Wondering if anyone has had any experience with this...

As per normal, I have my grid power entering my house, this then goes
through a 80A fuse that belongs to the electricity board, it then continues
to my electricity meter, and then onto my consumer unit...

The thing is, I want to disconnect the tails that come from my meter, and
connect them to a generator transfer switch - this then connects back to my
consumer unit, and also to a generator.

The options I have are..

Do it live - not a clever idea, especially as my consumer unit has a metal
back!

Pull the electricity boards fuse out, move it, and replace the fuse (minus
the metal tag/seal)

Call the electricity board, and see what extortionate rate they will charge
me..

I have however read about someone calling the electricity board up, and them
saying, "just pull the fuse, ring us when you are done, and we will send
someone out to check the installation, and replace the fuse and seal it up
again"

Any advise would be greatly appreciated!!

Sparks...


  #2   Report Post  
BigWallop
 
Posts: n/a
Default Playing with meter tails


"Sparks" wrote in message ...
Wondering if anyone has had any experience with this...

As per normal, I have my grid power entering my house, this then goes
through a 80A fuse that belongs to the electricity board, it then

continues
to my electricity meter, and then onto my consumer unit...

The thing is, I want to disconnect the tails that come from my meter, and
connect them to a generator transfer switch - this then connects back to

my
consumer unit, and also to a generator.

The options I have are..

Do it live - not a clever idea, especially as my consumer unit has a metal
back!

Pull the electricity boards fuse out, move it, and replace the fuse (minus
the metal tag/seal)

Call the electricity board, and see what extortionate rate they will

charge
me..

I have however read about someone calling the electricity board up, and

them
saying, "just pull the fuse, ring us when you are done, and we will send
someone out to check the installation, and replace the fuse and seal it up
again"

Any advise would be greatly appreciated!!

Sparks...



I go with pulling the fuse and then having it sealed again. Job's done.

The thing that's getting me though, is the fact that your tapping in to the
mains tails. Why ? Can't you take the bridge from the BUS bar side of the
mains switch in the CU ? Doing it this way gives you at least some sort of
isolation if you have to carry out any maintenance on the new system.


---
www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.521 / Virus Database: 319 - Release Date: 23/09/03


  #3   Report Post  
Sparks
 
Posts: n/a
Default Playing with meter tails

I go with pulling the fuse and then having it sealed again. Job's done.

So do you think I just do it, and plead ignorance if the missing/broken seal
is spotted
or do I call the electricity company and ask them (slightly harder to
subsequently plead ignorance after that!)

Another thing, is we had the meter changed about a year ago, so all the
seals are new :-/


The thing that's getting me though, is the fact that your tapping in to

the
mains tails. Why ? Can't you take the bridge from the BUS bar side of

the
mains switch in the CU ? Doing it this way gives you at least some sort

of
isolation if you have to carry out any maintenance on the new system.



In my CU, the meter tails go directly into the main breaker, (there is no
simple switch) and then two wire connect from this same point to the other
lighting breaker.

On the other side of both breakers, there is a copper bar that feeds all the
mcb's for both circuits - this way, if the main power breaker trips, we are
not left in the dark
Probably standard practice, but as I have never looked inside another split
load box before, I can't comment!

I want my generator connected before both of these breakers, and to both
circuits (so we can use the lights, and the sockets!)

I was actually going to purchase a 100A isolator, and connect the meter
tails to this, then on to the transfer switch, for the reason you suggest
;-)
....and possible upgrade to an automatic system later.

Apparently some people have an electricity board provided isolator between
their meter, and their CU - I am not that lucky :-s

Sparks...


  #4   Report Post  
BigWallop
 
Posts: n/a
Default Playing with meter tails


"Sparks" wrote in message ...
I go with pulling the fuse and then having it sealed again. Job's done.


So do you think I just do it, and plead ignorance if the missing/broken

seal
is spotted
or do I call the electricity company and ask them (slightly harder to
subsequently plead ignorance after that!)

Another thing, is we had the meter changed about a year ago, so all the
seals are new :-/


The thing that's getting me though, is the fact that your tapping in to

the
mains tails. Why ? Can't you take the bridge from the BUS bar side of

the
mains switch in the CU ? Doing it this way gives you at least some sort

of
isolation if you have to carry out any maintenance on the new system.



In my CU, the meter tails go directly into the main breaker, (there is no
simple switch) and then two wire connect from this same point to the other
lighting breaker.

On the other side of both breakers, there is a copper bar that feeds all

the
mcb's for both circuits - this way, if the main power breaker trips, we

are
not left in the dark
Probably standard practice, but as I have never looked inside another

split
load box before, I can't comment!

I want my generator connected before both of these breakers, and to both
circuits (so we can use the lights, and the sockets!)

I was actually going to purchase a 100A isolator, and connect the meter
tails to this, then on to the transfer switch, for the reason you suggest
;-)
...and possible upgrade to an automatic system later.

Apparently some people have an electricity board provided isolator between
their meter, and their CU - I am not that lucky :-s

Sparks...



Woa up there horsey !!! A generator doesn't have neutral potential on it.
Both connections become live feeds and if it is to take over supplying the
house in the event of a power cut, then you'll need to upgrade the earthing
and take only a single phase from the genny, to feed the house.

It works by making the grounding spike in to your neutral potential. Very
dangerous if not done properly. Not to mention the fact that, if the mains
supply then comes back on while the genny is running, then it could blow
every fuse you have in the house and may even trip out at the local sub
station if it is a large capacity generator.

I originally thought that you had automatic change over, to bring the genny
online when the mains failed. But you say "possible upgrade to an automatic
system later". That's a big NO NO !!!!!


---
www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.521 / Virus Database: 319 - Release Date: 23/09/03


  #5   Report Post  
Sparks
 
Posts: n/a
Default Playing with meter tails

Woa up there horsey !!! A generator doesn't have neutral potential on it.
Both connections become live feeds and if it is to take over supplying the
house in the event of a power cut, then you'll need to upgrade the

earthing
and take only a single phase from the genny, to feed the house.

It works by making the grounding spike in to your neutral potential. Very
dangerous if not done properly. Not to mention the fact that, if the

mains
supply then comes back on while the genny is running, then it could blow
every fuse you have in the house and may even trip out at the local sub
station if it is a large capacity generator.

I originally thought that you had automatic change over, to bring the

genny
online when the mains failed. But you say "possible upgrade to an

automatic
system later". That's a big NO NO !!!!!


FYI A proper automatic transfer switch makes it impossible for both grid and
generator feed to get connected together!

Generally speaking, with a non synchronised genset, the grid fails, so the
ATS disconnects all power to the house, starts the generator, waits for the
generator to stabilise, then switched the house from nothing, to generator
power
If the grid is then restored, it will wait a bit, to make sure the grid is
staying on, then it disconnects the house, waits a bit, then switches over
to the grid (If the grid and genset are not synced then switching directly
would be messy!)

It then keeps the generator running for a bit, then finally shuts it off

I understand where you are coming from, as I wouldn't want to try to supply
power to my whole road! or kill someone working on the street wiring by back
feeding (I presume a step-down transformer would work in reverse, ramping my
230v up to 1000's!)




  #6   Report Post  
BigWallop
 
Posts: n/a
Default Playing with meter tails


"Sparks" wrote in message ...
Woa up there horsey !!! A generator doesn't have neutral potential on

it.
Both connections become live feeds and if it is to take over supplying

the
house in the event of a power cut, then you'll need to upgrade the

earthing
and take only a single phase from the genny, to feed the house.

It works by making the grounding spike in to your neutral potential.

Very
dangerous if not done properly. Not to mention the fact that, if the

mains
supply then comes back on while the genny is running, then it could blow
every fuse you have in the house and may even trip out at the local sub
station if it is a large capacity generator.

I originally thought that you had automatic change over, to bring the

genny
online when the mains failed. But you say "possible upgrade to an

automatic
system later". That's a big NO NO !!!!!


FYI A proper automatic transfer switch makes it impossible for both grid

and
generator feed to get connected together!

Generally speaking, with a non synchronised genset, the grid fails, so the
ATS disconnects all power to the house, starts the generator, waits for

the
generator to stabilise, then switched the house from nothing, to generator
power
If the grid is then restored, it will wait a bit, to make sure the grid is
staying on, then it disconnects the house, waits a bit, then switches over
to the grid (If the grid and genset are not synced then switching directly
would be messy!)

It then keeps the generator running for a bit, then finally shuts it off

I understand where you are coming from, as I wouldn't want to try to

supply
power to my whole road! or kill someone working on the street wiring by

back
feeding (I presume a step-down transformer would work in reverse, ramping

my
230v up to 1000's!)



You could use a step down tranni' as a supressed earth to give a decent
neutral potential to supply the house circuits, and reduce the fuel
consumption of the generator into the bargain, using the transformer looped
from phase to primary winding, then on to the secondary winding and out to
earth. But as I say, both connections on an AC genny are phase, so it
literally doesn't have a neutral and is dangerous if used with capacitative
loads.

You could ruin your tele' or damage any IF filters in other appliances if
they rely on a phase to neutral supply, so it then becomes a very expensive
installation if you have replace everything. The grid itself is literally
phase and earth connections, but an AC generator is alternating phase /
phase supply.


---
www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.521 / Virus Database: 319 - Release Date: 23/09/03


  #7   Report Post  
Steve Dawson
 
Posts: n/a
Default Playing with meter tails


"Sparks" wrote in message ...
Woa up there horsey !!! A generator doesn't have neutral potential on

it.
Both connections become live feeds and if it is to take over supplying

the
house in the event of a power cut, then you'll need to upgrade the

earthing
and take only a single phase from the genny, to feed the house.

It works by making the grounding spike in to your neutral potential.

Very
dangerous if not done properly. Not to mention the fact that, if the

mains
supply then comes back on while the genny is running, then it could blow
every fuse you have in the house and may even trip out at the local sub
station if it is a large capacity generator.

I originally thought that you had automatic change over, to bring the

genny
online when the mains failed. But you say "possible upgrade to an

automatic
system later". That's a big NO NO !!!!!


FYI A proper automatic transfer switch makes it impossible for both grid

and
generator feed to get connected together!

Generally speaking, with a non synchronised genset, the grid fails, so the
ATS disconnects all power to the house, starts the generator, waits for

the
generator to stabilise, then switched the house from nothing, to generator
power
If the grid is then restored, it will wait a bit, to make sure the grid is
staying on, then it disconnects the house, waits a bit, then switches over
to the grid (If the grid and genset are not synced then switching directly
would be messy!)

It then keeps the generator running for a bit, then finally shuts it off

I understand where you are coming from, as I wouldn't want to try to

supply
power to my whole road! or kill someone working on the street wiring by

back
feeding (I presume a step-down transformer would work in reverse, ramping

my
230v up to 1000's!)



How big a generator are you installing ?? I build AMF panels for this
specific purpose.

Steve


  #8   Report Post  
 
Posts: n/a
Default Playing with meter tails

On Sat, 27 Sep 2003 01:33:34 +0100, "Sparks" wrote:

Wondering if anyone has had any experience with this...

As per normal, I have my grid power entering my house, this then goes
through a 80A fuse that belongs to the electricity board, it then continues
to my electricity meter, and then onto my consumer unit...

The thing is, I want to disconnect the tails that come from my meter, and
connect them to a generator transfer switch - this then connects back to my
consumer unit, and also to a generator.

The options I have are..

Do it live - not a clever idea, especially as my consumer unit has a metal
back!

Pull the electricity boards fuse out, move it, and replace the fuse (minus
the metal tag/seal)

Call the electricity board, and see what extortionate rate they will charge
me..

I have however read about someone calling the electricity board up, and them
saying, "just pull the fuse, ring us when you are done, and we will send
someone out to check the installation, and replace the fuse and seal it up
again"

Any advise would be greatly appreciated!!

Sparks...


I had no seal on my fuse for years and no meter reader ever noticed or
bothered to comment on it. A month ago I had my meter replaced, and to
save any questions I made up my own seal - stripped the plastic off a
thin piece of multi-strand elec wire and attached it with a piece cut
off an crimp. It looked reasonable enough, but even if it didn't and
anybody had said anything I wouldn't have cared too much. After all,
what are they likely to do? Take you to court for cutting off a
company seal?

MJ
  #9   Report Post  
Martin
 
Posts: n/a
Default Playing with meter tails


snip

I had no seal on my fuse for years and no meter reader ever noticed or
bothered to comment on it. A month ago I had my meter replaced, and to
save any questions I made up my own seal - stripped the plastic off a
thin piece of multi-strand elec wire and attached it with a piece cut
off an crimp. It looked reasonable enough, but even if it didn't and
anybody had said anything I wouldn't have cared too much. After all,
what are they likely to do? Take you to court for cutting off a
company seal?

MJ


When I moved in to my current house, there wasn't a seal on the main fuse
either; I asked the lecky company to check it over just in case the previous
owners had been fiddling the meter. They (eventually) sent someone round,
and just fitted a new seal, they didn't give a ... about checking the meter.


Martin.


  #10   Report Post  
chris French
 
Posts: n/a
Default Playing with meter tails

In message , Martin
writes

snip

I had no seal on my fuse for years and no meter reader ever noticed or
bothered to comment on it. A month ago I had my meter replaced, and to
save any questions I made up my own seal - stripped the plastic off a
thin piece of multi-strand elec wire and attached it with a piece cut
off an crimp. It looked reasonable enough, but even if it didn't and
anybody had said anything I wouldn't have cared too much. After all,
what are they likely to do? Take you to court for cutting off a
company seal?

MJ


When I moved in to my current house, there wasn't a seal on the main fuse
either; I asked the lecky company to check it over just in case the previous
owners had been fiddling the meter. They (eventually) sent someone round,
and just fitted a new seal, they didn't give a ... about checking the meter.


If you search for previous threads on this topic you'll find plenty of
people here who have pulled the fuse to work on the electrics.

Some have informed the Elec. Co. before hand, some after and some
haven't, either way the co. 's don't seemed bothered about it.
--
Chris French, Leeds


  #11   Report Post  
James Salisbury
 
Posts: n/a
Default Playing with meter tails


"Sparks" wrote in message ...
Wondering if anyone has had any experience with this...

As per normal, I have my grid power entering my house, this then goes
through a 80A fuse that belongs to the electricity board, it then

continues
to my electricity meter, and then onto my consumer unit...

The thing is, I want to disconnect the tails that come from my meter, and
connect them to a generator transfer switch - this then connects back to

my
consumer unit, and also to a generator.

The options I have are..

Do it live - not a clever idea, especially as my consumer unit has a metal
back!

Pull the electricity boards fuse out, move it, and replace the fuse (minus
the metal tag/seal)

Call the electricity board, and see what extortionate rate they will

charge
me..

I have however read about someone calling the electricity board up, and

them
saying, "just pull the fuse, ring us when you are done, and we will send
someone out to check the installation, and replace the fuse and seal it up
again"

Any advise would be greatly appreciated!!

Sparks...



Fit a dp isolator with an insulated case! I would advise takeing a look at
the 16th Ed of the wireing regs, there is a whole chapter about private
generation. You may also want to advise the supply company so they are
awere.


  #12   Report Post  
Colin Wilson
 
Posts: n/a
Default Playing with meter tails

The thing is, I want to disconnect the tails that come from my meter, and
connect them to a generator transfer switch - this then connects back to my
consumer unit, and also to a generator.


Contact your local electricity company and ask them to fit an isolator -
simple :-)

I say local electricity company, but depending on how anal they want to
get, the request *may* need to come from your supplier (the ones you pay
your bill to) which may be a different company.

If you need to go via your supplier, the request will be sent via a back-
end computer system called the Data Transfer Network (DTN), will be known
as a "flow", and will probably end up with their metering department -
it`s a simple job, usually free of charge.

--
Please add "[newsgroup]" in the subject of any personal replies via email
* old email address "btiruseless" abandoned due to worm-generated spam *
--- My new email address has "ngspamtrap" & @btinternet.com in it ;-) ---
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Meter reader clocked me! BigWallop UK diy 3 July 23rd 03 09:58 AM
noisy gas meter Bilbo Baggins UK diy 3 July 17th 03 09:22 PM


All times are GMT +1. The time now is 01:54 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"