UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1
Default Something to plug into to prevent the earth leakage outing the RCD

Following a thread on Sagazone (just one funny allowed!) where someone
has a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the
earth leakage outing the RCD"

Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?

The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."

Richard
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,066
Default Something to plug into to prevent the earth leakage outing the RCD

"Dickie mint" wrote in message
...
Following a thread on Sagazone (just one funny allowed!) where someone has
a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the earth
leakage outing the RCD"

Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?

The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."


The usual method of attaching a leaky device is to use an isolating
transformer (the output of which also floats thus halving the voltage to
ground).

--
Bob Mannix
(anti-spam is as easy as 1-2-3 - not)


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Something to plug into to prevent the earth leakage outing theRCD

On Aug 18, 1:35*pm, "Bob Mannix" wrote:
"Dickie mint" wrote in message
...


Following a thread on Sagazone (just one funny allowed!) where someone has
a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the earth
leakage outing the RCD"


Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?


The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."


The usual method of attaching a leaky device is to use an isolating
transformer (the output of which also floats thus halving the voltage to
ground).


It works and it gets rid of the shock risk, mostly, but there is still
capacitive leakage in the transformer and still the possiblity of a
2nd leak on the load which could again expose a shock risk. So yes it
works, but its not best practice.

Iso tranformers aren't 'coming onto the market' they've been around a
century or so.

Finding and fixing the fault would seem a more sensible approach. Only
if fixing wasnt practical and the item were of high value would I ever
consider an alternative protection system involving an iso tf.


NT
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,045
Default Something to plug into to prevent the earth leakage outing theRCD

wrote:
On Aug 18, 1:35 pm, "Bob Mannix" wrote:
"Dickie mint" wrote in message
...


Following a thread on Sagazone (just one funny allowed!) where someone has
a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the earth
leakage outing the RCD"
Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?
The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."

The usual method of attaching a leaky device is to use an isolating
transformer (the output of which also floats thus halving the voltage to
ground).


It works and it gets rid of the shock risk, mostly, but there is still
capacitive leakage in the transformer and still the possiblity of a
2nd leak on the load which could again expose a shock risk. So yes it
works, but its not best practice.

Iso tranformers aren't 'coming onto the market' they've been around a
century or so.

Finding and fixing the fault would seem a more sensible approach. Only
if fixing wasnt practical and the item were of high value would I ever
consider an alternative protection system involving an iso tf.


NT

The trouble is in many cases there is no fault: Just a lot of RFI style
filters and cable capacitance, that, combined with any spike on the
line, has enough surge to blow an RCD.

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,175
Default Something to plug into to prevent the earth leakage outing theRCD

On 18 Aug, 14:59, wrote:

Iso tranformers aren't 'coming onto the market' they've been around a
century or so.


"Century or so" sounds surprisingly long. Just how old is the first
isolating transformer (as a portable device, for the use of portable
appliances) and what was it used for?


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Something to plug into to prevent the earth leakage outing the RCD

In article ,
Dickie mint wrote:
Following a thread on Sagazone (just one funny allowed!) where someone
has a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the
earth leakage outing the RCD"


Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?


The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."


I'd be surprised if this happens in any domestic installation.
For a pro installation they should be suitable radial circuits with likely
loads calculated. Rings are for domestic use where these things (load etc)
vary somewhat - and aren't known at installation time. But so saying most
will use a radial for utility room appliances since these too can cause
problems with RCDs.

--
Small asylum seeker wanted as mud flap, must be flexible and willing to travel

Dave Plowman London SW
To e-mail, change noise into sound.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Something to plug into to prevent the earth leakage outing theRCD

On Aug 18, 3:32*pm, Andy Dingley wrote:
On 18 Aug, 14:59, wrote:


Iso tranformers aren't 'coming onto the market' they've been around a
century or so.


"Century or so" sounds surprisingly long. Just how old is the first
isolating transformer (as a portable device, for the use of portable
appliances) and what was it used for?


Late 1800s IIRC. I think they were first used for mains power
distribution.


NT
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Something to plug into to prevent the earth leakage outing the RCD

In article ,
Dickie mint writes:
Following a thread on Sagazone (just one funny allowed!) where someone
has a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the
earth leakage outing the RCD"

Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?

The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."


Max leakage for a piece of Class I (earthed) IT equipment is 0.75mA
You would need something like 40 pieces of Class I (earthed) IT
equipment to get near 30mA leakage, assuming they all leak the
max permitted. More likely, you have one faulty one.

You should design circuits with a leakage of no more than 25% of
the RCD trip rating. For a 30mA RCD, that's a design leakage of
7.5mA. That's a maximum of 10 Class I (earthed) IT appliances
per RCD. In conventional computer terms, that would be 5 PC base
units and 5 monitors. Some LCD monitors are Class II double
insulated nowadays, and in that case you could get away with 10
PC base units. Most other small computer peripherals are also
Class II double insulated and can be ignored, but larger ones
are often Class I (earthed) and need to be allowed for.

With increasing use of IT/entertainment equipment in the home
and increasing use of RCD protected circuits, provision of more
separately RCD protected socket outlet circuits should be
considered. Hanging them all off one RCD is asking for trouble.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,045
Default Something to plug into to prevent the earth leakage outing theRCD

Andrew Gabriel wrote:
In article ,
Dickie mint writes:
Following a thread on Sagazone (just one funny allowed!) where someone
has a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the
earth leakage outing the RCD"

Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?

The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."


Max leakage for a piece of Class I (earthed) IT equipment is 0.75mA
You would need something like 40 pieces of Class I (earthed) IT
equipment to get near 30mA leakage, assuming they all leak the
max permitted. More likely, you have one faulty one.


Is that DC or AC?

By my reckoning, 10nF of live to earth capacitance will make that figure
at nice clean 50Hz sinewave. Now shove a spike on it with loads of
harmonics..

In a typical house installation there is a huge amount of inter-wire
capacitance. Every RFI filter (mandatory on just about any piece of
electronics including CFL light bulbs) probbaly adds a few nF or more..




You should design circuits with a leakage of no more than 25% of
the RCD trip rating. For a 30mA RCD, that's a design leakage of
7.5mA. That's a maximum of 10 Class I (earthed) IT appliances
per RCD. In conventional computer terms, that would be 5 PC base
units and 5 monitors. Some LCD monitors are Class II double
insulated nowadays, and in that case you could get away with 10
PC base units. Most other small computer peripherals are also
Class II double insulated and can be ignored, but larger ones
are often Class I (earthed) and need to be allowed for.

With increasing use of IT/entertainment equipment in the home
and increasing use of RCD protected circuits, provision of more
separately RCD protected socket outlet circuits should be
considered. Hanging them all off one RCD is asking for trouble.

Oh,indeed.

However one wants that 'last line of defence' of an overall RCD..and
RCBO's are bulky and expensive.

Anyway, my point was that RCD's will trip with no fault as such other
than a lot of RFI capacitors across the mains.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 45
Default Something to plug into to prevent the earth leakage outing theRCD

On Aug 18, 3:04*pm, The Natural Philosopher wrote:
wrote:
On Aug 18, 1:35 pm, "Bob Mannix" wrote:
"Dickie mint" wrote in message
...


Following a thread on Sagazone (just one funny allowed!) where someone has
a ring main RCd trip out when switchong off or pulling the plug on a
computer distribution pattress. their electrician was quoted as saying :-
"there's something coming on the market to plug into to prevent the earth
leakage outing the RCD"
Apart from horrifying me that something might be available to thwart the
very reason for having an RCD, what is he on about?
The same electrician is reported as saying "when he tested the computer
and plug, the computer went to near the end of 30mA."
The usual method of attaching a leaky device is to use an isolating
transformer (the output of which also floats thus halving the voltage to
ground).


It works and it gets rid of the shock risk, mostly, but there is still
capacitive leakage in the transformer and still the possiblity of a
2nd leak on the load which could again expose a shock risk. So yes it
works, but its not best practice.


Iso tranformers aren't 'coming onto the market' they've been around a
century or so.


Finding and fixing the fault would seem a more sensible approach. Only
if fixing wasnt practical and the item were of high value would I ever
consider an alternative protection system involving an iso tf.


NT


The trouble is in many cases there is no fault: Just a lot of RFI style
filters and cable capacitance


dredges up remants of Electrical Engineering course

Ah yes, Capacitive coupling. I always assumed that it was an
inductance that made the earth wire voltage float upwards. Capacitive
makes a lot more sense.

P.



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Something to plug into to prevent the earth leakage outing theRCD

The Natural Philosopher wrote:

Andrew Gabriel wrote:
Max leakage for a piece of Class I (earthed) IT equipment is 0.75mA
You would need something like 40 pieces of Class I (earthed) IT
equipment to get near 30mA leakage, assuming they all leak the
max permitted. More likely, you have one faulty one.


By my reckoning, 10nF of live to earth capacitance will make that figure
at nice clean 50Hz sinewave.


Yes.

Now shove a spike on it with loads of harmonics..


RCDs will ignore spikes of short duration (fast transients). THD on the
mains voltage waveform is typically only 2 or 3%, despite its horrible
flat-topped appearance on a 'scope, and most of it is in low-order
harmonics - mainly 3rd and 5th - so I don't think harmonics are
particularly germane to the subject of RCD nuisance tripping.

In a typical house installation there is a huge amount of inter-wire
capacitance.


It might be huge to an RF engineer, but is hardly likely to be that
significant at 50 Hz. OOI I've just measured the L-E capacitance of a
metre of 2.5 T&E and its about 80 pF (with the neutral wire guarded
out). Call it 100 pF/m. There's probably something like 300 m of cable
in a typical house, so 30 nF total capacitance and about 2 mA leakage -
and that shouldn't all be going via a single RCD.

Every RFI filter [...] including CFL light bulbs) [...]


Bzzt. All CFLs are Class 2. There's no earth connection, and no earth
leakage unless you want to worry about a few nA through the stray
capacitance to earth.

[...] probbaly adds a few nF or more..


Seldom more than 4.7 nF for the Y-capacitors - less than 0.4 mA leakage
per filter

Anyway, my point was that RCD's will trip with no fault as such other
than a lot of RFI capacitors across the mains.


Obviously /in extremis/ that could happen. IME though it doesn't and
nuisance tripping is invariably caused by some sort of fault condition.

I wonder whether any of the electronic RCDs use phase-sensitive
detection and only respond to in-phase leakage?

--
Andy
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
swapping an oven plug for a clothes dryer plug pstock Home Repair 14 October 8th 10 05:54 PM
blade thickness, 13A plug earth pin ? Colin Wilson UK diy 8 January 9th 07 01:04 AM
When bulb blows, earth leakage circuit breaker is tripped MM UK diy 40 December 16th 06 11:22 AM
Rewire oven plug 3 to 4 wire, new home, plug it in and get sparks [email protected] Home Repair 3 August 16th 05 02:51 PM
Cooker appliance earth leakage problem Niels Cook UK diy 10 November 1st 04 02:48 PM


All times are GMT +1. The time now is 05:37 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"