Hey guys,

Got a question about circuit breakers, I have a HarbourFreight stick
welder, that is marked 120/240v draws 41 Amps, Does this mean it draws 41
Amps at 120 or 20.5 Amps at 240V? I'm talking about through each leg, if
hooked up as 220V.

I have it wired the welder hooked up for 220V operating, and have a dbl
pole 40 Amp breakers in my panel, it's been working fine for the
past year. Is the dbl pole 40 breaker the correct size for this
application? Does this mean that each leg of the break is capable of
drawing 40 amps each?

Should I reduce the size of this break to a dbl pole 25 Amp breaker? By
the way, I installed this dbl pole 40 Amp breaker myself last year.

Thanks.
Jeff
--
A7N8X-Deluxe, AMD XP2500+ (Un-locked)
2x256mb Crucial PC3200 DDR ram
Palit-Daytona Ti4200/64M AGP

  #2   Report Post  
Gigs
 
Posts: n/a
Default

You should size the breaker for the wire, not for the load.

Size the wire for the load.

  #3   Report Post  
Richard Ferguson
 
Posts: n/a
Default

As Gigs said, size the breaker for the wire. A 40 amp breaker should be
attached to 8 gauge wire, as I recall it. If the wire is 10 ga or less,
replace it with 8 gauge.

40 amps or 50 amps at 220 volts sounds right for a typical stick welder.
Mine is wired to a 50 amp breaker.

Richard



Gigs wrote:
You should size the breaker for the wire, not for the load.

Size the wire for the load.

  #4   Report Post  
Grant Erwin
 
Posts: n/a
Default

Jeff wrote:

Got a question about circuit breakers, I have a HarbourFreight stick
welder, that is marked 120/240v draws 41 Amps, Does this mean it draws 41
Amps at 120 or 20.5 Amps at 240V? I'm talking about through each leg, if
hooked up as 220V.

I have it wired the welder hooked up for 220V operating, and have a dbl
pole 40 Amp breakers in my panel, it's been working fine for the
past year. Is the dbl pole 40 breaker the correct size for this
application? Does this mean that each leg of the break is capable of
drawing 40 amps each?

Should I reduce the size of this break to a dbl pole 25 Amp breaker? By
the way, I installed this dbl pole 40 Amp breaker myself last year.


I think you should resize your breaker to a 30 amp double pole breaker.

Current flows out of one leg, through the welder, through the work, back through
the welder's ground lead, and back through the other leg. Yes, the current flows
in both legs. A little buzzbox stick welder can draw 41 amps at 240VAC. The part
you didn't mention is how many amps your welder can weld with. Let's suppose
it's 250 amps at 25 volts AC. Power is volts times amps, so that's delivered
power of 6250 watts. Let's assume your welder's transformer is 20% lossy, so
we'll divide 6250 by 0.8 and get 7812 watts of input power. To calculate the
current needed from a 220V plug, divide 7812 by 220 to get 35 amps. So you can
see that 41 amps at 220 is not unreasonable. You can almost certainly get by
with a 30 amp breaker. If you pulled wire that's too small for a 40 amp breaker
(did you use 8 gauge wire or 10 gauge wire?) then it may be prudent to downsize
the breaker to 30 amps. By the way, I have a little buzzbox welder, and I run it
through a 30 amp breaker and about 15 feet of conduit and a receptacle, and I
used no. 10 wire. I never ever turn my welder all the way up, or at least I
haven't yet, so this setup is fine for the little buzzbox.

Grant
  #5   Report Post  
Wild Bill
 
Posts: n/a
Default

What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing through
the welder's output leads.

Obviously it is not.

WB
...............



"Grant Erwin" wrote in message
...

Current flows out of one leg, through the welder, through the work, back

through
the welder's ground lead, and back through the other leg. Yes, the current

flows
in both legs. A little buzzbox stick welder can draw 41 amps at 240VAC.

The part
you didn't mention is how many amps your welder can weld with. Let's

suppose
it's 250 amps at 25 volts AC. Power is volts times amps, so that's

delivered
power of 6250 watts. Let's assume your welder's transformer is 20% lossy,

so
we'll divide 6250 by 0.8 and get 7812 watts of input power. To calculate

the
current needed from a 220V plug, divide 7812 by 220 to get 35 amps. So you

can
see that 41 amps at 220 is not unreasonable. You can almost certainly get

by
with a 30 amp breaker. If you pulled wire that's too small for a 40 amp

breaker
(did you use 8 gauge wire or 10 gauge wire?) then it may be prudent to

downsize
the breaker to 30 amps. By the way, I have a little buzzbox welder, and I

run it
through a 30 amp breaker and about 15 feet of conduit and a receptacle,

and I
used no. 10 wire. I never ever turn my welder all the way up, or at least

I
haven't yet, so this setup is fine for the little buzzbox.

Grant




----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----


  #6   Report Post  
Grant Erwin
 
Posts: n/a
Default

Wild Bill wrote:

What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing through
the welder's output leads.

Obviously it is not.

WB


(snicker) Wow what a goober I hacked up that time! I have to laugh at the fact
that electrical engineers are capable of the dumbest things sometimes. OK, let's
amend it: current flows down one leg, through the primary of the transformer and
back through the other leg. Point is, the same current flows in both legs. - GWE




"Grant Erwin" wrote in message
...

Current flows out of one leg, through the welder, through the work, back


through

the welder's ground lead, and back through the other leg. Yes, the current


flows

in both legs. A little buzzbox stick welder can draw 41 amps at 240VAC.


The part

you didn't mention is how many amps your welder can weld with. Let's


suppose

it's 250 amps at 25 volts AC. Power is volts times amps, so that's


delivered

power of 6250 watts. Let's assume your welder's transformer is 20% lossy,


so

we'll divide 6250 by 0.8 and get 7812 watts of input power. To calculate


the

current needed from a 220V plug, divide 7812 by 220 to get 35 amps. So you


can

see that 41 amps at 220 is not unreasonable. You can almost certainly get


by

with a 30 amp breaker. If you pulled wire that's too small for a 40 amp


breaker

(did you use 8 gauge wire or 10 gauge wire?) then it may be prudent to


downsize

the breaker to 30 amps. By the way, I have a little buzzbox welder, and I


run it

through a 30 amp breaker and about 15 feet of conduit and a receptacle,


and I

used no. 10 wire. I never ever turn my welder all the way up, or at least


I

haven't yet, so this setup is fine for the little buzzbox.

Grant





----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----

  #7   Report Post  
larry g
 
Posts: n/a
Default

Bill
If the utility system is not providing the current to accomplish the welding
process, who is?
lg
no neat sig line

"Wild Bill" wrote in message
...
What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing
through
the welder's output leads.

Obviously it is not.

WB
..............



"Grant Erwin" wrote in message
...

Current flows out of one leg, through the welder, through the work, back

through
the welder's ground lead, and back through the other leg. Yes, the
current

flows
in both legs. A little buzzbox stick welder can draw 41 amps at 240VAC.

The part
you didn't mention is how many amps your welder can weld with. Let's

suppose
it's 250 amps at 25 volts AC. Power is volts times amps, so that's

delivered
power of 6250 watts. Let's assume your welder's transformer is 20% lossy,

so
we'll divide 6250 by 0.8 and get 7812 watts of input power. To calculate

the
current needed from a 220V plug, divide 7812 by 220 to get 35 amps. So
you

can
see that 41 amps at 220 is not unreasonable. You can almost certainly get

by
with a 30 amp breaker. If you pulled wire that's too small for a 40 amp

breaker
(did you use 8 gauge wire or 10 gauge wire?) then it may be prudent to

downsize
the breaker to 30 amps. By the way, I have a little buzzbox welder, and I

run it
through a 30 amp breaker and about 15 feet of conduit and a receptacle,

and I
used no. 10 wire. I never ever turn my welder all the way up, or at least

I
haven't yet, so this setup is fine for the little buzzbox.

Grant




----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet
News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+
Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption
=----



  #8   Report Post  
Joseph Gwinn
 
Posts: n/a
Default

In article ,
Grant Erwin wrote:

Wild Bill wrote:

What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing through
the welder's output leads.

Obviously it is not.

WB


(snicker) Wow what a goober I hacked up that time! I have to laugh at the fact
that electrical engineers are capable of the dumbest things sometimes. OK, let's
amend it: current flows down one leg, through the primary of the transformer
and back through the other leg. Point is, the same current flows in both legs.


Don't laugh. I've done it. The "resistor" was a 100-watt light bulb in
series with 110-volt power (AC and DC), the welding "stick" was a carbon
rod liberated from a carbon-zinc "D" size battery, and the flux was
twenty mule team borax. We were welding chromel-alumel thermocouples
(with AC and flux) and 3mm diameter platinum capsules (with DC and no
flux aside from the carbon monoxide and hydrogen from the carbon rod and
moisture in the air), all in the 1970s. Simple, cheap, and worked well.

In those days, the University had its own powerplant, and supplied
110/220 volt DC to the labs. When AC power came, all but the labs
converted. In the sub-basement of the lab building there was a four by
six foot 1900s-era open-face power panel carrying the 220 volt DC power,
controlled by huge bare-metal knife switches and cylinder fuses, all
bolted to the front surface of a massive sheet of some kind of black
thermoset plastic, perhaps a bakelite composition. A terrifying
contraption if there ever was - one stumble or slip, and your goose was
*really* cooked. Especially if you were wearing any jewelry.

Joe Gwinn
  #10   Report Post  
Wild Bill
 
Posts: n/a
Default

My comment was to point out that the current from the service panel was not
passing through the welder's output leads.

A contact between service power and earth ground would be deadly.

The welder's transformer in a common AC welder isolates the utility current
(while at the same time decreasing the input voltage, and increasing the
output current capacity).
The output leads are floating and isolated.. although there is a very slight
leakage current in almost any transformer insulation, typically measured in
microamps.

A side note about transformer leakage.. when you see a transformer marked Hi
Pot, it's indicating that the transformer has passed a high voltage
potential test to insure that the leakage (between input and output) is
within safe limits.

WB
..............

"larry g" wrote in message
...
Bill
If the utility system is not providing the current to accomplish the

welding
process, who is?
lg
no neat sig line

"Wild Bill" wrote in message
...
What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing
through
the welder's output leads.

Obviously it is not.

WB
..............



"Grant Erwin" wrote in message
...

Current flows out of one leg, through the welder, through the work,

back
through
the welder's ground lead, and back through the other leg. Yes, the
current

flows
in both legs. A little buzzbox stick welder can draw 41 amps at 240VAC.

The part
you didn't mention is how many amps your welder can weld with. Let's

suppose
it's 250 amps at 25 volts AC. Power is volts times amps, so that's

delivered
power of 6250 watts. Let's assume your welder's transformer is 20%

lossy,
so
we'll divide 6250 by 0.8 and get 7812 watts of input power. To

calculate
the
current needed from a 220V plug, divide 7812 by 220 to get 35 amps. So
you

can
see that 41 amps at 220 is not unreasonable. You can almost certainly

get
by
with a 30 amp breaker. If you pulled wire that's too small for a 40 amp

breaker
(did you use 8 gauge wire or 10 gauge wire?) then it may be prudent to

downsize
the breaker to 30 amps. By the way, I have a little buzzbox welder, and

I
run it
through a 30 amp breaker and about 15 feet of conduit and a receptacle,

and I
used no. 10 wire. I never ever turn my welder all the way up, or at

least
I
haven't yet, so this setup is fine for the little buzzbox.

Grant




----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet
News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+
Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption
=----







----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----


  #11   Report Post  
Wild Bill
 
Posts: n/a
Default

I don't subscribe to the proposal that current flows back out the other
input lead. As I've stated before, I always have to ask Ok, THEN where does
it go?

The concept that there is a return line is counter-productive to
understanding electrical power circuits.
If all current travels back into the earth, or some other whimsical theory,
nothing would operate as it does.
Earth ground connections are for safety only, to insure that a person is
never the only path between an electrical potential and earth ground.

In the application of a transformer with a 240VAC input, the supply
conductors do just that, they supply.. there is no return.
Because it's AC, the two conductors take turns being different potentials to
each other (easier to just think that they take turns being zero).
When the other line's potential is not zero, current flows through the
xfmr's primary winding (back 'n forth within the winding, not out to
somewhere else).

In a hydraulic circuit, the oil is returned to the pump (by way of a
reservior usually), and the hydraulic circuit is basically a closed loop.
Electricity ain't that way.

In an application where the transformer input is 120VAC, the neutral isn't a
return line. It's there to establish a potential. No potential, no worky.

For either xfmr, the output of the secondary winding floats until circuit
potentials are established.
The potential between one of the secondary terminals (either one) and earth
ground is essentially zero.
No potential, no current (aside from the microamp xfmr leakage, assuming
that the xfmr is not faulty). Some digital voltmeters are flakey when
measuring similar points, and give false voltage readings, but there is
absolutely no usable current present.
When a circuit is established, the secondary winding terminals are both
supply lines, there is no return.

Yeah, but my AC amp clamp meter shows current in the neutral line.
Does the meter show which direction it's flowing? Didn't think so, 'cause
it's alternating.
An oscilloscope won't help. There's no point in trying to tag a sinewave
peak to see it being used up.
You can't count the number of sinewaves that a table lamp uses. It's not
helpful to consider sinewaves as quantitiy of consumables.
Ever heard of a sinewave storage capacity for an AC capacitor? 'Course not.

WB
................

"Grant Erwin" wrote in message
...
Wild Bill wrote:

What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing

through
the welder's output leads.

Obviously it is not.

WB


(snicker) Wow what a goober I hacked up that time! I have to laugh at the

fact
that electrical engineers are capable of the dumbest things sometimes. OK,

let's
amend it: current flows down one leg, through the primary of the

transformer and
back through the other leg. Point is, the same current flows in both

legs. - GWE







----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
  #12   Report Post  
Grant Erwin
 
Posts: n/a
Default

Think whatever you like, Bill. Whatever floats yer boat. Just size both
conductors sufficient to carry the full amps, not half the amps, and all will be
good. - GWE

Wild Bill wrote:
I don't subscribe to the proposal that current flows back out the other
input lead. As I've stated before, I always have to ask Ok, THEN where does
it go?

The concept that there is a return line is counter-productive to
understanding electrical power circuits.
If all current travels back into the earth, or some other whimsical theory,
nothing would operate as it does.
Earth ground connections are for safety only, to insure that a person is
never the only path between an electrical potential and earth ground.

In the application of a transformer with a 240VAC input, the supply
conductors do just that, they supply.. there is no return.
Because it's AC, the two conductors take turns being different potentials to
each other (easier to just think that they take turns being zero).
When the other line's potential is not zero, current flows through the
xfmr's primary winding (back 'n forth within the winding, not out to
somewhere else).

In a hydraulic circuit, the oil is returned to the pump (by way of a
reservior usually), and the hydraulic circuit is basically a closed loop.
Electricity ain't that way.

In an application where the transformer input is 120VAC, the neutral isn't a
return line. It's there to establish a potential. No potential, no worky.

For either xfmr, the output of the secondary winding floats until circuit
potentials are established.
The potential between one of the secondary terminals (either one) and earth
ground is essentially zero.
No potential, no current (aside from the microamp xfmr leakage, assuming
that the xfmr is not faulty). Some digital voltmeters are flakey when
measuring similar points, and give false voltage readings, but there is
absolutely no usable current present.
When a circuit is established, the secondary winding terminals are both
supply lines, there is no return.

Yeah, but my AC amp clamp meter shows current in the neutral line.
Does the meter show which direction it's flowing? Didn't think so, 'cause
it's alternating.
An oscilloscope won't help. There's no point in trying to tag a sinewave
peak to see it being used up.
You can't count the number of sinewaves that a table lamp uses. It's not
helpful to consider sinewaves as quantitiy of consumables.
Ever heard of a sinewave storage capacity for an AC capacitor? 'Course not.

WB
...............

"Grant Erwin" wrote in message
...

Wild Bill wrote:


What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing


through

the welder's output leads.

Obviously it is not.

WB


(snicker) Wow what a goober I hacked up that time! I have to laugh at the


fact

that electrical engineers are capable of the dumbest things sometimes. OK,


let's

amend it: current flows down one leg, through the primary of the


transformer and

back through the other leg. Point is, the same current flows in both


legs. - GWE






----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----

  #13   Report Post  
Glenn
 
Posts: n/a
Default

ROTFLMAO
And the earth is to flat!
"Wild Bill" wrote in message
...
I don't subscribe to the proposal that current flows back out the other
input lead. As I've stated before, I always have to ask Ok, THEN where
does
it go?

The concept that there is a return line is counter-productive to
understanding electrical power circuits.
If all current travels back into the earth, or some other whimsical
theory,
nothing would operate as it does.
Earth ground connections are for safety only, to insure that a person is
never the only path between an electrical potential and earth ground.

In the application of a transformer with a 240VAC input, the supply
conductors do just that, they supply.. there is no return.
Because it's AC, the two conductors take turns being different potentials
to
each other (easier to just think that they take turns being zero).
When the other line's potential is not zero, current flows through the
xfmr's primary winding (back 'n forth within the winding, not out to
somewhere else).

In a hydraulic circuit, the oil is returned to the pump (by way of a
reservior usually), and the hydraulic circuit is basically a closed loop.
Electricity ain't that way.

In an application where the transformer input is 120VAC, the neutral isn't
a
return line. It's there to establish a potential. No potential, no worky.

For either xfmr, the output of the secondary winding floats until circuit
potentials are established.
The potential between one of the secondary terminals (either one) and
earth
ground is essentially zero.
No potential, no current (aside from the microamp xfmr leakage, assuming
that the xfmr is not faulty). Some digital voltmeters are flakey when
measuring similar points, and give false voltage readings, but there is
absolutely no usable current present.
When a circuit is established, the secondary winding terminals are both
supply lines, there is no return.

Yeah, but my AC amp clamp meter shows current in the neutral line.
Does the meter show which direction it's flowing? Didn't think so, 'cause
it's alternating.
An oscilloscope won't help. There's no point in trying to tag a sinewave
peak to see it being used up.
You can't count the number of sinewaves that a table lamp uses. It's not
helpful to consider sinewaves as quantitiy of consumables.
Ever heard of a sinewave storage capacity for an AC capacitor? 'Course
not.

WB
...............

"Grant Erwin" wrote in message
...
Wild Bill wrote:

What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing

through
the welder's output leads.

Obviously it is not.

WB


(snicker) Wow what a goober I hacked up that time! I have to laugh at the

fact
that electrical engineers are capable of the dumbest things sometimes.
OK,

let's
amend it: current flows down one leg, through the primary of the

transformer and
back through the other leg. Point is, the same current flows in both

legs. - GWE







----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet
News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+
Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption
=----



  #14   Report Post  
lionslair at consolidated dot net
 
Posts: n/a
Default

If you think about it, only the electrons on my side of the transformer and those
in the ground that might mix in - flow in my circuits. The power company induce
current flow in the transformer. Without circular flow of some kind, only a static
or no current flow condition exists.

Now - if I can only charge the power company for use of 'my electrons'. :-)

Martin

Grant Erwin wrote:

Think whatever you like, Bill. Whatever floats yer boat. Just size both
conductors sufficient to carry the full amps, not half the amps, and all
will be good. - GWE

Wild Bill wrote:

I don't subscribe to the proposal that current flows back out the other
input lead. As I've stated before, I always have to ask Ok, THEN where
does
it go?

The concept that there is a return line is counter-productive to
understanding electrical power circuits.
If all current travels back into the earth, or some other whimsical
theory,
nothing would operate as it does.
Earth ground connections are for safety only, to insure that a person is
never the only path between an electrical potential and earth ground.

In the application of a transformer with a 240VAC input, the supply
conductors do just that, they supply.. there is no return.
Because it's AC, the two conductors take turns being different
potentials to
each other (easier to just think that they take turns being zero).
When the other line's potential is not zero, current flows through the
xfmr's primary winding (back 'n forth within the winding, not out to
somewhere else).

In a hydraulic circuit, the oil is returned to the pump (by way of a
reservior usually), and the hydraulic circuit is basically a closed loop.
Electricity ain't that way.

In an application where the transformer input is 120VAC, the neutral
isn't a
return line. It's there to establish a potential. No potential, no worky.

For either xfmr, the output of the secondary winding floats until circuit
potentials are established.
The potential between one of the secondary terminals (either one) and
earth
ground is essentially zero.
No potential, no current (aside from the microamp xfmr leakage, assuming
that the xfmr is not faulty). Some digital voltmeters are flakey when
measuring similar points, and give false voltage readings, but there is
absolutely no usable current present.
When a circuit is established, the secondary winding terminals are both
supply lines, there is no return.

Yeah, but my AC amp clamp meter shows current in the neutral line.
Does the meter show which direction it's flowing? Didn't think so, 'cause
it's alternating.
An oscilloscope won't help. There's no point in trying to tag a sinewave
peak to see it being used up.
You can't count the number of sinewaves that a table lamp uses. It's not
helpful to consider sinewaves as quantitiy of consumables.
Ever heard of a sinewave storage capacity for an AC capacitor? 'Course
not.

WB
...............

"Grant Erwin" wrote in message
...

Wild Bill wrote:


What's in this welder described below, a couple of resistors?

Everyone had better hope that utility system current is not passing



through

the welder's output leads.

Obviously it is not.

WB


(snicker) Wow what a goober I hacked up that time! I have to laugh at
the



fact

that electrical engineers are capable of the dumbest things
sometimes. OK,



let's

amend it: current flows down one leg, through the primary of the



transformer and

back through the other leg. Point is, the same current flows in both



legs. - GWE






----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet
News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World!
120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption
=----



--
Martin Eastburn
@ home at Lion's Lair with our computer lionslair at consolidated dot net
NRA LOH, NRA Life
NRA Second Amendment Task Force Charter Founder

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
  #15   Report Post  
Wild Bill
 
Posts: n/a
Default

There is no circular flow, this is a misconception.

The subject began as a discussion of a 240VAC circuit for a welder. Since
240VAC appliances do not require an earth ground (for anything other than
safety, not current) to produce an output , there is no return path to earth
ground.
The earth ground lead of the appliance's power cord isn't connected to the
welder's transformer terminals.
It's connected to the case of the welder to make it a safe appliance to use.
In the event of an internal fault, the case remains at earth ground
potential (zero volts). When the current level reaches the circuit breaker
rating, the circuit breaker will open.
The case is earth grounded so that the operator doesn't die in the event of
an internal fault in the welder.

In normal operation, there is no return to anywhere, and definitely not to
the utility company transformer. The appliance causes the power to be
expended/used/dissipated internally.

There is no trickery or deceit going on here. The 100W on the top of the
incandescent light bulb basically means that the bulb consumes 100W. Ten of
'em left on for an hour is 1 KWH that you'll be charged for. In the winter,
you've received the light plus the benefit of the heaters. In the summer,
you pay to have the heat removed from the house by an air conditioner.
Gotcha.
The water heater element wattage rating means the same thing.

Anyone can take a stab at an explanation of where the current goes when it
goes back thru one of the supply lines by calling it a return, but they have
no explanation of where it goes.
Just because it's a common belief that it must return, don't make it fact.
The fact that some of the utility power distribution points are grounded is
because power companies have to deal with lightning strikes, line breaks and
transformer failures. They have to pay for insurance too, and they don't
want household lines to suddenly jump up into the kilovolts range in the
event of a fault/failure or accident.
The ground rods driven into the dirt out at the pole or across the street
(or other points for underground service) don't create a return path for
your household appliances.

If I connect one terminal of a AA battery to an earth ground, is the battery
charging or draining?
What's going on with the hypothetical ground electrons? Pushing? No.
Pulling? No. Flowing in either direction? No.
A battery is an example of an isolated supply. We know the battery is
capable of providing useable current. Is it flowing? No.

Most homes are powered from the isolated secondary winding of the utility
company's transformer. (I already understand that there is a center tap, and
it's the home service panel's neutral bar).
That supply is a floating source, just as the secondary of an ordinary power
transformer is (explanation of a common power xfmr in earlier post).

There is no usable current path from a floating xfmr secondary winding to
earth ground (microamp xfmr leakage excluded).

There isn't much point in injecting electrons into a dicussion of electrical
power, but I'll go along. When the spark occurs at your finger tip when you
touch a door knob mounted in a wooden door, where do the electrons go? I
don't care either, but I'll read the explanations.

WB
..................

"lionslair at consolidated dot net" "lionslair at consolidated dot net"
wrote in message ...
If you think about it, only the electrons on my side of the transformer

and those
in the ground that might mix in - flow in my circuits. The power company

induce
current flow in the transformer. Without circular flow of some kind, only

a static
or no current flow condition exists.

Now - if I can only charge the power company for use of 'my electrons'.

:-)

Martin




----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----


  #16   Report Post  
 
Posts: n/a
Default

Although the NEC allows conductors supplying a welder to carry more
than their rated capacity, I would never size the breaker for more than
the ampacity of the wire. Remember the breaker will also carry more
than its rated capacity on a duty cycle of 20%. If you " protect " 14
gauge wire with a 40A breaker, you might have the insulation melt
before the breaker trips.

Dan



Ned Simmons wrote:
In article 1119797867.565455.246460
@g14g2000cwa.googlegroups.com, says...
You should size the breaker for the wire, not for the load.

Size the wire for the load.


Yes, *but*, the NEC allows the conductors supplying a
welder to carry more than their normal rated ampacity. For
example, if we assume the welder in question with a primary
rated current of 41 amps has a 20% duty cycle rating, then
the supply conductors need only have a rated ampacity of
18.5A. So you could conceivably have an installation with
14ga wire protected by a 40A breaker feeding the welder.


  #18   Report Post  
 
Posts: n/a
Default

There are several types of circuit breakers. One type is a thermal
circuit breaker. You would not want to use a 90a thermal circuit
breaker with 10 gauge wire.

Copied from Electronic Design article on circuit breakers.

"Appropriate for equipment where high-surge currents accompany the
start of motors, thermal circuit breakers use bimetal technology to
discriminate between safe switch-on currents/transients and prolonged
overloads. A typical thermal breaker must trip within one hour at 140%
of its rating. A latching mechanism makes these devices highly tolerant
of shock and vibration."

lets see 140 percent of 90 amps is 126 amps. So you think it might be
alright to run 126 amps through 10 gauge wire for an hour? Granted
most circuit breakers are not thermal breakers, but without knowing the
breaker type, I would not recommend sizing the breaker for more current
than the wire is rated for. I have no problem recommending using a
welder on a circuit with wire that can not handle the input current of
a welder on a 100 % duty cycle.

Dan

Nate Weber wrote:


That's the entire point of the duty cycle, You can hit the wire with a
high current but before it overheats, either you stop welding or the
welder trips on thermal and allows the wire to cool down. Alot like
pulse welding where ya set your peak amperage to 150 - 200% normal
amperage and can still make a good weld.
Don't forget also that you can size you breaker up to 200% the rated
input current of the welder, on a miller thunderbolt, one could be
running 10ga supply conductors on a 90A breaker and still be within code.
Everything depends on the particular welder you are using, The welder
will not draw more than the rated input amps unless there is a dead
short and the welder will not draw high currents for any length of time
due to the duty cycle. Change the welder and you are back to square one.

Nate

--
Http://www.Weber-Automation.net:8000


  #19   Report Post  
footy
 
Posts: n/a
Default

I think with the typical residential installation in the U.S.A. you are
going to be relying on the thermal trip characteristics of the breaker.
But with good equipment, it should not be as bad as it might sound.

My house has a Square D QO load center, which is generally considered a
good brand and line, and is used in commercial buildings as well as
residences. The breakers have both thermal and magnetic trips. The
higher the overcurrent condition, the faster the thermal trip. Moderate
overcurrent conditions will indeed take a while to trip, in the case of
a 50A QO breaker, something on the order of 40 seconds at 150%. The
magnetic trip does not come into play until something close to 20 times
the rated current is going through the breaker, when it trips nearly
instantaneously. The magnetic trip is there only to deal with
catastrophic problems like dead shorts in the equipment or line. That
said, there are a lot of other brands and lines out there, and some may
have very different trip characteristics.

FWIW, I would use the largest wire within reason that will fit the
terminals of the breaker and receptacle if for no other reason than to
minimize voltage drop. On a short run, it won't make much of a
difference in cost. On a long run, you may need the bigger size to
maintain a reasonable input voltage or have the required ampacity after
derating for ambient temperature.
  #20   Report Post  
Nate Weber
 
Posts: n/a
Default





lets see 140 percent of 90 amps is 126 amps. So you think it might be
alright to run 126 amps through 10 gauge wire for an hour? Granted
most circuit breakers are not thermal breakers, but without knowing the
breaker type, I would not recommend sizing the breaker for more current
than the wire is rated for. I have no problem recommending using a
welder on a circuit with wire that can not handle the input current of
a welder on a 100 % duty cycle.

Dan


If the welder has a max rated input current of 48.5 Amps and a Duty
cycle of 20% how is anyone going to pull 126 amps for an hour?
I could dead short the welder leads at max output and draw 48.5 amps for
about 2 or so minutes. After that it would cool down for 8 minutes.

--
Http://www.Weber-Automation.net:8000


  #21   Report Post  
Ned Simmons
 
Posts: n/a
Default

In article 1120098843.355098.302240
@g47g2000cwa.googlegroups.com, says...
There are several types of circuit breakers. One type is a thermal
circuit breaker. You would not want to use a 90a thermal circuit
breaker with 10 gauge wire.

Copied from Electronic Design article on circuit breakers.

"Appropriate for equipment where high-surge currents accompany the
start of motors, thermal circuit breakers use bimetal technology to
discriminate between safe switch-on currents/transients and prolonged
overloads. A typical thermal breaker must trip within one hour at 140%
of its rating. A latching mechanism makes these devices highly tolerant
of shock and vibration."

lets see 140 percent of 90 amps is 126 amps. So you think it might be
alright to run 126 amps through 10 gauge wire for an hour? Granted
most circuit breakers are not thermal breakers, but without knowing the
breaker type, I would not recommend sizing the breaker for more current
than the wire is rated for. I have no problem recommending using a
welder on a circuit with wire that can not handle the input current of
a welder on a 100 % duty cycle.


The circuit breakers described in that article are not
permitted for branch circuit protection. In fact, if you
look at the catalogs published by Cutler-Hammer, SquareD,
Siemens, etc., they avoid "circuit breaker" when talking
about these devices and refer to them as "supplementary
protectors," and reserve the term "circuit breaker" for
devices that can be used as branch circuit protection.

The 90A number for #10 wire that's been bandied about is
incorrect, at least for the more common insulation classes.
There's an additional provision in the NEC section on
welders that says that the overcurrent device must be set
to no more than twice the conductor rating, so 70A(for 75C
insulation - romex) or 80A(for 90C - THHN) is a more
realistic high end.

Ned Simmons
  #22   Report Post  
 
Posts: n/a
Default

Bill,

It is preposterous to say that the electrons flow out and go somewhere
mysterious and never return during normal operation. There is
definitely a return on a 240V circuit going to a welder. Electrons flow
down one leg, thought the transformer winding in the welder, then back
up the other leg. Re-examining the situation 16.6mS later, of course
the current is flowing the opposite direction. But whatever electrons
flow out on one leg of the circuit come back up the other side. Thats
why its called a "circuit".

I'm not sure what point you are shooting for here, and you are correct
in many cases, i.e. saying that there is no current flow to earth
ground. But you are mistaken in saying there is no return. A conductor
can provide a return path without being at earth ground potential.
Similarly on 120V circuits, the return path is the neutral line, which
is also not necessarily at earth ground potential (indeed, because of
the return current flowing across its resistance).

-Holly

  #23   Report Post  
Wild Bill
 
Posts: n/a
Default

Yeah, folks keep insisting that half of the supply leads are returns, but no
one is saying where the power or current is returning to/going.

You present a contradiction, I think, by stating (agreeing) that there is no
current path to earth ground in 120V circuits, but then stating that the
neutral provides a current return path, although the neutral is actually
bonded to the structure's earth ground rod in most instances.

Neutral isn't anything other than a reference point. That reference point is
essentially zero since it's bonded to earth ground. That essentially zero
point is present at one side of a 120V lamp or appliance cord.
It stays at the reference point of essentially zero. One exception to this
would be at the precise instant of a very close lightning strike, when the
reference changes, and often results in damage.
In a 120V lamp circuit, the neutral is lower or higher in potential than the
home panel's bus bar (either one), depending upon the amplitude of the
zero-crossing sinewave.
The 120V lamp doesn't care if the voltage potential is lower or higher, it
just lights, dims and lights at 60 cycles per second.

So, for those that insist that the neutral is a return path, they're still
not correct in thinking that the neutral is returning current half the time,
as a result from being a lower or higher potential (to the bus bar), because
it is still just an essentially zero reference point. The only time the lamp
lights is when the line (bus bar) potential is not zero.

Where the current goes in a 120V lamp, is into the filament resistance. The
neutral is still just an essentially zero reference point. The light and
heat are the product of the 120v being dissipated by the filament's
resitance, and there is no left over power or current to return to anywhere
else.

As I said before, I don't see the point in discussing electrons when
considering electrical power applications.
The duration of a sinewave is not it's rate of travel, it's the frequency at
which the AC alternates. The frequency of the cycles has nothing to do with
how long a cycle spends in the load, or how fast it passes out to somewhere
else.

In a 240VAC circuit, what about the other phase, then? Is current from L1
returning "out" on L2, then L2's current returning "out" on L1?
Fascinating, if you could show that happening, don't you think so?
If everyone would limit the "return" current, they would save energy?

What I have said before, is that the two 240VAC input terminals at the
welder transformer are basically taking turns being the higher potential,
while the difference in potential is 240VAC.
The changes in potential (alternating voltage changes) create current in the
resistance of the winding, and are dissipated in the transformer's primary
winding.

AC can be distributed for long distances with only minimal losses. It
doesn't flow in a circular pattern, out one conductor and through a load and
back out to the other.
It's either present, or it's not.

Any of this real science can be tested/proven by experimenting with a common
power transformer. Since many homes are supplied power from a nearly
identical source, it would be simple enough to make an equivalent house
service panel setup with an isolated center-tapped 24VAC transformer
secondary winding (or secondary voltage of choice).

-Holly
"But you are mistaken in saying there is no return".
"A conductor can provide a return path without being at earth ground

potential".

For AC, it's not a return path, it is only a different potential. My
question remains.. return to where?

WB
..................

wrote in message
oups.com...
Bill,

It is preposterous to say that the electrons flow out and go somewhere
mysterious and never return during normal operation. There is
definitely a return on a 240V circuit going to a welder. Electrons flow
down one leg, thought the transformer winding in the welder, then back
up the other leg. Re-examining the situation 16.6mS later, of course
the current is flowing the opposite direction. But whatever electrons
flow out on one leg of the circuit come back up the other side. Thats
why its called a "circuit".

I'm not sure what point you are shooting for here, and you are correct
in many cases, i.e. saying that there is no current flow to earth
ground. But you are mistaken in saying there is no return. A conductor
can provide a return path without being at earth ground potential.
Similarly on 120V circuits, the return path is the neutral line, which
is also not necessarily at earth ground potential (indeed, because of
the return current flowing across its resistance).

-Holly





----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Popping circuit breaker w/ TS Don97623 Woodworking 14 December 1st 04 01:49 AM
circuit breaker popping once every 24 hrs Dan Kuechle Home Repair 8 August 5th 04 07:04 PM
circuit is off, circuit breaker is on Massi Home Repair 1 July 4th 04 11:31 PM
circuit breaker Smerby Home Repair 3 March 6th 04 04:51 AM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM


All times are GMT +1. The time now is 04:53 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"