Hi All,

My spark has let me down - didnt turn up to look at the job this weekend
(Grrr)

SO... I am looking to get a parts list together so that I can order what
I need for my garage electric install.

I have 4mm2 2 core SWA with glands and a bare 6 way contactum CU for the
garage already.

I want a lighting circuit in the garage and a ring / radial for
sockets that will run various DIY power tools (not all at the same time)
and I would like a circuit for garden lights too.

The garage is about 10 meters away from the house CU and there is a
spare way in the house CU.

With this info, can anyone tell me what rating of breakers etc that I
should order for the house CU and what breakers RCDs I should order for
the garage?

Thanks
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default garage electrics

Cuprager wrote:

I have 4mm2 2 core SWA with glands and a bare 6 way contactum CU for the
garage already.


What is the total length of your SWA going to be?

Is your CU a split load one?

I want a lighting circuit in the garage and a ring / radial for sockets
that will run various DIY power tools (not all at the same time) and I
would like a circuit for garden lights too.

The garage is about 10 meters away from the house CU and there is a
spare way in the house CU.


What earthing system does your house use?

With this info, can anyone tell me what rating of breakers etc that I
should order for the house CU and what breakers RCDs I should order for
the garage?


Yup, if we have a bit more info.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 85
Default garage electrics

John Rumm wrote:
Cuprager wrote:

I have 4mm2 2 core SWA with glands and a bare 6 way contactum CU for
the garage already.


What is the total length of your SWA going to be?


It is going to be 10 meters long, maybe 11.


Is your CU a split load one?


No it isnt.


I want a lighting circuit in the garage and a ring / radial for
sockets that will run various DIY power tools (not all at the same
time) and I would like a circuit for garden lights too.

The garage is about 10 meters away from the house CU and there is a
spare way in the house CU.


What earthing system does your house use?


I am unsure to be honest, how can I check?


With this info, can anyone tell me what rating of breakers etc that I
should order for the house CU and what breakers RCDs I should order
for the garage?


Yup, if we have a bit more info.


Thanks for the reply John.



  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default garage electrics

In article ,
Cuprager writes:

What earthing system does your house use?


I am unsure to be honest, how can I check?


http://www.diyfaq.org.uk/electrical/...al.html#system

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 85
Default garage electrics

Andrew Gabriel wrote:
In article ,
Cuprager writes:
What earthing system does your house use?

I am unsure to be honest, how can I check?


http://www.diyfaq.org.uk/electrical/...al.html#system

Thanks for that, it looks like a TN-S system I have then.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default garage electrics

Cuprager wrote:
Andrew Gabriel wrote:


http://www.diyfaq.org.uk/electrical/...al.html#system

Thanks for that, it looks like a TN-S system I have then.


The would mean that you could probably export the house earth to the
garage since it is not that far away, and you won't need to be quite as
exacting maintaining the equipotential zone as you would with a TN-C-S
system. I take it the garage has a concrete floor or other solid floor?

If you are planning on using the space as a workshop then you need to
think about how you will achieve discrimination between the power and
lighting circuits. (i.e. the power circuit ought to have RCD protection,
but you probably don't want to lose the lights while you have a spinning
power tool in your hands). There are several options he A split
load CU would do this, alternatively you could use RCBOs for the power
circuits, or you could use a "whole CU" RCD and then provide some
battery backed up emergency lighting.

Since it is not a TT install, you won't need RCD protection at the head
end of the SWA - you can feed this from a spare non RCD protected way on
the house CU. You will need to think carefully about the size of
protective devices you use with regard to the discrimination issue
again, not much point in having (for example) a nice split load CU in
the garage if a short on the power circuit in there takes out the MCB in
the house at the same time (or instead of) the one for power the circuit
in the garage. One solution is to ensure the cascaded MCB is at least
two ratings down from its parent (refer to the manufactures data sheets
however since these characteristics vary between brands). Another way is
to use a HRC fuse carrier in the house CU.

You may also want to protect the feed that goes off into the garden on a
separate RCD since this circuit is the most likely to cause spurious
trip problems should dampness get into it.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default garage electrics

"Since it is not a TT install, you won't need RCD protection at the head
end of the SWA "


Could you explain the significance of this please ? I've a TT system
with the garage something like 16m away fed off a 15A fuse in the
house (seperate CU from the main split load CU with RCD). In the
garage there is a split load CU wirh RCD and an earth rod effectively
paralleled with the house rod.

Rob

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default garage electrics

robgraham wrote:

"Since it is not a TT install, you won't need RCD protection at the head
end of the SWA "


Could you explain the significance of this please ? I've a TT system
with the garage something like 16m away fed off a 15A fuse in the
house (seperate CU from the main split load CU with RCD). In the
garage there is a split load CU wirh RCD and an earth rod effectively
paralleled with the house rod.


If you have a TT system at the house, but the SWA submain is fed from a
non RCD protected CU, then you have a potential problem should either
the SWA be damaged in such a way as to cause a phase to earth fault, or
the downstream CU suffer a similar fault (say melting in a fire in the
outbuilding). You would then probably not get sufficient fault current
flowing to the (high impedance) earth to open the protective device at
the head end.

Having TN-S at the house, and TT in the garage however, is fine even
without RCD protection on the submain from the house.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default garage electrics

On 12 Feb, 09:13, Cuprager wrote:
Hi All,

My spark has let me down - didnt turn up to look at the job this weekend
(Grrr)

SO... I am looking to get a parts list together so that I can order what
I need for my garage electric install.

I have 4mm2 2 core SWA with glands and a bare 6 way contactum CU for the
garage already.

I want a lighting circuit in the garage and a ring / radial for
sockets that will run various DIY power tools (not all at the same time)
and I would like a circuit for garden lights too.

The garage is about 10 meters away from the house CU and there is a
spare way in the house CU.

With this info, can anyone tell me what rating of breakers etc that I
should order for the house CU and what breakers RCDs I should order for
the garage?

Thanks


Wise to use RCBOs in the garage rather than MCBs, otherwise any earth
leakage fault will leave you taken by surprise and plunged into
darkness while the power tool youre holding is running.

Lighting inside: 6A mcb or prferably 5A fuse, less likely to nuisance
trip.

Garden lighting 6A mcb unless youve got a very large property

garage sockets: if 13A sockets, 32A mcb with ring or 20A mcb with
radial.


NT

  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default garage electrics

Cuprager wrote:

Would something like the split load board below be a wiser choice at the
garage end? Then I could have the sockets and outside lights etc on the
RCD side of the board with the interior lighting coming off the non rdc
side?

http://www.tlc-direct.co.uk/Products/CMPS6slash63N.html


Yup, those are ok.

I refer to the building as a garage as it is garage sized, however it is
actually a shed so it has a wooden floor and not a concrete one.


The material the floor is made from becomes more significant if you have
a TN-C-S earth in the house and wish to export that. You then have the
usual potential problem of what happens when the supply neutral is
disconnected[1]. This means that you have to make sure that the same
Faraday cage earthing principle is employed in the outbuilding as is
used in the house to prevent this situation becoming very dangerous for
the occupants. With an earth floor for example (say in a greenhouse, or
cheap shed) it impossible to prevent easy access to a local earth which
would be at a very different potential to the exported one in a fault
condition. In these circumstances it is normal to make the outbuilding a
TT install in its own right and not export the main earth.



[1] With the house neutral disconnected no current flows, no voltage is
dropped over the electrical loads in the house and the neutral rises
toward 240V. The earth, being connected to the neutral at the house,
and therefore all exposed metalwork hence also rises to 240V

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrics CJC UK diy 72 December 14th 06 10:33 PM
Bathroom electrics sploop UK diy 21 April 27th 06 02:53 AM
Outside Electrics Charles Middleton UK diy 8 September 13th 05 01:05 PM
American electrics [email protected] UK diy 266 August 2nd 05 02:35 PM
Shed Electrics (Oh no, this again...!) Wilf UK diy 2 May 4th 04 02:03 PM


All times are GMT +1. The time now is 08:57 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"