Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tuesday, July 18, 2017 at 8:00:26 AM UTC-4, Bob wrote:
Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob


As long as the device is listed for use that way, that's correct,
it's self-grounding when installed in a metal box.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 961
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tue, 18 Jul 2017 08:00:20 -0400, Bob wrote:

Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob


Bob, if you are positive the box is grounded, then run a pigtail from
a ground screw in the box to the GFCI. If there is a separate ground
wire in the circuit, connect that to the GFCI (and to the metal box).

Obtaining a ground through the tabs and mounting screws is possible,
but many times, in order to get the outlet to mate properly with the
wall cover plate, the outlets tabs are not always snug up against the
box. In that case, the electrical ground would be only through the
threads of the screws, which, IMHO, is less then desirable.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tuesday, July 18, 2017 at 9:50:42 AM UTC-4, Stormin' Norman wrote:
On Tue, 18 Jul 2017 08:00:20 -0400, Bob wrote:

Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob


Bob, if you are positive the box is grounded, then run a pigtail from
a ground screw in the box to the GFCI. If there is a separate ground
wire in the circuit, connect that to the GFCI (and to the metal box).

Obtaining a ground through the tabs and mounting screws is possible,
but many times, in order to get the outlet to mate properly with the
wall cover plate, the outlets tabs are not always snug up against the
box. In that case, the electrical ground would be only through the
threads of the screws, which, IMHO, is less then desirable.


His question was if self-grounding is allowed. The answer is NEC allows
it, as long as the receptacle is listed for that purpose, which many are.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 961
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tue, 18 Jul 2017 07:25:32 -0700 (PDT), trader_4
wrote:

On Tuesday, July 18, 2017 at 9:50:42 AM UTC-4, Stormin' Norman wrote:
On Tue, 18 Jul 2017 08:00:20 -0400, Bob wrote:

Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob


Bob, if you are positive the box is grounded, then run a pigtail from
a ground screw in the box to the GFCI. If there is a separate ground
wire in the circuit, connect that to the GFCI (and to the metal box).

Obtaining a ground through the tabs and mounting screws is possible,
but many times, in order to get the outlet to mate properly with the
wall cover plate, the outlets tabs are not always snug up against the
box. In that case, the electrical ground would be only through the
threads of the screws, which, IMHO, is less then desirable.


His question was if self-grounding is allowed. The answer is NEC allows
it, as long as the receptacle is listed for that purpose, which many are.


Thanks for your input.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tue, 18 Jul 2017 14:35:51 +0000, Stormin' Norman
wrote:

On Tue, 18 Jul 2017 07:25:32 -0700 (PDT), trader_4
wrote:

On Tuesday, July 18, 2017 at 9:50:42 AM UTC-4, Stormin' Norman wrote:
On Tue, 18 Jul 2017 08:00:20 -0400, Bob wrote:

Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob

Bob, if you are positive the box is grounded, then run a pigtail from
a ground screw in the box to the GFCI. If there is a separate ground
wire in the circuit, connect that to the GFCI (and to the metal box).

Obtaining a ground through the tabs and mounting screws is possible,
but many times, in order to get the outlet to mate properly with the
wall cover plate, the outlets tabs are not always snug up against the
box. In that case, the electrical ground would be only through the
threads of the screws, which, IMHO, is less then desirable.


His question was if self-grounding is allowed. The answer is NEC allows
it, as long as the receptacle is listed for that purpose, which many are.


Thanks for your input.


You were always allowed to use the tab for grounding if at least one
of the fiber, screw retention, washers was removed and the tab was
made up tight to a metal box. (not hanging out on "drywall ears")
What changed was the product. As Trader points out, newer spec grade
devices have a metal spring in one of the mounting tabs that makes
direct contact with the mounting screw and gives you a better ground.
It is legal but I am still not sure I would trust my life to it with
anything but a GFCI, although an Arc Fault breaker is to some extent a
GFCI. It operates at a 30ma level on a ground fault.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 961
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tue, 18 Jul 2017 11:21:28 -0400, wrote:

On Tue, 18 Jul 2017 14:35:51 +0000, Stormin' Norman
wrote:

On Tue, 18 Jul 2017 07:25:32 -0700 (PDT), trader_4
wrote:

On Tuesday, July 18, 2017 at 9:50:42 AM UTC-4, Stormin' Norman wrote:
On Tue, 18 Jul 2017 08:00:20 -0400, Bob wrote:

Hello,

Let me try to ask this in an understandable way.

Been many, many years since I wired any outlets, switches, etc.,
so possibly the building codes have changed ? (live in Mass.)

Previously, when you installed or replaced a switch, outlets, or even a
GFCI, it was "required" that you run a green grounding wire from the
back of the metal box where you would have a screw grounding together
the box, and All the green wires from the outlets, etc grounds
to the switch or outlet grounding screw.

It was not allowed, I think, to just have the mounting tabs
do the grounding thru the box shell, although the mounting tabs
were (usually) common with the outlet or switch grounding screw.

I now see that Leviton implies for their their GFCI devices
that you can simply use the mounting tabs, and that a separate ground
wire to the box grounding screw is not required.

Do I have this right ?
Has the code changed.

Just use the GFCI mounting tabs, and don't run a separate ground wire ?

Or,...?

Thanks,
Bob

Bob, if you are positive the box is grounded, then run a pigtail from
a ground screw in the box to the GFCI. If there is a separate ground
wire in the circuit, connect that to the GFCI (and to the metal box).

Obtaining a ground through the tabs and mounting screws is possible,
but many times, in order to get the outlet to mate properly with the
wall cover plate, the outlets tabs are not always snug up against the
box. In that case, the electrical ground would be only through the
threads of the screws, which, IMHO, is less then desirable.

His question was if self-grounding is allowed. The answer is NEC allows
it, as long as the receptacle is listed for that purpose, which many are.


Thanks for your input.


You were always allowed to use the tab for grounding if at least one
of the fiber, screw retention, washers was removed and the tab was
made up tight to a metal box. (not hanging out on "drywall ears")
What changed was the product. As Trader points out, newer spec grade
devices have a metal spring in one of the mounting tabs that makes
direct contact with the mounting screw and gives you a better ground.
It is legal but I am still not sure I would trust my life to it with
anything but a GFCI, although an Arc Fault breaker is to some extent a
GFCI. It operates at a 30ma level on a ground fault.


I do not disagree with what you have written. However, I have seen
many older installations with poorly grounded or ungrounded boxes.

My perspective of code is; it is the bare minimum acceptable to pass
inspection. If one makes good, wired ground connections, with a
degree of redundancy, it will not only meet code, but exceed it.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Outlet And Switch Grounding In The Metal Wall Box ?

On Tue, 18 Jul 2017 18:04:05 +0000, Stormin' Norman
wrote:

On Tue, 18 Jul 2017 12:33:27 -0400, wrote:

On Tue, 18 Jul 2017 15:34:14 +0000, Stormin' Norman
wrote:

On Tue, 18 Jul 2017 11:21:28 -0400,
wrote:


You were always allowed to use the tab for grounding if at least one
of the fiber, screw retention, washers was removed and the tab was
made up tight to a metal box. (not hanging out on "drywall ears")
What changed was the product. As Trader points out, newer spec grade
devices have a metal spring in one of the mounting tabs that makes
direct contact with the mounting screw and gives you a better ground.
It is legal but I am still not sure I would trust my life to it with
anything but a GFCI, although an Arc Fault breaker is to some extent a
GFCI. It operates at a 30ma level on a ground fault.

I do not disagree with what you have written. However, I have seen
many older installations with poorly grounded or ungrounded boxes.

My perspective of code is; it is the bare minimum acceptable to pass
inspection. If one makes good, wired ground connections, with a
degree of redundancy, it will not only meet code, but exceed it.


Ungrounded boxes have not been legal since the Eisenhower
administration but I agree there has always been bad workmanship and
sloppy inspection.


Well, he is in Mass with metal boxes so, who knows how old his
electrical system is?


It is easy enough to test. I recommend something like the good
Suretest or an Ecos and not a regular VOM tho since they actually test
under a load. Unfortunately they may not detect a bootleg ground tied
to the neutral if that happens more than ~20 feet from the place you
are testing. It will find one right in the same box tho. They want 1
ohm but more than zero.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
new metal back box sunken into wall.... wall plastered..... screwthread missing in side lug when trying to screw new socket to the wall....what to do? Stephen[_16_] UK diy 18 July 7th 14 08:23 PM
Grounding A Metal (outlet) Gang Box Question Robert11 Home Repair 6 March 6th 05 03:27 PM
[Fwd: Self-grounding outlets vs. grounding wire] Phil Munro Home Repair 0 December 1st 04 07:52 PM
Doulble Receptacle Grounding Question/ Switch Grounding Michael Roback Home Repair 1 September 7th 03 07:37 AM
Change ceiling outlet pull switch to wall switch? Space Cowboy Home Ownership 12 July 1st 03 02:30 PM


All times are GMT +1. The time now is 05:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"