome.
Probably the diverter valve, especially as it works OK after you have used
the heating (and thus disturbed the DV).


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,861
Default Combination boiler hot water

In message , Ed Sirett
writes
On Mon, 15 Sep 2008 02:14:50 -0700, Ryan wrote:

On 15 Sep, 09:39, Andy Burns wrote:
On 15/09/2008 09:31, Ryan wrote:

The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...

So long as you're sure the new problem started at the time the fan was
replaced (rather than being a coincidental issue that started shortly
afterwards) make it clear in writing to the original plumber that if
they don't fix the new problem within a reasonable period of time (7
days?) you will engage someone else to repair it and then pursue the
original plumber for the cost of the remedial work.



Thanks for your post.

The guy fixed the fan in the afternoon, and when I got home in the
evening the hot water wasn't working. I only had the fan replaced
because it was making a high pitch squeek when warming up, there was
nothing actually wrong with the boiler. Wish I hadn't bothered....

I'm not sure writing will do much good, but I'll give it a try. I
haven't had hot water now for 4 days and I needed it sorted asap...

Anyone got any ideas to exactly what the problem could be?

Sounds like a new fault tome.
Probably the diverter valve, especially as it works OK after you have used
the heating (and thus disturbed the DV).

Yeah - completely different faults

The fan is venting the combustion chamber and doesn't know whether it's
for CH or DHW

Having not mentioned what boiler it is (AFAICS) there is the possibility
that he could have damaged the pcb, but it's very much an outsider and
extremely unlikely

--
geoff


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7
Default Combination boiler hot water

On 16 Sep, 00:17, geoff wrote:
In message , Ed Sirett
writes



On Mon, 15 Sep 2008 02:14:50 -0700, Ryan wrote:


On 15 Sep, 09:39, Andy Burns wrote:
On 15/09/2008 09:31, Ryan wrote:


The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...


So long as you're sure the new problem started at the time the fan was
replaced (rather than being a coincidental issue that started shortly
afterwards) make it clear in writing to the original plumber that if
they don't fix the new problem within a reasonable period of time (7
days?) you will engage someone else to repair it and then pursue the
original plumber for the cost of the remedial work.


Thanks for your post.


The guy fixed the fan in the afternoon, and when I got home in the
evening the hot water wasn't working. *I only had the fan replaced
because it was making a high pitch squeek when warming up, there was
nothing actually wrong with the boiler. *Wish I hadn't bothered....


I'm not sure writing will do much good, but I'll give it a try. *I
haven't had hot water now for 4 days and I needed it sorted asap...


Anyone got any ideas to exactly what the problem could be?


Sounds like a new fault tome.
Probably the diverter valve, especially as it works OK after you have used
the heating (and thus disturbed the DV).


Yeah - completely different faults

The fan is venting the combustion chamber and doesn't know whether it's
for CH or DHW

Having not mentioned what boiler it is (AFAICS) there is the possibility
that he could have damaged the pcb, but it's very much an outsider and
extremely unlikely

--
geoff- Hide quoted text -

- Show quoted text -


It's a glow worm Compact 80e fanned flue combination boiler. It looks
like I'm going to have to get someone else to have a look at this
then. Previous plumber has gone underground. I take your point that
it is a different fault, but it is a hell of a coincenence. The least
the guy could have done was check that it was working correctly before
he left...

Thanks for everyones input

Ryan

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7
Default Combination boiler hot water

On 16 Sep, 17:01, Ryan wrote:
On 16 Sep, 00:17, geoff wrote:





In message , Ed Sirett
writes


On Mon, 15 Sep 2008 02:14:50 -0700, Ryan wrote:


On 15 Sep, 09:39, Andy Burns wrote:
On 15/09/2008 09:31, Ryan wrote:


The original plumber has twice promised to come round to fix it and
not turned up either time, and now I can't get hold of him...


So long as you're sure the new problem started at the time the fan was
replaced (rather than being a coincidental issue that started shortly
afterwards) make it clear in writing to the original plumber that if
they don't fix the new problem within a reasonable period of time (7
days?) you will engage someone else to repair it and then pursue the
original plumber for the cost of the remedial work.


Thanks for your post.


The guy fixed the fan in the afternoon, and when I got home in the
evening the hot water wasn't working. *I only had the fan replaced
because it was making a high pitch squeek when warming up, there was
nothing actually wrong with the boiler. *Wish I hadn't bothered.....


I'm not sure writing will do much good, but I'll give it a try. *I
haven't had hot water now for 4 days and I needed it sorted asap...


Anyone got any ideas to exactly what the problem could be?


Sounds like a new fault tome.
Probably the diverter valve, especially as it works OK after you have used
the heating (and thus disturbed the DV).


Yeah - completely different faults


The fan is venting the combustion chamber and doesn't know whether it's
for CH or DHW


Having not mentioned what boiler it is (AFAICS) there is the possibility
that he could have damaged the pcb, but it's very much an outsider and
extremely unlikely


--
geoff- Hide quoted text -


- Show quoted text -


It's a glow worm Compact 80e fanned flue combination boiler. *It looks
like I'm going to have to get someone else to have a look at this
then. *Previous plumber has gone underground. *I take your point that
it is a different fault, but it is a hell of a coincenence. *The least
the guy could have done was check that it was working correctly before
he left...

Thanks for everyones input

Ryan- Hide quoted text -

- Show quoted text -


If anyone is interested, another plumber fixed the problem. It was
caused by bad fitting of the flue, which was causing the boiler to
switch off when running the hot water.

I still haven't got hold of the original plumber, but there isn't much
point now. I would definitely not recommend City Boilers (based SW
London), but seeing as though the phones aren't answered I doubt
anyone will.

Ryan
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combination Boiler or Condensing Boiler Tyler UK diy 12 December 5th 07 10:21 AM
combination boiler neil parcs UK diy 5 July 24th 07 01:50 PM
Combination Boiler SOS muthaleech UK diy 2 February 10th 06 10:45 PM
combination boiler dave UK diy 2 May 17th 05 02:43 PM
Combination boiler question MartinP UK diy 3 October 16th 04 10:43 PM


All times are GMT +1. The time now is 09:19 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"