As part of the planning for my new kitchen, I looked at the current layout
today. I would have helped my dad to rewire it but Part P seems to have put
paid to that. I would still like to know what to ask the electrician and
get an idea of what he will do. I've done plenty of searching on here and
found lots of useful information but not everything yet.

As is usual for a 70s two-bed semi, the current layout is inadequate and in
my case badly altered by previous owners. The house has a single ring main
with a 32A MCB and cooker radial also with 32A MCB.

The kitchen has two single sockets above the worktop on the ring, one each
side of the hob. From one, a spur cable runs diagonally unshielded under
the plaster to the cooker hood, with no form of isolation! The other single
socket has a spur cable going to a socket under the worktop, itself having a
spur cable along the floor to a small CU with RCD under the sink for
powering the garden circuit. The cooker outlet (with socket) supplies the
electric oven and igniter for the gas hob.

Obviously the diagonal hood cable is a no-no but I was wondering how the
cable(s) to the hood could be run. Dropping from the ceiling, as the two
sockets above the worktop are wired, would be feasible but where could an
isolation switch go? I wouldn't want it behind the chimney. How is it done
from below? Keeping to the vertical/horizontal from an accessory rule, a
cable dropped vertically from the hood could necessitate an accessory behind
the hob? I won't be having units on either side of the extractor. Is
putting the cable in metal conduit, a switched FCU to one side of the hob
and unswitched outlet behind the hood the best method?

Under Part P, must the approved person do absolutely everything? If I left
some nicely chased walls in the (to be) gutted kitchen, where the
electrician would want them, I gather he could use them? To save on
expensive electrician's time and cost, it would make sense to do as much
prep work as possible. Where does Part P draw the line on what is
electrical? Could I put back-boxes in?

I expect a new ring main to supply the kitchen would be desirable. The
kitchen items on the ring would take a dishwasher, fridge freezer, combi
microwave, gas hob, extractor and kettle. The washing machine and tumble
drier are in the downstairs loo - but that's another wiring issue.

I expect an electrician would route the cable along the wall in the adjacent
integral garage containing the consumer unit. Since the cable would not be
coming from the ceiling, would it be acceptable to run cables on the surface
(in trunking if necessary) in the void behind base units? This would be on
the right level for the hob and dishwasher outlets (accessed from units to
the side of these).

Even if the wall was chased horizontally on the line of the above-worktop
sockets, how would the dishwasher cable be dropped? The dishwasher will be
midway between the cooker and sink-drainer, with the outlet under the
drainer. Could the cable do a right angle above the drainer, in the
horizontal plane of the above-worktop sockets and vertical plane of
dishwasher outlet, even though there is no visible accessory at the point of
the right-angle?

Would the following be a valid new ring layout, with S being a switched
socket, the bottom two being for the dishwasher (right) and hob (left)
mounted under the worktop in accessible cupboards. Everything else is
above. The rough location of the appliances is shown, the cooker outlet for
the oven is not. Hopefully the ASCII art is readable.


Hood---|
(m/w) (kettle) |
|
---SS------SS------SS--------FCU----SS-------|
-| (Hob) |
| (f/f) (Oven} (D/W) |
| |
|-----------------S-------------------------S


This suggestion ignores adding RCD protection. Is it especially necessary?
Is the electrician likely to suggest it?

Lastly, I need to move the garden electrics, as the CU is mounted in the
sink unit that is being replaced, and the spur socket from which it is
unsuitably wired will no longer be there. As garden wiring is notifiable,
even though it is already there, I presume I cannot do the rewiring for
that? Would the electrician consider spurring from the bottom-right S above
if he did it?

Sorry there's lots here, but thanks in advance for any helpful answers.

James



  #2   Report Post  
John Rumm
 
Posts: n/a
Default

James H wrote:

As part of the planning for my new kitchen, I looked at the current layout
today. I would have helped my dad to rewire it but Part P seems to have put
paid to that. I would still like to know what to ask the electrician and


Why? Part P does not stop you DIYing it. The only difference from before
is you need to either a) submit a building notice to the council prior
to starting work, or b) ignore part P ;-)

The kitchen has two single sockets above the worktop on the ring, one each
side of the hob. From one, a spur cable runs diagonally unshielded under
the plaster to the cooker hood, with no form of isolation! The other single
socket has a spur cable going to a socket under the worktop, itself having a
spur cable along the floor to a small CU with RCD under the sink for
powering the garden circuit. The cooker outlet (with socket) supplies the
electric oven and igniter for the gas hob.


Hmmm nice ;-)

What does the garden circuit feed?

Obviously the diagonal hood cable is a no-no but I was wondering how the
cable(s) to the hood could be run. Dropping from the ceiling, as the two
sockets above the worktop are wired, would be feasible but where could an
isolation switch go? I wouldn't want it behind the chimney. How is it done


Is there a cupboard adjacent to the hood? If so you could have a single
socket in the cupboard and simply plug the cooker hood into that.

from below? Keeping to the vertical/horizontal from an accessory rule, a
cable dropped vertically from the hood could necessitate an accessory behind
the hob? I won't be having units on either side of the extractor. Is
putting the cable in metal conduit, a switched FCU to one side of the hob
and unswitched outlet behind the hood the best method?


If you mechanically protect the cable than you can run it in non
standard places (or bury it 2" deep if the walls are thick enough).

Under Part P, must the approved person do absolutely everything? If I left


Nope you can do it all yourself (with building notice, and allowing the
council to have it inspected at the stages they want). Councils in
general don't seem to have got their act together with this, so you will
need to speak to yours to find out how they play it.

some nicely chased walls in the (to be) gutted kitchen, where the
electrician would want them, I gather he could use them? To save on
expensive electrician's time and cost, it would make sense to do as much
prep work as possible. Where does Part P draw the line on what is
electrical? Could I put back-boxes in?


Yes you can...

I expect a new ring main to supply the kitchen would be desirable. The


Yup. Possibly a non RCD protected radial to feed the fridge and boiler
as well.

kitchen items on the ring would take a dishwasher, fridge freezer, combi
microwave, gas hob, extractor and kettle. The washing machine and tumble
drier are in the downstairs loo - but that's another wiring issue.

I expect an electrician would route the cable along the wall in the adjacent
integral garage containing the consumer unit. Since the cable would not be
coming from the ceiling, would it be acceptable to run cables on the surface
(in trunking if necessary) in the void behind base units? This would be on
the right level for the hob and dishwasher outlets (accessed from units to
the side of these).


Yup probably.

Even if the wall was chased horizontally on the line of the above-worktop
sockets, how would the dishwasher cable be dropped? The dishwasher will be
midway between the cooker and sink-drainer, with the outlet under the
drainer. Could the cable do a right angle above the drainer, in the
horizontal plane of the above-worktop sockets and vertical plane of
dishwasher outlet, even though there is no visible accessory at the point of
the right-angle?


Not quite sure I am am visualising this correctly, but it sounds like
you are saying you want to come straight up from the under worktop
socket to a cable chase that runs horizontally between two other
accessories (one possibly being the isolating switch for said socket),
turn 90 degrees and carry on to the switch? If so then it complies with
the requirement that the cable runs are in direct line of the visible
accessories so sounds ok to me.

Would the following be a valid new ring layout, with S being a switched
socket, the bottom two being for the dishwasher (right) and hob (left)
mounted under the worktop in accessible cupboards. Everything else is
above. The rough location of the appliances is shown, the cooker outlet for
the oven is not. Hopefully the ASCII art is readable.


Hood---|
(m/w) (kettle) |
|
---SS------SS------SS--------FCU----SS-------|
-| (Hob) |
| (f/f) (Oven} (D/W) |
| |
|-----------------S-------------------------S



Layout looks mostly ok (depending on how to solve the extractor issues).
You want to design the cable layout so that you don't end up
concentrating all the big loads at one end of the circuit - you want
them spread out around the ring, or toward the middle of it. Things like
kettles/toasters you can largely ignore since they are short duration
loads.

This suggestion ignores adding RCD protection. Is it especially necessary?
Is the electrician likely to suggest it?


Is there any possibility that someone may in future plug in an appliance
that they may use outside? If so then the answer is a definite yes. You
have also not mentioned what type of earthing system you have (i.e. TN
or TN-C-S with an earth provided along with the supply, or a TT setup
with local earth rod). If your earthing is TT then *all*circuits need
RCD protection.

Lastly, I need to move the garden electrics, as the CU is mounted in the
sink unit that is being replaced, and the spur socket from which it is
unsuitably wired will no longer be there. As garden wiring is notifiable,
even though it is already there, I presume I cannot do the rewiring for
that? Would the electrician consider spurring from the bottom-right S above
if he did it?


Again it depends on what we are talking about. If it is just a single
exterior socket for example, then it would not be uncommon to provide
that from the ring or a spur from it. Perhaps with the addition of a
dedicated RCD if the main supply circuit is not already protected by it.
If on the other hand you are talking about a 30m cable run to a
collection of out buildings which have power and light circuits then you
would be looking for a dedicated submain run from the main CU or even
taken as a split feed before it.

Sorry there's lots here, but thanks in advance for any helpful answers.


Hope that helps...


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
James H wrote:
Obviously the diagonal hood cable is a no-no but I was wondering how the
cable(s) to the hood could be run.


IIRC, It's ok if either deep enough or protected. If this makes it easier,
I'd put it in steel conduit.

--
*There's two theories to arguing with a woman. Neither one works *

Dave Plowman London SW
To e-mail, change noise into sound.
  #4   Report Post  
James H
 
Posts: n/a
Default

Thanks for the replies.

Why? Part P does not stop you DIYing it. The only difference from before
is you need to either a) submit a building notice to the council prior to
starting work, or b) ignore part P ;-)


Ignoring Part P seems a tempting option, saying it was all done and dusted
in late 2004/early 2005, honest guv'nor
Looking through the council's building control webpages, they have forms for
building work insisting the electrician details are filled in for Part P,
with no mention of inspecting DIY. I'm guessing they're one of the many
that haven't prepared enough. I'll give them a call.

Is there a cupboard adjacent to the hood? If so you could have a single
socket in the cupboard and simply plug the cooker hood into that.


I'm not having cupboards either side. From my days in a shared house,
having to clear the grease off the units either side of the hood wasn't
pleasant and put me off having anything near the hood. That said, in those
days I would often enter the kitchen to find the fog of a full fry-up in
progress with the hood turned off. Nice.

Going deep enough into the walls can't be done so shielding seems the best
method.

This suggestion ignores adding RCD protection. Is it especially
necessary?
Is the electrician likely to suggest it?


Is there any possibility that someone may in future plug in an appliance
that they may use outside? If so then the answer is a definite yes. You
have also not mentioned what type of earthing system you have (i.e. TN or
TN-C-S with an earth provided along with the supply, or a TT setup with
local earth rod). If your earthing is TT then *all*circuits need RCD
protection.


I don't have a TT earth so I won't need everything RCD'd. The garden
circuit just contains a water feature, pair of outdoor uplighters and a
floodlamp. I would also like an outdoor socket installed, protected by the
RCD of the existing garden setup. That would save having to make the socket
in the kitchen nearest the back door RCD protected.

Sounds like spurring off the new kitchen ring using the RCD CU for the
garden should be okay.

Thanks,

James


  #5   Report Post  
Owain
 
Posts: n/a
Default

James H wrote:
I'm not having cupboards either side. From my days in a shared house,
having to clear the grease off the units either side of the hood wasn't
pleasant and put me off having anything near the hood. That said, in those
days I would often enter the kitchen to find the fog of a full fry-up in
progress with the hood turned off. Nice.


If you're using an electric hob, take the fan supply off the load
terminals of the cooker control unit, via an unswitched FCU. That way
the fan will be on whenever the cooker is on.

Owain





  #6   Report Post  
 
Posts: n/a
Default

Nowt to do with electrics, but line the tops of the cupboards with old
newspaper.
In this way, when you do the five-year-thorough clean all you need do
is
remove, discard and replace the contaminated newspaper.
I've learned the hard way...

HTH

Mungo :-)

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Routing laundry drain to kitchen drain possible? orangetrader Home Repair 11 March 7th 05 03:14 AM
Cabinet, Furniture Design Software, Autodesk QuickCAD v8.0, Punch Software Home Design Architectural Series 18 v6.0, SOLID V3.5 - CABINET VISION, Cabinet Design Centre v7.0 - Cubit, 20-20 Kitchen Design V6.1,Cabinet Vision Solid, Planit Millennium II athens.gr. Home Repair 0 September 3rd 04 07:44 AM
telephone wiring question barry martin Home Repair 0 August 11th 04 02:43 AM
help kitchen cooker wiring belgarion UK diy 5 March 2nd 04 12:05 PM
Cabinet Design Centre v7.0 - Cubit, 20-20 Kitchen Design V6.1,CabinetVision Solid, Planit Millennium II [2 CDs], TurboCAD Pro V9.0 [3 CDs] (Turbocad Pro V9.0, TurboCad Deluxe 9.2 FloorPlan v7.3, TurboProjectExpress v4S), Big Hammer Do It Yourself (De TEL Woodworking 0 February 6th 04 06:34 AM


All times are GMT +1. The time now is 01:45 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"