Default Bryant Plus 90t Furnace "fan not turning OFF"

Hi i found a similar problem i have in this group and i like to get great
advises from here..

I have Bryant Plus 90t Gas Furnace, Model # 352AAV036080, Series A,
Manufacture Date 2007,

My quistion is "HOW TO FIX BLOWER FAN NOT TURNING OFF"

HERE ARE THE DETAILS:
my thermostat set to 20'C, the FAN was set to "AUTO", and HEAT "ON".
we where out to grocery store and when we came back we feel so hot inside
the house. i check the thermostat it was set to 20'C and the temperature
inside was 25'C and the furnace keep running...

I set the thermostat to heat OFF and the furnace stop. but i notice the
fan still running all the time..
I try to set fan ON or AUTO its running all the time.

So I call the Gas Emergency Service in the city and they check... . The
service guy said my furnace has no problem..and he said thermostat has a
problem.... he told me to call a sevice contactor to replace the
thermostat.. and he walked away because its just a free service of the
city..
So I didn't call a service contactor. i did go to home depot and buy a new
thermostat, i open it, follow the instruction inside and replace it by my
self..
turn on the power back with a new thermostat and its working. the furnace
stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it only stop
if i switch OFF the power at the furnace. should be auto off when it
reach the set temperature.. ANY HELPFULL ADVISE will be apreciated

THANK YOU IN ADVANCE

Benny.




--


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default Bryant Plus 90t Furnace "fan not turning OFF"

On Fri, 13 Feb 2015 04:44:02 +0000, benny
wrote:

Hi i found a similar problem i have in this group and i like to get great
advises from here..

I have Bryant Plus 90t Gas Furnace, Model # 352AAV036080, Series A,
Manufacture Date 2007,

My quistion is "HOW TO FIX BLOWER FAN NOT TURNING OFF"

HERE ARE THE DETAILS:
my thermostat set to 20'C, the FAN was set to "AUTO", and HEAT "ON".
we where out to grocery store and when we came back we feel so hot inside
the house. i check the thermostat it was set to 20'C and the temperature
inside was 25'C and the furnace keep running...

I set the thermostat to heat OFF and the furnace stop. but i notice the
fan still running all the time..
I try to set fan ON or AUTO its running all the time.

So I call the Gas Emergency Service in the city and they check... . The
service guy said my furnace has no problem..and he said thermostat has a
problem.... he told me to call a sevice contactor to replace the
thermostat.. and he walked away because its just a free service of the
city..
So I didn't call a service contactor. i did go to home depot and buy a new
thermostat, i open it, follow the instruction inside and replace it by my
self..
turn on the power back with a new thermostat and its working. the furnace
stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it only stop
if i switch OFF the power at the furnace. should be auto off when it
reach the set temperature.. ANY HELPFULL ADVISE will be apreciated

THANK YOU IN ADVANCE

Benny.

Is the furnace controller set to run the fan full time? I have mine
set to run on low constantly untill it calls for either heat or cool -
when the fan runs faster.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 625
Default Bryant Plus 90t Furnace "fan not turning OFF"

wrote:
On Fri, 13 Feb 2015 04:44:02 +0000, benny
wrote:

Hi i found a similar problem i have in this group and i like to get great
advises from here..

I have Bryant Plus 90t Gas Furnace, Model # 352AAV036080, Series A,
Manufacture Date 2007,

My quistion is "HOW TO FIX BLOWER FAN NOT TURNING OFF"

HERE ARE THE DETAILS:
my thermostat set to 20'C, the FAN was set to "AUTO", and HEAT "ON".
we where out to grocery store and when we came back we feel so hot inside
the house. i check the thermostat it was set to 20'C and the temperature
inside was 25'C and the furnace keep running...

I set the thermostat to heat OFF and the furnace stop. but i notice the
fan still running all the time..
I try to set fan ON or AUTO its running all the time.

So I call the Gas Emergency Service in the city and they check... . The
service guy said my furnace has no problem..and he said thermostat has a
problem.... he told me to call a sevice contactor to replace the
thermostat.. and he walked away because its just a free service of the
city..
So I didn't call a service contactor. i did go to home depot and buy a new
thermostat, i open it, follow the instruction inside and replace it by my
self..
turn on the power back with a new thermostat and its working. the furnace
stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it only stop
if i switch OFF the power at the furnace. should be auto off when it
reach the set temperature.. ANY HELPFULL ADVISE will be apreciated

THANK YOU IN ADVANCE

Benny.

Is the furnace controller set to run the fan full time? I have mine
set to run on low constantly untill it calls for either heat or cool -
when the fan runs faster.


If the furnace controller is NOT set to always provide fan, the culprit
could be the thermostat wiring. Remove the wire connected to the G terminal
at the furnace, typically a green wire. If the fan stops, the wiring is
causing the fan to run.

I am assuming the two thermostats are not both defective !
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Bryant Plus 90t Furnace "fan not turning OFF"

benny wrote:
Hi i found a similar problem i have in this group and i like to get great
advises from here..

I have Bryant Plus 90t Gas Furnace, Model # 352AAV036080, Series A,
Manufacture Date 2007,

My quistion is "HOW TO FIX BLOWER FAN NOT TURNING OFF"

HERE ARE THE DETAILS:
my thermostat set to 20'C, the FAN was set to "AUTO", and HEAT "ON".
we where out to grocery store and when we came back we feel so hot inside
the house. i check the thermostat it was set to 20'C and the temperature
inside was 25'C and the furnace keep running...

I set the thermostat to heat OFF and the furnace stop. but i notice the
fan still running all the time..
I try to set fan ON or AUTO its running all the time.

So I call the Gas Emergency Service in the city and they check... . The
service guy said my furnace has no problem..and he said thermostat has a
problem.... he told me to call a sevice contactor to replace the
thermostat.. and he walked away because its just a free service of the
city..
So I didn't call a service contactor. i did go to home depot and buy a new
thermostat, i open it, follow the instruction inside and replace it by my
self..
turn on the power back with a new thermostat and its working. the furnace
stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it only stop
if i switch OFF the power at the furnace. should be auto off when it
reach the set temperature.. ANY HELPFULL ADVISE will be apreciated

THANK YOU IN ADVANCE

Benny.




Hi,
When runs how long did you wait. An hour or longer and still running?
If furnace has cooled down and fan is still going, hi limit switch stuck
closed, fan relay on the control board stuck closed, etc. could be the
cause.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 253
Default Bryant Plus 90t Furnace "fan not turning OFF"

On 12 Feb 2015, benny
wrote in
alt.home.repair:

So I didn't call a service contactor. i did go to home depot and
buy a new thermostat, i open it, follow the instruction inside
and replace it by my self..
turn on the power back with a new thermostat and its working. the
furnace stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it
only stop if i switch OFF the power at the furnace. should be
auto off when it reach the set temperature.. ANY HELPFULL
ADVISE will be apreciated


I went through a similar exercise a few weeks ago. The furnace would
heat and cool normally, but the blower ran constantly. I determined
that the problem was not the thermostat but was unable to troubleshoot
it any further, so I called a repairman. It turned out that the main
computer board in the furnace had gone bad and had to be replaced. Many
furnaces like mine are so computerized that there aren't very many
small replaceable parts inside - much of the system is integrated into
that board.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Bryant Plus 90t Furnace "fan not turning OFF"

On Friday, February 13, 2015 at 1:49:36 AM UTC-5, Nil wrote:
On 12 Feb 2015, benny
wrote in
alt.home.repair:

So I didn't call a service contactor. i did go to home depot and
buy a new thermostat, i open it, follow the instruction inside
and replace it by my self..
turn on the power back with a new thermostat and its working. the
furnace stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it
only stop if i switch OFF the power at the furnace. should be
auto off when it reach the set temperature.. ANY HELPFULL
ADVISE will be apreciated


I went through a similar exercise a few weeks ago. The furnace would
heat and cool normally, but the blower ran constantly. I determined
that the problem was not the thermostat but was unable to troubleshoot
it any further, so I called a repairman. It turned out that the main
computer board in the furnace had gone bad and had to be replaced. Many
furnaces like mine are so computerized that there aren't very many
small replaceable parts inside - much of the system is integrated into
that board.


It certainly could be a defective controller board in the furnace.
Possible it's the wiring between furnace and thermostat too where a
short has occured. Or it could be that the new thermostat is wired
incorrectly, check the fan wire, which is usually green. Also a
simple test would be to locate the other end of the fan wire at the
furnace and disconnect it. If the fan still runs, it's the controller.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Bryant Plus 90t Furnace "fan not turning OFF"

Nil wrote:
On 12 Feb 2015, benny
wrote in
alt.home.repair:

So I didn't call a service contactor. i did go to home depot and
buy a new thermostat, i open it, follow the instruction inside
and replace it by my self..
turn on the power back with a new thermostat and its working. the
furnace stop when it reach the set temperature...
but i notice again the blower fan still running all the time.it
only stop if i switch OFF the power at the furnace. should be
auto off when it reach the set temperature.. ANY HELPFULL
ADVISE will be apreciated


I went through a similar exercise a few weeks ago. The furnace would
heat and cool normally, but the blower ran constantly. I determined
that the problem was not the thermostat but was unable to troubleshoot
it any further, so I called a repairman. It turned out that the main
computer board in the furnace had gone bad and had to be replaced. Many
furnaces like mine are so computerized that there aren't very many
small replaceable parts inside - much of the system is integrated into
that board.

Hmm,
If relay is stuck, it can be replaced with some soldering skill. If
logic controlling the relay is bad little harder to deal with it,
but still repairable. When run into ASIC, it is almost impossible to
get a replacement chip. They charge few hundred $$ for a replacement
board. It is not really a computer but contains micro processor chip.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,029
Default Bryant Plus 90t Furnace "fan not turning OFF"

It is possible that the contactor that senses the air flow temperature in the furnace is stuck closed, resulting in the blower running continuuously instead of shutting off when the air flow temperature is below some set temperature. My funace sensor started sticking, I could get the contacts to open by banging on the furnace plenum near where the sensor was located. Got to be a nuisance, so went to myh local parts store with the old sensor and got a new one. Less than 25 bucks.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Bryant Plus 90t Furnace "fan not turning OFF"

replying to benny, benny wrote:


Thank you guys to your ideas you have put in here...after reading of all
those comments i might have to call a repairman to fix it. i convince my
self that it might be the control board problem...
thank verry much.


benny

--


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,730
Default Bryant Plus 90t Furnace "fan not turning OFF"

On 2/13/2015 11:44 PM, benny wrote:
replying to benny, benny wrote:


Thank you guys to your ideas you have put in here...after reading of all
those comments i might have to call a repairman to fix it. i convince my
self that it might be the control board problem...
thank verry much.


benny

About a decade ago, I got a call from a friend from church, who had a
furnace failure. He was at work, and his wife was home with the kids. I
went and asked what had happened. Well, for some reason the circuit
breaker tripped. This was summer, and they were using the AC. Nice warm
day, too. As the breaker had tripped, no cooling, and they wanted to be
cool and comfortale.

I chatted with the wife. She said that the circuit breaker was off, so
she turned it on. It tripped right off again. So, she reset it (dozen or
more times) and finally the circuit breaker stayed on.

I started to check things, and found out that the fan blower mtoor had
developed a short. Each time she reset the breaker, the furance tried to
power the fan which was dead short. So, the breaker tripped again.
Finally, the contacts on the fan relay on the circuit board vaporized,
and the breaker stayed on.

Was a decade or so ago. I remember the fan motor was about $60 and the
circuit board was about $200, had to get it throught he carier Bryant
place, and they didn't go cheaply.

to the OP, might want to research, might find board for sale online
cheaper than having a tech out.


-
..
Christopher A. Young
learn more about Jesus
.. www.lds.org
..
..


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Bryant Plus 90t Furnace "fan not turning OFF"

Stormin Mormon wrote:
On 2/13/2015 11:44 PM, benny wrote:
replying to benny, benny wrote:


Thank you guys to your ideas you have put in here...after reading of all
those comments i might have to call a repairman to fix it. i convince my
self that it might be the control board problem...
thank verry much.


benny

About a decade ago, I got a call from a friend from church, who had a
furnace failure. He was at work, and his wife was home with the kids. I
went and asked what had happened. Well, for some reason the circuit
breaker tripped. This was summer, and they were using the AC. Nice warm
day, too. As the breaker had tripped, no cooling, and they wanted to be
cool and comfortale.

I chatted with the wife. She said that the circuit breaker was off, so
she turned it on. It tripped right off again. So, she reset it (dozen or
more times) and finally the circuit breaker stayed on.

I started to check things, and found out that the fan blower mtoor had
developed a short. Each time she reset the breaker, the furance tried to
power the fan which was dead short. So, the breaker tripped again.
Finally, the contacts on the fan relay on the circuit board vaporized,
and the breaker stayed on.

Was a decade or so ago. I remember the fan motor was about $60 and the
circuit board was about $200, had to get it throught he carier Bryant
place, and they didn't go cheaply.

to the OP, might want to research, might find board for sale online
cheaper than having a tech out.


-
.
Christopher A. Young
learn more about Jesus
. www.lds.org
.
.

Hi,
If OP is handy kind, board often shows up on eBay for more reasonable price.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
I am looking for a local source for "Rockwool" / "Mineral Wool" /"Safe & Sound" / "AFB" jtpr Home Repair 3 June 10th 10 06:27 AM
For women who desire the traditional 12-marker dials, the "Faceto,""Juro" and "Rilati" all add a little more functionality, without sacrificingthe diamonds. [email protected] Woodworking 0 April 19th 08 11:12 AM
"ruts" and "nubbins" in concave turning rjdankert Woodturning 5 April 18th 08 03:51 PM
Bryant Central Air Unit does not turn on without a little "tap" [email protected] Home Repair 0 May 11th 07 01:45 AM
Where does "turning" end and "machining" begin? charlieb Woodturning 7 April 13th 07 08:28 PM


All times are GMT +1. The time now is 05:53 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"