Wiring Regs. - 17th Edition - rumour confirmed?
I notice that the NICEIC have recently updated their note about the
major changes between the 16th and 17th editions: http://www.niceic.org.uk/17thedition...orChanges2.pdf (file created 1st November). Rumours regarding changes to regulation 522.6.6 of the public draft edition appear to be confirmed - to quote: "The requirements relating to cables concealed in a wall or partition have been altered so that protection by a 30mA RCD is an additional requirement for €˜unprotected cables (e.g. twin and earth cables installed in a chase less than 50mm deep); it must be emphasised that such cables must still be installed in €˜safe zones." -- Andy |
#2
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 2007-12-02 10:27:24 +0000, Andy Wade said:
I notice that the NICEIC have recently updated their note about the major changes between the 16th and 17th editions: http://www.niceic.org.uk/17thedition...orChanges2.pdf (file created 1st November). Rumours regarding changes to regulation 522.6.6 of the public draft edition appear to be confirmed - to quote: "The requirements relating to cables concealed in a wall or partition have been altered so that protection by a 30mA RCD is an additional requirement for €˜unprotected cables (e.g. twin and earth cables installed in a chase less than 50mm deep); it must be emphasised that such cables must still be installed in €˜safe zones." So do you read the implication of this as being 30mA RCD protection for all circuits regardless of where the cables are run? i.e. even in the 150mm safe zones? This implies whole house RCDs or RCBOs. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Hall wrote:
So do you read the implication of this as being 30mA RCD protection for all circuits regardless of where the cables are run? i.e. even in the 150mm safe zones? In effect, yes. What it appears to mean is that if you want to run a non-RCD-protected circuit then the cables must either - be one of the prescribed types which incorporate an earthed armour, screen or covering, or - be run in earthed metal conduit, or - be buried deeper than 50 mm in a wall, or - be wholly surface-wired. This implies whole house RCDs or RCBOs. Or multiple RCDs, or some combination of RCDs and RCBOs. -- Andy |
#4
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 2007-12-02 12:17:00 +0000, Andy Wade said:
Andy Hall wrote: So do you read the implication of this as being 30mA RCD protection for all circuits regardless of where the cables are run? i.e. even in the 150mm safe zones? In effect, yes. What it appears to mean is that if you want to run a non-RCD-protected circuit then the cables must either - be one of the prescribed types which incorporate an earthed armour, screen or covering, I haven't seen anything for interior use that fits this bill. Surely not SWA? or - be run in earthed metal conduit, implies a lot of labour or - be buried deeper than 50 mm in a wall, which can't be done in a modern domestic property. or - be wholly surface-wired. which won't be aesthetically acceptable This implies whole house RCDs or RCBOs. Or multiple RCDs, or some combination of RCDs and RCBOs. I think that I might go and buy some Honeywell shares (as in MK) ....... |
#5
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Or multiple RCDs, or some combination of RCDs and RCBOs. I think that I might go and buy some Honeywell shares (as in MK) ....... I think we're about to see a big ramp-down in the price of RCBO's (as there's nothing particularly expensive materials wise or rocket science about the technology in them) and for the manufacturers to launch CU's pre-populated with RCBO's at a much reduced bundle price. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 2007-12-02 13:04:33 +0000, " said:
Or multiple RCDs, or some combination of RCDs and RCBOs. I think that I might go and buy some Honeywell shares (as in MK) ....... I think we're about to see a big ramp-down in the price of RCBO's (as there's nothing particularly expensive materials wise or rocket science about the technology in them) and for the manufacturers to launch CU's pre-populated with RCBO's at a much reduced bundle price. Consumer units will need to be redesigned though - e,g, the busbar arrangements, I would have thought ,because of the extra connections. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Hall wrote:
I haven't seen anything for interior use that fits this bill. Surely not SWA? That's one option. The full list is: - BS 5467 - SWA (XLPE/PVC) - BS 6346 - SWA (PVC/PVC) - BS 6724 - SWA (XLPE/LSF) - BS 7846 - SWA (XLPE/OHLS) - BS 8346 - e.g. 'Earthshield' [1] - BS EN 60702-1 - MICC [1] See http://www.voltimum.co.uk/news/4178/...ng-cables.html I think that I might go and buy some Honeywell shares (as in MK) ....... Might not be a bad idea... -- Andy |
#8
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 2007-12-02 13:23:04 +0000, Andy Wade said:
Andy Hall wrote: I haven't seen anything for interior use that fits this bill. Surely not SWA? That's one option. The full list is: - BS 5467 - SWA (XLPE/PVC) - BS 6346 - SWA (PVC/PVC) - BS 6724 - SWA (XLPE/LSF) - BS 7846 - SWA (XLPE/OHLS) - BS 8346 - e.g. 'Earthshield' [1] - BS EN 60702-1 - MICC [1] See http://www.voltimum.co.uk/news/4178/...ng-cables.html Ah, so add Pirelli to the portfolio. It seems that Earthshield is not mechanical protection but rather that it is assumed that someone driving in a nail will reach the CPC outer screen first and will then hit a phase conductor, thus tripping the MCB? I think that I might go and buy some Honeywell shares (as in MK) ....... Might not be a bad idea... |
#9
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On Sun, 02 Dec 2007 12:17:00 +0000, Andy Wade
wrote: Andy Hall wrote: So do you read the implication of this as being 30mA RCD protection for all circuits regardless of where the cables are run? i.e. even in the 150mm safe zones? In effect, yes. What it appears to mean is that if you want to run a non-RCD-protected circuit then the cables must either - be one of the prescribed types which incorporate an earthed armour, screen or covering, or - be run in earthed metal conduit, or - be buried deeper than 50 mm in a wall, or - be wholly surface-wired. This implies whole house RCDs or RCBOs. Or multiple RCDs, or some combination of RCDs and RCBOs. Sod that. Good job I used my old 4mm cooker radial circuit as a non-RCD-protected circuit for the fridge-freezer. It shouldn't need rewiring for a decade or two... -- Frank Erskine |
#10
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Hall wrote:
Ah, so add Pirelli to the portfolio. Or Prysmian, as the cable operation seems to itself these days. It seems that Earthshield is not mechanical protection but rather that it is assumed that someone driving in a nail will reach the CPC outer screen first and will then hit a phase conductor, thus tripping the MCB? That principle in all cases, ultimately. The level of mechanical protection obviously varies, steel conduit probably being the best. Another point with BS 8436 cable is that the shield is very thin, so there are constraints on what protective device can be used to keep within the I^2*t capability of the cable. You're confined to Type B MCBs or RCBOs of energy limiting class 3. This MS Word document from the ECA has chapter and verse: http://www.voltimum.co.uk//popup.php...rd,%252029.5kB -- Andy |
#11
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Wade wrote:
I notice that the NICEIC have recently updated their note about the major changes between the 16th and 17th editions: http://www.niceic.org.uk/17thedition...orChanges2.pdf (file created 1st November). Rumours regarding changes to regulation 522.6.6 of the public draft edition appear to be confirmed - to quote: "The requirements relating to cables concealed in a wall or partition have been altered so that protection by a 30mA RCD is an additional requirement for €˜unprotected cables (e.g. twin and earth cables installed in a chase less than 50mm deep); it must be emphasised that such cables must still be installed in €˜safe zones." Once solution here would seem to be to treat all installs as we currently would a TT one. That way one can still have "non protected" (i.e. 100mA or higher trips thresholds and time delays) on circuits where appropriate. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#12
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
John Rumm wrote:
Once solution here would seem to be to treat all installs as we currently would a TT one. That way one can still have "non protected" (i.e. 100mA or higher trips thresholds and time delays) on circuits where appropriate. How would that help? 100 mA and/or time-delayed RCDs will not meet the 30 mA / 40 ms requirement [in 415.1] for additional protection. -- Andy |
#13
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Wade wrote:
I notice that the NICEIC have recently updated their note [...] And here's the ECA's contribution: http://www.eca.co.uk/17thEdition/17E...tation.pdf.pdf -- Andy |
#14
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Wade wrote:
John Rumm wrote: Once solution here would seem to be to treat all installs as we currently would a TT one. That way one can still have "non protected" (i.e. 100mA or higher trips thresholds and time delays) on circuits where appropriate. How would that help? 100 mA and/or time-delayed RCDs will not meet the 30 mA / 40 ms requirement [in 415.1] for additional protection. Missed that bit... obviously it wouldn't 30mA trip seems excessive if the only intention is to protect the wiring itself and against indirect contact risks (or whatever the new phrase is) - especially on lighting circuits. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#15
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
And here's the ECA's contribution: http://www.eca.co.uk/17thEdition/17E...tation.pdf.pdf And the cost-benefit analysis and/or regulatory impact assessment is where please? -- Robin |
#16
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
In article 4752bc68@qaanaaq, Andy Hall writes
On 2007-12-02 13:23:04 +0000, Andy Wade said: Andy Hall wrote: I haven't seen anything for interior use that fits this bill. Surely not SWA? That's one option. The full list is: - BS 5467 - SWA (XLPE/PVC) - BS 6346 - SWA (PVC/PVC) - BS 6724 - SWA (XLPE/LSF) - BS 7846 - SWA (XLPE/OHLS) - BS 8346 - e.g. 'Earthshield' [1] - BS EN 60702-1 - MICC [1] See http://www.voltimum.co.uk/news/4178/...ng-cables.html Ah, so add Pirelli to the portfolio. It seems that Earthshield is not mechanical protection but rather that it is assumed that someone driving in a nail will reach the CPC outer screen first and will then hit a phase conductor, thus tripping the MCB? I'm sure Pirelli has carried out tests but I wonder what the chances are of the foil vaporising in an annulus around such a nail before a 32A breaker trips? When Mr W first raised this issue I assumed that everyone would just move over to non-split CUs with everything on the trip or add an RCD to the previously non-RCD side in retrofit, this would be far less than the cost of specialist cabling and IMO it is cost that will drive this market. -- fred Plusnet - I hope you like vanilla |
#17
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 02/12/2007 19:27, fred wrote:
I'm sure Pirelli has carried out tests but I wonder what the chances are of the foil vaporising in an annulus around such a nail before a 32A breaker trips? Dunno, but surely the intention of the 17th Ed. is that there is no worry about an MCB having to trip because an RCD (or RCBO) will do instead? |
#18
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 02/12/2007 18:42, Andy Wade wrote:
http://www.eca.co.uk/17thEdition/17E...tation.pdf.pdf So rather than have no definition of a competent person it now has the definition of ... "A person who possesses sufficient technical knowledge and experience for the nature of the electrical work undertaken and is able at all times to prevent danger, and where appropriate, injury to themselves and others." At _ALL_ times? |
#19
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
In article , Andy Burns
writes On 02/12/2007 19:27, fred wrote: I'm sure Pirelli has carried out tests but I wonder what the chances are of the foil vaporising in an annulus around such a nail before a 32A breaker trips? Dunno, but surely the intention of the 17th Ed. is that there is no worry about an MCB having to trip because an RCD (or RCBO) will do instead? IIUC the Pirelli is designated as a protected cable and so does not require to be on an RCD protected circuit. -- fred Plusnet - I hope you like vanilla |
#20
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Burns wrote:
On 02/12/2007 18:42, Andy Wade wrote: http://www.eca.co.uk/17thEdition/17E...tation.pdf.pdf So rather than have no definition of a competent person it now has the definition of ... "A person who possesses sufficient technical knowledge and experience for the nature of the electrical work undertaken and is able at all times to prevent danger, and where appropriate, injury to themselves and others." Which looking at the bright side, is actually a definition of competence that most would recognise, an does not (yet) include requirements to belong to any particular trade organisation. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#21
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 2007-12-02 19:17:03 +0000, "Robin"
said: And here's the ECA's contribution: http://www.eca.co.uk/17thEdition/17E...tation.pdf.pdf And the cost-benefit analysis and/or regulatory impact assessment is where please? Oh don't worry about that. This is like Alice in Wonderland - the Queen of Hearts. Sentence first, trial afterwards. Work out the legislation that you want then make the RIA fit that complete with promotions for the civil servants involved. Part P was done in this way, so this one is a mere bagatelle |
#22
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
John Rumm wrote:
30mA trip seems excessive if the only intention is to protect the wiring itself and against indirect contact risks (or whatever the new phrase is) - especially on lighting circuits. The thinking seems to be a belt & braces approach to avoiding incidents like the electrified plate rack that killed Jenny Tonge's daughter - safe zones routing plus either a 30 mA RCD or earthed protection of the cable to operate the OPD. Where the RCD is used with unprotected cable it's there to provide additional basic protection (supplementary direct contact protection in oldspeak) so it does need to be 30 mA. Apparently a solution NICEIC are proposing at their seminars, for 2-storey houses, is to have a split-load CU (main switch and two 30 mA RCDs) with two groups of MCBs, one group feeding upstairs lighting and downstairs power and the other group vice-versa. What fun. -- Andy |
#23
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On Sun, 02 Dec 2007 20:28:15 +0000, Andy Burns wrote:
At _ALL_ times? Wot, even Monday Mornings? Even Friday afternoons after a session down at The Olde Fuse & Circuit Breaker? What is the world coming to?! -- John Stumbles Time flies like an arrow Fruit flies like a banana Tits like coconuts |
#24
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Apparently a solution NICEIC are proposing at their seminars, for 2-storey houses, is to have a split-load CU (main switch and two 30 mA RCDs) with two groups of MCBs, one group feeding upstairs lighting and downstairs power and the other group vice-versa. What fun. Anyone have an opportunity to ask them "given the current performance of RCDs and domestic equipment, what is the estimated increase in the number/cost of accidents when use of a socket etc downstairs plunges upstairs into darkness or vice-versa? And the future forecasts bearing in mind the forecast increase in elderly, single occupancy households?" -- Robin |
#25
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 02/12/2007 20:33, fred wrote:
IIUC the Pirelli is designated as a protected cable and so does not require to be on an RCD protected circuit. Ah yes. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
In article , Robin
writes Apparently a solution NICEIC are proposing at their seminars, for 2-storey houses, is to have a split-load CU (main switch and two 30 mA RCDs) with two groups of MCBs, one group feeding upstairs lighting and downstairs power and the other group vice-versa. What fun. Anyone have an opportunity to ask them "given the current performance of RCDs and domestic equipment, what is the estimated increase in the number/cost of accidents when use of a socket etc downstairs plunges upstairs into darkness or vice-versa? And the future forecasts bearing in mind the forecast increase in elderly, single occupancy households?" Cue requirements for emergency lighting in domestic installations in future legislation. -- fred Plusnet - I hope you like vanilla |
#27
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
Andy Wade wrote:
Apparently a solution NICEIC are proposing at their seminars, for 2-storey houses, is to have a split-load CU (main switch and two 30 mA RCDs) with two groups of MCBs, one group feeding upstairs lighting and downstairs power and the other group vice-versa. What fun. I think I prefer a dedicated CU for lighting and ancillary circuits with its own RCD in this circumstance, supplemented with some emergency lighting in appropriate places. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#28
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On 2007-12-02 13:44:12 +0000, Owain said:
Andy Hall wrote: Consumer units will need to be redesigned though - e,g, the busbar arrangements, I would have thought ,because of the extra connections. Don't the French use double-pole MCBs or RCBOs in their consumer units? From what I can make out, they are typically groups of single pole MCBs protected by RCDs. There usually seem to be twice the number as there are here, probably due to radial circuits. So handy for isolating le s*n*f*o ... One would expect to see a lot of them, but they seem to be curiously absent from the shelves of bricolage places. I think that they are a secret weapon. |
#29
Posted to uk.d-i-y
|
|||
|
|||
Wiring Regs. - 17th Edition - rumour confirmed?
On Sun, 02 Dec 2007 21:33:26 +0000, Andy Wade wrote:
Apparently a solution NICEIC are proposing at their seminars, for 2-storey houses, is to have a split-load CU (main switch and two 30 mA RCDs) with two groups of MCBs, one group feeding upstairs lighting and downstairs power and the other group vice-versa. What fun. Surely that violates the (informal?) principle of least surprise? -- John Stumbles Testiculate [v.t] To wave one's arms around while talking ********. |