Default Grounding An Electrical Service Panel

I understand that a residential service panel requires 2 sources for
grounding. I was looking at a newly installed panel the other day and I'm
not sure that it was installed correctly.

This panel has a neutral bar on both sides of the panel and ground bar on
the right hand side only.

At the electric meter on the side of the house, there are 2 bare copper
wires running down the wall into the earth. These wires were existing prior
to the installation of the new panel. They look like this:

http://www.altfab.com/library/large/...TR-GRND-02.jpg

When the new panel was installed, a new ground wire was run from within 5'
of the water meter to the neutral bar of the panel. The neutral bar is
bonded to the panel with a large green screw next to the incoming service
neutral lug. I believe that this part is OK.

However, this is the part that I'm not too sure about:

Above the panel, there a ground wire clamped to a water pipe. This wire was
there before the new panel was installed. The wire was pulled into the new
panel attached to the ground bar.

Does that wire count as a second grounding point for the panel or is it
essentially the same point as the new ground that was run from the water
meter to the panel?

Shouldn't I be seeing something that directly connects the ground wires at
the electric meter to the panel?
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Grounding An Electrical Service Panel

On 3/24/2014 9:56 AM, DerbyDad03 wrote:
I understand that a residential service panel requires 2 sources for
grounding.


Not necessarily. Old services used to only be connected to a metal water
service pipe. (Now you need a "supplemental" electrode for new services.)

A house might be built now with plastic water service pipe and a
"concrete encased electrode" (Ufer ground) used as the only grounding
electrode.

I was looking at a newly installed panel the other day and I'm
not sure that it was installed correctly.

This panel has a neutral bar on both sides of the panel and ground bar on
the right hand side only.

At the electric meter on the side of the house, there are 2 bare copper
wires running down the wall into the earth. These wires were existing prior
to the installation of the new panel. They look like this:

http://www.altfab.com/library/large/...TR-GRND-02.jpg


You can connect grounding electrodes anywhere from the connection to an
overhead service drop (or at the connection to a service lateral) up to
the neutral bus at the service disconnect. But that is irrelevant here
- see below.


When the new panel was installed, a new ground wire was run from within 5'
of the water meter to the neutral bar of the panel.


That is how connections to a water pipe service is made now. The
"supplemental" electrode is presumably 2 ground rods connected at the meter.

I presume the water meter is bonded and that is irrelevant to your
questions.

The neutral bar is
bonded to the panel with a large green screw next to the incoming service
neutral lug. I believe that this part is OK.

However, this is the part that I'm not too sure about:

Above the panel, there a ground wire clamped to a water pipe. This wire was
there before the new panel was installed. The wire was pulled into the new
panel attached to the ground bar.

Does that wire count as a second grounding point for the panel or is it
essentially the same point as the new ground that was run from the water
meter to the panel?


You used to be able to connect to a metal water pipe electrode anywhere
on the interior metal water pipe system. This was the grounding
electrode connection for the old service. It is not required now, but is
a little improvement. It is not a "supplemental" electrode.


Shouldn't I be seeing something that directly connects the ground wires at
the electric meter to the panel?


Generally you want to connect all the grounding electrodes together and
make the connection to the service neutral at one point.

But "supplemental" electrodes can be connected several places, including
the meter. Ground rods are a pretty crappy electrode.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 33
Default Grounding An Electrical Service Panel

On 3/24/2014 4:24 PM, wrote:
On Mon, 24 Mar 2014 15:56:16 +0000 (UTC), DerbyDad03
wrote:

I understand that a residential service panel requires 2 sources for
grounding. I was looking at a newly installed panel the other day and I'm
not sure that it was installed correctly.

This panel has a neutral bar on both sides of the panel and ground bar on
the right hand side only.

At the electric meter on the side of the house, there are 2 bare copper
wires running down the wall into the earth. These wires were existing prior
to the installation of the new panel. They look like this:

http://www.altfab.com/library/large/...TR-GRND-02.jpg

When the new panel was installed, a new ground wire was run from within 5'
of the water meter to the neutral bar of the panel. The neutral bar is
bonded to the panel with a large green screw next to the incoming service
neutral lug. I believe that this part is OK.

However, this is the part that I'm not too sure about:

Above the panel, there a ground wire clamped to a water pipe. This wire was
there before the new panel was installed. The wire was pulled into the new
panel attached to the ground bar.

Does that wire count as a second grounding point for the panel or is it
essentially the same point as the new ground that was run from the water
meter to the panel?

Shouldn't I be seeing something that directly connects the ground wires at
the electric meter to the panel?


You really only need 2 electrodes if one of them is the water pipe.


The problem is, as far as I can tell, both of them are the same water pipe.


As long as your grounding electrode conductor goes from the neutral
bar to the pipe, within 5 feet of where it comes through the wall and
there is nothing between that and the dirt (meter, filter or whatever"
that is your primary electrode. A water pipe has to be supplemented
with another electrode and it sounds like that is a rod or two
outside. (they usually get installed in pairs)


I think this is what I should see, but I'm not sure that I do:

http://www.justanswer.com/uploads/El...g_of_panel.JPG

What I don't see is a connection from the ground rod(s) to the panel.
Please see the images below.


I can't see it but it sounds right.



See he

The first image is of the meter and the ground wires going into the earth:

http://i440.photobucket.com/albums/q...psb64ede78.jpg

This second image is of the panel. It shows the old bare copper wire
that is attached to the water pipe right above the panel. That is the
wire that is attached to the grounding bus.

It also shows the new black, insulated ground wire that runs back all
the way across the basement to the water meter.

I don't understand how the ground wires at the meter/rods are connected
to the panel as shown in the web image above.

http://i440.photobucket.com/albums/q...ps7cef4247.jpg
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Grounding An Electrical Service Panel

On Monday, March 24, 2014 7:43:57 PM UTC-4, DerbyDad03 wrote:
On 3/24/2014 4:24 PM, wrote:

On Mon, 24 Mar 2014 15:56:16 +0000 (UTC), DerbyDad03


wrote:




I understand that a residential service panel requires 2 sources for


grounding. I was looking at a newly installed panel the other day and I'm


not sure that it was installed correctly.




This panel has a neutral bar on both sides of the panel and ground bar on


the right hand side only.




At the electric meter on the side of the house, there are 2 bare copper


wires running down the wall into the earth. These wires were existing prior


to the installation of the new panel. They look like this:




http://www.altfab.com/library/large/...TR-GRND-02.jpg



When the new panel was installed, a new ground wire was run from within 5'


of the water meter to the neutral bar of the panel. The neutral bar is


bonded to the panel with a large green screw next to the incoming service


neutral lug. I believe that this part is OK.




However, this is the part that I'm not too sure about:




Above the panel, there a ground wire clamped to a water pipe. This wire was


there before the new panel was installed. The wire was pulled into the new


panel attached to the ground bar.




Does that wire count as a second grounding point for the panel or is it


essentially the same point as the new ground that was run from the water


meter to the panel?




Shouldn't I be seeing something that directly connects the ground wires at


the electric meter to the panel?




You really only need 2 electrodes if one of them is the water pipe.




The problem is, as far as I can tell, both of them are the same water pipe.





As long as your grounding electrode conductor goes from the neutral


bar to the pipe, within 5 feet of where it comes through the wall and


there is nothing between that and the dirt (meter, filter or whatever"


that is your primary electrode. A water pipe has to be supplemented


with another electrode and it sounds like that is a rod or two


outside. (they usually get installed in pairs)




I think this is what I should see, but I'm not sure that I do:



http://www.justanswer.com/uploads/El...g_of_panel.JPG



What I don't see is a connection from the ground rod(s) to the panel.

Please see the images below.





I can't see it but it sounds right.








See he



The first image is of the meter and the ground wires going into the earth:



http://i440.photobucket.com/albums/q...psb64ede78.jpg



This second image is of the panel. It shows the old bare copper wire

that is attached to the water pipe right above the panel. That is the

wire that is attached to the grounding bus.



It also shows the new black, insulated ground wire that runs back all

the way across the basement to the water meter.



I don't understand how the ground wires at the meter/rods are connected

to the panel as shown in the web image above.



http://i440.photobucket.com/albums/q...ps7cef4247.jpg


In the pic of the panel you have three ground wires identified.
One goes to the water service pipe. One goes to the water pipe in
the house. Where does the third one go?
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Grounding An Electrical Service Panel

trader_4 wrote:
On Monday, March 24, 2014 7:43:57 PM UTC-4, DerbyDad03 wrote:
On 3/24/2014 4:24 PM, wrote:


....snip...

http://i440.photobucket.com/albums/q...ps7cef4247.jpg

In the pic of the panel you have three ground wires identified.
One goes to the water service pipe. One goes to the water pipe in
the house. Where does the third one go?


Actually, I only have 2 grounds identified, but I can see where the
confusion might come from.

If you read the 2 text boxes related to the "bare ground wire" the upper
one says that the ground wire that is attached to pipe above the panel
"runs behind the joist" and the middle text box says that the bare ground
wire "emerges from behind the joist".

That is the same ground wire.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Grounding An Electrical Service Panel

On Tuesday, March 25, 2014 11:07:28 AM UTC-4, DerbyDad03 wrote:
trader_4 wrote:

On Monday, March 24, 2014 7:43:57 PM UTC-4, DerbyDad03 wrote:


On 3/24/2014 4:24 PM, wrote:






...snip...



http://i440.photobucket.com/albums/q...ps7cef4247.jpg



In the pic of the panel you have three ground wires identified.


One goes to the water service pipe. One goes to the water pipe in


the house. Where does the third one go?




Actually, I only have 2 grounds identified, but I can see where the

confusion might come from.



If you read the 2 text boxes related to the "bare ground wire" the upper

one says that the ground wire that is attached to pipe above the panel

"runs behind the joist" and the middle text box says that the bare ground

wire "emerges from behind the joist".



That is the same ground wire.


So you have one grounding electrode, ie the water service pipe
that comes directly into the panel.
According to Bud, the supplemental electrode(s) can be at the meter
and it sounds like that's where they are. The only part I'm confused
about is that you appear to have just two hots and a neutral coming into
the panel from the meter. So the neutral which is a current carrying
conductor would be what ties the grounding system together, ie it
connects the water pipe ground at the panel to the supplemental grounds
across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems questionable to me. Bud?
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Grounding An Electrical Service Panel

trader_4 wrote:
On Tuesday, March 25, 2014 11:07:28 AM UTC-4, DerbyDad03 wrote:
trader_4 wrote:

On Monday, March 24, 2014 7:43:57 PM UTC-4, DerbyDad03 wrote:


On 3/24/2014 4:24 PM, wrote:






...snip...



http://i440.photobucket.com/albums/q...ps7cef4247.jpg

In the pic of the panel you have three ground wires identified.
One goes to the water service pipe. One goes to the water pipe in
the house. Where does the third one go?


Actually, I only have 2 grounds identified, but I can see where the
confusion might come from.

If you read the 2 text boxes related to the "bare ground wire" the upper
one says that the ground wire that is attached to pipe above the panel
"runs behind the joist" and the middle text box says that the bare ground
wire "emerges from behind the joist".

That is the same ground wire.


So you have one grounding electrode, ie the water service pipe
that comes directly into the panel.
According to Bud, the supplemental electrode(s) can be at the meter
and it sounds like that's where they are. The only part I'm confused
about is that you appear to have just two hots and a neutral coming into
the panel from the meter. So the neutral which is a current carrying
conductor would be what ties the grounding system together, ie it
connects the water pipe ground at the panel to the supplemental grounds
across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems
questionable to me. Bud?


That, my friend, is exactly what I find questionable too.

The homeowner has already called the owner of the company that installed
the panel and informed him that the circuit grounds and neutrals should not
be on the same lugs (my post from last weekend). The owner will be coming
out to fix it. He will order a new ground bus for the left side of the
panel and remove the grounds from the neutral bar.

The owner (electrician) told the homeowner that he can't believe that one
of his guys actually wired it that way. "He should know better!" Makes you
wonder what else this guy has wired that is still in use. If I hadn't of
been curious and and wanting to see how the new panel was wired, this one
would have gone unnoticed, probably until the homeowner tried to sell the
house and the buyer got it inspected.

Now I'm trying to find out if he has to fix the service ground connections
also. The homeowner doesn't want to call this guy back more than once.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Grounding An Electrical Service Panel

bud-- wrote:
On 3/25/2014 3:09 PM, wrote:
On Tue, 25 Mar 2014 12:35:59 -0700 (PDT), trader_4

So you have one grounding electrode, ie the water service pipe
that comes directly into the panel.
According to Bud, the supplemental electrode(s) can be at the meter
and it sounds like that's where they are. The only part I'm confused
about is that you appear to have just two hots and a neutral coming into
the panel from the meter. So the neutral which is a current carrying
conductor would be what ties the grounding system together, ie it
connects the water pipe ground at the panel to the supplemental grounds
across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems
questionable to me. Bud?


In this case the most useful ground is the water pipe, which is connected
at the panel. Other comments below.


You can attach the grounding electrode conductor any place between the
service point to the service disconnect enclosure. Connecting in the
meter base is pretty common around here.


In this system there are 2 points of attachment. I don't think that is OK
in general, but in this case it is OK to attach the "supplemental" ground
rods at a separate place (the meter, if that is what is attached there).

You can have all the grounding electrodes (GEC) attached at the meter (as
at g's location). And the N-G bond ("main bonding jumper") is at the
service disconnect. That is code compliant, but seems a bit odd to me.
Like ferinstance if you had a neutral connection failure on the neutral
from the meter to the disconnect it wouldn't be too healthy. Comment?

(I have never seen one done that way, but basements are very common here.)

Minneapolis still has a municipal metal water system. If the GEC
(including water pipe) is connected at the panel, and the service neutral
opens at any point, the neutral current will be to the water pipe, to
other houses, and back to the service neutral. The neutral voltage shouldn't float much.



Thanks for the responses.

I'm still confused how the situation we're discussing matches up with this
picture. Maybe it doesn't have to?

http://www.justanswer.com/uploads/El...g_of_panel.JPG

What I don't see is the connection from the ground rod to the panel. Does
the connection of the ground rod at the meter eliminate the need to connect
the panel to the ground rod?

If that's the case, then does that mean that the short ground wire to the
pipe just above the panel is redundant since a new ground wire was run from
the panel all the way back to the meter?

Seems to me that the section of pipe above the panel could easily become
not grounded if a section of pipe between it and the meter was replaced
with PEX, etc. I thought that was why you had to be bonded within 5' feet
of the meter now.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Grounding An Electrical Service Panel

On 3/25/2014 3:09 PM, wrote:
On Tue, 25 Mar 2014 12:35:59 -0700 (PDT), trader_4

So you have one grounding electrode, ie the water service pipe
that comes directly into the panel.
According to Bud, the supplemental electrode(s) can be at the meter
and it sounds like that's where they are. The only part I'm confused
about is that you appear to have just two hots and a neutral coming into
the panel from the meter. So the neutral which is a current carrying
conductor would be what ties the grounding system together, ie it
connects the water pipe ground at the panel to the supplemental grounds
across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems questionable to me. Bud?


In this case the most useful ground is the water pipe, which is
connected at the panel. Other comments below.


You can attach the grounding electrode conductor any place between the
service point to the service disconnect enclosure. Connecting in the
meter base is pretty common around here.


In this system there are 2 points of attachment. I don't think that is
OK in general, but in this case it is OK to attach the "supplemental"
ground rods at a separate place (the meter, if that is what is attached
there).

You can have all the grounding electrodes (GEC) attached at the meter
(as at g's location). And the N-G bond ("main bonding jumper") is at the
service disconnect. That is code compliant, but seems a bit odd to me.
Like ferinstance if you had a neutral connection failure on the neutral
from the meter to the disconnect it wouldn't be too healthy. Comment?

(I have never seen one done that way, but basements are very common here.)

Minneapolis still has a municipal metal water system. If the GEC
(including water pipe) is connected at the panel, and the service
neutral opens at any point, the neutral current will be to the water
pipe, to other houses, and back to the service neutral. The neutral
voltage shouldn't float much.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Grounding An Electrical Service Panel

On 3/25/2014 4:27 PM, DerbyDad03 wrote:
bud-- wrote:
On 3/25/2014 3:09 PM, wrote:
On Tue, 25 Mar 2014 12:35:59 -0700 (PDT), trader_4

So you have one grounding electrode, ie the water service pipe
that comes directly into the panel.
According to Bud, the supplemental electrode(s) can be at the meter
and it sounds like that's where they are. The only part I'm confused
about is that you appear to have just two hots and a neutral coming into
the panel from the meter. So the neutral which is a current carrying
conductor would be what ties the grounding system together, ie it
connects the water pipe ground at the panel to the supplemental grounds
across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems
questionable to me. Bud?


In this case the most useful ground is the water pipe, which is connected
at the panel. Other comments below.


You can attach the grounding electrode conductor any place between the
service point to the service disconnect enclosure. Connecting in the
meter base is pretty common around here.


In this system there are 2 points of attachment. I don't think that is OK
in general, but in this case it is OK to attach the "supplemental" ground
rods at a separate place (the meter, if that is what is attached there).

You can have all the grounding electrodes (GEC) attached at the meter (as
at g's location). And the N-G bond ("main bonding jumper") is at the
service disconnect. That is code compliant, but seems a bit odd to me.
Like ferinstance if you had a neutral connection failure on the neutral
from the meter to the disconnect it wouldn't be too healthy. Comment?

(I have never seen one done that way, but basements are very common here.)

Minneapolis still has a municipal metal water system. If the GEC
(including water pipe) is connected at the panel, and the service neutral
opens at any point, the neutral current will be to the water pipe, to
other houses, and back to the service neutral. The neutral voltage shouldn't float much.



Thanks for the responses.

I'm still confused how the situation we're discussing matches up with this
picture. Maybe it doesn't have to?

http://www.justanswer.com/uploads/El...g_of_panel.JPG


The NEC can be much more complicated than the picture. For instance in
new construction a Ufer ground is usually installed, which replaces the
ground rods (which are a POS).


What I don't see is the connection from the ground rod to the panel. Does
the connection of the ground rod at the meter eliminate the need to connect
the panel to the ground rod?


Yes


If that's the case, then does that mean that the short ground wire to the
pipe just above the panel is redundant since a new ground wire was run from
the panel all the way back to the meter?


Yes [to the water meter]


Seems to me that the section of pipe above the panel could easily become
not grounded if a section of pipe between it and the meter was replaced
with PEX, etc. I thought that was why you had to be bonded within 5' feet
of the meter now.


It is. The connection to the water pipe near the panel is likely the
connection that was made before the service was upgraded, and was just
easily connected to the new panel. Connection at that point used to be
kosher. Them pex guys are ruining the world.





  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Grounding An Electrical Service Panel

bud-- wrote:
On 3/25/2014 4:27 PM, DerbyDad03 wrote:
bud-- wrote:
On 3/25/2014 3:09 PM, wrote:
On Tue, 25 Mar 2014 12:35:59 -0700 (PDT), trader_4

So you have one grounding electrode, ie the water service pipe
that comes directly into the panel.
According to Bud, the supplemental electrode(s) can be at the meter
and it sounds like that's where they are. The only part I'm confused
about is that you appear to have just two hots and a neutral coming into
the panel from the meter. So the neutral which is a current carrying
conductor would be what ties the grounding system together, ie it
connects the water pipe ground at the panel to the supplemental grounds
across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems
questionable to me. Bud?

In this case the most useful ground is the water pipe, which is connected
at the panel. Other comments below.


You can attach the grounding electrode conductor any place between the
service point to the service disconnect enclosure. Connecting in the
meter base is pretty common around here.


In this system there are 2 points of attachment. I don't think that is OK
in general, but in this case it is OK to attach the "supplemental" ground
rods at a separate place (the meter, if that is what is attached there).

You can have all the grounding electrodes (GEC) attached at the meter (as
at g's location). And the N-G bond ("main bonding jumper") is at the
service disconnect. That is code compliant, but seems a bit odd to me.
Like ferinstance if you had a neutral connection failure on the neutral
from the meter to the disconnect it wouldn't be too healthy. Comment?

(I have never seen one done that way, but basements are very common here.)

Minneapolis still has a municipal metal water system. If the GEC
(including water pipe) is connected at the panel, and the service neutral
opens at any point, the neutral current will be to the water pipe, to
other houses, and back to the service neutral. The neutral voltage shouldn't float much.



Thanks for the responses.

I'm still confused how the situation we're discussing matches up with this
picture. Maybe it doesn't have to?


http://www.justanswer.com/uploads/El...g_of_panel.JPG


The NEC can be much more complicated than the picture. For instance in
new construction a Ufer ground is usually installed, which replaces the
ground rods (which are a POS).


What I don't see is the connection from the ground rod to the panel. Does
the connection of the ground rod at the meter eliminate the need to connect
the panel to the ground rod?


Yes


If that's the case, then does that mean that the short ground wire to the
pipe just above the panel is redundant since a new ground wire was run from
the panel all the way back to the meter?


Yes [to the water meter]


Seems to me that the section of pipe above the panel could easily become
not grounded if a section of pipe between it and the meter was replaced
with PEX, etc. I thought that was why you had to be bonded within 5' feet
of the meter now.


It is. The connection to the water pipe near the panel is likely the
connection that was made before the service was upgraded, and was just
easily connected to the new panel. Connection at that point used to be
kosher. Them pex guys are ruining the world.



Thanks, Bud!

I will tell my neighbor that he doesn't have to worry about the service
grounding situation. The owner of the company whose worker paired up the
circuit grounds and neutrals under the same lugs is coming out next week to
fix that situation.

If I have the time, I want to be there when he does the work and have my
neighbor ask him about the service ground. I just want to hear what he has
to say.

Thanks again.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 Electrical Questions: Loops in Service Panel, Slack at Boxes [email protected] Home Repair 5 February 9th 08 09:20 PM
branch panel grounding question bill allemann Home Repair 11 March 23rd 07 10:26 PM
Electrical service panel door mismatch...how to fix? [email protected] Home Repair 30 March 5th 07 11:11 PM
ELECTRICAL SERVICE PANEL HUNG TODAY [email protected] Home Repair 17 November 20th 06 10:25 PM
question on electrical service panel upgrade Chris Friesen Home Repair 5 November 17th 06 03:21 AM


All times are GMT +1. The time now is 08:36 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"