You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I
need THWN wire last week. What wire sizes should I order?

Karl


  #2   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 353
Default pump wire sizes


"Karl Townsend" wrote in message
anews.com...
You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red wire -
27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I need
THWN wire last week. What wire sizes should I order?

Karl


I don't have my book at home to figure it out but, explain to me why the
imbalance, I'm curious.



  #3   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 762
Default pump wire sizes

The run cap sits at the top of the well in the control box, the motor is
at the bottom of the well. These are leads that you normally don't see
when you have a motor with L1/L2 and included cap. The yellow and black
amps add to the the red amps with a bit of phase shift to account for
the difference.

Tom Gardner wrote:
"Karl Townsend" wrote in message
anews.com...
You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red wire -
27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I need
THWN wire last week. What wire sizes should I order?

Karl


I don't have my book at home to figure it out but, explain to me why the
imbalance, I'm curious.


  #4   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 30
Default pump wire sizes

On Jul 12, 7:28*pm, "Karl Townsend"
wrote:
You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More

If you have a long run and high current, mighy be a good time to
consider a relay close to the pump, you can run thinner wires from the
switch to the relay... Joel in FLorida
=========
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I
need THWN wire last week. What wire sizes should I order?

Karl


  #5   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 762
Default pump wire sizes

Your load could be (maginally) handled by a #10 wire in terms of not
overheating the wire and insulation. So that means you need to size the
wire for voltage drop. A quick calc (assuming 2 wire circuit) says that
#10 copper will give you slightly over 10% voltage drop out at the well
head, #8 gives 6% drop, #6 would give you 4% drop. If this is an extreme
service unit (running for weeks on end during the summer when the grid
supply voltage is sagging), go with the heavier wire.

Karl Townsend wrote:
You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I
need THWN wire last week. What wire sizes should I order?

Karl




  #6   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 30
Default pump wire sizes

Well, I didn't read the original post carefully enough, I guess the
relay was a stupid suggestion, considering the long run is from the
source to the pump - not much you can do here except use larger wires
- if the switch is a long way from the pump, a relay would let you use
lighter wires to and from the switch... joel
======
On Jul 13, 7:37*am, " wrote:


If you have a long run and high current, mighy be a good time to
consider a relay close to the pump, you can run thinner wires from the
switch to the relay... Joel in FLorida
=========




  #7   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 3,286
Default pump wire sizes


"RoyJ" wrote in message
m...
Your load could be (maginally) handled by a #10 wire in terms of not
overheating the wire and insulation. So that means you need to size the
wire for voltage drop. A quick calc (assuming 2 wire circuit) says that
#10 copper will give you slightly over 10% voltage drop out at the well
head, #8 gives 6% drop, #6 would give you 4% drop. If this is an

....
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I


I assume you're talking the red wire. How does a #6 red, #8 black, and
#10 yellow compute? I need to order Monday morning.

This is just a V=IR problem. Anybody know where to find R per 100' on
different wire sizes?

Karl


  #8   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 558
Default pump wire sizes

On Sat, 12 Jul 2008 18:28:53 -0500, "Karl Townsend"
wrote:

You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I
need THWN wire last week. What wire sizes should I order?

Karl


Oops - well, I have the book in front of me now...

For a two wire single phase circuit:
Vd = (2K x L x I) / Cm *or* Cm = (2K x L x I) / Vd

Vd - Voltage drop
I - current in amps
L - one-way length of circuit
K - resistance in ohms of one circular mil foot of conductor
K = 12.9 for Copper 21.2 for Aluminum at 75C
Cm - cross section of wire in circular mils
#10 10380
#8 16510
#6 26240
#4 41740
#2 66360
#1 83690
#1/0 105600
#2/0 133100
#3/0 167800
#4/0 211600

5 horse 1Ph well pump might be 28 A Full Load, but it should have a
200% breaker or fuse to hold on the start surges. 60A would be a
conservative sizing. So we do the math for 60A and get...

42.4 x 380 X 60 / 5 volts = 193344 cm = 4/0 Aluminum

25.8 x 380 x 60 /5 volts = 117648 cm = 2/0 Copper

5 volts drop during the start surge is being rather conservative, but
now you have the numbers - and you can decide how conservative you
want to be.

Remember you also have that 180' of pump lead going down the well to
the motor that is NOT figured in, and unless you pull the whole pump
and stack out of the hole you can't change it.

2" Rigid PVC Sched 40 max fill is three 300MCM THHN/THWN or four #4/0.

Myself, I would go for a 70A or 100A sub-panel out at the wellhead.
If the majority of the load is 240V you can undersize the neutral one
gauge from the hots, but not under the normal minimum. 4/0 4/0 2/0 4
makes it easy to ID the neutral and ground.

That way WHEN (not if) the load grows out in that direction (*) for
lights or a battery charger and block heater for the tractor, or a
chlorine dosing pump because some bugs get into the well, you don't
have to rework it again. And wire prices aren't going to go down
much, if at all.

* - We do work for a few ranches and camps, it always does.

Oh, and if you want to move the pressure switch to the wellhead (I
would, save on running those control leads and eliminate several
points of failure) you need to either move one of the stored-pressure
tanks to the wellhead or add a surge chamber with a needle valve in
front of the pressure switch. That should smooth the pressure surges
in the line enough to stop any short-cycling.

-- Bruce --
  #9   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,417
Default pump wire sizes

On Sat, 12 Jul 2008 18:28:53 -0500, "Karl Townsend"
wrote:

You may remember I asked about the pressure switch wire for my pump last
week...

The group convinced me to replace all the wires and put in conduit. More
investigation shows I should move the pump control box to near the pressure
switch at the same time, in the basement.

Anyway, I now will have a 380 foot run from the basement to the well with 2"
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I learned I
need THWN wire last week. What wire sizes should I order?

Karl


This Redjacket document for their control boxes has
suggested cable length and size for their submersible pumps:

http://www.redjacke****erproducts.com/pdf/BRJCONTRO.pdf

Maybe that will give you some figures to go by.

--
Leon Fisk
Grand Rapids MI/Zone 5b
Remove no.spam for email
  #10   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 35
Default pump wire sizes

In article s.com,
"Karl Townsend" wrote:

"RoyJ" wrote in message
m...
Your load could be (maginally) handled by a #10 wire in terms of not
overheating the wire and insulation. So that means you need to size the
wire for voltage drop. A quick calc (assuming 2 wire circuit) says that
#10 copper will give you slightly over 10% voltage drop out at the well
head, #8 gives 6% drop, #6 would give you 4% drop. If this is an

...
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I


I assume you're talking the red wire. How does a #6 red, #8 black, and
#10 yellow compute? I need to order Monday morning.

This is just a V=IR problem. Anybody know where to find R per 100' on
different wire sizes?

Karl


http://www.powerstream.com/Wire_Size.htm

Handy...


  #11   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 5,154
Default pump wire sizes

On Sun, 13 Jul 2008 11:53:42 -0500, with neither quill nor qualm,
"Karl Townsend" quickly quoth:


"RoyJ" wrote in message
om...
Your load could be (maginally) handled by a #10 wire in terms of not
overheating the wire and insulation. So that means you need to size the
wire for voltage drop. A quick calc (assuming 2 wire circuit) says that
#10 copper will give you slightly over 10% voltage drop out at the well
head, #8 gives 6% drop, #6 would give you 4% drop. If this is an

...
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I


I assume you're talking the red wire. How does a #6 red, #8 black, and
#10 yellow compute? I need to order Monday morning.

This is just a V=IR problem. Anybody know where to find R per 100' on
different wire sizes?


Would that be for A/C, D/C, or Bisexual wire, Karl? wink

http://www.epanorama.net/documents/w...esistance.html
http://www.eskimo.com/~billb/tesla/wire1.txt
http://www.wiringfordcc.com/trakwire.htm


P.S: Shouldn't guys with pumps be asking about _pipe_ sizes instead of
wire sizes?

--
"Giving every man a vote has no more made men wise and free
than Christianity has made them good." --H. L. Mencken
---
  #12   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 76
Default pump wire sizes

Karl,

guage: ohms/foot:
8 .000628
6 .000395
4 .000248

Hul


Karl Townsend wrote:

"RoyJ" wrote in message
m...
Your load could be (maginally) handled by a #10 wire in terms of not
overheating the wire and insulation. So that means you need to size the
wire for voltage drop. A quick calc (assuming 2 wire circuit) says that
#10 copper will give you slightly over 10% voltage drop out at the well
head, #8 gives 6% drop, #6 would give you 4% drop. If this is an

...
conduit installed. The pump uses three wires with loads as follows: red
wire - 27.5 amps, black wire - 19.1 amps, yellow wire 10.8 amps. I


I assume you're talking the red wire. How does a #6 red, #8 black, and
#10 yellow compute? I need to order Monday morning.


This is just a V=IR problem. Anybody know where to find R per 100' on
different wire sizes?


Karl



  #13   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 523
Default pump wire sizes

Roy J sez:

"I don't have my book at home to figure it out but, explain to me why the imbalance, I'm curious"

If I might take a stab at it, my W.A.G. is:

Karl, like so many who build RPCs, probably lost sight of the need to properly balance the
idler-motor / load network. They throw in a few random-valued capacitors and step back to admire
their work, giving no thought to completing the job in anything resembling good electrical design.
They seem totally thrilled their RPC will start and run and assume that is good enough.

In all likelihood the currents are measured with a "clamp-on" type of ammeter. In that process true
currents are not being measured among wildly different phase relationships in the 3 leads of an
unbalanced RPC.

IMO, guys like Karl would do well to build proper RPCs before asking questions on RCM about wire
sizing for bogus currents. People like Bruce with electrical backgrounds would be better able to
give meaningful advice re. wire sizing if they had any notion of what the 3-phase currents in
question were all about. It is impossible, as far as I know, to accurately measure unbalanced
3-phase currents with an clamp-on ammeter.

Bob Swinney



** Posted from http://www.teranews.com **
  #14   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 762
Default pump wire sizes

You need to understand that Karl has a single phase (NOT 3phase!!!) 240
volt submersible pump where the run cap is topside. So the currents are
measured between leads that are normally buried inside the motor. The
currents he is quoting come directly from the manufacturer's service
literature.



Robert Swinney wrote:
Roy J sez:

"I don't have my book at home to figure it out but, explain to me why the imbalance, I'm curious"

If I might take a stab at it, my W.A.G. is:

Karl, like so many who build RPCs, probably lost sight of the need to properly balance the
idler-motor / load network. They throw in a few random-valued capacitors and step back to admire
their work, giving no thought to completing the job in anything resembling good electrical design.
They seem totally thrilled their RPC will start and run and assume that is good enough.

In all likelihood the currents are measured with a "clamp-on" type of ammeter. In that process true
currents are not being measured among wildly different phase relationships in the 3 leads of an
unbalanced RPC.

IMO, guys like Karl would do well to build proper RPCs before asking questions on RCM about wire
sizing for bogus currents. People like Bruce with electrical backgrounds would be better able to
give meaningful advice re. wire sizing if they had any notion of what the 3-phase currents in
question were all about. It is impossible, as far as I know, to accurately measure unbalanced
3-phase currents with an clamp-on ammeter.

Bob Swinney



** Posted from http://www.teranews.com **

  #15   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 558
Default pump wire sizes

On Sun, 13 Jul 2008 19:18:36 -0500, RoyJ
wrote:
Robert Swinney wrote:


If I might take a stab at it, my W.A.G. is:

Karl, like so many who build RPCs, probably lost sight of the need to properly balance the
idler-motor / load network. They throw in a few random-valued capacitors and step back to admire
their work, giving no thought to completing the job in anything resembling good electrical design.
They seem totally thrilled their RPC will start and run and assume that is good enough.


Your Wild Ass Guess is stunningly wrong. Karl clearly stated this
was a single-phase pump a while back. See below:

You need to understand that Karl has a single phase (NOT 3 phase!!!) 240
volt submersible pump where the run cap is topside. So the currents are
measured between leads that are normally buried inside the motor. The
currents he is quoting come directly from the manufacturer's service
literature.


The run capacitor and the motor coils (and the 180' of downlead
cable in between) play hell with leading and lagging currents in the
windings, and a clamp-amp isn't going to be all that accurate on
oddball waveforms - even a digital one. If you need true accuracy
(even though it won't accomplish anything other than bragging rights)
you need to hook up an oscilloscope and watch all three lines, or
spend huge bucks on a laboratory grade True RMS clamp-amp unit.

The current you really have to worry about is the line current to
the pump control box, and to a lesser extent check for ground leakage
which is a harbinger of a failing motor or a damaged pump lead cable.

-- Bruce --




  #16   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 3,286
Default pump wire sizes

....
Karl, like so many who build RPCs, probably lost sight of the need to
properly balance the
idler-motor / load network. They throw in a few random-valued capacitors
and step back to admire
their work, giving no thought to completing the job in anything resembling
good electrical design.
They seem totally thrilled their RPC will start and run and assume that is
good enough.


I don't know what i did to get on your bad side. FWIW, you're right I know
nothing of balancing. So, I had Fitch tune my units(three) I sent him loaded
and unloaded voltages. He told me what to install.

BTW, anybody heard from Fitch lately?

Karl


  #17   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 523
Default pump wire sizes

Sorry Karl. I shouldn't have personalized my reply. My mistake and I apologise. But you will note,
I did say "probably lost sight of the need to properly balance . . ." having not read previous
threads, as Bruce pointed out, I assumed you were talking about a 3-phase installation. (think
definition of assume here ! ) So, please accept my apology, and disregard my comments as
personalized. Certainly, if your 3-phase units were balanced, ala Fitch, there is nothing more to
be done there.

What I was addressing was the posting in RCM of some individuals that have made rotary phase
converters. They throw a few components together, more often than not without regard to good
electrical practice; then set out to brag about how they built a rotary phase converter.

Bob Swinney



"Karl Townsend" wrote in message
anews.com...
....
Karl, like so many who build RPCs, probably lost sight of the need to
properly balance the
idler-motor / load network. They throw in a few random-valued capacitors
and step back to admire
their work, giving no thought to completing the job in anything resembling
good electrical design.
They seem totally thrilled their RPC will start and run and assume that is
good enough.


I don't know what i did to get on your bad side. FWIW, you're right I know
nothing of balancing. So, I had Fitch tune my units(three) I sent him loaded
and unloaded voltages. He told me what to install.

BTW, anybody heard from Fitch lately?

Karl


** Posted from http://www.teranews.com **
  #18   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 523
Default pump wire sizes

Bruce,

I stand corrected !! My WAG was ""stunningly wrong"" about Karl's question being in regard to
single-phase currents. Guess I didn't read back far enough. Your answer to Karl could have been a
little more clear in as much as you addressed it to the entire group. I wonder if it confused me
whether you, as a professional, were talking about single or 3-phase currents, how it may have come
across to others.

Bob Swinney




"Bruce L. Bergman" wrote in message
...
On Sun, 13 Jul 2008 19:18:36 -0500, RoyJ
wrote:
Robert Swinney wrote:


If I might take a stab at it, my W.A.G. is:

Karl, like so many who build RPCs, probably lost sight of the need to properly balance the
idler-motor / load network. They throw in a few random-valued capacitors and step back to admire
their work, giving no thought to completing the job in anything resembling good electrical
design.
They seem totally thrilled their RPC will start and run and assume that is good enough.


Your Wild Ass Guess is stunningly wrong. Karl clearly stated this
was a single-phase pump a while back. See below:

You need to understand that Karl has a single phase (NOT 3 phase!!!) 240
volt submersible pump where the run cap is topside. So the currents are
measured between leads that are normally buried inside the motor. The
currents he is quoting come directly from the manufacturer's service
literature.


The run capacitor and the motor coils (and the 180' of downlead
cable in between) play hell with leading and lagging currents in the
windings, and a clamp-amp isn't going to be all that accurate on
oddball waveforms - even a digital one. If you need true accuracy
(even though it won't accomplish anything other than bragging rights)
you need to hook up an oscilloscope and watch all three lines, or
spend huge bucks on a laboratory grade True RMS clamp-amp unit.

The current you really have to worry about is the line current to
the pump control box, and to a lesser extent check for ground leakage
which is a harbinger of a failing motor or a damaged pump lead cable.

-- Bruce --


** Posted from http://www.teranews.com **
  #19   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 76
Default pump wire sizes


"Robert Swinney" wrote in message
...
Sorry Karl. I shouldn't have personalized my reply. My mistake and I apologise. But

you will note,
I did say "probably lost sight of the need to properly balance . . ." having not read

previous
threads, as Bruce pointed out, I assumed you were talking about a 3-phase installation.

(think
definition of assume here ! ) So, please accept my apology, and disregard my comments

as
personalized. Certainly, if your 3-phase units were balanced, ala Fitch, there is

nothing more to
be done there.

What I was addressing was the posting in RCM of some individuals that have made rotary

phase
converters. They throw a few components together, more often than not without regard to

good
electrical practice; then set out to brag about how they built a rotary phase converter.

Bob Swinney



And a few of them brag about a hell of a lot less than that...


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wire Size for heat Pump komobu Home Repair 9 April 5th 08 08:13 AM
3 wire pump voltage [email protected] Home Repair 1 September 18th 07 05:10 PM
? advantage of a 3-wire submersible pump [email protected] Home Repair 3 January 7th 07 05:47 AM
3-wire submersible pump controller specs Robert Scott Home Repair 5 July 19th 06 03:42 PM
Wire Sizes a12vman Home Repair 7 August 28th 05 12:36 AM


All times are GMT +1. The time now is 08:40 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"