  #1   Report Post  
Sparks
 
Posts: n/a
Default Connecting two ovens

I currenly have a 6mm cable running from a 32A MCB in my CU to where my
ovens are going to be put.

The two ovens are rated at 3500w and 3600w.

I want to use the same 6mm feed for both.

Do need to install a fuse at the oven, nearer to the ovens rating (Say 16A)
If so, where do I get such a fuse, as a normal FCU only goes up to 13A.

Personally, I would want to install a fuse, so if the oven tries to draw too
much for any rason,the fuse/MCB whatever, will blow.trip, but do I actually
need to do this!?

The old ovens we had was a double oven, and a steam oven, the steam oven was
only rated at about 800w or so, and this had been connected via 2.5mm to the
isolator (connected to a 32A MCB in the CU)

Also, what size cable do I need to use between the oven and the isolator?
Would 2.5mm be ok, as this is a short run (about 1m) or do I need to use 4
or 6mm?

Ta!

Sparks...


  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default

The two ovens are rated at 3500w and 3600w.

I want to use the same 6mm feed for both.


This will depend on the oven. I would suspect that most UK specific ovens
over 3kW will be OK at 32A. However, an oven in the 3kW to 3.7kW range might
be a European model designed for 16A and not expecting a 32A circuit. This
is because the UK commonly uses 32A circuits where the Europeans would
expect multiple 16A ones.

You basically need to see what the installation instructions say. If you
can't find any, or they stipulate 16A or 20A protection, then you need to do
one of two things:

1. Run an additional circuit from the MCB (presumably you're trying to avoid
this).
2. Install a "local" consumer unit at the end of the 6mm cable (preferably
hidden in a cupboard or suchlike) with 2 16A MCBs. From there, 2.5mm cable
can be run to the ovens.

With a 25A fusing requirement, you might get away with it using diversity,
although I'm not entirely sure you are allowed to use it for two ovens,
rather than one oven and hob.

Also, what size cable do I need to use between the oven and the isolator?
Would 2.5mm be ok, as this is a short run (about 1m) or do I need to use 4
or 6mm?


2.5mm will normally be fine, even using a 32A MCB only. However, it must be
short and you should really calculate that the earth loop impedence will
allow immediate disconnection of the MCB. When using the 16A MCBs, the 2.5mm
can afford to be much longer, as the maximum allowed earth loop impedence
will be double.

Christian.


  #3   Report Post  
Sparks
 
Posts: n/a
Default

This will depend on the oven. I would suspect that most UK specific ovens
over 3kW will be OK at 32A. However, an oven in the 3kW to 3.7kW range
might
be a European model designed for 16A and not expecting a 32A circuit. This
is because the UK commonly uses 32A circuits where the Europeans would
expect multiple 16A ones.

You basically need to see what the installation instructions say. If you
can't find any, or they stipulate 16A or 20A protection, then you need to
do
one of two things:


OK, the combination Microwave oven is a Siemens HB86K.70B
The Installation instructions only say
"Great Britan and Australia
This appliance is designed for permanant connection to a 3-wire cable.
This appliance must only be connected by a qualified electrician in
accordance with the wiring diagram attached to the connecting cable"

This "Wiring diagram" is simply some wording, explaing what colour cable is
what, and also stating "A plug must have a nominal current of at least 15
ampere or more"

So no mention of any fusing requirements there!

The normal oven hasn't got a cable, but does have a beefy looking cable
clamp.

Sparks...


  #4   Report Post  
Christian McArdle
 
Posts: n/a
Default

So no mention of any fusing requirements there!

Without further information, I'd have to go for one of the 16A options.
Either a local consumer unit with 2 16A MCBs or an additional circuit back
to the main CU.

Alternatively, you could contact the manufacturer's technical department.

Christian.


  #5   Report Post  
Sparks
 
Posts: n/a
Default

So no mention of any fusing requirements there!

Without further information, I'd have to go for one of the 16A options.
Either a local consumer unit with 2 16A MCBs or an additional circuit back
to the main CU.

Alternatively, you could contact the manufacturer's technical department.


Well Siemens were pretty useless really

"All I can advise is the current rating of the appliances. The fuse rating
should be the next size up.
For the HB86K70B is a 3.6KW appliance which takes 16amps For the HB76L550B
is a 3.5KW appliance which takes 16 amps"

Looks like a small 2 way CU un the cupboard above then (Not really what I
wanted to do!!)

Sparks...


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
wiring for ovens etc finney UK diy 4 March 10th 05 03:25 PM
13 amp fan ovens - any good? Alister Whitford UK diy 13 February 23rd 05 09:07 PM
OT new ovens James Salisbury UK diy 2 November 28th 04 11:08 PM
Need Help Connecting TTL Data to RS232 Doug Kent Electronics 3 July 28th 04 12:00 AM
strange problem connecting light to dimmer John Hunter Home Repair 6 January 19th 04 07:57 PM


All times are GMT +1. The time now is 09:31 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"