I am replacing a fan-only unit with a fan-heater unit in my bathroom.

The switch for the existing fan is in a 1-gang box on a 15A, 14g circuit.
Next to the fan switch, in a separate 1-gang box is a dimmer for the
bathroom light which is on a *different* 15A, 14g circuit. The new
fan-heater requires a 20A circuit so I have pulled 12g Romex up into the
attic. The existing 15A circuit for the existing fan will be removed.

My plan is to use a 3-gang switch box for the dimmer, humidity sensing
switch for the fan and countdown timer for the heater. I want the dimmer to
remain on the existing 15A, 14g circuit. Moving it to the 20A circuit would
require rewiring of the walls sconces with 12g and a bunch of other work.

I know that I am allowed to have 2 different circuits in the same switch
box and i know that I should derate the dimmer, which is not a problem -
it's a 600 watt dimmer for two 60 watt bulbs.

However, I'm not sure if I am getting into a situation where I should be
derating the conductors to the dimmer, which would mean rewiring that whole
circuit. When I do I need to be concerned with derating the conductors that
are in a 3-gang switch box?

If it matters, the 3-gang box is 3.5 inches deep, the deepest I could find.
It will contain the switched hot wire for the 15A light circuit, the source
wire for the 20A circuit, a switch leg for the fan and a switch leg for the
heater.

Thanks.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,228
Default Derating Switches And Conductors In A 3-Gang Switch Box


"DerbyDad03" wrote in message
...
However, I'm not sure if I am getting into a situation where I should be
derating the conductors to the dimmer, which would mean rewiring that
whole
circuit. When I do I need to be concerned with derating the conductors
that
are in a 3-gang switch box?


Not sure what you mean by derating the conductors. I take it that you have
# 14 wire and maybe you think you should have something like # 16. You do
not do that. YOu can always use larger wire.

I take it the breaker is set up for 15 amps so you have # 14 wire for it.
You do not derate the wire going to the dimmer from whatever the breaker is
rated. If the breaker is rated 15 amps, then you must use # 14 wire or
larger going from the breaker to the dimmer and then to the lights.



---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Derating Switches And Conductors In A 3-Gang Switch Box

"Ralph Mowery" wrote:
"DerbyDad03" wrote in message
...
However, I'm not sure if I am getting into a situation where I should be
derating the conductors to the dimmer, which would mean rewiring that
whole
circuit. When I do I need to be concerned with derating the conductors
that
are in a 3-gang switch box?


Not sure what you mean by derating the conductors.


I don't claim to understand all of it, but see here for a discussion on
derating conductors.

http://www.southwire.com/support/DeratingAmpacities.htm

One of the requirements related to derating is the number of conductors in
a raceway or cable. I'm trying to find out if that impacts what I want to
do in the switch for the light/fan/heater.

I take it that you have
# 14 wire and maybe you think you should have something like # 16. You do
not do that. YOu can always use larger wire.


Yes, I know that. No, I would never go smaller. That is why I mentioned
that I will have 12g wire for the 20A circuit in the same switch box as the
14g for the 15A. The question is exactly that. Do I have to go up to 12g
for the 15A circuit?


I take it the breaker is set up for 15 amps so you have # 14 wire for it.
You do not derate the wire going to the dimmer from whatever the breaker is
rated. If the breaker is rated 15 amps, then you must use # 14 wire or
larger going from the breaker to the dimmer and then to the lights.


See above.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Derating Switches And Conductors In A 3-Gang Switch Box

wrote:
On Fri, 14 Mar 2014 23:32:25 +0000 (UTC), DerbyDad03
wrote:

"Ralph Mowery" wrote:
"DerbyDad03" wrote in message
...
However, I'm not sure if I am getting into a situation where I should be
derating the conductors to the dimmer, which would mean rewiring that
whole
circuit. When I do I need to be concerned with derating the conductors
that
are in a 3-gang switch box?

Not sure what you mean by derating the conductors.


I don't claim to understand all of it, but see here for a discussion on
derating conductors.

http://www.southwire.com/support/DeratingAmpacities.htm

One of the requirements related to derating is the number of conductors in
a raceway or cable. I'm trying to find out if that impacts what I want to
do in the switch for the light/fan/heater.

I take it that you have
# 14 wire and maybe you think you should have something like # 16. You do
not do that. YOu can always use larger wire.


Yes, I know that. No, I would never go smaller. That is why I mentioned
that I will have 12g wire for the 20A circuit in the same switch box as the
14g for the 15A. The question is exactly that. Do I have to go up to 12g
for the 15A circuit?


I take it the breaker is set up for 15 amps so you have # 14 wire for it.
You do not derate the wire going to the dimmer from whatever the breaker is
rated. If the breaker is rated 15 amps, then you must use # 14 wire or
larger going from the breaker to the dimmer and then to the lights.


See above.


You don't derate for box fill. If they fit they fit.
2 cu/in for all the 14s, 2.25 for the 20s.(current carrying) Count all
the grounds as one 2.5" conductor and 4.5 cu/in for each switch.

The only time you have to derate is for dimmers.


Thanks. That's what I was hoping to hear.

However, I do have to question your statement about only derating for
dimmers. Not arguing, just trying to understand. I understand the need to
derate for dimmers because of the heat. What about this site (and others)
where they discuss the need to derate the conductors based on temperature
and the number of conductors in a raceway/cable?

http://www.southwire.com/support/DeratingAmpacities.htm

The whole issue of the derating of conductors is confusing to me, although
as far as I can tell, I'll probably never have to deal with it.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Renovating gang switches N_Cook Electronics Repair 3 March 7th 13 08:16 AM
2-gang 2-way switch John UK diy 13 October 19th 06 12:04 PM
2 gang switch in double box mayday UK diy 15 May 17th 06 09:47 AM
Gang switches rile Home Repair 16 December 14th 05 12:12 PM
1 Gang - 2 Way Switch [email protected] UK diy 2 December 13th 05 01:39 PM


All times are GMT +1. The time now is 08:46 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"