"Mike Henry" wrote in message
...
I've got a dead circuit in the garage which worked fine until I

plugged in a
new-to-me tool and apparently shorted the power switch to the

machine base.
That created a noticeable spark at the tool and instant power loss

to that
outlet. Unplugged the tool, popped downstairs to the main

electrical panel
and reset a tripped breaker. Back upstairs but still no power to

the outlet
or one other nearby.that is apparently on the same circuit. I

turned off
all of the circuit breakers that were likely to power the blown

circuit and
pulled the duplex recptacle ffrom the wall for inspection. It has

two black
wires on the hot side and two gray wires on the neutral side.

Ground is
apparently supplied through the conduit. No evidence of arcing or

damage to
the receptacle and there was 40 M-ohm resistance across the hot

and
neutral terminals. The receptacle was replaced with a new one, just

in
case.

All of the circuit breakers were turned on in the panel, but there

is still
no power to the outlet - voltage across the hot/neutral terminals is

around
1 VAC. I checked all of the breakers again and they are all in the

on
position.

I'm perplexed - what might be causing the problem?

Mike


You sure there isn't a GFCI upstream of the outlet?