Hi all, I'm a newbie at troubleshooting furnace problems, so please bear
with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed |
#2
|
|||
|
|||
Furnace not turning on
get the motor replaced
|
#3
|
|||
|
|||
Furnace not turning on
"Ed" wrote in message news:EDM2c.101332$A12.38409@edtnps84... Hi all, I'm a newbie at troubleshooting furnace problems, so please bear with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed This is Turtle. I can't see it from here because of your 36" TV is in the way looking through your front window, but Like Ransley said replace the blower motor. now in a lot of cases you have to buy the blower housing attached because it being made all together. TURTLE --- Outgoing mail is certified Virus Free. Checked by AVG anti-virus system (http://www.grisoft.com). Version: 6.0.611 / Virus Database: 391 - Release Date: 3/3/2004 |
#4
|
|||
|
|||
Furnace not turning on
"Ed" wrote in message news:EDM2c.101332$A12.38409@edtnps84... Hi all, I'm a newbie at troubleshooting furnace problems, so please bear with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed Man..its already failed. I dont know where you are at, but you need to call a qualified repair tech out, and allow them to replace the unit thats failed, and insure that you have not done some damage to anything by allowing the unit to run with a bad motor, motor control, or such. That is called an inducer motor, and it is there for a reason. It has at least 3 safety devices connected to it, and its possible that one has failed in a manner that the shock of hitting it is allowing it to "run fine for a day or so..." You need to stop poking around, and get someone that understands how these work out there to check out the unit. Its not going to be cheap if you get someone that has a clue, but you will find its cheaper than creating a condition that just might be deadly, or, at the very least, harmful to you or your family. There is a damn good reason why there is warnings on those units that tell you not to muck around with them unless you are qualified, and its obvious you are not. You will want to insure that the person working on your unit is licenced, if thats required in your area, and insured. ASK for the proof of insurance. |
#5
|
|||
|
|||
Furnace not turning on
040307 1638 - Ed posted:
Hi all, I'm a newbie at troubleshooting furnace problems, so please bear with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed The furnace purge motor has to be operating before the main gas valve will operate. There is usually a paddle in the air flow of this purge system to let the system know that there is air flow and gases are being exhausted out so that a gas flame doesn't ignite leftover gases and explode. It sounds like this purge motor is lacking lubrication in its bearings, or the fan blade is rubbing against something. If you want to work on this yourself, you can remove the purge fan motor and fan and spin the motor shaft and see if the bearings are OK. Check for sloppiness in the shaft rotation. Connect the motor to its appropriate voltage and see if it operates properly. If you need a new motor, you can contact your local furnace company and give them the model of the furnace, and the model of the motor and get a new one. |
#6
|
|||
|
|||
Furnace not turning on
"indago" wrote in message ... 040307 1638 - Ed posted: Hi all, I'm a newbie at troubleshooting furnace problems, so please bear with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed The furnace purge motor has to be operating before the main gas valve will operate. There is usually a paddle in the air flow of this purge system to let the system know that there is air flow and gases are being exhausted out so that a gas flame doesn't ignite leftover gases and explode. It sounds like this purge motor is lacking lubrication in its bearings, or the fan blade is rubbing against something. If you want to work on this yourself, you can remove the purge fan motor and fan and spin the motor shaft and see if the bearings are OK. Check for sloppiness in the shaft rotation. Connect the motor to its appropriate voltage and see if it operates properly. If you need a new motor, you can contact your local furnace company and give them the model of the furnace, and the model of the motor and get a new one. Thanks to everyone for your informative replies. I'll have a closer look at this inducer/purge motor and see how difficult it'll be to replace. I do appreciate the safety risks involved in fixing a furnace, so if I don't feel confortable with the task at hand I will call a heating technician out to fix the problem. Even then, with the info you all have provided, it'll hopefully help me be more informed when dealing with the technician. I'll try to keep everyone posted once I get this problem resolved. Ed. |
#7
|
|||
|
|||
Furnace not turning on
On Mon, 08 Mar 2004 07:40:06 GMT, "Ed" wrote:
"indago" wrote in message ... 040307 1638 - Ed posted: Hi all, I'm a newbie at troubleshooting furnace problems, so please bear with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed The furnace purge motor has to be operating before the main gas valve will operate. There is usually a paddle in the air flow of this purge system to let the system know that there is air flow and gases are being exhausted out so that a gas flame doesn't ignite leftover gases and explode. f It sounds like this purge motor is lacking lubrication in its bearings, or the fan blade is rubbing against something. If you want to work on this yourself, you can remove the purge fan motor and fan and spin the motor shaft and see if the bearings are OK. Check for sloppiness in the shaft rotation. Connect the motor to its appropriate voltage and see if it operates properly. If you need a new motor, you can contact your local furnace company and give them the model of the furnace, and the model of the motor and get a new one. Thanks to everyone for your informative replies. I'll have a closer look at this inducer/purge motor and see how difficult it'll be to replace. I do appreciate the safety risks involved in fixing a furnace, so if I don't feel confortable with the task at hand I will call a heating technician out to fix the problem. Even then, with the info you all have provided, it'll hopefully help me be more informed when dealing with the technician. I'll try to keep everyone posted once I get this problem resolved. Ed. Yeah, let us know. You could easily save yourself some big money. We have seen on those news shows what those so-called technicians do when you invite them into your home. PJ |
#8
|
|||
|
|||
Furnace not turning on
"PJx" wrote in message ... On Mon, 08 Mar 2004 07:40:06 GMT, "Ed" wrote: "indago" wrote in message ... 040307 1638 - Ed posted: Hi all, I'm a newbie at troubleshooting furnace problems, so please bear with me........ I've got a home gas furnace that's failing to consistently turn on when it is supposed to. Here's what I've done so far: 1) Checked circuit breaker for Furnace - OK 2) Reset the furnace by following the instructions inside the furnace to turn it off & on - Done 3) Checked thermostat - OK. Removed thermostat and manually jumped the two wires to make sure that furnace is turned on. Nothing happens to the furnace. 4) If I hit the exhaust(??) blower - not the main blower that blows warm air through the house, but the one by the flue pipe - the blower will start to spin and in turn lights up the igniter. I'm not sure how this blower has anything to do with the electronic ignition system, but this blower unit must work before the igniter lights up. I should also note that this blower unit has been squealing over the last while when it first starts up but I didn't think much of it. 5) Once I get the unit up and running by tapping the blower, it may continue to work fine for another half a day or so. 6) When it stops working, I have to repeat step 4 again. Seems like its going to fail for good soon. I hope this makes sense. Can anybody please tell me what the problem might be?? and what can I do to fix it? Thanks, Ed The furnace purge motor has to be operating before the main gas valve will operate. There is usually a paddle in the air flow of this purge system to let the system know that there is air flow and gases are being exhausted out so that a gas flame doesn't ignite leftover gases and explode. f It sounds like this purge motor is lacking lubrication in its bearings, or the fan blade is rubbing against something. If you want to work on this yourself, you can remove the purge fan motor and fan and spin the motor shaft and see if the bearings are OK. Check for sloppiness in the shaft rotation. Connect the motor to its appropriate voltage and see if it operates properly. If you need a new motor, you can contact your local furnace company and give them the model of the furnace, and the model of the motor and get a new one. Thanks to everyone for your informative replies. I'll have a closer look at this inducer/purge motor and see how difficult it'll be to replace. I do appreciate the safety risks involved in fixing a furnace, so if I don't feel confortable with the task at hand I will call a heating technician out to fix the problem. Even then, with the info you all have provided, it'll hopefully help me be more informed when dealing with the technician. I'll try to keep everyone posted once I get this problem resolved. Ed. Yeah, let us know. You could easily save yourself some big money. We have seen on those news shows what those so-called technicians do when you invite them into your home. PJ Yea..some of us actually fix the problem and dont even charge for the service calls...but you never hear about those do you? Sheesh. |
#9
|
|||
|
|||
Furnace not turning on
sounds like you found the problem, now just to get someone out to replace
the part. Sometimes it might be an air paddle, but I'm used to seeing a vacuum actuated switch. Same idea -- the furnace requires a positive air flow through the combustion chamber before the gas turns on. So that you don't pump carbon monoxide into your house. -- Christopher A. Young Learn more about Jesus www.lds.org www.mormons.com "Ed" wrote in message news:qrV2c.168128$Hy3.93966@edtnps89... The furnace purge motor has to be operating before the main gas valve will operate. There is usually a paddle in the air flow of this purge system to let the system know that there is air flow and gases are being exhausted out so that a gas flame doesn't ignite leftover gases and explode. It sounds like this purge motor is lacking lubrication in its bearings, or the fan blade is rubbing against something. If you want to work on this yourself, you can remove the purge fan motor and fan and spin the motor shaft and see if the bearings are OK. Check for sloppiness in the shaft rotation. Connect the motor to its appropriate voltage and see if it operates properly. If you need a new motor, you can contact your local furnace company and give them the model of the furnace, and the model of the motor and get a new one. Thanks to everyone for your informative replies. I'll have a closer look at this inducer/purge motor and see how difficult it'll be to replace. I do appreciate the safety risks involved in fixing a furnace, so if I don't feel confortable with the task at hand I will call a heating technician out to fix the problem. Even then, with the info you all have provided, it'll hopefully help me be more informed when dealing with the technician. I'll try to keep everyone posted once I get this problem resolved. Ed. |