Garden Electrics
When landscaping my back garden, I decided to install some electric
cable for future lighting and power requirements. I was advised to install 4-core cable which would run from a separate consumer unit in a shed, itself fed from the main consumer unit positioned in the house. I am now at the point of wanting to connect the electrics up, but have now been told that I needed a 5 core cable to feed both lighting and power sockets. Originally, I was told that it would be acceptable to operate a common neutral, leaving me with 2 lives (one for lighting and one for power), and the earth. If this method really can't be used, is it acceptable to use the outer armour as the earth, freeing up a cable for a second neutral? Forgive my apparent ignorance, but I want to try and understand my best options (short of digging up the garden and replacing the cable with a 5 core!) Thanks for any advice. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
MB wrote:
If this method really can't be used, is it acceptable to use the outer armour as the earth, freeing up a cable for a second neutral? In simple terms, and assuming that the cable is a steel wire armoured one, then yes you can use the armour for the earth. Forgive my apparent ignorance, but I want to try and understand my best options (short of digging up the garden and replacing the cable with a 5 core!) Outdoor electrics are not always straightforward, and there are a few gottchas. We would need a bit more background to give any really useful advice. In particular, what sort of lights and sockets are you feeding? How is the shed CU fed with power, and what sort of earthing system does your house use. Also what cable lengths are involved. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#3
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
MB wrote:
When landscaping my back garden, I decided to install some electric cable for future lighting and power requirements. I was advised to install 4-core cable which would run from a separate consumer unit in a shed, itself fed from the main consumer unit positioned in the house. I am now at the point of wanting to connect the electrics up, but have now been told that I needed a 5 core cable to feed both lighting and power sockets. Originally, I was told that it would be acceptable to operate a common neutral, leaving me with 2 lives (one for lighting and one for power), and the earth. If this method really can't be used, is it acceptable to use the outer armour as the earth, freeing up a cable for a second neutral? Forgive my apparent ignorance, but I want to try and understand my best options (short of digging up the garden and replacing the cable with a 5 core!) Thanks for any advice. Life is so much simpler if you run 12v around instead. No regulations, no significant safety issue, no rcd trips, no wiring failures due to water ingress, run the cable where you want, fuse it how you want, plenty of lights readily available that will run on it etc. You could keep your cable for 240 power and add another for 12v lighting. NT |
#4
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
John Rumm wrote:
MB wrote: If this method really can't be used, is it acceptable to use the outer armour as the earth, freeing up a cable for a second neutral? In simple terms, and assuming that the cable is a steel wire armoured one, then yes you can use the armour for the earth. I would still be tempted to put an earth spike in and earth to that AS WELL. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
|
#7
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Thanks everyone for your comments.
In answer to the queries: 1. I don't know what type of earthing the main house uses - sorry, I am not an electrician (and it probably shows). However, if it helps, the house is only a few years old - so this might indicate the type of earthing used? 2. The CU in the shed would be supplied from a spare 32A fuse on the main CU in the house. I ran a 6mm 3 core armoured cable underground to supply this from the house to the shed. 3. The distances involved are quite large. I don't have the figures to hand, but it is c. 40 metres from the house to the shed. From the shed 5 cables radiate out across the garden. The furthest point that I am looking to supply is about 80 metres from the shed. The cable for these runs is 4 core 2.5mm. Voltage drops were calculated at the time, and I know that it worked out considering the likely level of loading. 4. I intend to use low voltage lighting, but due to the distances involved, I had to run 240v to as near as possible to the point of use. Naturally, I needed 240v for the power outlets. I am intrigued about this idea of using separate lives for switching - my original intention was to have separate lighting zones in the garden, being able to turn each on independently. However, as I want to incorporate power sockets in these same zones using the same 4 core cable this is where the problem starts. If I am allowed to wire both lives from the 4 core into the same MCB in the shed, then presumably to allow the switching, I would pass the live for the lighting through a separate switch, while the live for the power sockets runs uninterupted? Alternatively, is it possible to 'link' two MCBs (a bit like the di-pole switch) so that if any maintenance is to carried out on one circuit, both have to be switched off at the same time? Thanks everyone for their interest - please let me know if you need any more clarification. Best regards Michael. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
MB wrote: 1. I don't know what type of earthing the main house uses - sorry, I am not an electrician Then you should fix both of these (to a small, but useful extent). Go to your local wholesaler and splash out a tenner or so for a copy of "The On-site Guide". This explains pretty much all you ever need to know regularly for most situations, including the rules you need to follow for your earthing here. Well worth a read. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Thank you for your advice.
I should make it clear that I have no intention of installing this myself - and will be looking for the help of a qualified electrican - I value my life too much. However, I do like to understand broadly what can and can't be done before paying the professional. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Sorry, John, I neglected to answer one of your questions.
The power sockets to be supplied would be single gang 13Amp sockets, probably the MK Masterseal type which have a good IP rating. I intend to use low volatge lighting, probably 12v - no SBS or SES type arrangements. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
|
#12
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
The Natural Philosopher wrote:
wrote: MB wrote: When landscaping my back garden, I decided to install some electric cable for future lighting and power requirements. I was advised to Life is so much simpler if you run 12v around instead. No regulations, no significant safety issue, no rcd trips, no wiring failures due to water ingress, run the cable where you want, fuse it how you want, plenty of lights readily available that will run on it etc. You could keep your cable for 240 power and add another for 12v lighting. Except that 3KW at 12v is about 300A, which requires twin cables slightly thicker the mains water pipes to do any distance without losing most of the voltage. And a ****ING big 12v transformer at the other end, I'd be surprised if the OP intended to put 3kW of lighting in his garden Chris Green: ... and you need very thick cable for any runs more than a few metres long which have significant power consumption through them. Very thick cables are one way, but not a necessity. Now that I know the OP is looking at long wiring runs, this is one point against 12v, but its still quite doable without resorting to monster cables. For very long runs the OP talks about, put one 12v light on each 2 cores, calculate the Vdrop on the cable, and set your 12v supply to deliver 12v + cable Vdrop. Calcs are needed to see what the Vdrop is, or I suppose it could be measured if preferred. Another option is to put lamps in groups of 2 in series, and run them from 24v. Andy Wade: NT: Life is so much simpler if you run 12v around instead. No regulations, Incorrect. The requirements of Part P and BS 7671 apply to the whole of no significant safety issue Significant risks of overheating and fire could exist if proper overcurrent protection is not provided. Correct fusing is elementary. Plus 12v PSUs normally have some sort of overcurrent protectiion built in. Protection against electric shock requires correct application of the many regulations in BS 7671 relating to SELV (or other ELV) systems. Since one can hold 12v without feeling a thing, its hard to see all those regs being relevant to shock protection IRL. The main real life advantage of 12v systems is their ability to survive water contamination. Generally speaking outdoor 240v lighting is prone too being troubled by water, and does not have the long term reliability of survivability that indoor kit has. 12v gets round this because it will continue to function (safely) when wet, and dry itself out. Plus at just 6v from ground, the risk is so low one could put a tongue ontoa bare wire and be unharmed. NT |
#13
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Except that 3KW at 12v is about 300A, which requires twin cables slightly
thicker the mains water pipes to do any distance without losing most of the voltage. And a ****ING big 12v transformer at the other end, It's garden lighting, not a floodlighting for a Premiership football field. Christian. |
#14
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Thanks for your reply Owain. A couple of questions.......
Very careful consideration will have to be given to equipotential zones. Can you explain what you mean by this? You can still do this if you use X10 or similar mains-borne remote control switching. This would allow you to control your lights etc from the house, or multiple locations. I don't understand how the X10 or similar would allow me to use a common neutral. Or are you assuming that both lives would be wired through the same MCB? I like the idea behind the X10 product - originally, I had intended to use a remote switch panel which used similar technology to that used in remote garage doors and gates etc. However, the range on these can be a bit limited. Thanks for your help. |
#15
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
MB wrote:
In answer to the queries: 1. I don't know what type of earthing the main house uses - sorry, I am not an electrician (and it probably shows). However, if it helps, the house is only a few years old - so this might indicate the type of earthing used? A fair chance you have TN-C-S then... however to confirm, have a read of a couple of pages starting he http://www.diyfaq.org.uk/electrical/....html#earthing If it is still not obvious then post a picture of your supply installation (i.e. where the supply cable enters the house and connects up to the meter etc) for us to have a look at. 2. The CU in the shed would be supplied from a spare 32A fuse on the main CU in the house. I ran a 6mm 3 core armoured cable underground to supply this from the house to the shed. Cable wise that sounds ok. The length of the cable would suggest that your shed will need to be a TT install (i.e. local earth spike with RCD protection on all circuits). In which case you would not usually use the exported earth from the house (it would be there to protect the cable, but not connected to the CU in the shed). If you do have a TN-C-S installation then that is another strong indication that the shed supply should be TT since otherwise you would need to export and continue the equipotential zone in the shed. Depending on its construction this may be difficult. 3. The distances involved are quite large. I don't have the figures to hand, but it is c. 40 metres from the house to the shed. From the shed 5 cables radiate out across the garden. The furthest point that I am looking to supply is about 80 metres from the shed. The cable for these runs is 4 core 2.5mm. Voltage drops were calculated at the time, and I know that it worked out considering the likely level of loading. With that long run you will need to watch voltage drop. A 2kw appliaance for example would pull the voltage down below spec even without including the 6mm SWA run to the shed. For lighting however it will probably be fine. 4. I intend to use low voltage lighting, but due to the distances involved, I had to run 240v to as near as possible to the point of use. Naturally, I needed 240v for the power outlets. In this circumstance you don't actually gain much advantage from the low voltage lighting. I am intrigued about this idea of using separate lives for switching - my original intention was to have separate lighting zones in the garden, being able to turn each on independently. However, as I want to incorporate power sockets in these same zones using the same 4 core cable this is where the problem starts. Can't see why. With 4 cores and a shield used as an earth you have plenty of options. For example you could have a live and neutral for a lighting circuit and use the other two wires for the socket. You could have three switched lives (starting at the same MCB) and one neutral to provide three discrete lighting zones (and no socket). If I am allowed to wire both lives from the 4 core into the same MCB in the shed, then presumably to allow the switching, I would pass the live for the lighting through a separate switch, while the live for the power sockets runs uninterupted? Yes, with the caveat that the lighting fixtures you use will need to be of a design that allows the use of a supply with a high protective device current rating. (i.e. a 16A MCB), Many lamp holders require lower rating protective devices than this. Alternatively, is it possible to 'link' two MCBs (a bit like the di-pole switch) so that if any maintenance is to carried out on one circuit, both have to be switched off at the same time? No, absolutely not. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#17
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
MB wrote:
Thanks for your reply Owain. A couple of questions....... Very careful consideration will have to be given to equipotential zones. Can you explain what you mean by this? I alluded to this in my ealier post as well. If you have a TN-C-S install, it is very important that your equipotential bonding is up to current standards. This is because there are some fault conditions, like for example a break in the neutral connection to your property, that could leave all exposed earthed metalwork in your house sat at mains voltage. This is because with TN-C-S the connection between neutral and earth is made at your house and not at the substation. Take away the neutral and everything floats up to mains voltage. The solution to this problem is to ensure that any metalwork that you are likely to come into contact with is all electrically bonded together, keeping it all at the same fault voltage, and hence unlikly to give rise to a serious shock hazard. Now when you take power outside, things become much more trickey. Access to an independant earth is in many cases now easy (you are standing on it!) So it is much harder to prevent you from simultaneously coming into contact with an electrical earth sat at a fault voltage, and a another local earth at a much lower potential. It is possible to do this in a well made shed or garrage with an insulating floor for example, but almost impossible in a building sat directly on the ground. For most practical applications it is simpler to disconnect from the house earth and use your own local one. You can still do this if you use X10 or similar mains-borne remote control switching. This would allow you to control your lights etc from the house, or multiple locations. I don't understand how the X10 or similar would allow me to use a common neutral. Or are you assuming that both lives would be wired through the same MCB? You don't have a common neutral as such, you just have one live and an associated neutral. There is no need to have multiple switched circuits anymore to achieve control of the lights. Basically you daisy chain your lights between a live and neutral on a circuit. The X10 device provides switching for the light local to the switch (not for the whole circuit necessarily - unless that is what you want). The control information that instructs a X10 device to swithc on or off passes down the mains wiring to it. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#18
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Owain & John
Thank you for your very useful advice. One final question (for now at least), would the X10 system work across multiple consumer units? For example, were I to plug the controller in somewhere in the house, the signal would have to pass through the main house CU, to the proposed shed CU and then down the cable to the lights. Thanks once again for your help. Michael. |
#19
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
Thanks - I'll probably give that a go.
|
#20
Posted to uk.d-i-y
|
|||
|
|||
Garden Electrics
In article . com,
"MB" writes: Owain & John Thank you for your very useful advice. One final question (for now at least), would the X10 system work across multiple consumer units? For example, were I to plug the controller in somewhere in the house, the signal would have to pass through the main house CU, to the proposed shed CU and then down the cable to the lights. Connect the X10 sender to a socket near to the CU if possible. That will give best possible chance of coverage to everywhere. -- Andrew Gabriel |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Shallow well far from the garden: Pump location question | Home Repair | |||
Garden Electrics - Advice Needed | UK diy | |||
Garden cabling / electricity - part two! | UK diy | |||
Building a two story garden building! | UK diy | |||
On the subject of a garden shed | UK diy |