#1
|
|||
|
|||
Dead 120 VAC circuit - troubleshoot?
I've got a dead circuit in the garage which worked fine until I plugged in a
new-to-me tool and apparently shorted the power switch to the machine base. That created a noticeable spark at the tool and instant power loss to that outlet. Unplugged the tool, popped downstairs to the main electrical panel and reset a tripped breaker. Back upstairs but still no power to the outlet or one other nearby.that is apparently on the same circuit. I turned off all of the circuit breakers that were likely to power the blown circuit and pulled the duplex recptacle ffrom the wall for inspection. It has two black wires on the hot side and two gray wires on the neutral side. Ground is apparently supplied through the conduit. No evidence of arcing or damage to the receptacle and there was 40 M-ohm resistance across the hot and neutral terminals. The receptacle was replaced with a new one, just in case. All of the circuit breakers were turned on in the panel, but there is still no power to the outlet - voltage across the hot/neutral terminals is around 1 VAC. I checked all of the breakers again and they are all in the on position. I'm perplexed - what might be causing the problem? Mike |
#2
|
|||
|
|||
"Mike Henry" wrote in message ... I've got a dead circuit in the garage which worked fine until I plugged in a new-to-me tool and apparently shorted the power switch to the machine base. That created a noticeable spark at the tool and instant power loss to that outlet. Unplugged the tool, popped downstairs to the main electrical panel and reset a tripped breaker. Back upstairs but still no power to the outlet or one other nearby.that is apparently on the same circuit. I turned off all of the circuit breakers that were likely to power the blown circuit and pulled the duplex recptacle ffrom the wall for inspection. It has two black wires on the hot side and two gray wires on the neutral side. Ground is apparently supplied through the conduit. No evidence of arcing or damage to the receptacle and there was 40 M-ohm resistance across the hot and neutral terminals. The receptacle was replaced with a new one, just in case. All of the circuit breakers were turned on in the panel, but there is still no power to the outlet - voltage across the hot/neutral terminals is around 1 VAC. I checked all of the breakers again and they are all in the on position. I'm perplexed - what might be causing the problem? Mike You sure there isn't a GFCI upstream of the outlet? |
#3
|
|||
|
|||
And do you know where the wiring from the breaker goes before it gets
to the outlet? Some do-it-yourself electrician may have left a loose wire nut somewhere. Dennis in nca |
#4
|
|||
|
|||
and, just because the breaker lever says "ON" doesn't mean that it is in
fact ON - I'd start by being sure that there is voltage coming out of the breaker - if yes, then you can follow the circuit and see where it goes away "rigger" wrote in message oups.com... And do you know where the wiring from the breaker goes before it gets to the outlet? Some do-it-yourself electrician may have left a loose wire nut somewhere. Dennis in nca |
#5
|
|||
|
|||
On 2 Jul 2005 21:53:24 -0700, the renowned "rigger"
wrote: And do you know where the wiring from the breaker goes before it gets to the outlet? Some do-it-yourself electrician may have left a loose wire nut somewhere. Dennis in nca I fixed a dead outlet in the (professionally wired) basement by finding the junction where the electrician had nicked the wire. It broke, leaving the outlet dead. It was a PITA to find, at least for me. I doubt that's the exact problem here, but if it was wired using the push-in holes of receptacles it could have burned one of those in another box. Best regards, Spehro Pefhany -- "it's the network..." "The Journey is the reward" Info for manufacturers: http://www.trexon.com Embedded software/hardware/analog Info for designers: http://www.speff.com |
#6
|
|||
|
|||
"Rick" wrote in message ink.net... "Mike Henry" wrote in message ... I've got a dead circuit in the garage which worked fine until I plugged in a new-to-me tool and apparently shorted the power switch to the machine base. That created a noticeable spark at the tool and instant power loss to that outlet. Unplugged the tool, popped downstairs to the main electrical panel and reset a tripped breaker. Back upstairs but still no power to the outlet or one other nearby.that is apparently on the same circuit. I turned off all of the circuit breakers that were likely to power the blown circuit and pulled the duplex recptacle ffrom the wall for inspection. It has two black wires on the hot side and two gray wires on the neutral side. Ground is apparently supplied through the conduit. No evidence of arcing or damage to the receptacle and there was 40 M-ohm resistance across the hot and neutral terminals. The receptacle was replaced with a new one, just in case. All of the circuit breakers were turned on in the panel, but there is still no power to the outlet - voltage across the hot/neutral terminals is around 1 VAC. I checked all of the breakers again and they are all in the on position. I'm perplexed - what might be causing the problem? Mike You sure there isn't a GFCI upstream of the outlet? Be aware of a common GFCI "mousetrap." If the GFIC is wired backward, i.e., power connected to the output side and downstream outlets connected to the input side, it will protect the downstream outlets, but not itself. In other words, if it trips, the downstream will be dead, but it will have power itself, leading one to conclude it is not the problem. If you have GFCIs, it is a real good idea to hit the "test" button to trip it and then check to make sure it is, itself, off. Jerry |
#7
|
|||
|
|||
|
#8
|
|||
|
|||
There are also some breakers which require the handle to be pushed further
"OFF", then "ON" to reset after tripping. Just flipping this type to "ON" will not reset it. Don Young "Ned Simmons" wrote in message ... In article , says... All of the circuit breakers were turned on in the panel, but there is still no power to the outlet - voltage across the hot/neutral terminals is around 1 VAC. I checked all of the breakers again and they are all in the on position. First thing is to check for voltage right at the screw terminal on the breaker. Maybe the short damaged the breaker? Ned Simmons |
#9
|
|||
|
|||
As others have noted, check to see that you have not toasted the
breaker. There are some real trash manufacturers of breakers and panels, some of the breakers will only take a few hard shorts before they act like a fuse and burn out. Use a voltmeter to check for 120 at the breaker terminal. Check to see if you lost the hot or the neutral. On the bad outlet check the voltage from the hot terminal (black or the narrow blade on the outside) to ground (round pin). If you get 120 volts or so, you lost the neutral side. If that checks ok, you likely opened up a connection **upstream** from the offending outlet. Classic case of problem and symptom in different places. Map your circuits by turning off the offending circuit, find ALL the outlets affected by the one in question. Then open up the closest good outlet to either of the bad outlets. You may have to try several to find the culprit. Look for a wire nut that has one loose or burned wire, it could be either the black or white/grey. If the outlet is wired as a through point, you should see one pair of wires to upper set of terminals, the other pair of wires to the lower set. If these are screws, tighten them. If they are just pushed in the back, (ACK!!!, I HATE it when people use those!), push them in and see if they wiggle. Insert usual comments about working safe, you need to be super aware of what you are doing if you have wires out, dangling, and exposed. Don't stand on wet concrete while you do this sort of thing. Mike Henry wrote: I've got a dead circuit in the garage which worked fine until I plugged in a new-to-me tool and apparently shorted the power switch to the machine base. That created a noticeable spark at the tool and instant power loss to that outlet. Unplugged the tool, popped downstairs to the main electrical panel and reset a tripped breaker. Back upstairs but still no power to the outlet or one other nearby.that is apparently on the same circuit. I turned off all of the circuit breakers that were likely to power the blown circuit and pulled the duplex recptacle ffrom the wall for inspection. It has two black wires on the hot side and two gray wires on the neutral side. Ground is apparently supplied through the conduit. No evidence of arcing or damage to the receptacle and there was 40 M-ohm resistance across the hot and neutral terminals. The receptacle was replaced with a new one, just in case. All of the circuit breakers were turned on in the panel, but there is still no power to the outlet - voltage across the hot/neutral terminals is around 1 VAC. I checked all of the breakers again and they are all in the on position. I'm perplexed - what might be causing the problem? Mike |
#10
|
|||
|
|||
Thanks for all the suggestions.
As it turns out there is a GFCI in a bathroom adjacent to the garage that had tripped and which apparently feeds the garage outlet. The GFCI outlet is not used so we never noticed that it was tripped. I got off on several tangents in trying to troubleshoot this. This is a townhome that we purchased new and it looks like the electricians did a fairly decent job (wires screwed to receptacle terminals) and there were no worries about what another owner might have done. Aside from not remembering the bath room GFCI, the main problem was that I couldn't figure out which breaker was supplying power to the garage outlet and didn't want to pull the receptacle until I was sure that the wires were unpowered. The main panel breakers are labeled but a bit more obtusely than I would have liked. There is a "garage" CB but it turns out to be on a different circuit and the correct one is labeled only "GFI". I got sidetracked by a GFCI in a utility room which seemed to be a logical tie point for the garage outlet parttially because I noticed my wife had partially painted over the recptacle slots. That was a red herring. At one point I decided to check voltages from the outlet to hots and neutrals on a known good circuit. I was getting 12-13 VAC on the hot & neutral from one pair of wires to the outlet and 68-72 VAC from the other pair of hot/neutral wires. Is that normal? As an unexpected bonus, I did find one GFCI in the house that filed to test properly. It's located directly below the main electrical panel between two window wells. I replaced that one today. Some time spent mapping CBs and circuits is probably in order against the next time something like this happens. Mike "RoyJ" wrote in message k.net... As others have noted, check to see that you have not toasted the breaker. There are some real trash manufacturers of breakers and panels, some of the breakers will only take a few hard shorts before they act like a fuse and burn out. Use a voltmeter to check for 120 at the breaker terminal. Check to see if you lost the hot or the neutral. On the bad outlet check the voltage from the hot terminal (black or the narrow blade on the outside) to ground (round pin). If you get 120 volts or so, you lost the neutral side. If that checks ok, you likely opened up a connection **upstream** from the offending outlet. Classic case of problem and symptom in different places. Map your circuits by turning off the offending circuit, find ALL the outlets affected by the one in question. Then open up the closest good outlet to either of the bad outlets. You may have to try several to find the culprit. Look for a wire nut that has one loose or burned wire, it could be either the black or white/grey. If the outlet is wired as a through point, you should see one pair of wires to upper set of terminals, the other pair of wires to the lower set. If these are screws, tighten them. If they are just pushed in the back, (ACK!!!, I HATE it when people use those!), push them in and see if they wiggle. Insert usual comments about working safe, you need to be super aware of what you are doing if you have wires out, dangling, and exposed. Don't stand on wet concrete while you do this sort of thing. Mike Henry wrote: I've got a dead circuit in the garage which worked fine until I plugged in a new-to-me tool and apparently shorted the power switch to the machine base. That created a noticeable spark at the tool and instant power loss to that outlet. Unplugged the tool, popped downstairs to the main electrical panel and reset a tripped breaker. Back upstairs but still no power to the outlet or one other nearby.that is apparently on the same circuit. I turned off all of the circuit breakers that were likely to power the blown circuit and pulled the duplex recptacle ffrom the wall for inspection. It has two black wires on the hot side and two gray wires on the neutral side. Ground is apparently supplied through the conduit. No evidence of arcing or damage to the receptacle and there was 40 M-ohm resistance across the hot and neutral terminals. The receptacle was replaced with a new one, just in case. All of the circuit breakers were turned on in the panel, but there is still no power to the outlet - voltage across the hot/neutral terminals is around 1 VAC. I checked all of the breakers again and they are all in the on position. I'm perplexed - what might be causing the problem? Mike |
#11
|
|||
|
|||
"Mike Henry" wrote in message ... Thanks for all the suggestions. As it turns out there is a GFCI in a bathroom adjacent to the garage that had tripped and which apparently feeds the garage outlet. The GFCI outlet is not used so we never noticed that it was tripped. I got off on several tangents in trying to troubleshoot this. This is a townhome that we purchased new and it looks like the electricians did a fairly decent job (wires screwed to receptacle terminals) and there were no worries about what another owner might have done. Aside from not remembering the bath room GFCI, the main problem was that I couldn't figure out which breaker was supplying power to the garage outlet and didn't want to pull the receptacle until I was sure that the wires were unpowered. The main panel breakers are labeled but a bit more obtusely than I would have liked. There is a "garage" CB but it turns out to be on a different circuit and the correct one is labeled only "GFI". I got sidetracked by a GFCI in a utility room which seemed to be a logical tie point for the garage outlet parttially because I noticed my wife had partially painted over the recptacle slots. That was a red herring. At one point I decided to check voltages from the outlet to hots and neutrals on a known good circuit. I was getting 12-13 VAC on the hot & neutral from one pair of wires to the outlet and 68-72 VAC from the other pair of hot/neutral wires. Is that normal? Did you use a digital voltmeter to measure this by any chance? |
#12
|
|||
|
|||
"Rick" wrote in message link.net... "Mike Henry" wrote in message ... Thanks for all the suggestions. As it turns out there is a GFCI in a bathroom adjacent to the garage that had tripped and which apparently feeds the garage outlet. The GFCI outlet is not used so we never noticed that it was tripped. I got off on several tangents in trying to troubleshoot this. This is a townhome that we purchased new and it looks like the electricians did a fairly decent job (wires screwed to receptacle terminals) and there were no worries about what another owner might have done. Aside from not remembering the bath room GFCI, the main problem was that I couldn't figure out which breaker was supplying power to the garage outlet and didn't want to pull the receptacle until I was sure that the wires were unpowered. The main panel breakers are labeled but a bit more obtusely than I would have liked. There is a "garage" CB but it turns out to be on a different circuit and the correct one is labeled only "GFI". I got sidetracked by a GFCI in a utility room which seemed to be a logical tie point for the garage outlet parttially because I noticed my wife had partially painted over the recptacle slots. That was a red herring. At one point I decided to check voltages from the outlet to hots and neutrals on a known good circuit. I was getting 12-13 VAC on the hot & neutral from one pair of wires to the outlet and 68-72 VAC from the other pair of hot/neutral wires. Is that normal? Did you use a digital voltmeter to measure this by any chance? Yep, it was a digital VOM - would analog have given different results? |
#13
|
|||
|
|||
Yes, an analog volt meter is definitely more reliable than a lot of DMMs for
AC volts. With a DMM sitting on a table, not connected to any circuit, you might notice that if you only hold a single meter lead tip with your fingers, that the reading jumps around. A quick check for the relative quality of a DMM is to set it on the lowest voltage range with no leads attached. The display should be zero or a very low reading that doesn't fluctuate. Fluctuation can indicate that there is no shielding, or that it's inadequate, and some low-end meters are the worst. Depending upon the design of the DMM meter's input and conversion circuitry, the readings can be very unreliable, especially when checking for AC voltages. Generally, the only analog AC meters that will give unusual-looking readings, are the amplified ones that are intended to measure very small potentials in the micro or millivolt potentials (not for AC house/building wiring troubleshooting). WB ............... "Mike Henry" wrote in message ... Did you use a digital voltmeter to measure this by any chance? Yep, it was a digital VOM - would analog have given different results? ----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==---- http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups ----= East and West-Coast Server Farms - Total Privacy via Encryption =---- |
#14
|
|||
|
|||
Glad you isolated your problem. Just a comment about digital meters: A low
battery can give bad readings. Ace "Mike Henry" wrote in message ... "Rick" wrote in message link.net... "Mike Henry" wrote in message ... Thanks for all the suggestions. As it turns out there is a GFCI in a bathroom adjacent to the garage that had tripped and which apparently feeds the garage outlet. The GFCI outlet is not used so we never noticed that it was tripped. I got off on several tangents in trying to troubleshoot this. This is a townhome that we purchased new and it looks like the electricians did a fairly decent job (wires screwed to receptacle terminals) and there were no worries about what another owner might have done. Aside from not remembering the bath room GFCI, the main problem was that I couldn't figure out which breaker was supplying power to the garage outlet and didn't want to pull the receptacle until I was sure that the wires were unpowered. The main panel breakers are labeled but a bit more obtusely than I would have liked. There is a "garage" CB but it turns out to be on a different circuit and the correct one is labeled only "GFI". I got sidetracked by a GFCI in a utility room which seemed to be a logical tie point for the garage outlet parttially because I noticed my wife had partially painted over the recptacle slots. That was a red herring. At one point I decided to check voltages from the outlet to hots and neutrals on a known good circuit. I was getting 12-13 VAC on the hot & neutral from one pair of wires to the outlet and 68-72 VAC from the other pair of hot/neutral wires. Is that normal? Did you use a digital voltmeter to measure this by any chance? Yep, it was a digital VOM - would analog have given different results? |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Bad Circuit | Home Repair | |||
Help changing circuit breakers | Home Repair | |||
2-pole GFCI breaker for Edison (shared neutral) circuit | Home Ownership | |||
Newbie Service Panel Question | Home Repair | |||
Is it a radial or ring circuit? | UK diy |