On Aug 2, 2:55*pm, "Dave Plowman (News)" wrote:
In article , * wrote: If it can't achieve the required disconnect time, then it is at best marginal. (and that's just the old 0.4 sec requirement). There is no required disconnect time for existing installations. Required times apply to new wiring. Whether a domestic socket circuit takes 0.45s or 0.35s to fuse makes absolutely blank all difference to real world death rates. And /that/ is whats relevant here, nowt else. One thing with fuses is it's all too easy to fit a larger one to an overloaded circuit - I've seen this many times. Yes FWIW In some cases changing from 5A to 10A can remain withint the cable ratings and be a deliberate upgrade. NT |
#42
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
In article ,
John Rumm writes: John Rumm wrote: Andy Hall wrote: What are the small grey wires at the bottom? Part of the automation system? MK RCBOs have a dedicated earth connection on each device. Not so commonly found on other brands... Sorry, brain fart, make that Mem! (MK and Hager are similar though IIRC) Original MK RCBO's (which I think were made for them by Merlin Gerin) have an earth connection. They use it for detecting L-N swapped, and disconnected N, both of which cause it to trip (and I presume the earth connection must carry the trip solenoid current in the case of disconnected N). Later MK ones also seem to have an earth connection, but don't include any of the extra supervisory features AFAIK. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#43
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
On Aug 2, 6:28*pm, John Rumm wrote:
wrote: On Aug 2, 4:00 am, John Rumm wrote: wrote: On Aug 1, 1:13 am, John Rumm wrote: wrote: Rewirable fuses are still fully compliant for new installation. You'd derive very little safety benefit from adding MCBs. The reason the fuses didnt pop is that any trip device takes a cvertain amount of i times t to blow, and the fault, while it may have looked impressive, didnt draw enough i x t, and the fault blew itself open circuit first. You may have been scared by this, but safetywise its pretty much a non- issue. While this is true, there are two caveats worth mentioning: If the cables are the older style PVC with only a 1mm^2 CPC (modern cable has 1.5mm^2) then it is worth moving away from rewireable fuses since the protection will be marginal or insufficient in many cases. 1mm2 T&E CPC will not have any difficulty at all blowing rewirable fuses. Its a long way from marginal. What can be marginal is its compliance with disconnect times for new wiring regulations - but thats nowhere near enough of an issue to prompt a CU replacment for 99% of the population. If it can't achieve the required disconnect time, then it is at best marginal. (and that's just the old 0.4 sec requirement). There is no required disconnect time for existing installations. Required times apply to new wiring. Whether a domestic socket circuit takes 0.45s or 0.35s to fuse makes absolutely blank all difference to real world death rates. And /that/ is whats relevant here, nowt else. Disconnect times have been specified in the regs for many years. Yes, but there is no requirement for existing installs to meet them. And whats relevant is the real world safety implications. The difference of .1 sec etc may not have a huge impact, however when disconnect times start creeping up into the multiple of seconds then the risks do become more significant (not only due to prolonged exposure to high voltage earthed metalwork, but also that the CPC in the cable will fail, or the cable sustain damage before the fuse operates). As we have both said, the question of whether a BS 3036 semi-enclosed fuse CU should be replaced is a broader question that needs to take account of a number of factors. Compatibility with the installed wiring is one factor. I think the biggest factor is the ratio of safety benefit to expense. Since the safety factor is about zero, and there are mass killers in the average house, twiddling with the fusebox is both pointless and counterproductive. The improving stats for safety of electrical installations in general would seem to disprove that the safety factor is zero, those are due to many factors, so cant prove or disprove anything. The slow disappearance of 1950s and earlier installations is doubtless one factor. also blanket statements about the pros and cons of changing a CU are not really much use since they concentrate on too small a part of the picture. There will be times when swapping out a working BS3036 CU for a modern one will bring no improvement in safety, and there are times when it will bring about a dramatic and significant improvement. yes. If the power (i.e. socket) circuits currently have no RCD protection then again it is worth introducing this, which realistically will also mean a CU swap.. Again, the benefit exists but is so small that only a miniscule percentage of the population would consider it worthwhile to fit the new CU. Almost no-one rewires their house every time a minor safety advance comes along. No, I disagree strongly with this. There is no way you can call a RCD a "minor safety advance". RCD protection makes a significant impact on the survivability of electric shocks, and unlike nonsense like part P, the the use of them has a big impact preventing death and serious injury as a result of (ab)use of hand held appliances (which as we know is a significant number, unlike those attributable to fixed wiring faults). I agree theyre much more significant than fuses/mcbs, but. Twenty something deaths a year, of which some are down to appliance abuse. IIUC the = 20 per year are those attributable to fixed wiring I understand, not the those from appliance abuse. I thought it was total electrocutions, but I dont have a reference to hand. RCDs would indeed stop some of those deaths. But they also encourage people to do things they never would have before, causing more of the This is probably true - but only in a very small subset of cases where the user of the appliance has a good technical appreciation for what the RCD is and does. IME the vast majority of people have little grasp of what is in the CU or what it does, other than there being lots of "little switches" that they need to reset from time to time, and never necessarily even associate the need to reset them with any other event. So I would be very surprised if having a CU with RCDs prefitted is going to influence behaviour for many people. True enough, but I think there's more to it. An illustration we can hopefully all agree on... Decades ago lots of schookids got a shock at some point or another. We all learnt from that how nasty and scary it was, either directly or by seeing how shaken our friend was. That taught people about electricity and changed peoples' behaviour, everyone's. As safety practices advanced, most kids grew up without learning this. Now today its the other way round. Kids muck about, short things out and get a shock, but the RCD trips, and the whole experience is a lot less nasty. The lesson the rest of the kids learn from this is different: if you **** about with it, it'll bite very briefly, and the thingy will trip. That's it. This influence's almost everyone's behaviour, not just those with some understanding of the technicalities. Its one of several reasons why safety innovations so often fail to deliver the benefit that early promoters claim. Then here are the many that put themselvs at risk using RCDs. Typical case: RCD on drill plug. It does nothing to protec the user from drilling into a live wire. Nothing at all, but they think it does so are a lot less careful. (you only need look at the group of accidents that occur with extension leads in the garden - its not usually mowing over it that causes the shock, its the dopey pillock picking up the severed ends to look at them!) situations, and they cause loss of sair lighting, loss of lighting in fires etc, which we know kills people. So the real world safety cost or benefit is anything but clear. We simply don't have the figures yet. Well this has been known about for some time (most of the reign of the 16th edition) and remedies put in place to address the problem. What remedies have you in mind? AIUI the 17th's requirement for RCDs on all circuits has merely ensured these safety problems will apply to every house newly wired. But once again... if you want to save lives in the home, there are much greater results to be had by spending much less on the real risk issues. Again, it depends on circumstances. In situations where students are likely to overload circuits in their lodging house, and replace fuses with tinfoil etc, or where there are lots of ankle biters roaming about trying to push bits of metal into sockets to see what happens, you have a real risk that needs addressing as a mater of urgency. In both cases there are much bigger risks. If you look up the death rates you'll immediately see that. Kids have been putting things in sockets for over half a decade, but the resultant deaths are few. The big risks to them lie elsewhere. The deaths from heart disease and cancer are several orders of magnitude larger, and we know that what kids do does affect their later life outcomes - just for one example. In other cases where a couple of adults share a flat, never need to mow a lawn, and do nothing more exotic than plug in the TV and the phone charger there is relatively little risk with 3036 fuses and no RCD. Its not that bad. There are many millions of houses with rewirables and no RCD, and the electrocution death rate is tiny. For various reasons a sense of proportion is too often missing from safety discussions. NT |
#44
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
On Aug 2, 9:03*am, Terry Fields wrote:
Are any figures available that show injury and/or deaths rates are less under the new regime (in this case an RCD CU) than the old (a fused CU)? A casual reading of the group suggests that there are a number potential benefits from the technical advances in going from the former to the other latter - but how does it work out in practice? AFAIK the data isnt collected. NT |
#46
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
Andrew Gabriel wrote:
Original MK RCBO's (which I think were made for them by Merlin Gerin) have an earth connection. They use it for detecting L-N swapped, and disconnected N, both of which Interesting point, but I would expect you need quite an inventive solution to swap L&N on most CUs given the nature of the live connection to the device... (still I suppose it is easy enough to swap them at the tails on the way in) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#47
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
John Rumm wrote: Terry Fields wrote: Are any figures available that show injury and/or deaths rates are less under the new regime (in this case an RCD CU) than the old (a fused CU)? Its a good question, and I don't know how easy it would be to get figures in the exact form required... Until recently[1] deaths from electrocution have fallen year on year in absolute terms for quite a number of years, even though usage of appliances has risen. This won't be attributable to just one improvement in safety, but a collective effect of which RCDs have been a part quite a number of years now. [1] In the last couple of years this trend seems to be showing signs of reversing - strangely coincident with the introduction of Part P That was my impression too, based on comments on the ng; but I was wondering if any officcial figures were available. It seems to be common for 'the authorities' to set a policy (i.e Part P) but to fail to put in to place any monitoring of the effects of that policy. Perhaps it's a question of 'if you don't want to know the answer, then don't ask the question'. A casual reading of the group suggests that there are a number potential benefits from the technical advances in going from the former to the other latter - but how does it work out in practice? Not sure I follow the question - do you mean what will be the change in user experience? or the actual process of making the change? It was just a convoluted way of trying to link the technicalities such as the release time for an RCD, or better earthing arrangements, with reduction or otherwise in casualties, but if there's no figures collected, then there's no way to link the cause with the effect. It all seems to run on a 'feel-good' factor. |
#48
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
|
#49
Posted to uk.d-i-y
|
|||
|
|||
Replacing a fused CU ?
Terry Fields wrote:
John Rumm wrote: Terry Fields wrote: Are any figures available that show injury and/or deaths rates are less under the new regime (in this case an RCD CU) than the old (a fused CU)? Its a good question, and I don't know how easy it would be to get figures in the exact form required... Until recently[1] deaths from electrocution have fallen year on year in absolute terms for quite a number of years, even though usage of appliances has risen. This won't be attributable to just one improvement in safety, but a collective effect of which RCDs have been a part quite a number of years now. [1] In the last couple of years this trend seems to be showing signs of reversing - strangely coincident with the introduction of Part P That was my impression too, based on comments on the ng; but I was wondering if any officcial figures were available. It seems to be common for 'the authorities' to set a policy (i.e Part P) but to fail to put in to place any monitoring of the effects of that policy. Perhaps it's a question of 'if you don't want to know the answer, then don't ask the question'. IIRC there was a question asked in the house recently on the apparent rise coincident with part P. A search of Hansard will probably turn up something. A casual reading of the group suggests that there are a number potential benefits from the technical advances in going from the former to the other latter - but how does it work out in practice? Not sure I follow the question - do you mean what will be the change in user experience? or the actual process of making the change? It was just a convoluted way of trying to link the technicalities such as the release time for an RCD, or better earthing arrangements, with reduction or otherwise in casualties, but if there's no figures collected, then there's no way to link the cause with the effect. It all seems to run on a 'feel-good' factor. There are figures available and well documented for the effects of shock and the implications of shock current and duration of exposu http://www.memonline.com/rcd3.html So RCD protection offers very much more than a "feel good factor" - unless you include the ability to breathe and absence of ventricular fibrillation as "feel good" ;-) Note also RCDs are used not only to lessen shock risks, but also as a earth fault protection mechanism. A TT install with a 6 ohms fault loop impedance could end up sinking 40A for an extended period of time into a protective conductor without tripping a typical 32A MCB on a power circuit. This would (in the absence of the RCD) result in at best cable damage, and possibly fire. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |