  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 18
Default Electrical cable outside

Hi,

If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit? Or does it have
to be armoured cable as well?

TIA
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Electrical cable outside

In article ,
Nobody wrote:
If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit? Or does it have
to be armoured cable as well?


Yes - but SWA is the cheaper option material cost wise - and quicker to
install.

--
*Never test the depth of the water with both feet.*

Dave Plowman London SW
To e-mail, change noise into sound.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical cable outside

Nobody wrote:

If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit?


Yes... or plastic

Or does it have
to be armoured cable as well?


No, but you could use that without additional protection.


http://wiki.diyfaq.org.uk/index.php?...Cable_c hoice


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,319
Default Electrical cable outside

Dave Plowman (News) wrote:
In article ,
Nobody wrote:
If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit? Or does it have
to be armoured cable as well?


Yes - but SWA is the cheaper option material cost wise - and quicker
to install.


I see dozens of examples of T&E cable surface mounted to exterior walls,
mostly above head height for security lights.

Are we saying this should be in trunking? Or armoured?


--
Dave - The Medway Handyman
www.medwayhandyman.co.uk
01634 717930
07850 597257


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 30
Default Electrical cable outside


"John Rumm" wrote in message
...
Nobody wrote:

If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit?


Yes... or plastic

Or does it have
to be armoured cable as well?


No, but you could use that without additional protection.


http://wiki.diyfaq.org.uk/index.php?...Cable_c hoice


'Fraid I have to take exception to that article John. If the conduit is to
protect the T&E from physical damage, ie, being hit with something then fair
enough perhaps, but I really do wish that we could end the myth that
ordinary PVC T&E is attacked by UV and becomes brittle and cracks.

This subject came up either last year or the year before on the group and I
replied then as I will now. We have a run of approximately 7 metres of 1.0mm
T&E clipped directly to the *south facing* (so it's exposed to a lot of
sunshine and UV) wall at the back of our house, which feeds an external
light. It was installed about 20 years ago now but last year (maybe the year
before) I had to unclip it while I did some other, unrelated work, and it
was still very flexible, was not in any way brittle, and did not break or
crack at all.

After completing what I had to do, it was clipped back up again and is none
the worse, either for being moved or for sitting in sunlight for 20 years.
So if the OP is asking the question on sunlight/UV grounds alone, I'd say
that it can be clipped directly with no need for conduit or capping at all,
but if it's in danger of being hit or damaged by something else, then fair
enough, use conduit/capping.

John




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical cable outside

The Medway Handyman wrote:
Dave Plowman (News) wrote:
In article ,
Nobody wrote:
If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit? Or does it have
to be armoured cable as well?

Yes - but SWA is the cheaper option material cost wise - and quicker
to install.


I see dozens of examples of T&E cable surface mounted to exterior walls,
mostly above head height for security lights.


Its not UV safe, and so will harden and risks the insulation cracking.
Painting it would help, and would a sheltered location.

Are we saying this should be in trunking? Or armoured?


Either, or use an exterior rated cable like HiTuf

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 18
Default Electrical cable outside

On Thu, 22 Nov 2007 11:59:17 +0000, John Rumm
wrote:

Nobody wrote:

If you wish to run a cable up a wall on the outside of a house, can
this be ordinary T&E inside metal piping or conduit?


Yes... or plastic

Or does it have
to be armoured cable as well?


No, but you could use that without additional protection.



Thanks for all the responses. I should clarify that this would be
from the consumer unit on the ground floor and up to the loft to
provide a ring main and llighting circuit. I had been told that the
"rules" didn't allow it to be bare or in a conduit and the builders
wanted to put it down inside the cavity wall - which is now full of
insulation from two years back. I couldn't see why conduit wasn't
allowed. Mention of NICE (spit) etc.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 410
Default Electrical cable outside

Nobody was thinking very hard :
I had been told that the
"rules" didn't allow it to be bare or in a conduit and the builders
wanted to put it down inside the cavity wall - which is now full of
insulation from two years back.


Installation in the cavity wall is not permitted. Can you not find a
route up through the inside of the house?

--

Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Electrical cable outside

As stated you can not run cables in a cavity wall.
BS7671 16th OSG specifically refers to this IIRC.

Hituff...
o Some NICEIC inspectors dislike it as "h/duty flex"
---- it has stranded core, but so does FP200-Flex
---- FP200-Flex is permitted for fixed wiring apps
o Many dislike Hituff gland arrangement
---- outer sheath is *rigid hard plastic*
---- most glands require that rigid outer to be removed
---- so the gland can seal around inner cable bedding
---- some inspectors dislike this as a weak point

They can/often make up regulations as they go or
rewrite regulations to meet financial requirements.


Your later post changes your requirements :-)
You require a Ring & Lighting circuit in the loft.

This can be achieved in 2 ways...
1. Ring Main & Lighting cables
---- Ring -- 2 runs of FTE-2.5mm (Flat Twin & Earth)
---- Lighting -- 1 run of FTE-1.5mm
2. Distribution Circuit to Mini-CU in the loft
---- Single cable, but probably not using FTE-4.0mm
---- FTE-4.0mm length limited by small 1.5mm CPC (ELFI)

Lighting using 1.5mm allows grouping of the lighting cable
to be ignored because 18A maximum fused at 6A is 30%.

Option-1 is difficult...
1.1 Multiple FTE do not fit well in conduit
---- 2x FTE-2.5 & 1x FTE-1.5 really needs 32mm conduit
---- the variety of fittings for 32mm conduit is limited
---- using 1x FTE-4.0 will not work re distance (1.5mm CPC)
---- cable grouping ok (lighting cables 30% max so ignored)
---- bend radius is the challenge here re bundle of FTE
1.2 Multiple 6491X "Singles" are more suited to conduit
---- assuming 5m straight run with 90-degree bends top/bottom
---- 25mm conduit cable factor is 358 (OSG p114 Table 5D)
---- assuming ring & light in 2.5mm 6491X so just 3 cable reels
---- 9x 2.5mm cables have a combined cable factor of 9*30 = 270
---- combined cable factor (270) is below conduit (358) so ok
---- top/bottom junction box connects to FTE-2.5mm & 1.5mm
---- cable grouping ok (lighting cables 30% max so ignored)
1.3 SWA with 4 cores & CPC (armour)
---- 4-core 2.5mm SWA has o.d. 14.4mm, max in duct 34A
---- high current rating is due to 90oC XLPE insulation vs PVC
---- 2 cores for ring + 2 cores for lighting + armour for earth
---- top/bottom junction box connects to FTE-2.5mm & 1.5mm
---- really need Earthing Nut on both glands for reliable earth
---- label junction box "2 final circuits in SWA, isolate both"
---- cable grouping ok (lighting cables 30% max so ignored)
---- bend radius is 6D or 90mm - take note

Option-2 is a little easier...
2.1 Single FTE can fit ok in conduit with FEW bends
---- 1x FTE-6.0 may fit in 25mm conduit & 2 bends, not easy
---- plenty of fittings for 25mm conduit, black, white
---- FTE-6.0 has a 2.5mm CPC so probably ok (check)
---- Mini-CU in loft w/ 32A MCB & 6A MCB FTE-2.5 & 1.5mm
2.2 Multiple 6491X are more suited to conduit
---- 25mm conduit with 4.0mm singles for Phase/Neutral *&* CPC
---- Mini-CU in loft connects 32A MCB & 6A MCB FTE-2.5 & 1.5mm
2.3 SWA with 2 cores & CPC (armour)
---- 2-core 2.5mm would probably do, 4.0mm preferable
---- bend radius is 6D or 90mm - take note
---- Mini-CU in loft w/ 32A MCB & 6A MCB FTE-2.5 & 1.5mm


I would choose option 1.2...
o 25mm black conduit, available in 3m lengths
---- heavy duty type
o 25mm black conduit 1-way terminal box (round BESA)
---- rear entry via female bushing to conduit going thro wall
---- PVC glue (solvent) or clear silicone for bushing & conduit
---- rubber gasket under terminal box lid, M4x10 brass screws
---- drill drain hole at the bottom of the bottom conduit box
---- conduit box at each end (top/bottom)
o On inside wall deep 2G metal box w/25mm rear hole
---- most 2G boxes lack a rear 25mm hole
---- use flush or surface, plastic or metal "adaptable box"
---- 30A & 15A terminal strips (ideally glass filled nylon)
o Feed bottom junction box with 2x FTE-2.5mm & FTE-1.5mm
---- run to dedicated 32A RCBO & 6A MCB in CU
o Take top junction box with 2x FTE-2.5mm & FTE-1.5mm
---- remember rubber grommets on all cable entries

www.gil-lec.co.uk will sell you 6491X by the metre, so you
need not buy 3x 100m reels of 2.5mm but just the cut lengths
of 3x 4.0mm (ring) & 3x 1.5mm (lighting) you require.

Very simple, perfectly acceptable.
I fit cable shrouds over the conduit-entry to conduit box
just as an extra, it actively prevents any water loading.
PVC glue never seals conduit after a while due to the
expansion/contraction of plastic (higher than metal), so
to be honest a quality flexible silicone can be better.


Had you just required a single cable upstairs...
I would suggest FP200 (Firetuf) in white (UV ok). Routinely
used for outside power & lighting from M&S to Post Office.
Use a waterproof gland to a malleable iron conduit box, they
have a thread exit to suit the gland thread. Then a rear hole
through the wall to conduit & junction box on the inside.
FP200/Firetuff sheath is removed as soon as it enters the
gland to turn it into "singles" so as to make the tight turn
through the rear exit & through conduit to the jn-box inside.
FP200 is a pseudo concentric cable like SWA, very tough
outer skin, but no armour (concentric foil under sheath).
It is small (8-11mm dia), but subject to 6D bend radius.


The ideal solution is to route indoors.

Failing that, the above option 1.2 is the least messy.
A straight conduit between 2x conduit 1-way boxes on
a wall in 25mm is discrete and functional. I suspect you
will exit the wall quite high, so mechanical protection is
less important and heavy duty conduit is actually fine.
I would not bother running in steel, if you do: galvanised.
--
DB.


  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical cable outside

John wrote:

http://wiki.diyfaq.org.uk/index.php?...Cable_c hoice


'Fraid I have to take exception to that article John. If the conduit is to
protect the T&E from physical damage, ie, being hit with something then fair
enough perhaps, but I really do wish that we could end the myth that
ordinary PVC T&E is attacked by UV and becomes brittle and cracks.

replied then as I will now. We have a run of approximately 7 metres of 1.0mm

....
was still very flexible, was not in any way brittle, and did not break or
crack at all.


What you have highlighted is that *your* bit of T&E was fine. I don't
think the same can be stated with complete confidence as a general case
though.

IME some brands are very much better than others. Generally plasticised
PVC will lose plasticiser with UV exposure (which is why most PVC stuff
designed for use outside is made from uPVC). However this may not mean
that it becomes non-handleable, but just less flexible than it once was.

In Table 3A The OSG states that clipped to an external wall ordinary
flat T&E may be ok, although it does also say "protection from direct
sunlight may be necessary. Black sheath colour is better for cables in
sunlight"

BS7671 says:

"522-11 Solar radiation (AN) and ultra-violet radiation
522-11-01 Where significant solar radiation (AN2) or ultra-violet
radiation is experienced or expected, a wiring system suitable for the
conditions shall be selected and erected or adequate shielding shall be
provided."

(where AN2 refers to the medium band of solar radiation in the range 500
- 700 W/m^2)

In light of the above, and your comments I think it would be appropriate
to tone down the recommendations on the wiki a little though. Try this:

http://wiki.diyfaq.org.uk/index.php?...#Cable_t ypes


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical cable outside

Nobody wrote:

Thanks for all the responses. I should clarify that this would be
from the consumer unit on the ground floor and up to the loft to
provide a ring main and llighting circuit. I had been told that the
"rules" didn't allow it to be bare or in a conduit and the builders
wanted to put it down inside the cavity wall - which is now full of
insulation from two years back. I couldn't see why conduit wasn't
allowed. Mention of NICE (spit) etc.


Conduit *is* allowed - as long as one accounts for the current de-rating
effect in the circuit designs. Since for 2.5mm^2 T&E this is only a
reduction from 27A capacity when clipped direct, to 23A (Table 4D2A)
when enclosed in conduit (reference method 3 it should not be an issue
for conventional 32A ring circuits unless other de-rating factors come
into play.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 18
Default Electrical cable outside

On Thu, 22 Nov 2007 19:23:23 GMT, "Dorothy Bradbury"
wrote:

[snip]

Thanks to all for the information and advice. I wanted to confirm I
was being told rubbish in the first place. I will look at internal
routing as well - looks like the floorboards will be murdered again
:-))

Best regards.

  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Electrical cable outside

To add more detail re option 1.2...

In brief...
o Correction for Cable Grouping eliminates some options.
o Option 1.1 -- fails re cable grouping
o Option 1.2 with 6491X 2.5mm -- fails re cable grouping
o Option 1.2 with 6491X 4.0mm -- ok re cable grouping

In detail...
o 1.1 - Twin FTE-2.5mm & FTE-1.5mm in 32mm conduit
---- not possible because FTE-2.5 in Method M3 is just 23A
---- lighting cable is disregarded as 30% loading hence N=2
---- Cg = 0.80 for N=2 (2 cables for each ring leg)
---- 23A x 0.80 = 18.4A *BELOW* the required 20A per-ring-leg
---- Twin FTE-4.0mm would be required, gets chunky
o 1.2 - Multiple 6491X "Singles" 2.5mm
---- not possible because 2.5mm in Method M3 is just 24A
---- lighting cable is disregarded as 30% loading hence N=2
---- Cg = 0.80 for N=2 (2 cables for each ring leg)
---- 24A * 0.80 = 19.2A *BELOW* the required 20A per-ring-leg
---- single 6491X 4.0mm would be required - no problem
o 1.2 - Multiple 6491X "Singles" 4.0mm
---- possible because *single* 4.0mm in Method M3 is 32A
---- lighting cable is disregarded as 30% loading hence N=1
---- Cg = 1.00 for N=1 (1 cable required)
---- 32A * 1.00 = 32A which matches the 32A ring requirement
---- single 6491X "Singles" 4.0mm is thus ok


So I stand by my suggestion of Option 1.2 in 4.0mm 6491X
for the 32A ring feed, with 1.5mm 6491X for lighting feed.

The conduit 6491X run is still fed by twin FTE-2.5mm &
single FTE-1.5mm from the CU (ring+light) and leaves by
twin FTE-2.5mm & single FTE-1.5mm at the loft end.

www.gil-lec.co.uk for 6491X 4.0mm Ring, 1.5mm Lighting.
Sorry, I had steel conduit with 6491B singles on the brain.
--
DB.


  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Electrical cable outside

See my updated comment - and do look at floorboards :-)

Option 1.2 4.0+1.5mm is simple, but can get ugly.
Just been at a dentist where the plumber went mad with
angles/couplings/brackets/standoffs on the outside walls!
Adding conduit runs to the mix really puts off buyers.

Cables outside is visually better kept for lights-n-sheds.
The Lloyds Building approach does not work on houses.
--
DB.


  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 30
Default Electrical cable outside


"John Rumm" wrote in message
...
John wrote:

http://wiki.diyfaq.org.uk/index.php?...Cable_c hoice


'Fraid I have to take exception to that article John. If the conduit is
to protect the T&E from physical damage, ie, being hit with something
then fair enough perhaps, but I really do wish that we could end the myth
that ordinary PVC T&E is attacked by UV and becomes brittle and cracks.

replied then as I will now. We have a run of approximately 7 metres of
1.0mm

...
was still very flexible, was not in any way brittle, and did not break or
crack at all.


What you have highlighted is that *your* bit of T&E was fine. I don't
think the same can be stated with complete confidence as a general case
though.

IME some brands are very much better than others. Generally plasticised
PVC will lose plasticiser with UV exposure (which is why most PVC stuff
designed for use outside is made from uPVC). However this may not mean
that it becomes non-handleable, but just less flexible than it once was.

In Table 3A The OSG states that clipped to an external wall ordinary flat
T&E may be ok, although it does also say "protection from direct sunlight
may be necessary. Black sheath colour is better for cables in sunlight"

BS7671 says:

"522-11 Solar radiation (AN) and ultra-violet radiation
522-11-01 Where significant solar radiation (AN2) or ultra-violet
radiation is experienced or expected, a wiring system suitable for the
conditions shall be selected and erected or adequate shielding shall be
provided."

(where AN2 refers to the medium band of solar radiation in the range 500 -
700 W/m^2)

In light of the above, and your comments I think it would be appropriate
to tone down the recommendations on the wiki a little though. Try this:

http://wiki.diyfaq.org.uk/index.php?...#Cable_t ypes


Yes, that's better mate,

cheers,

John




  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,045
Default Electrical cable outside

Dorothy Bradbury wrote:
As stated you can not run cables in a cavity wall.


All my cables run in a (wood) cavity wall. BCO never turned a hair.
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default Electrical cable outside


"Dorothy Bradbury" wrote...
As stated you can not run cables in a cavity wall.
BS7671 16th OSG specifically refers to this IIRC.


Just took a look in the TLC guide[1] to the 16th ed' and it looks like it's
derating if buried in insulation (50% of free-air current capacity), and
caution re leaching of plasticisers etc. along with cautions re damp
bridging (although wall ties certainly touch both leaves of the cavity?) - I
have a through-the-cavity 16sq.mm feed to the "loft CU" myself, but that's
in what was the external cavity (uninsulated) before the house was extended
and is now a double-leaf internal wall... Whether it complies or not is a
mystery to me, as it was put in long before Prat P came into force - I have
replaced the old cable like for like with new "harmonised" due to slight
mechanical damage, as permitted under part P ;o)

--
Dave H.
(The engineer formerly known as Homeless)

"Rules are for the obedience of fools, and the guidance of wise men" -
Douglas Bader

[1] http://www.tlc-direct.co.uk/Book/4.3.6.htm


  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Electrical cable outside

Dorothy Bradbury wrote:
As stated you can not run cables in a cavity wall.


All my cables run in a (wood) cavity wall. BCO never turned a hair.


I think the limitation on cables in a cavity wall is thus...
o Some people used to drill at two points thro the inner leaf
o At the top drop a plumbob
o At the bottom feed in a metal loop so it expands left & right
o Thus feed cables through brick cavities

In this instance cables are potentially...
o Unsupported over a large vertical run
o Against metal brick ties, risk of unseen damage during fitting
o In unknown positions re adventurous CWI drillers etc
o Subject to future additional insulation requiring derating
o Difficult to replace and "left to cook" if insulation added
o Routed without regard to min bend radius inside leaf

Of course one can argue the cable is 2" from the surface
thus need no protection & need not run vertically etc etc.

Part P of course requires you to use the same route as old,
no mention of the route requiring adherence to BS7671.
That may be a factor in IEE "going all RCBO" re zones.

I suspect many houses do run cables down the brick cavity,
especially for loft & showers - too tempting vs alternatives.


I agree re risk of obsession about fixed vs appliance wiring.
Local "co-op" has perfect hierarchical sized trunking/conduit,
beautifully arranged singles, cables, everything throughout.
It would make a BT linesman weep at obsessive precision.
Every fridge has sheath 4"+ short of BS4343 cord grip,
bare singles holding a 3m cable drop, one with CPC out.
Each one with green PAT label attached. I suspect partly
caused by walking on cords - so pulling on ceiling plugs.

All our cables ran thro a cavity, impossible to get to re
built-in tanks above, chimney below & to side, absolutely no
consideration for ambient derating. Every single cable has the
copper conductor black with cupric oxide, insulation will not
slide off the conductor. Insulation must be physically scrapped
off tiny bit by bit with a knife - the copper shaves more easily.
Replacements take a distinctly cooler (& BS7671) route.

Local brick-outer-leaf, shed-inner-leaf apartments ran cables
(white so LSOH) thro holes in the wood inner leaf. Others ran
cables thro metal studding without protection so that will be
an interesting problem in years to come re vibration. LSOH
cable sheath has as much abrasion resistance as cheese.
--
DB.


  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Electrical cable outside

although wall ties certainly touch both leaves of the cavity?

Wall ties are designed to drain from inner to outer leaf.
Unless your brickie fitted them the wrong way around,
whereupon they will train from the outer to inner leaf.


I have replaced the old cable like for like


Same route & size, perfect compliance under Part P :-)
Slight mechanical damage is... so useful.

Elec Factors odds are on earth rods for PME installations re
risk of broken neutral. I suspect they just have a shed full :-)

Talking of cavities...
I prefer burying gov't officials face down, so you always
have somewhere to park the bike if you see what I mean.
--
DB.


  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Electrical cable outside

So effectively in conduit or trunking you can only have one
2.5mm^2 or else it is derated below the magical 20A. This
seems ludicrous for 4" or even 2" trunking.


Reason is not the size of trunking - but cable separation :-)

Eg, installation Method M1 for cables on surface...
o 1 Dia separation, N= 2, Cg = 0.94
o 0 Dia separation, N= 2, Cg = 0.85 -- cables touching on surface

Cable bunching between joists requires Cg = 0.90.


When we ran 8 cables they were arranged in 4 pairs with one
of each pair being 1.5mm 6A (Lights Smoke Alarm). Thus 30%
cable load allows N=2 cable grouping to be disregarded (N=1).

Each pair ran through a P-clip/screw/wallplug to maintain
separation 2D largest cable major axis from the next pair.
Bricks too hard for clips, mortar too weak for clips. That
way derating was kept to a minimum, buried direct M2.

Physically very tedious, with hindsight it may seem better
to use a single 6242Y or SWA to a mini-CU instead. Even
10mm SWA fits thro a standard 20mm backbox hole if
you want to mark a route outside zones, min bend radius
is handled via bending up the wall on internal corners.
Typical problem is you end up routing N cables "back"
along the route you took to where needed - so rejected.


Where cables are grouped for short distances you can
ignore grouping - basically as you would for a joist width.
However it may be wise to assume bunching Cg of 0.90,
for domestic usage this should rarely be a problem.


Industrially they (literally) throw CSA at the problem if
in supersized trunking or use cable trays accordingly.
Cable trays often carry SWA which is XLPE, so absorbs
cable derating problems re higher current rating. It is not
practical to do that with say XLPE 6242B domestically
because the 90oC figure does not apply to fittings. Plus
you can not use that figure & route by PVC cables.

The FP200/400 etc concentric cables are popular as they
remove the need for armour in some circumstances, so
are quicker to fit (altho not cheaper). Unfortunately it
seems nearly all are 70oC rated vs SWA XLPE so as
a result the "grouping problem absorption" is lost, but
since they are smaller than SWA separation increases.


With planning you can avoid most grouping problems.
However 24-way MK Grid boxes must be *fun* to do.
--
DB.




  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical cable outside

Dorothy Bradbury wrote:

I have replaced the old cable like for like


Same route & size, perfect compliance under Part P :-)
Slight mechanical damage is... so useful.


There is a slight vagueness in part P there also since it speaks of
"same current carrying capacity" which does leave option the argument of
using a larger size as well since it will be able to carry the same
current as the previous cable.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Electrical cable outside

John Rumm wrote:

In Table 3A The OSG states that clipped to an external wall ordinary
flat T&E may be ok, although it does also say "protection from direct
sunlight may be necessary. Black sheath colour is better for cables in
sunlight"

BS7671 says:
[...]


There is also the issue of reduction in the current rating of cables
being warmed by sunlight. While this can safely be ignored for
low-current things like small-scale outside lighting, that wouldn't
necessarily be the case for power applications such as sub-mains to
outbuildings.

The fact that such cables will probably have been sized on voltage drop
rather than current rating may provide some leeway. Nevertheless the
matter should be considered in the design. Table 4C1 of BS 7671 applies
and common experience suggests that things in the sun can reach
temperatures of 50 or 60 deg. (sometimes more). The de-rating factor
for 70 deg. rated PVC cables is 0.71 at 50 deg. and 0.50 at 60 deg. For
90 deg. rated XLPE cables the corresponding factors are 0.82 and 0.71
respectively.

If at all possible fix outdoor cables where they will stay out of the
full glare of the sun.

--
Andy
  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default Electrical cable outside


"Dorothy Bradbury" wrote...


Talking of cavities...
I prefer burying gov't officials face down, so you always
have somewhere to park the bike if you see what I mean.
--
DB.

Ah, so that's why the kids' bikes fall over, not enough visits from the
bureaucrats yet... We should be fine once the loft conversion gets under way
(

Mind you, with four motorbikes we're going to need to clone Prescott first,
aren't we? Just a question of accommodating the wider tyres, you see...

--
Dave H.
(The engineer formerly known as Homeless)

"Rules are for the obedience of fools, and the guidance of wise men" -
Douglas Bader


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical: working with 1/0 SER cable Wayne Whitney Home Repair 7 May 3rd 07 03:41 AM
Electrical cable outside Andy Lewis UK diy 14 February 8th 05 06:52 PM
Chipmunks and electrical cable ?? Harry Home Repair 10 October 29th 04 01:41 PM
Running Electrical Cable [email protected] Kill the 2 trees in e Home Repair 4 October 15th 04 07:02 AM