Home |
Search |
Today's Posts |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Hello all,
A friend of mine has just (Yesterday) had a hot tub installed at his house, in the garden. All seems to work fine. However, We (I) just (out of curiosity) put one probe of a multimeter in the water and the other one into the grass next to the tub. I got a reading of about 35v AC @ 0.12mA between the two. We can't feel any shocks etc. from the water (with bare feet on the (wet!) grass) His earthing is provided by the armour of the main feed to the house. He has about 3m of 2.5mm T&E from the house CU to a plastic box, then about 15m of 2.5mm armoured cable between there and the CU in the shed (Three core, using one core for the earth), then from a 20A MCB, a FCU with a 13A fuse (Via about 40cms of 2.5mm T&E) then from there (Via a metal box) 2m of 2.5mm armoured cable (Three core, using one core for the earth) to a triple pole isolator near the tub (like this) http://www.tlc-direct.co.uk/Products/CMDX020.html Then from there, about 4m of 2.5mm armoured cable (Three core, using one core for the earth) to the tub. It is protected by two 30mA RCD's (One in the house, then a second one in a consumer unit in the shed next to the tub) We are not getting any RCD tripping. Is it just because this path to earth is favoured slightly, as it is a shorter distance than via the main supply armour? - If so, should we install an earth rod from the shed consumer unit, but leave the house earth connected too? (This seems the logical thing to do in my mind) If so, would 10mm cable between the CU and the rod be the right choice? Any advice would be gladly received! -- Sparks... (Not an electrician!) |
#2
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Sparks wrote:
Hello all, A friend of mine has just (Yesterday) had a hot tub installed at his house, in the garden. All seems to work fine. However, We (I) just (out of curiosity) put one probe of a multimeter in the water and the other one into the grass next to the tub. I got a reading of about 35v AC @ 0.12mA between the two. Kill the power to it immediately. Something serious is wrong. NT |
#3
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
|
#4
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
"Guy King" wrote in message
... The message . com from contains these words: Kill the power to it immediately. Something serious is wrong. Probably because the earth has been exported to some way from where it's actually earthed. -- Skipweasel Pay no attention to that man behind the curtain. That is what I was thinking, I assume the earth supplied by the power company is actually connected to planet earth at the substation, this, I assume, is quite a way away from the house, so some current is flowing to planet earth via the shorter route. So the solution is to install an earth rod near the tub? Sparks... |
#5
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Sparks wrote:
"Guy King" wrote in message ... The message . com from contains these words: Kill the power to it immediately. Something serious is wrong. Probably because the earth has been exported to some way from where it's actually earthed. -- Skipweasel Pay no attention to that man behind the curtain. That is what I was thinking, I assume the earth supplied by the power company is actually connected to planet earth at the substation, this, I assume, is quite a way away from the house, so some current is flowing to planet earth via the shorter route. So the solution is to install an earth rod near the tub? Possibly. In my installation here, with a substation (sic!) in the garden. My own very own substation (did you want 3 phase with that, sir?)..the outer sheath of the underground cable I had to lay is neutral AND ground both. I assume they connected that to teh frame of teh equipment in the cabinet. That leaves a potential (sic!) way for local house earth to be very different, if large currents flow, so I ran a bloody thick cable to an earth rod whacked 5 ft into the wet clay, from the consumer unit area...I am not sure whether or not the outer of the incoming is connected to earth somehow or not...I suspect we left it as neutral only. I managed to not destroy a valve radio once that some cheerful co apprentices had wired up with the loudspeaker across the mains, because it hummed as soon as it was plugged in, (but not switched on) a meter revealed that there was 15v AC between neutral and earth..and they had missed the fact that they had connected the switched live to the EARTHED side of the loudspeaker..and the neutral to the 'hot' side of it. What teh effects of this crass vandalism would have been I do not know. I had the satisfaction of getting out my soldering iron and removing all the b'modifications' , and turning it up to 11....;-) Sparks... |
#6
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
The message
from "Sparks" contains these words: That is what I was thinking, I assume the earth supplied by the power company is actually connected to planet earth at the substation, this, I assume, is quite a way away from the house, so some current is flowing to planet earth via the shorter route. So the solution is to install an earth rod near the tub? That'd depend on which earth system is in use. In our house there's a tag beside the incoming cable which says which sort of earth it's got. There are several. -- Skipweasel Pay no attention to that man behind the curtain. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Guy King wrote:
The message . com from contains these words: Kill the power to it immediately. Something serious is wrong. Probably because the earth has been exported to some way from where it's actually earthed. That could explain 3.5v but not 35v. NT |
#8
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
That could explain 3.5v but not 35v. Is it not possible that the water itself is acting as a weak electrolyte and that is where the REAL voltage being read is coming from? I.e .it's nothing to do with the mains. Easy to test for this. Just totally disconnect ALL wiring to the mains and see if the reading is still there. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Just Another DIY Fan wrote: That could explain 3.5v but not 35v. Is it not possible that the water itself is acting as a weak electrolyte and that is where the REAL voltage being read is coming from? I.e .it's nothing to do with the mains. Easy to test for this. Just totally disconnect ALL wiring to the mains and see if the reading is still there. electrolytic action would supply a DC current and not AC I would have thought. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
The message .com
from "Just Another DIY Fan" contains these words: Is it not possible that the water itself is acting as a weak electrolyte and that is where the REAL voltage being read is coming from? I.e .it's nothing to do with the mains. If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! -- Skipweasel Pay no attention to that man behind the curtain. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Guy King wrote:
The message .com from "Just Another DIY Fan" contains these words: Is it not possible that the water itself is acting as a weak electrolyte and that is where the REAL voltage being read is coming from? I.e .it's nothing to do with the mains. If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! Possibly, but more likely from pyrotechnics than battery manufacture. The higher the cell voltage, the faster things fry up. Cells of 4v or so are usually over in seconds, so 35v would be a firework or bomb. And an ac cell would certainly interest everyone NT |
#12
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
|
#13
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Just Another DIY Fan wrote: wrote: If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! True but it would be interesting to know how the extremely low current was measured as well before saying that the meter was displaying the truth. Many digital meters display all sorts of rubbish under adverse conditions. It would be interesting to put a frequency counter or a 'scope in place to see if it was indeed 50 Hertz mains ac. It could even be picking up stray rf ".It could even be picking up stray rf." At 35v !! that would be some new kind of power transmission, needs to be marketed, overhead cables will be no more !!! :-) |
#14
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
The message . com
from "Staffbull" contains these words: ".It could even be picking up stray rf." At 35v !! that would be some new kind of power transmission, needs to be marketed, overhead cables will be no more !!! :-) Wasn't it Tesla who wanted to transmit power by RF? -- Skipweasel Pay no attention to that man behind the curtain. |
#15
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Guy King wrote: The message . com from "Staffbull" contains these words: ".It could even be picking up stray rf." At 35v !! that would be some new kind of power transmission, needs to be marketed, overhead cables will be no more !!! :-) Wasn't it Tesla who wanted to transmit power by RF? -- Skipweasel Pay no attention to that man behind the curtain. Tesla coils, yes. Transmitted across small distances as the air breaks down, lightning does it fairly well over greater distances!! not the safest option for power transmission me thinks :-) Be a nice option though, would save me having to channel the cables in the extension :-) |
#16
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Staffbull wrote: Be a nice option though, would save me having to channel the cables in the extension :-) Dunno if anyone still does it but years ago was experiments with transmitting power through ground itself. |
#17
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Just Another DIY Fan wrote:
someone else wrote: If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! True but it would be interesting to know how the extremely low current was measured as well before saying that the meter was displaying the truth. Many digital meters display all sorts of rubbish under adverse conditions. in this case its displaying correct, as the source is low impedance. It would be interesting to put a frequency counter or a 'scope in place to see if it was indeed 50 Hertz mains ac. It could even be picking up stray rf. It probably is, but that will contribute only microvolts. Unless someone's hidden 3 car batteries under there and put them in the earth lead, its mains. And whats worse there are 2 dangerous faults. First mains is flowing through the water due to bad insulaiton or wrong wiring, and 2nd the thing isnt earthed. Whoever wired it up should kill themselves by using it. NT |
#18
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
We were somewhere around Barstow, on the edge of the desert, when the
drugs began to take hold. I remember Guy King saying something like: Is it not possible that the water itself is acting as a weak electrolyte and that is where the REAL voltage being read is coming from? I.e .it's nothing to do with the mains. If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! The Soap and FartGas Cell? -- Dave |
#19
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
The message
from Grimly Curmudgeon contains these words: If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! The Soap and FartGas Cell? Hmmm, methane fuel-cells. Won't the sulphur contamination poison the cell like it does the rest of us? -- Skipweasel Pay no attention to that man behind the curtain. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Sparks wrote:
A friend of mine has just (Yesterday) had a hot tub installed at his house, in the garden. In the open, or in some kind of outbuilding? What is the 'flooring' adjacent to the bath? Form later comments it does sound as it it's in the open. All seems to work fine. However, We (I) just (out of curiosity) put one probe of a multimeter in the water and the other one into the grass next to the tub. I got a reading of about 35v AC @ 0.12mA between the two. Presumably you mean 35 V open-circuit voltage (meter on volts) and 0.12 mA short-circuit current (meter on mA). The latter reading is pretty meaningless with the short meter probes just stuck into the water and ground. Repeat the test between the metalwork of the bath (presumably earthed to the exported house earth) and a more substantial electrode in the ground - a 2 ft. offcut of 15 mm copper water pipe is handy for this. His earthing is provided by the armour of the main feed to the house. And the house earthing system is what? TN-S, TN-C-S (PME) or TT? 35 V is quite a high difference between a supplier's mains earth and the local ground these days, with their multiply-earthed networks - but it clearly can occur. What's more to the point is that it might only take one fault in the network to turn that 35 V into 230 V and that would make getting in and out of the bath rather dangerous... In fact the whole installation sounds quite dangerous. An exported mains earth (probably TN) into an outdoor situation and no attempt to make an equipotential zone around the tub. And the two 30 mA RCDs in cascade, no discrimination between them, sends out a message about the lack of competence of the installer. To use an exported TN earth in this situation the very least I would have suggested is that there must be a bonded metal grid under the tub and immediate surroundings, and the bonding should meet the requirements for a main bonding conductor (min. 6mm^2 for TN-S or 10 for PME). Bits of 2.5 T&E (with 1.5 mm^2 earths) just aren't up to the job here. The practical fix is to convert this to a local TT system. Isolate and insulate the exported earth at the outdoor end of the cable and provide a local earth system to which the tub and all its ancillaries should be earthed, via a local main earth terminal. The local earth system should consist of an adequate rod electrode (probably 8 ft.) and the aforesaid mat or grid under the tub. If the latter is impracticable then I'd advise putting in four earth rods to form an exscribed square enclosing the tub site and its immediate surroundings. These should be connected together and to the local main earth terminal using 16 mm^2 copper conductors. I presume the water supply is via plastic pipe, but any local copper plumbing that is in contact with the ground should be main-bonded to the local main earth terminal in 10 or 16 mm^2. HTH -- Andy |
#21
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
In message , Guy King
writes The message from Grimly Curmudgeon contains these words: If you can find an electrochemical pair that can make 35 volts with a single cell you're going to be rich beyond the dreams of avarice! The Soap and FartGas Cell? Hmmm, methane fuel-cells. Won't the sulphur contamination poison the cell like it does the rest of us? I wonder if there are any figures relating to how human flatulence contributes to global warming .... and hence how bad a vegetarian diet might be for the planet -- geoff |
#22
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
"Andy Wade" wrote in message
... Sparks wrote: A friend of mine has just (Yesterday) had a hot tub installed at his house, in the garden. In the open, or in some kind of outbuilding? What is the 'flooring' adjacent to the bath? Form later comments it does sound as it it's in the open. All seems to work fine. However, We (I) just (out of curiosity) put one probe of a multimeter in the water and the other one into the grass next to the tub. I got a reading of about 35v AC @ 0.12mA between the two. Presumably you mean 35 V open-circuit voltage (meter on volts) and 0.12 mA short-circuit current (meter on mA). Hi Andy, I was hoping you would reply! Yes, this is correct, meter on volts, one probe in the water and one stuck in the wet surrounding ground, then meter on mA with the probles in the same place. The latter reading is pretty meaningless with the short meter probes just stuck into the water and ground. Repeat the test between the metalwork of the bath There is the problem, the frame is wooden and the tub is fiberglass - there arn't any metal bits on it! (presumably earthed to the exported house earth) and a more substantial electrode in the ground - a 2 ft. offcut of 15 mm copper water pipe is handy for this. His earthing is provided by the armour of the main feed to the house. And the house earthing system is what? TN-S, TN-C-S (PME) or TT? This is what I meant by "His earthing is provided by the armour of the main feed to the house" - So I guess TN-S or TN-C-S - how do we tell, or don't we care?) There are actually two, single phase, economy 7 meters, side by side in the house (Snot sure if they are on the same phase). A consumer unit directly connected to meter 1, then a switch fuse from the other meter, then on to anoter CU about 8M away in a different room. The supply to the shed is via the first CU (this has a 30mA RCD and about 8 MCB's) - The earth for this CU is connected to the armour of both incoming supplies (There are actually two seperate cables, side by side) 35 V is quite a high difference between a supplier's mains earth and the local ground these days, with their multiply-earthed networks - but it clearly can occur. What's more to the point is that it might only take one fault in the network to turn that 35 V into 230 V and that would make getting in and out of the bath rather dangerous... This was exactly my thought - not actually causing a physical problem right now, but it could later. In fact the whole installation sounds quite dangerous. An exported mains earth (probably TN) into an outdoor situation and no attempt to make an equipotential zone around the tub. There is no metal anywhere near the tub though - the tub is just sitting on a concrete base about 1ft wider than the tub, then there is mud/grass around this at the moment - the plan is to deck all around the tub. Here is a simalar tub http://www.bayocean.com/images/Hot-tub.jpg And the two 30 mA RCDs in cascade, no discrimination between them, sends out a message about the lack of competence of the installer. I assume this is because the house does not have a split load CU....yet! To use an exported TN earth in this situation the very least I would have suggested is that there must be a bonded metal grid under the tub and immediate surroundings, and the bonding should meet the requirements for a main bonding conductor (min. 6mm^2 for TN-S or 10 for PME). Bits of 2.5 T&E (with 1.5 mm^2 earths) just aren't up to the job here. The practical fix is to convert this to a local TT system. Isolate and insulate the exported earth at the outdoor end of the cable and provide a local earth system to which the tub and all its ancillaries should be earthed, via a local main earth terminal. They tub has an earth terminal inside it's control box, but there arn't any metal parts on or near the tub (Asside from the screws holding the side panels on, but these are screwed into the wooden structure of the tub) The local earth system should consist of an adequate rod electrode (probably 8 ft.) and the aforesaid mat or grid under the tub. If the latter is impracticable then I'd advise putting in four earth rods to form an exscribed square enclosing the tub site and its immediate surroundings. These should be connected together and to the local main earth terminal using 16 mm^2 copper conductors. The plan is to deck all around the tub wit hwooden decking. Does this change anything, as it will them be impossible to have one foot on the actual ground and another part of the body in the tub. I presume the water supply is via plastic pipe, No water supply, it is filled with the aid of a hose (Connected to the kitchen mixer, so it was filled with warm water, so it was ready to go as soon as it was full!) (It only holds about 1000l) but any local copper plumbing that is in contact with the ground should be main-bonded to the local main earth terminal in 10 or 16 mm^2. HTH -- Andy Thanks for your reply Andy, most appreciated :-) -- Sparks... (Not an electrician) |
#23
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
|
#24
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Sparks wrote:
[Quoting order changed to make arguments flow better.] There is the problem, the frame is wooden and the tub is fiberglass - there arn't any metal bits on it! [...] There is no metal anywhere near the tub though - the tub is just sitting on a concrete base about 1ft wider than the tub, then there is mud/grass around this at the moment - the plan is to deck all around the tub. Here is a simalar tub http://www.bayocean.com/images/Hot-tub.jpg [...] They tub has an earth terminal inside it's control box, but there arn't any metal parts on or near the tub (Asside from the screws holding the side panels on, but these are screwed into the wooden structure of the tub) OK, this clarifies things a bit. The tub is a Class 1 (earthed) appliance but the tonne of water in it is not in contact with any large earthed metal surface. Nevertheless there are presumably pump(s) and/or heater(s) which might bring the water into contact with some earthed metalwork internally. I now think your 35 V reading is a complete red herring. The water mass is probably loosely capacitively coupled to live mains voltage somewhere "in the works" and, being poorly earthed, is picking up a voltage by capacitive coupling (aka electrostatic induction). This will be pretty inconsequential from a safety point of view as the impedances involved are very high. Certainly the 120 uA touch current you measured is nowhere near high enough to give a dangerous shock, although it could result in perceptible tingles. And the house earthing system is what? TN-S, TN-C-S (PME) or TT? This is what I meant by "His earthing is provided by the armour of the main feed to the house" - So I guess TN-S or TN-C-S - how do we tell, or don't we care?) Oh we do care... There are actually two, single phase, economy 7 meters, side by side in the house (Snot sure if they are on the same phase). A consumer unit directly connected to meter 1, then a switch fuse from the other meter, then on to anoter CU about 8M away in a different room. The supply to the shed is via the first CU (this has a 30mA RCD and about 8 MCB's) - The earth for this CU is connected to the armour of both incoming supplies (There are actually two seperate cables, side by side) .... if the earthing is to the lead sheath (rather than armour, usually) of a supply cable then it's almost certainly TN-S. In fact the whole installation sounds quite dangerous. An exported mains earth (probably TN) into an outdoor situation and no attempt to make an equipotential zone around the tub. That point still stands, although the danger level is perhaps not quite so high as I first assumed, as there are no exposed-conductive-parts (i.e. no accessible metalwork connected to the appliance's earth terminal). And the two 30 mA RCDs in cascade, no discrimination between them, sends out a message about the lack of competence of the installer. I assume this is because the house does not have a split load CU....yet! It's not split-load, but you said it did have an RCD - so there are two 30 mA RCDs in cascade to the tub. An earth fault at the tub could trip either or both RCDs and, by the sound of it, possibly black out half the house. This is a violation of Regulations 314-01-01 and 314-01-02 of BS 7671. If there is an intention to convert the relevant house CU to split-load, with the tub feed on the non-RCD side then there is some logic to what's been done. [big snip] The plan is to deck all around the tub wit hwooden decking. Does this change anything, as it will them be impossible to have one foot on the actual ground and another part of the body in the tub. In principle no, I still think it needs to be converted to a local TT system by isolating the exported earth. Outdoors things like the concrete base and wooden decking could well be conductive enough to allow dangerous shock current to flow. But maybe you don't need to be quite so anal about the earth system as I suggested at first, if there really are no exposed-conductive-parts. A good single earth rod somewhere near the tub is probably adequate. -- Andy |
#25
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
"Andy Wade" wrote in message ... Sparks wrote: I assume this is because the house does not have a split load CU....yet! It's not split-load, but you said it did have an RCD - so there are two 30 mA RCDs in cascade to the tub. An earth fault at the tub could trip either or both RCDs and, by the sound of it, possibly black out half the house. This is a violation of Regulations 314-01-01 and 314-01-02 of BS 7671. If there is an intention to convert the relevant house CU to split-load, with the tub feed on the non-RCD side then there is some logic to what's been done. [big snip] The plan is to deck all around the tub wit hwooden decking. Does this change anything, as it will them be impossible to have one foot on the actual ground and another part of the body in the tub. In principle no, I still think it needs to be converted to a local TT system by isolating the exported earth. Outdoors things like the concrete base and wooden decking could well be conductive enough to allow dangerous shock current to flow. But maybe you don't need to be quite so anal about the earth system as I suggested at first, if there really are no exposed-conductive-parts. A good single earth rod somewhere near the tub is probably adequate. This may sound a silly question but; if the pump is double insulated, the tub and pipework are plastic, what's the earth rod going to be attached to? |
#26
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Fred wrote:
This may sound a silly question but; if the pump is double insulated, the tub and pipework are plastic, what's the earth rod going to be attached to? To the earth terminal which the OP referred to when he said: They tub has an earth terminal inside it's control box, So it does appear to be Class 1 equipment with parts that need earthing. It would be interesting toe have sight of the installation instructions; are they on the Web anywhere? -- Andy |
#27
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
On Tue, 19 Sep 2006 19:21:28 GMT Raden wrote :
I wonder if there are any figures relating to how human flatulence contributes to global warming .... and hence how bad a vegetarian diet might be for the planet It doesn't affect it since what is being released is what was taken in from the atmosphere a short while ago - unlike unlocking the CO2 in buried gas, coal and oil. In the new Building Regs Part L you get the same effect: put in a coal stove and the CO2 goes up (as compared with the default electric secondary heating); put in a woodburner and it tumbles. -- Tony Bryer SDA UK 'Software to build on' http://www.sda.co.uk |
#28
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
Tony Bryer wrote: On Tue, 19 Sep 2006 19:21:28 GMT Raden wrote : I wonder if there are any figures relating to how human flatulence contributes to global warming .... and hence how bad a vegetarian diet might be for the planet It doesn't affect it since what is being released is what was taken in from the atmosphere a short while ago - unlike unlocking the CO2 in buried gas, coal and oil. I am not entirely convinced raden was being serious :-). .... but allow me to correct this misunderstanding. The problem with flatulence (both human and bovine) is that it largely consists of methane (not CO2). Methane is a more powerful greenhouse gas than carbon dioxide (molecule for molecule), so turning lots of atmospheric carbon from CO2 to methane would be bad news. |
#29
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
The message
from Tony Bryer contains these words: I wonder if there are any figures relating to how human flatulence contributes to global warming .... and hence how bad a vegetarian diet might be for the planet It doesn't affect it since what is being released is what was taken in from the atmosphere a short while ago - unlike unlocking the CO2 in buried gas, coal and oil. Ah, well, it's not quite that simple. Methane is a much more potent greenhouse gas than CO2, so converting atmospheric CO2 to CH4 may be carbon neutral, but it certainly isn't greenhouse neutral. -- Skipweasel Pay no attention to that man behind the curtain. |
#30
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
"Andy Wade" wrote in message
... Fred wrote: This may sound a silly question but; if the pump is double insulated, the tub and pipework are plastic, what's the earth rod going to be attached to? To the earth terminal which the OP referred to when he said: They tub has an earth terminal inside it's control box, So it does appear to be Class 1 equipment with parts that need earthing. It would be interesting toe have sight of the installation instructions; are they on the Web anywhere? -- Andy I will ask him if his manual has them in! Thanks for your replies Andy, very helpful :-) And yes, there is a heater in this tub, it has a metal outer body (Not sure about the insides!), also, when it was installed, there was a problem with the blower (that blows bubbles in the tub, I noticed this has an earth connection too, although, this does not (Should not!) come into contact with the water, maybe the earth s here too, in case this fan gets flooded somhow. |
#31
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
In message , Tony Bryer
writes On Tue, 19 Sep 2006 19:21:28 GMT Raden wrote : I wonder if there are any figures relating to how human flatulence contributes to global warming .... and hence how bad a vegetarian diet might be for the planet It doesn't affect it since what is being released is what was taken in from the atmosphere a short while ago - unlike unlocking the CO2 in buried gas, coal and oil. I was thinking more of methane If I was talking about CO2, I would have used the word "lager" -- geoff |
#32
Posted to uk.d-i-y
|
|||
|
|||
Hot Tub - small potential differance between water and the ground
In message .com,
Martin Bonner writes Tony Bryer wrote: On Tue, 19 Sep 2006 19:21:28 GMT Raden wrote : I wonder if there are any figures relating to how human flatulence contributes to global warming .... and hence how bad a vegetarian diet might be for the planet It doesn't affect it since what is being released is what was taken in from the atmosphere a short while ago - unlike unlocking the CO2 in buried gas, coal and oil. I am not entirely convinced raden was being serious :-). ... but allow me to correct this misunderstanding. The problem with flatulence (both human and bovine) is that it largely consists of methane (not CO2). Methane is a more powerful greenhouse gas than carbon dioxide (molecule for molecule), so turning lots of atmospheric carbon from CO2 to methane would be bad news. Gold star that man -- geoff |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|