Hi,
I've moved into a house where the primary hot water supply is a gas
boiler and hot water tank. However, there is also an ensuite in the
attic that is supplied by an Ariston Classico unvented electric
immersion heater (model STD 125). The tank has 2 immersion heaters,
one at the bottom and one at the top and according to the manual, the
bottom one is for night time and the top one for a day time top up. I
understand this is typically for use with Economy 7 tariff. Each
immersion heater is wired to a separate mains switch.

The previous owner told us that in order to get hot water we should
turn on both immersion heaters for a few hours. This all works fine,
however, it is not that convenient to turn the water on an off
manually each day. Is it advisable to put a timer switch that will
turn on both heaters for a couple of hours each morning? Or separate
timer switches for the two heaters?

Any advice on a simple setup would be much appreciated. btw, we're
not on economy 7.

Thanks and regards,

Simon
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 30
Default Electric immersion water heater - timer question

wrote:
Hi,
I've moved into a house where the primary hot water supply is a gas
boiler and hot water tank. However, there is also an ensuite in the
attic that is supplied by an Ariston Classico unvented electric
immersion heater (model STD 125). The tank has 2 immersion heaters,
one at the bottom and one at the top and according to the manual, the
bottom one is for night time and the top one for a day time top up. I
understand this is typically for use with Economy 7 tariff. Each
immersion heater is wired to a separate mains switch.

The previous owner told us that in order to get hot water we should
turn on both immersion heaters for a few hours. This all works fine,
however, it is not that convenient to turn the water on an off
manually each day. Is it advisable to put a timer switch that will
turn on both heaters for a couple of hours each morning? Or separate
timer switches for the two heaters?

Any advice on a simple setup would be much appreciated. btw, we're
not on economy 7.

Thanks and regards,

Simon


Immersion heater timers are generally hard-wired downstream of the switch.

You will most likely need one timer per immersion heater, because the
timer will not be rated to switch the power of two heating elements.

In a couple of hours, the lower heater should heat your tank on its own
I would have thought, so you may wish to put the lower heater on a
regular timer and have a 1 hour boost timer (e.g. Horstmann E30.) for
the top heater,

http://www.tlc-direct.co.uk/Main_Ind...red/index.html

http://www.horstmann.co.uk/water-heating.asp

http://www.heatingcontrolsonline.co....rols-c-27.html
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default Electric immersion water heater - timer question

Many thanks for that - makes sense. I'll probably put a timer switch
on each, have the night one come on for a couple of hours and then the
day one come on for 15 mins in the morning before i use the shower.

Cheers,

Simon

On 8 Jan, 10:05, Rumble wrote:
wrote:
Hi,
I've moved into a house where the primary hot water supply is a gas
boiler and hot water tank. However, there is also an ensuite in the
attic that is supplied by an Ariston Classico unvented electric
immersion heater (model STD 125). The tank has 2 immersion heaters,
one at the bottom and one at the top and according to the manual, the
bottom one is for night time and the top one for a day time top up. I
understand this is typically for use with Economy 7 tariff. Each
immersion heater is wired to a separate mains switch.


The previous owner told us that in order to get hot water we should
turn on both immersion heaters for a few hours. This all works fine,
however, it is not that convenient to turn the water on an off
manually each day. Is it advisable to put a timer switch that will
turn on both heaters for a couple of hours each morning? Or separate
timer switches for the two heaters?


Any advice on a simple setup would be much appreciated. btw, we're
not on economy 7.


Thanks and regards,


Simon


Immersion heater timers are generally hard-wired downstream of the switch.

You will most likely need one timer per immersion heater, because the
timer will not be rated to switch the power of two heating elements.

In a couple of hours, the lower heater should heat your tank on its own
I would have thought, so you may wish to put the lower heater on a
regular timer and have a 1 hour boost timer (e.g. Horstmann E30.) for
the top heater,

http://www.tlc-direct.co.uk/Main_Ind...dex/Timers_Wir...

http://www.horstmann.co.uk/water-heating.asp

http://www.heatingcontrolsonline.co....-controls-c-27...


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default Electric immersion water heater - timer question

On Tue, 8 Jan 2008 01:36:00 -0800 (PST) someone who may be
wrote this:-

However, there is also an ensuite in the
attic that is supplied by an Ariston Classico unvented electric
immersion heater (model STD 125). The tank has 2 immersion heaters,
one at the bottom and one at the top and according to the manual, the
bottom one is for night time and the top one for a day time top up. I
understand this is typically for use with Economy 7 tariff. Each
immersion heater is wired to a separate mains switch.


That is the case. The bottom one would come on automatically at
off-peak periods to warm the whole cylinder. The (expensive) top one
would be switched on as necessary to top up the cylinder
temperature.

The previous owner told us that in order to get hot water we should
turn on both immersion heaters for a few hours.


The top one should be adequate to heat enough water for a shower and
general washing. If it isn't then perhaps you spend too long in the
shower and are using as much water as a bath would:-)

Is it advisable to put a timer switch that will
turn on both heaters for a couple of hours each morning? Or separate
timer switches for the two heaters?


Personally, as a first stage, I would put a timer on the top
immersion heater. Models are available which replace an existing
switch. I would ignore the bottom heater. This can be set depending
on usage, for example on all day or on twice a day as appropriate.

After that I would consider the options. Why does the en-suite have
a separate storage system as opposed to being connected to the main
storage? Unless there are long pipe runs due to a badly designed
room layout few houses are big enough to warrant more than one
source of hot water.

Depending on the answer to this there would be many options for a
more permanent solution, depending on inclination and circumstances.

One idea that might fit some situations is to fit a retrofit heater
battery in place of the lower immersion heater. This could take hot
water from the boiler or a solar panel. Such heaters are not ideal
due to their low surface area, but they avoid the disruption of a
new cylinder.

Any advice on a simple setup would be much appreciated. btw, we're
not on economy 7.


Then heating up the whole cylinder with the bottom immersion heater
will be expensive. I would avoid using it.




--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default Electric immersion water heater - timer question

That's really useful - thanks very much. This looks like a simple
replacement for the switch on the top heater:

http://www.tlc-direct.co.uk/Products/TCGP24.html

I agree about the need for a second boiler for the ensuite - I don't
know why they went down that route. We moved from a flat that had a
basic combi boiler for heating and HW to this house with a hot water
tank, cold water tank and a second immersion heater etc. Before we
actually moved in we thought we'd replace it all with a combi boiler,
however, it all works really well and has been carefully maintained
and serviced - so for now we're going to change as little as possible!

Many thanks,

Simon

On 8 Jan, 13:16, David Hansen wrote:
On Tue, 8 Jan 2008 01:36:00 -0800 (PST) someone who may be
wrote this:-

However, there is also an ensuite in the
attic that is supplied by an Ariston Classico unvented electric
immersion heater (model STD 125). The tank has 2 immersion heaters,
one at the bottom and one at the top and according to the manual, the
bottom one is for night time and the top one for a day time top up. I
understand this is typically for use with Economy 7 tariff. Each
immersion heater is wired to a separate mains switch.


That is the case. The bottom one would come on automatically at
off-peak periods to warm the whole cylinder. The (expensive) top one
would be switched on as necessary to top up the cylinder
temperature.

The previous owner told us that in order to get hot water we should
turn on both immersion heaters for a few hours.


The top one should be adequate to heat enough water for a shower and
general washing. If it isn't then perhaps you spend too long in the
shower and are using as much water as a bath would:-)

Is it advisable to put a timer switch that will
turn on both heaters for a couple of hours each morning? Or separate
timer switches for the two heaters?


Personally, as a first stage, I would put a timer on the top
immersion heater. Models are available which replace an existing
switch. I would ignore the bottom heater. This can be set depending
on usage, for example on all day or on twice a day as appropriate.

After that I would consider the options. Why does the en-suite have
a separate storage system as opposed to being connected to the main
storage? Unless there are long pipe runs due to a badly designed
room layout few houses are big enough to warrant more than one
source of hot water.

Depending on the answer to this there would be many options for a
more permanent solution, depending on inclination and circumstances.

One idea that might fit some situations is to fit a retrofit heater
battery in place of the lower immersion heater. This could take hot
water from the boiler or a solar panel. Such heaters are not ideal
due to their low surface area, but they avoid the disruption of a
new cylinder.

Any advice on a simple setup would be much appreciated. btw, we're
not on economy 7.


Then heating up the whole cylinder with the bottom immersion heater
will be expensive. I would avoid using it.

--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default Electric immersion water heater - timer question

On Tue, 8 Jan 2008 06:13:24 -0800 (PST) someone who may be
wrote this:-

That's really useful - thanks very much. This looks like a simple
replacement for the switch on the top heater:

http://www.tlc-direct.co.uk/Products/TCGP24.html

My only concern would be whether the clock has double pole contacts
with a separation of at least 3mm. If not then a separate switch
should be provided to isolate the heater. This can often be done by
placing the clock in the kitchen, where there is often a second
switch controlling top-up and leaving the switch by the heater
alone. This may not be possible in your case, in which case I would
probably install the clock as a replacement for the existing switch
and mount it alongside with a little new cable to link the two.

I agree about the need for a second boiler for the ensuite - I don't
know why they went down that route. We moved from a flat that had a
basic combi boiler for heating and HW to this house with a hot water
tank, cold water tank and a second immersion heater etc. Before we
actually moved in we thought we'd replace it all with a combi boiler,


Why? They can have advantages in small flats, but have few
advantages in larger places.

however, it all works really well and has been carefully maintained
and serviced - so for now we're going to change as little as possible!


Then I would just consider a replacement heater battery for the
lower immersion heater, in order to reduce electricity bills.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default Electric immersion water heater - timer question

Thanks again. So there's a timer switch, then an isolating switch
(i.e. the existing switch) and then the heater? Just looking at the
guide for the appliance and that seems to be what they suggest also.

Regarding combi boilers - that was just our lack of experience - we're
much happier with what we have now. Offtopic - when our boiler
eventually dies, can we basically keep this system and get a
replacement boiler (presumably condensing?)

Cheers,

Simon

On 8 Jan, 14:27, David Hansen wrote:
On Tue, 8 Jan 2008 06:13:24 -0800 (PST) someone who may be
wrote this:-

That's really useful - thanks very much. This looks like a simple
replacement for the switch on the top heater:


http://www.tlc-direct.co.uk/Products/TCGP24.html


My only concern would be whether the clock has double pole contacts
with a separation of at least 3mm. If not then a separate switch
should be provided to isolate the heater. This can often be done by
placing the clock in the kitchen, where there is often a second
switch controlling top-up and leaving the switch by the heater
alone. This may not be possible in your case, in which case I would
probably install the clock as a replacement for the existing switch
and mount it alongside with a little new cable to link the two.

I agree about the need for a second boiler for the ensuite - I don't
know why they went down that route. We moved from a flat that had a
basic combi boiler for heating and HW to this house with a hot water
tank, cold water tank and a second immersion heater etc. Before we
actually moved in we thought we'd replace it all with a combi boiler,


Why? They can have advantages in small flats, but have few
advantages in larger places.

however, it all works really well and has been carefully maintained
and serviced - so for now we're going to change as little as possible!


Then I would just consider a replacement heater battery for the
lower immersion heater, in order to reduce electricity bills.

--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default Electric immersion water heater - timer question

Thanks for all the advice - much appreciated.

On 8 Jan, 17:57, David Hansen wrote:
On Tue, 8 Jan 2008 06:47:55 -0800 (PST) someone who may be
wrote this:-

So there's a timer switch, then an isolating switch
(i.e. the existing switch) and then the heater?


That's what I would do, with the timeclock where the current switch
is and a new short length of suitable cable between the two.

That assumes the existing cable cannot be pulled out enough to
install the clock without disturbing the switch.

Regarding combi boilers - that was just our lack of experience - we're
much happier with what we have now. Offtopic - when our boiler
eventually dies, can we basically keep this system and get a
replacement boiler (presumably condensing?)


Yes. However, I would use the upheaval as an excuse for modifying
the system along the lines I have suggested. I would also go for a
heater battery replacing the lower immersion heater, perhaps in the
spring.http://www.navitron.org.uk/pricelist.htmdoes one for £105,
though it would also need controls and pipework to the existing
system.

--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Immersion heater timer billy1 UK diy 2 June 5th 07 06:44 PM
kingshield 7 day immersion heater timer kay Home Repair 1 July 25th 06 10:03 PM
Immersion Heater Timer wiring. Uno Hoo! UK diy 9 September 16th 05 09:39 PM
Wiring Immersion Heater Timer Ken Knott UK diy 15 September 13th 04 01:42 PM
Wiring an Immersion Heater Timer Nathan UK diy 4 December 5th 03 10:23 AM


All times are GMT +1. The time now is 11:15 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"