Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Tom
 
Posts: n/a
Default Home Heating System

I have a forced hot air heating system. Even when the thermostat is
set to Off, power to the heating element in the heater stays on,
although the blower stays off. I can hear the heater clicking on and
off - I assume there is some sort of emergency shut off so it doesn't
get too hot if the blower is not on to remove the heat. The only way
to shut the system is at the circuit breaker. Does anyone know
whether the problem would be with the heater or the thermostat? I am
thinking it is a faulty thermostat since it wouldn't make sense that
the heater is receiving power with the thermostat in the Off position
unless the thermostat were faulty.
  #2   Report Post  
m Ransley
 
Posts: n/a
Default Home Heating System

You should call a pro before serious damage happens, no one can see your
unit to give you the correct advise.

  #3   Report Post  
GeoMan
 
Posts: n/a
Default Home Heating System


"Tom" wrote in message
om...
I have a forced hot air heating system. Even when the thermostat is
set to Off, power to the heating element in the heater stays on,
although the blower stays off. I can hear the heater clicking on and
off - I assume there is some sort of emergency shut off so it doesn't
get too hot if the blower is not on to remove the heat. The only way
to shut the system is at the circuit breaker. Does anyone know
whether the problem would be with the heater or the thermostat? I am
thinking it is a faulty thermostat since it wouldn't make sense that
the heater is receiving power with the thermostat in the Off position
unless the thermostat were faulty.


Being in the trade for over 20 years I know what you should do, you should call a heating
contractor in right away! I'm VERY serious on this issue. Most fires as a result of a
furnace failure does NOT occur right away, it sometimes takes hours, days or even weeks. I
have seen your particular situation that over time caused the insulation to come loose and
then catch on fire etc. It didn't happen right away. The homeowner said he was having
problems for the last week or so before his home burned. Not a total loss but substantial.

Seriously, you have a very bad situation there and you could die from it. Its worth the
over time charge for a weekend call to have it serviced.

Rich

  #4   Report Post  
Lawrence James
 
Posts: n/a
Default Home Heating System

The problem is most likely in the system, not the thermostat. You don't
say, is this a heat pump with aux electrical heat? The thermostat simply
calls for heat, the control board in the unit turns on the element and the
fan. There is a safety sensor that will turn off the element if it gets too
hot. You also did not say if the unit does work correctly when the
thermostat calls for heat? There is usually a relay that actually powers
the heating strip. It sounds like the relay is either stuck closed or the
control board in the unit is keeping it closed. This can be determined with
a VOM but you do need to be familiar with electrical systems. If not I
suggest you keep the breaker off and calla service tech.


"Tom" wrote in message
om...
I have a forced hot air heating system. Even when the thermostat is
set to Off, power to the heating element in the heater stays on,
although the blower stays off. I can hear the heater clicking on and
off - I assume there is some sort of emergency shut off so it doesn't
get too hot if the blower is not on to remove the heat. The only way
to shut the system is at the circuit breaker. Does anyone know
whether the problem would be with the heater or the thermostat? I am
thinking it is a faulty thermostat since it wouldn't make sense that
the heater is receiving power with the thermostat in the Off position
unless the thermostat were faulty.



  #5   Report Post  
CBhvac
 
Posts: n/a
Default Home Heating System


"Tom" wrote in message
om...
I have a forced hot air heating system. Even when the thermostat is
set to Off, power to the heating element in the heater stays on,
although the blower stays off. I can hear the heater clicking on and
off - I assume there is some sort of emergency shut off so it doesn't
get too hot if the blower is not on to remove the heat. The only way
to shut the system is at the circuit breaker. Does anyone know
whether the problem would be with the heater or the thermostat? I am
thinking it is a faulty thermostat since it wouldn't make sense that
the heater is receiving power with the thermostat in the Off position
unless the thermostat were faulty.



Is this a full electric or a heat pump with electric backup?
If its a heat pump, is it a Goodman or Janitrol by chance?


Either way, ten to one....its NOT the thermostat. Chances are you will reply
its a Goodman unit and that its a heat pump. If so, its a bad fan relay,
that also controls the electric strips and its bad. I keep several on the
vans...not van..but VANS....as in about 6 per. It is a VERY common issue,
and if not careful, sometihng that Goodman will get sued over.

What you need to do, in all seriousness, and no matter what make of unit you
have, is call a pro that knows what to look for, where to look and how to
repair it quickly...if not, you may find that your homeowers insurance isnt
as good as you had hoped....





  #7   Report Post  
CBhvac
 
Posts: n/a
Default Home Heating System


"alt-hvac Moderated" wrote in message
...
Well, this seems to be one of those cases where replacing the thermostat
won't help.

I'm guessing you have electric heat, you don't mention gas. Yes, it's time
to call a repair guy, sticking contctor sounds right.


Contactor?? Bud..you need to work on electric units more.


--

Christopher A. Young
Join Alt-Hvac Moderated if you like hacks
A free, easy to use Yahoo! group where Chris is trying to learn

something



"Tom" wrote in message
om...
I have a forced hot air heating system. Even when the thermostat is
set to Off, power to the heating element in the heater stays on,
although the blower stays off. I can hear the heater clicking on and
off - I assume there is some sort of emergency shut off so it doesn't
get too hot if the blower is not on to remove the heat. The only way
to shut the system is at the circuit breaker. Does anyone know
whether the problem would be with the heater or the thermostat? I am
thinking it is a faulty thermostat since it wouldn't make sense that
the heater is receiving power with the thermostat in the Off position
unless the thermostat were faulty.




  #8   Report Post  
Tom
 
Posts: n/a
Default Home Heating System

The unit is a Tappan electric heat and AC system (not a heat pump).
Thanks for all the good info.
  #9   Report Post  
CBhvac
 
Posts: n/a
Default Home Heating System


"Tom" wrote in message
m...
The unit is a Tappan electric heat and AC system (not a heat pump).
Thanks for all the good info.



Tappan, and Amana are practically Goodmans.....about as much trouble.
Looking at the Tappan diagrams for the last few years, a few of them have
the same exact sequencer as the Goodmans...definitly get it checked ASAP.


  #10   Report Post  
kjpro
 
Posts: n/a
Default Home Heating System

"CBhvac" stephenaddressscfrewedonpurpose@carolinabreezehva c.com wrote in
message news:qb9Fb.201
"alt-hvac Moderated" wrote in message
...
Well, this seems to be one of those cases where replacing the thermostat
won't help.

I'm guessing you have electric heat, you don't mention gas. Yes, it's

time
to call a repair guy, sticking contctor sounds right.


Contactor?? Bud..you need to work on electric units more.



DON'T encourage Chris to work on ANY thing that has to do with Electrical,
Heating, Cooling...

That's just asking for trouble.


Christopher A. Young
Join Alt-Hvac Moderated if you like hacks
A free, easy to use Yahoo! group where Chris is trying to learn

something


--
kjpro
_-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-_

( kjpro @ starband . net ) remove spaces to e-mail

Want it done yesterday? Or done right today, to save money tomorrow!!

_________________________ __







  #11   Report Post  
AJScott
 
Posts: n/a
Default Home Heating System

I take exception to this post. Chris in fact built a 3-story treehouse
complete with air conditioning, elecrical, and naural gas heat up my
bum this past summer, and matter of fact, Better Homes and Gradens is
interested in doing a major story on it. I look pretty funny walking
around town with kids riding around on a rope ladder hanging out my butt
and the mailman wondering exactly where to deliver the utlity bills, but
I figure that's the price one pays for success.

AJS


In article ,
"kjpro" ( kjpro @ starband . com ) see-my-sig-for-e-mail wrote:

DON'T encourage Chris to work on ANY thing that has to do with Electrical,
Heating, Cooling...

That's just asking for trouble.

  #12   Report Post  
CBhvac
 
Posts: n/a
Default Home Heating System


"AJScott" wrote in message
...
I take exception to this post. Chris in fact built a 3-story treehouse
complete with air conditioning, elecrical, and naural gas heat up my
bum this past summer, and matter of fact, Better Homes and Gradens is
interested in doing a major story on it. I look pretty funny walking
around town with kids riding around on a rope ladder hanging out my butt
and the mailman wondering exactly where to deliver the utlity bills, but
I figure that's the price one pays for success.

AJS


Now that is plain funny..



In article ,
"kjpro" ( kjpro @ starband . com ) see-my-sig-for-e-mail wrote:

DON'T encourage Chris to work on ANY thing that has to do with

Electrical,
Heating, Cooling...

That's just asking for trouble.



  #13   Report Post  
Stormin Mormonn
 
Posts: n/a
Default Home Heating System

And it cost me an extra $2,815.34 to have the hazmat crew haul away the moon
suit I wore while working in, uh, well, "in there". Have you considered a
diet change?

--

Christopher A. Young
Jesus: The Reason for the Season
www.lds.org
www.mormons.com


"AJScott" wrote in message
...
I take exception to this post. Chris in fact built a 3-story treehouse
complete with air conditioning, elecrical, and naural gas heat up my
bum this past summer, and matter of fact, Better Homes and Gradens is
interested in doing a major story on it. I look pretty funny walking
around town with kids riding around on a rope ladder hanging out my butt
and the mailman wondering exactly where to deliver the utlity bills, but
I figure that's the price one pays for success.

AJS


In article ,
"kjpro" ( kjpro @ starband . com ) see-my-sig-for-e-mail wrote:

DON'T encourage Chris to work on ANY thing that has to do with Electrical,
Heating, Cooling...

That's just asking for trouble.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Depot Scorns Christian Groups Ben Siders Woodworking 63 August 26th 04 02:52 PM
Central heating problem after draining/filling system. JJC001 UK diy 7 July 7th 04 05:08 PM
Alpha CB24X Heating System Inhibitor (advice needed) Richard G UK diy 0 October 30th 03 04:01 PM
Flushing a closed central heating system aris UK diy 1 October 17th 03 09:19 PM
Suggestions please Central Heating system crazy_mad_bandit UK diy 2 July 25th 03 02:36 PM


All times are GMT +1. The time now is 11:45 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"