Guys

Posting from sunny New Zealand. Getting a spa pool delivered soon and
just had wiring done.

Specs say it needs 32amp. It has 2 pumps rated at 2.25KW each. A
blower at 700w and a circ pump at 0.25 kw. Reckon that should be
everything if all switched on at same time...

Importer who sold it to me said his was running on a 40amp MCB and 6mm
square cable....Sparkie who just did a homer used 4mm square cable
instead saying it was ample. Two core and earth - PVC sheathed.

Cable run is 23 metres from fuse to outside switch to spa.... Will
4mm cable be sufficient? Suffice to say my experience of some of the
building codes etc here is they stretch the specs somewhat more than
when I lived in the UK.

Thanks for your input.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3
Default Cable size adn MCB size for Spa pool

Sorry.....Also has a 3 KW heater..
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 278
Default Cable size adn MCB size for Spa pool

On Jun 14, 6:50*am, GC wrote:
Sorry.....Also has a 3 KW heater..


Are you on 230V there?

Your total load is 8.45kW which is 36.74 amps. You would need 6mm
cable to meet the minimum voltage drop requirement here in the UK.

But - having said all that, I don't think you have listed the specs
correctly. Are you sure it really has two pumps rated at 2.25kW each?
That seems excessive to say the least - are you sure it doesn't have
two *heaters* rated at 2.25kW each? That seems more likely...

Assuming the extra 3kW you added on there at the end is a mistake,
your total load would be 5.45kW which is 23.7A which would be fine
with 4mm cable over 27M

Steve

Steve
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3
Default Cable size adn MCB size for Spa pool

On Jun 14, 8:33*pm, stevelup wrote:
On Jun 14, 6:50*am, GC wrote:

Sorry.....Also has a 3 KW heater..


Are you on 230V there?

Your total load is 8.45kW which is 36.74 amps. You would need 6mm
cable to meet the minimum voltage drop requirement here in the UK.

But - having said all that, I don't think you have listed the specs
correctly. Are you sure it really has two pumps rated at 2.25kW each?
That seems excessive to say the least - are you sure it doesn't have
two *heaters* rated at 2.25kW each? That seems more likely...

Assuming the extra 3kW you added on there at the end is a mistake,
your total load would be 5.45kW which is 23.7A which would be fine
with 4mm cable over 27M

Steve

Steve


Hi Steve

Thanks for your reply...Yep..The supply is 230V / 50 Hz give or
take... Rechecked the specs - Pump 1 - 2.25Kw, Pump 2 - 2.25Kw, Blower
for Air Jets - 700w, Circulation Pump - 250 W and heater - 3Kw...

Now from further research I don't ' think' you run the 2 pumps AND the
air jet pump at the same time...Its one or the other...

But yes, definintely 2 main pumps rated at 2.25Kw each...It seats upto
8 people...A big beast of a spa...

Cable run is 23 to 25 metres max..Into an IP56 rated switch and out
into the Spa connection. The total length quoted includes the 2 metres
on the spa side of the switch. So roughly 22 metres from fusebox to
switch and a couple from switch to spa..

Am I correct in thinking that the 4mm is being pushed to its max...It
is generally clipped to top of joists in loft space, and run down
plastic trunking inside a cupboard before exiting the building into
the switch.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 278
Default Cable size adn MCB size for Spa pool

On Jun 14, 12:14*pm, GC wrote:
On Jun 14, 8:33*pm, stevelup wrote:



On Jun 14, 6:50*am, GC wrote:


Sorry.....Also has a 3 KW heater..


Are you on 230V there?


Your total load is 8.45kW which is 36.74 amps. You would need 6mm
cable to meet the minimum voltage drop requirement here in the UK.


But - having said all that, I don't think you have listed the specs
correctly. Are you sure it really has two pumps rated at 2.25kW each?
That seems excessive to say the least - are you sure it doesn't have
two *heaters* rated at 2.25kW each? That seems more likely...


Assuming the extra 3kW you added on there at the end is a mistake,
your total load would be 5.45kW which is 23.7A which would be fine
with 4mm cable over 27M


Steve


Steve


Hi Steve

Thanks for your reply...Yep..The supply is 230V / 50 Hz give or
take... Rechecked the specs - Pump 1 - 2.25Kw, Pump 2 - 2.25Kw, Blower
for Air Jets - 700w, Circulation Pump - 250 W and heater - 3Kw...

Now from further research I don't ' think' you run the 2 pumps AND the
air jet pump at the same time...Its one or the other...

But yes, definintely 2 main pumps rated at 2.25Kw each...It seats upto
8 people...A big beast of a spa...


I don't understand the manufacturers rating then - they quote 32A
supply required yet it is going to draw almost 37A. It looks like the
advice your importer gave was correct rather than the manufacturers
information.

Cable run is 23 to 25 metres max..Into an IP56 rated switch and out
into the Spa connection. The total length quoted includes the 2 metres
on the spa side of the switch. So roughly 22 metres from fusebox to
switch and a couple from switch to spa..

Am I correct in thinking that the 4mm is being pushed to its max...It
is generally clipped to top of joists in loft space, and run down
plastic trunking inside a cupboard before exiting the building into
the switch.


It's outside of regulations here in the UK. The voltage drop would be
too great over that length on a 40A MCB. The regulations may differ
where you are and that may be why your electrician is saying 4mm is
OK.

You could ask him for his calculations - ie. on what basis is he
asserting that 4mm is adequate.

Steve


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 203
Default Cable size adn MCB size for Spa pool

4mm flat twin & earth if 1.5mm CPC also imposes EFLI limits.
Type-B CPD 32A is 1.20ohm max EFLI, 40A is 0.96ohm. So
as well as current limitations your house supply type (Ze)
combined with 23m in 4mm (R1+R2) may push EFLI over spec.

Cable technically needs derating for the run in trunking (which
is installation method 3 in the UK or about 12.5%). Some may
not bother if the run is very short. I assume the cable is not
*surrounded* in insulation anywhere (which if 500mm needs
a derating of 50% so your 4mm would be quite unsuitable).

Spark may have applied diversity calculations to the loading.
So just query him on the calculations and actual design, he
should be happy to provide as it justifies his skills/charge.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 671
Default Cable size adn MCB size for Spa pool

GC wrote:
Guys

Posting from sunny New Zealand. Getting a spa pool delivered soon and
just had wiring done.

Specs say it needs 32amp. It has 2 pumps rated at 2.25KW each. A
blower at 700w and a circ pump at 0.25 kw. Reckon that should be
everything if all switched on at same time...

Importer who sold it to me said his was running on a 40amp MCB and 6mm
square cable....Sparkie who just did a homer used 4mm square cable
instead saying it was ample. Two core and earth - PVC sheathed.


That's the optional underpatio heating version.... )


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,447
Default Cable size adn MCB size for Spa pool

On Jun 14, 7:11*pm, "Steve Walker" wrote:
GC wrote:
Guys


Posting from sunny New Zealand. Getting a spa pool delivered soon and
just had wiring done.


Specs say it needs 32amp. It has 2 pumps rated at 2.25KW each. *A
blower at 700w and a circ pump at 0.25 kw. Reckon that should be
everything if all switched on at same time...


Importer who sold it to me said his was running on a 40amp MCB and 6mm
square cable....Sparkie who just did a homer used 4mm square cable
instead saying it was ample. Two core and earth - PVC sheathed.


That's the optional underpatio heating version.... *)


Voltage not mentioned but assuming it's 230 volts? Single phase?
Using some North American design tables for the wire gauge closest to
4mm diam. it looks like voltage drop (with everything on) will be
about 2% or roughly 5 volts. Wire length being twice 23 metres
(roughly 140 feet).
However a 40 amp breaker seems to be 'close to the wire' (pun
intended!).
Cos if you add up all the normal running wattages, ignoring start up
surges of pump motors and also that heaters until warmed up draw more
current one gets something of the order of 8.5 kilowatts? That's
around 37 amps!!!!
So if a 50 amp breaker then needed, to avoid trip outs, it may be
necessary to comply with local wiring/insurance codes to use another
(heavier gauge) of wire?
Seems wise that you are checking. Not sure what's the legal or
insurance liability outcome of knowingly installing inadequate wiring,
to local code, would be, in your part of the world.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 278
Default Cable size adn MCB size for Spa pool

On Jun 15, 3:22*am, terry wrote:
That's
around 37 amps!!!!
So if a 50 amp breaker then needed, to avoid trip outs,


Not sure I understand this bit. A 40A breaker will run a 40A load
indefinitely without tripping.

I don't think there is an issue with the breaker rating but the cable
would certainly under rated at 4mm according to UK regs.



  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Cable size adn MCB size for Spa pool

terry wrote:

Voltage not mentioned but assuming it's 230 volts? Single phase?
Using some North American design tables for the wire gauge closest to
4mm diam. it looks like voltage drop (with everything on) will be


Note we are assuming the OP means 4mm^2 cross section area and not 4mm
diameter wire here. The latter would be in excess of our 6mm^2 cable.

Perhaps comparison with the outside dimensions listed here might help:

http://wiki.diyfaq.org.uk/index.php?...n_Mains_Cables

However a 40 amp breaker seems to be 'close to the wire' (pun
intended!).
Cos if you add up all the normal running wattages, ignoring start up
surges of pump motors and also that heaters until warmed up draw more
current one gets something of the order of 8.5 kilowatts? That's
around 37 amps!!!!


Using the type of breaker we traditionally do, this would not usually be
considered a problem. It may be normal to specify a type C MCB to cope
with the motor inrush currents however.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Swimming pool filter size help. Wes Home Repair 3 August 10th 06 03:59 AM
pool filter size? [email protected] Home Repair 4 June 8th 06 09:14 PM
Pool Filter Wiring Size Ron in NY Home Repair 1 June 28th 05 01:02 AM
nano size laser weld spot size for stainless steel sheets Venky Metalworking 3 February 7th 05 04:25 PM
Cable Size Help Please xavier UK diy 5 October 13th 04 04:43 PM


All times are GMT +1. The time now is 02:59 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"