From: Jane )


I just read Black & Decker's Home Wiring Guide in an effort to
understand how the service panel distributes electricity, but they use
the word "circuit" to mean the wall socket / receptical sometimes, and
alternately to mean circuit *breaker* and it isn't clear to me when
they mean one or the other. Consequently I am not clear on the
following concept:

Simplistic Hypothetical: ------------------------------------------

Circuit Breaker #1 on the service panel is a 20amp 120v circuit.

It's wired to *four* wall circuits [recepticles].
Each recepticle is now a 120v 20a outlet.

-------------------------------------------------------------------------

----------

Confusion point:
The book states that a full load for a 120v 20amp circuit is:
120v x 20a = 2400 watts x 80% (safe capacity) = 1900 watts

Does that mean each one of those recepticles can have up to a 1900
watt load on them *simultaneously* without tripping the breaker,


No.

or
that *collectively* at any given time their load in summary shouldn't
exceed the safe capacity of 1900 watts total?


Yes, and no. it means that at any given time, collectively that circuit cannot
exceed 2400 watts. Since there's no way you can control the total wattage on
any given receptacle circuit, the 1900 watt "limit" is only a design limit.


The reason I ask is this... the book also says that microwaves and
large appliances should have a "dedicated circuit." Do they simply
mean a dedicated wall outlet, or a dedicated circuit *breaker* --
meaning no other outlet is wired to that circuit breaker but the one
the appliance is plugged into...??


Right, dedicated to that one appliance, either directly wired or via 1 single
dedicated receptacle.

Because the way I read it, is I need a separate *circuit breaker* for
my washer/dryer outlet...


Yes.

one for my 1700watt treadmill (which can
also run a TV and lights in the garage, but then reaches the 1900watt
safe mark)...


No - A treadmill load is not considered a constant load, it won't be on longer
than 4 hours.

one for my garbage disposal


Yes

and one for my microwave...

Yes

and the circuit breakers just keep adding up...!

Or do they mean a single circuit breaker can *share* outlets with
major appliances because each outlet it services has a *simultaneous*
capacity for a 1900 watt safe load?

Was that confusing enough???

Jane

  #2   Report Post  
I-zheet M'drurz
 
Posts: n/a
Default Newbie Service Panel Question

On 19 Nov 2003, wrote:

Simplistic Hypothetical: ------------------------------------------

Circuit Breaker #1 on the service panel is a 20amp 120v circuit.

It's wired to *four* wall circuits [recepticles].
Each recepticle is now a 120v 20a outlet.
-----------------------------------------------------------------------
------------

Confusion point:
The book states that a full load for a 120v 20amp circuit is:
120v x 20a = 2400 watts x 80% (safe capacity) = 1900 watts

Does that mean each one of those recepticles can have up to a 1900
watt load on them *simultaneously* without tripping the breaker, or
that *collectively* at any given time their load in summary shouldn't
exceed the safe capacity of 1900 watts total?


Collectively. They are sometimes call "convenience outlets", and
the thinking is that you will never use them all at one time, or
even if you do, they will all be low load devices. You could
load up all 4 of those receptacles (8 spots) with things like
stereo systems, lamps, cordless phone bases, chargers for your
cell phone, etc, etc and never come anywhere near drawing 1900W.
But change those things to toaster ovens, coffee makers, hair
dryers, etc, and you get to your next question...

The reason I ask is this... the book also says that microwaves and
large appliances should have a "dedicated circuit." Do they simply
mean a dedicated wall outlet, or a dedicated circuit *breaker* --
meaning no other outlet is wired to that circuit breaker but the one
the appliance is plugged into...??


Exactly. One breaker, one outlet.

Because the way I read it, is I need a separate *circuit breaker* for
my washer/dryer outlet... one for my 1700watt treadmill (which can
also run a TV and lights in the garage, but then reaches the 1900watt
safe mark)... one for my garbage disposal and one for my microwave...


Actually, your usage will determine this. Your Treadmill/lights/
TV example is a good one. If you don't have a dedicated outlet
for those heavy drawing devices, you need to play the "I-can't-
run-this-thing-while-my-treadmill-is-running" game, effectively
creating a dedicated outlet, even though there are other duplex
receptacles on the same circit. People have been doing this since
we've had indoor electrical service, and as long as you do it in
a -SAFE- manner, it's OK. "SAFE" being not sticvking pennies in
the fusebox, propping a breaker handle in a closed position with
a chunk of wood, etc. That kind of stuff burns your house down,
the trial and error "learning" of your circuit limits gets you a
workout running to the breaker box.

Was that confusing enough???


Not a bit. You knew how to voice your questions, that's better
than half of the (cough)dim bulbs who show up here!

--
Baisez-les s'ils ne peuvent pas prendre une plaisanterie
--------------------------------------------------------
Tom Pendergast e-mail is for sissies, say it on line
  #3   Report Post  
Steve Smith
 
Posts: n/a
Default Newbie Service Panel Question

Jane wrote in message
...
I just read Black & Decker's Home Wiring Guide in an effort to
understand how the service panel distributes electricity, but they use
the word "circuit" to mean the wall socket / receptacle sometimes, and
alternately to mean circuit *breaker* and it isn't clear to me when
they mean one or the other. Consequently I am not clear on the
following concept:


A circuit is actually a complete loop through which electrons can flow.
Nobody in residential wiring really means that when the use the word
though.. It typically refers to the wiring hooked up to an individual
breaker, at least around here.

Simplistic Hypothetical: ------------------------------------------

Circuit Breaker #1 on the service panel is a 20amp 120v circuit.

It's wired to *four* wall circuits [recepticles].
Each recepticle is now a 120v 20a outlet.
Confusion point:
The book states that a full load for a 120v 20amp circuit is:
120v x 20a = 2400 watts x 80% (safe capacity) = 1900 watts


The 80% rule is for resistive loads, and even then it's only applied to
special circuits (heating, water heater, other dedicated resistive load
circuits). For everything else there is a "12 box rule". That is you can
have any combination of light fixture and receptacle boxes (excluding boxes
for switches and splices only) as long as the total of that combination is
no more than 12. Most electricians like to keep it at 8 or 10. i.e.:

Circuit 1: 4 recessed light fixtures in the bedroom plus 5
receptacles = 9
Circuit 2: 6 receptacles in the living room, 2 in the hallway, 8 in
the den = 16

Circuit 1 is ok because it only has 9 "outlet boxes", however circuit 2
is a violation, because it has 4 too many boxes.

The reason being is because you have no idea what someone will plug in
some day. Someone might plug in two 1200 watt heaters. If the electrical
installation is sound a 20A circuit will handle it

Does that mean each one of those recepticles can have up to a 1900
watt load on them *simultaneously* without tripping the breaker, or
that *collectively* at any given time their load in summary shouldn't
exceed the safe capacity of 1900 watts total?


For branch circuits it's always collectively. A 20A circuit can run 20A
collectively. ie: 10A on one outlet, plus 10A on another. 20A on only and
10A on the other would be pulling 30A through a wire (12gauge) that's only
meant for 20.

The reason I ask is this... the book also says that microwaves and
large appliances should have a "dedicated circuit." Do they simply
mean a dedicated wall outlet, or a dedicated circuit *breaker* --
meaning no other outlet is wired to that circuit breaker but the one
the appliance is plugged into...??

Because the way I read it, is I need a separate *circuit breaker* for
my washer/dryer outlet... one for my 1700watt treadmill (which can
also run a TV and lights in the garage, but then reaches the 1900watt
safe mark)... one for my garbage disposal and one for my microwave...


Unless your treadmill is hardwired in (no plug) or attached to the house
it doesn't need it's own circuit. The reason being is because it's
portable, and will probably be moved around.

and the circuit breakers just keep adding up...!


They do so blazingly fast! When I bought my 200A, 40 position Square D
panel a year ago for our 2200 sq.ft house I never dreamed I would get close
to filling it. Yet I am now close-- at 5 spaces left.

Every motor load circuit will need it's own breaker (code). This
includes the microwave, refrigerator, dishwasher, washing machine, furnace,
garburator, AC units, pumps, central vac, etc. Most small fans (ceiling
fans, range hood, bathroom exhaust) can be placed on regular lighting
circuits. If you have a lot of cool toys(like a garburator, hot tub or
central vac) you'll fill up a panel quick.

The stove, dryer and electric water heater will all need separate
breakers as well.

Most panels come as a 'kit' with a bunch of breakers included. It's
almost a sure bet that you'll be buying extra.

If you are replacing an existing service, and using the existing wiring,
the rules are often relaxed (sometimes even ignored) in many localities, you
should call your inspector. (And for a service upgrade you WILL need to be
inspected, the utility won't touch you otherwise).


Or do they mean a single circuit breaker can *share* outlets with
major appliances because each outlet it services has a *simultaneous*
capacity for a 1900 watt safe load?


Nope, major appliances and outlets that have a purpose to serve things like
microwaves and washing machines need their own dedicated breaker. That's
the code.

-- Steve

p.s. the 12 box rule is based on my knowledge of the CEC, I understand
it's the same for the NEC but I may be corrected.




  #4   Report Post  
Mark or Sue
 
Posts: n/a
Default Newbie Service Panel Question

"Jane" wrote in message
...
Thanks to everyone for the answers! I really appreciated that.

So it was what I thought but when the electrician kept telling me the
100 amp panel would be fine and that it would be impossible for me to
trip a breaker even with everything turned on, I thought I must have
it wrong.

1 - Garbage disposal
2 - microwave
3 - washer/dryer in garage (both gas)
4 - treadmill in garage (heavy duty stays in garage, 17 amps when
running and I want to use it when I'm doing laundry), can also use
this outlet for light fixure, 113 watt TV, CD. VCR = just about 1926
watts
5 - gas stove/energy-saving fridge
6 - desktop computer

So that's already 120 amps without another two breakers for wall
outlets in the 2 bedrooms, living room and bath.


You're missing three things. First, you have a 240V, 100A service. This
means you can run 200 amps of 120V eqipment if everything is perfectly
distributed across the two incoming power legs. Next, just because a circuit
has a 20A breaker doesn't mean it counts as 20A of load (washing machine may
be 10A, microwave may be 12A, etc). Finally, there is a huge factor for
"load diversity" in a dwelling. This means you are most likely not using all
of this stuff at exactly the same time. The fridge and microwave cycle on
and off when being used. Can you use the garbage disposal and treadmill at
the same time (assuming only you live there)?

So all of these things are factored in when your total electrical demand is
calculated. It would not be unusual to add up all the breakers and get 300
amps worth in a 200 amp service (and that's 300A per side or 600A if couning
a double pole breaker twice).


Yet a 150 amp panel is $450 more than a 100 watt panel. The job's
already costing $1800 to switch out the panel and wire seven new
recepticles.

decisions decisions...!


From what I've seen, 100A and 200A are the cheapest services to install.
Some of the 200A equipment is even cheaper than 100A since 200A is the most
common service installed today. If the electrician says you don't need to
upgrade past 100A, believe him. Houses that are all gas rarely go over 100
amps unless you have a welder, kiln, or huge air conditioner. If you want to
increase anyway, I'd consider going to 200 amps.

--
Mark
Kent, WA



  #5   Report Post  
Paul Franklin
 
Posts: n/a
Default Newbie Service Panel Question

On Wed, 19 Nov 2003 20:03:39 GMT, Jane ) wrote:
snip
Confusion point:
The book states that a full load for a 120v 20amp circuit is:
120v x 20a = 2400 watts x 80% (safe capacity) = 1900 watts

Does that mean each one of those recepticles can have up to a 1900
watt load on them *simultaneously* without tripping the breaker, or
that *collectively* at any given time their load in summary shouldn't
exceed the safe capacity of 1900 watts total?

The reason I ask is this... the book also says that microwaves and
large appliances should have a "dedicated circuit." Do they simply
mean a dedicated wall outlet, or a dedicated circuit *breaker* --
meaning no other outlet is wired to that circuit breaker but the one
the appliance is plugged into...??

Because the way I read it, is I need a separate *circuit breaker* for
my washer/dryer outlet... one for my 1700watt treadmill (which can
also run a TV and lights in the garage, but then reaches the 1900watt
safe mark)... one for my garbage disposal and one for my microwave...

and the circuit breakers just keep adding up...!

snip

Yes, it's a bit confusing. It's the circuit breaker that limits the
maximum power that can be used by everything connected to it, whether
you have one outlet connected to a single breaker or 6 outlets, or 4
outlets and 2 ceiling lights, etc. Generally, a dedicated circuit
refers to a circuit breaker connected to a single load, whether it is
directly wired to it, as would be done for a dishwasher, or whether it
is wired to a single outlet, such as would be done for a microwave.

In new construction today, there would indeed be a separate circuit
breaker for the microwave, disposal, dishwasher, refrigerator, and
other large, dedicated appliances. Those separate breakers would
either each be wired directly to the appliance or each wired to a
single oulet serving each appliance.

The treadmill is a marginal case. Technically, you could get by
without a dedicated circuit if you were careful not to turn on any
other large loads connected to the same circuit while you were using
the treadmill. So if you had an electic heater plugged into an outlet
connected to the same circuit breaker as the treadmill, you would be
ok as long as you didn't use the heater and treadmill at the same
time.

The circuit breaker is there to limit the maximum power that can be
drawn from all the wiring connected to it. This prevents overloading
the wiring which can cause a fire. Generally, if you are not tripping
any circuit breakers, then you are OK. I say generally, because
circuit breakers are not precision devices. If the overload is large,
they will trip quickly. But if the overload is small they may run for
hours before they trip. This is usually not a problem because there
is enough safety margin to prevent problems from small overloads.

Still, if you know when you use your treadmill that you are going to
want the TV on and all the lights in the garage on, then you may want
to consider having a dedicated circuit installed.

HTH,

Paul



  #6   Report Post  
Mark or Sue
 
Posts: n/a
Default Newbie Service Panel Question

"Jane" wrote in message
...
"Mark or Sue" kindly wrote:
You're missing three things. First, you have a 240V, 100A service. This
means you can run 200 amps of 120V eqipment if everything is perfectly
distributed across the two incoming power legs.


THANK YOU. This was the part of the puzzle I wanted to clear up. I
know 2 lines come in at 120v but I didn't understand how it gets
distributed if you have (say) only (5) 20amp circuit breakers. Is each
CB wired to each leg, to actually deliver 40amps power each? (If wired
correctly.)??


A 20A breaker will deliver 20 amps. In most modern panels, the incoming
power legs alternate with each row. So the top two breakers could draw 40A
from leg 1, the next row of breakers could draw 40A from leg 2, the third
row of breakers could cause 80A to be drawn from leg 1 (rows 1 and 3), and
so on. You have 100 amps available on each leg.

A 240V device uses a double pole breaker. This gives you 240V with each side
of the circuit breakered at the amp rating. A 30A double pole breaker would
provide two 120V circuits at 30A, or 1 240V circuit at 30A.

The fridge and microwave cycle on
and off when being used. Can you use the garbage disposal and treadmill

at
the same time (assuming only you live there)?


No, but no one wants to wire a house for one person. Someone may move
in later, someone may be staying over... there are certain sacrifices
that are no big deal (like don't use the microwave while running the
garbage disposal) but otherwise I don't want to worry about it.


My example wasn't very good, but the code knows you can't use all your
circuits at once. A service calculation takes most of your receptacle outlet
circuits and adds up the load. The first 3000 watts are counted at 100%.
Each watt over that is only counted at 35%. It is similar with fastened in
place appliances. If you have 4 or more, then you can apply a .75 factor to
each appliance load. Certain things must be kept at 100%, such as
heat/cooling, clothes dryer, motors, and a special demand rating for
electric ranges/stoves. Add all of these values up and that is how many
watts your service must provide.

--
Mark
Kent, WA



  #7   Report Post  
Rick
 
Posts: n/a
Default Newbie Service Panel Question

I'm in kinda the same boat as you are Jane...

I've gotten a great 'education' reading "Wiring a House" by Rex Cauldwell.
It is one of Tauntons' "For Pros by Pros" series of books. Clearly written
and supported with excellent color pictures and drawings.

If you have no luck finding this locally or online, you are welcome to order
it from my employer, Craftsman Book Company

http://www.craftsman-book.com/cgi-bi...htm?E+cbcstore

copy and paste if necessary...

Rick

"Jane" wrote in message
...
Thanks very much for your explanation. I don't quite grasp the
mechanics though. The electrician says that a 100amp panel is really
like a 180 amp panel,(b/c of the two legs which you brought up) but I
don't understand how the circuits utilize the two legs to make an
electrican say that. It seems to fly in the face of the basic advice
of needing a circuit breaker for: garbage disposal, microwave,
desktop, etc... which all adds up to a 100amp panel very fast. If I go
by the advice in the book, I would get a 150amp panel to satisfy all
the equations of load, etc. for the house, yet he tells me the 100 amp
is like a 180 and I'll never trip it even with everything on. And he's
probably right b/c of the "two-legs."

I wish I knew of a book I could read that detailed how a service panel
works. Black and Deckers book is more about how to wire stuff up, than
the mechanics of how the service panel handles the (2) 120v lines and
how the breakers distribute it. Their explanation does not take into
account the two legs in terms of "so your 100 amp panel is really like
a 180 or 200 amp panel because of this and this and this."

Sorry to be so dense. I know you gave an explanation but as with
anyone who is new to a concept, I am missing the basic understanding
that lies at the foundation of the thing. It's something that people
(who already know it) take it for granted that someone would
understand, because it's so basic. So that if that piece were filled
in and I did a "EUREKA!" they would say, "Well DUH, of course THAT's
blah blah blah!" KWIM?

I'm going to search the Web some more for something to read that will
enlighten me. If anyone has a link to offer, I'm all ears. (eyes?)

Jane



  #8   Report Post  
Mark or Sue
 
Posts: n/a
Default Newbie Service Panel Question

"Jane" wrote in message
...
Thanks very much for your explanation. I don't quite grasp the
mechanics though. The electrician says that a 100amp panel is really
like a 180 amp panel,(b/c of the two legs which you brought up) but I
don't understand how the circuits utilize the two legs to make an
electrican say that. It seems to fly in the face of the basic advice
of needing a circuit breaker for: garbage disposal, microwave,
desktop, etc... which all adds up to a 100amp panel very fast. If I go
by the advice in the book, I would get a 150amp panel to satisfy all
the equations of load, etc. for the house, yet he tells me the 100 amp
is like a 180 and I'll never trip it even with everything on. And he's
probably right b/c of the "two-legs."


I'm going to search the Web some more for something to read that will
enlighten me. If anyone has a link to offer, I'm all ears. (eyes?)



Yeah, when you know this stuff well, you forget how to explain things to
people who've never looked inside a panel before. Try this link:

http://www.homewiringandmore.com/hom...ng/meter/100as
ubpanel.jpg

This is a 100A panel without a main breaker. The incoming 100A feed comes in
on the red and blue wires (100A available from each). There is 240V between
the red and blue feed wires, and 120 between either the red or blue and the
white feed wire. There are three single pole breakers in this panel, and
lets say they are 20A each. The bottom two breakers get their current from
the incoming red feed wire. If both those circuits are on and using their
full rating, 40A will be sucked off that red feed wire.The higher breaker on
the rights gets it current from the blue feed wire. This could suck 20A from
the blue wire irrespective of what the bottom two breakers are doing. Put in
another breaker on the right side above the two that are there, and it will
get its current from the red feed wire making the total potential draw from
the red 60A. Put in another above that one, and the blue feed could be
loaded to 40A and the red line to 60A. This is 100A, but you still have 40
more available on the red and 60 more available on the blue.

So a 20A breaker doesn't utilize both legs, it is on one or the other. The
layout of the panel makes it such that a column of breakers alternates
between the red feed and blue feed wires. So as long as you're not putting
your breakers in just every other row, you'll be able to suck current from
both incoming lines. This means you effectively have 200A available if
you're only using single breakers.

A 240V double pole breaker, like you'd use for a water heater, range, or
dryer, sucks it current from both lines. So a clothes dryer rated at 25A at
240V would allow only 75 amps to be available on the red and blue legs to
serve your 120V loads (which really means 150 total amps since there are two
legs to choose from on 120V loads).

--
Mark
Kent, WA



  #9   Report Post  
Terry
 
Posts: n/a
Default Newbie Service Panel Question

" wrote:


Re 'dedicated' circuit. Agree the terminology can be confusing.
To illustrate;
There some rules in this jurisdiction that a kitchen shall have a
certain number of 'dedicated' outlet/receptacles. This means that
there is only one 'dedicated' outlet wired directly from one
particular circuit breaker; for each dedicated circuit. I'm not
sure what the requiremnt is now; but when we built this house
some 30 years ago it was, I believe, a minimum of two dedicated
and and also a certain number of 'convenience' outlets per 'X'
feet of counter space!
This requirement has come into use as more and heavier appliances
have become common. Microwave ovens for example, a steam iron or
electric kettle can each require sufficient power that to plug
two such items into the one circuit (and use them at the same
time!), would exceed the total current capacity of say 20 amps.
Also for example non-dedicated (normal) outlets are around the
walls of rooms or adjacent rooms. Usually such 'convenience'
outlets are limted by local jurisdiction to some maximum number;
such as eight or ten on the one run of wiring from one circuit
breaker). Sometimes such outlets or half of them are controlled
by a wall switch in order to turn on/off coffe table lamps.
Dedicated outlets would normally NEVER be switched like that.
One example of a dedicated outlet, in our case is the one wired
specifically for an older style, large, microwave oven, on its
own trolley, to 'it's own' circuit breaker.
Any help? Terry.
  #10   Report Post  
Tom Horne
 
Posts: n/a
Default Newbie Service Panel Question / with mended link

"Jane" wrote in message
...

Thanks very much for your explanation. I don't quite grasp the
mechanics though. The electrician says that a 100amp panel is really
like a 180 amp panel,(b/c of the two legs which you brought up) but I
don't understand how the circuits utilize the two legs to make an
electrican say that. It seems to fly in the face of the basic advice
of needing a circuit breaker for: garbage disposal, microwave,
desktop, etc... which all adds up to a 100amp panel very fast. If I go
by the advice in the book, I would get a 150amp panel to satisfy all
the equations of load, etc. for the house, yet he tells me the 100 amp
is like a 180 and I'll never trip it even with everything on. And he's
probably right b/c of the "two-legs."


I'm going to search the Web some more for something to read that will
enlighten me. If anyone has a link to offer, I'm all ears. (eyes?)




Yeah, when you know this stuff well, you forget how to explain things to
people who've never looked inside a panel before. Try this link:

"http://www.homewiringandmore.com/homewiringusa/2002/maindwelling/meter/100asubpanel.jpg"

This is a 100A panel without a main breaker. The incoming 100A feed comes in
on the red and blue wires (100A available from each). There is 240V between
the red and blue feed wires, and 120 between either the red or blue and the
white feed wire. There are three single pole breakers in this panel, and
lets say they are 20A each. The bottom two breakers get their current from
the incoming red feed wire. If both those circuits are on and using their
full rating, 40A will be sucked off that red feed wire.The higher breaker on
the rights gets it current from the blue feed wire. This could suck 20A from
the blue wire irrespective of what the bottom two breakers are doing. Put in
another breaker on the right side above the two that are there, and it will
get its current from the red feed wire making the total potential draw from
the red 60A. Put in another above that one, and the blue feed could be
loaded to 40A and the red line to 60A. This is 100A, but you still have 40
more available on the red and 60 more available on the blue.

So a 20A breaker doesn't utilize both legs, it is on one or the other. The
layout of the panel makes it such that a column of breakers alternates
between the red feed and blue feed wires. So as long as you're not putting
your breakers in just every other row, you'll be able to suck current from
both incoming lines. This means you effectively have 200A available if
you're only using single breakers.

A 240V double pole breaker, like you'd use for a water heater, range, or
dryer, sucks it current from both lines. So a clothes dryer rated at 25A at
240V would allow only 75 amps to be available on the red and blue legs to
serve your 120V loads (which really means 150 total amps since there are two
legs to choose from on 120V loads).

--
Mark
Kent, WA



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical service question - old house, new addition - expert advice needed major domo Home Repair 4 November 20th 03 10:39 PM
Elec: Do you need to re-tighten Al service entrance cable? Mike O. Home Repair 6 September 8th 03 10:48 PM
newbie question: spindle to a point Ken Grunke Woodturning 8 August 18th 03 08:51 PM


All times are GMT +1. The time now is 01:36 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"