During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.

They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.

Ok, who's right here?

BTW, he's my older brother so I just let it go.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,730
Default Anything wrong with grounding metal conduit to a cold waterpipe in a 2-wire house?

On 2/6/2014 4:02 PM, Paul Drahn wrote:
Best to leave things as they are. We once owned a 1948 house. Part of
the wiring was done backwards so the white was hot and black was common.
Yours could be the same way.

Paul


I'd want to find out.

--
..
Christopher A. Young
Learn about Jesus
www.lds.org
..
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Thursday, February 6, 2014 3:51:11 PM UTC-5, wrote:
During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.



I would think that if metal conduit is being used, it's already
grounded back at the panel, no?

As to making the grounded outlets work properly, it;s clearly
a major code violation to install grounded outlets if they are
not grounded properly to begin with. New outlets cannot be put
in during a renovation without conforming to the grounding
requiremets. And since it's a kitchen, GFCI as well.




They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.



Ok, who's right here?



BTW, he's my older brother so I just let it go.


You seem to be more on track then your brother. There is no fire
risk from properly grounding the conduit. Did you ask him how the
new outlets are grounded? If they were put in without a ground,
no GFCI, etc, then that is a real shock hazard? Who's doint this
work? Permits pulled?
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,341
Default Anything wrong with grounding metal conduit to a cold water pipe in a 2-wire house?

On Thu, 6 Feb 2014 13:07:39 -0800 (PST), "
wrote:

On Thursday, February 6, 2014 3:51:11 PM UTC-5, wrote:
During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.



I would think that if metal conduit is being used, it's already
grounded back at the panel, no?

I agree. You can test this pretty easy with an ohm meter. The
resistance between the conduit and the water pipe should be very near
0 ohms.

As to making the grounded outlets work properly, it;s clearly
a major code violation to install grounded outlets if they are
not grounded properly to begin with. New outlets cannot be put
in during a renovation without conforming to the grounding
requiremets. And since it's a kitchen, GFCI as well.




They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.



Ok, who's right here?



BTW, he's my older brother so I just let it go.


You seem to be more on track then your brother. There is no fire
risk from properly grounding the conduit. Did you ask him how the
new outlets are grounded? If they were put in without a ground,
no GFCI, etc, then that is a real shock hazard? Who's doint this
work? Permits pulled?



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 296
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Thursday, February 6, 2014 3:51:11 PM UTC-5, wrote:
During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.



They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.



Ok, who's right here?



BTW, he's my older brother so I just let it go.


If it's conduit all the way to the panel then it is likely grounded at the panel.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,341
Default Anything wrong with grounding metal conduit to a cold water pipe in a 2-wire house?

On Thu, 06 Feb 2014 15:11:58 -0600, philo* wrote:

On 02/06/2014 02:51 PM, wrote:
During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.

They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.

Ok, who's right here?

BTW, he's my older brother so I just let it go.




The conduit goes back to your breaker box (or fuse box if the system has
not been upgraded) and the breaker box itself is ground...OR SHOULD BE.
The proper way to ground the outlets, it you are using a standard three
wire plug is to have the ground terminal connected to a ground wire
which would normally be inside the conduit. If there is no ground wire
inside you will need to run one to do things properly.

Other wise, I'd leave it alone.


A ground wire is not necessary. You can use a bond jumper screwed
into the box. Which I surprisingly can't find a google image of.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,377
Default Anything wrong with grounding metal conduit to a cold waterpipe in a 2-wire house?

On 02/06/2014 05:12 PM, Metspitzer wrote:
OX



The conduit goes back to your breaker box (or fuse box if the system has
not been upgraded) and the breaker box itself is ground...OR SHOULD BE.
The proper way to ground the outlets, it you are using a standard three
wire plug is to have the ground terminal connected to a ground wire
which would normally be inside the conduit. If there is no ground wire
inside you will need to run one to do things properly.

Other wise, I'd leave it alone.


A ground wire is not necessary. You can use a bond jumper screwed
into the box. Which I surprisingly can't find a google image of.




Yes, that will work . I do not know if it would be "code" or not.

The problem I see would be the case of a bad coupling junction. I think
a ground wire would be the safer way to go.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Thursday, February 6, 2014 4:11:58 PM UTC-5, philo* wrote:
On 02/06/2014 02:51 PM, wrote:

During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.




They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.




Ok, who's right here?




BTW, he's my older brother so I just let it go.










The conduit goes back to your breaker box (or fuse box if the system has

not been upgraded) and the breaker box itself is ground...OR SHOULD BE.

The proper way to ground the outlets, it you are using a standard three

wire plug is to have the ground terminal connected to a ground wire

which would normally be inside the conduit. If there is no ground wire

inside you will need to run one to do things properly.



Other wise, I'd leave it alone.


AFAIK, there is nothing in code that says metal conduit can't be
used as the grounding conductor, ie that you don't have to pull
a separate wire.


  #11   Report Post  
Posted to alt.home.repair
N8N N8N is offline
external usenet poster
 
Posts: 1,192
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Friday, February 7, 2014 6:44:51 AM UTC-5, wrote:
On Thursday, February 6, 2014 4:11:58 PM UTC-5, philo* wrote:

On 02/06/2014 02:51 PM, wrote:




During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.








They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.








Ok, who's right here?








BTW, he's my older brother so I just let it go.




















The conduit goes back to your breaker box (or fuse box if the system has




not been upgraded) and the breaker box itself is ground...OR SHOULD BE.




The proper way to ground the outlets, it you are using a standard three




wire plug is to have the ground terminal connected to a ground wire




which would normally be inside the conduit. If there is no ground wire




inside you will need to run one to do things properly.








Other wise, I'd leave it alone.




AFAIK, there is nothing in code that says metal conduit can't be

used as the grounding conductor, ie that you don't have to pull

a separate wire.


True. However if the house was built in '48, the insulation on the conductors in the conduit is possibly cloth covered rubber, in which case I'd give serious thought to repulling the home run. If the conduit is big enough I would go ahead and pull 12AWG conductors as the old ones are likely 14AWG - and maybe two hots, see comment Edison circuit below - with a dedicated ground conductor - not required, but belt and suspenders.

Read up on your code (NEC aka NFPA 70) ... a kitchen remodel requires a minimum of two dedicated 20A (12AWG) circuits with GFCIs for counter receptacles. I'm not sure if a single Edison circuit for the home run would be code compliant now or if you're required to have an AFCI breaker in the kitchen as well.

Using a water pipe as a ground in a situation where you're replacing a two wire receptacle with a grounding type receptacle *used* to be an accepted method, but is no longer code compliant. That would have only applied when there was no ground present however, and a continuous run of metal conduit back to the panel counts as a ground.

You will probably need new (deeper) boxes in the wall as well to comply with current box fill requirements. You definitely will if you are using 12AWG.

Finally, check your *local* codes for what you have to do for any new work; sometimes they are more restrictive than the NEC.

One thing that you may want to do, if you are concerned about grounding (not a bad thing to worry about) more bang for your buck and code legal is making sure that your water service is bonded to the ground/neutral bus at the panel, and if you don't have ground rods or a Ufer ground (I doubt it in a house that old) consider driving some ground rods. Also since you're upgrading, a surge protector at the panel can be helpful if you're in a storm prone area.

good luck

nate
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Friday, February 7, 2014 8:30:34 AM UTC-5, N8N wrote:
On Friday, February 7, 2014 6:44:51 AM UTC-5, wrote:

On Thursday, February 6, 2014 4:11:58 PM UTC-5, philo* wrote:




On 02/06/2014 02:51 PM, wrote:








During a kitchen remodel in my mom's circa 1948 house (post WWII made out of reinforced concrete!) with 2-wire electrical and metal conduit, I mentioned to my brother and nephew that, since it was exposed, it probably wouldn't be a bad idea to ground the wiring conduit to a cold water pipe, thereby grounding the entire conduit run and at the very least making grounded outlets work properly.
















They reacted in horror saying it could cause a fire or even worse. I said that at least you'd know if you had a short circuit because the breaker would trip and touching something metal wouldn't kill you.
















Ok, who's right here?
















BTW, he's my older brother so I just let it go.








































The conduit goes back to your breaker box (or fuse box if the system has








not been upgraded) and the breaker box itself is ground...OR SHOULD BE.








The proper way to ground the outlets, it you are using a standard three








wire plug is to have the ground terminal connected to a ground wire








which would normally be inside the conduit. If there is no ground wire








inside you will need to run one to do things properly.
















Other wise, I'd leave it alone.








AFAIK, there is nothing in code that says metal conduit can't be




used as the grounding conductor, ie that you don't have to pull




a separate wire.




True. However if the house was built in '48, the insulation on the conductors in the conduit is possibly cloth covered rubber, in which case I'd give serious thought to repulling the home run. If the conduit is big enough I would go ahead and pull 12AWG conductors as the old ones are likely 14AWG - and maybe two hots, see comment Edison circuit below - with a dedicated ground conductor - not required, but belt and suspenders.



Read up on your code (NEC aka NFPA 70) ... a kitchen remodel requires a minimum of two dedicated 20A (12AWG) circuits with GFCIs for counter receptacles. I'm not sure if a single Edison circuit for the home run would be code compliant now or if you're required to have an AFCI breaker in the kitchen as well.



You started out replying to my post with a "true" and then
segued into the above, about reading code, which I think you meant
for the OP. I agree with your observations. How much, if any of that
applies, depends on what he means by "kitchen renovation". So
far all he's said about anything to do with the electrical was the
one very limited question. If they are adding outlets, etc, which
is certainly typical of many kitchen renovation, particularly in
that age houe, I agree there are a whole lot of issues beyond
the question asked. And it also sounds like they are beyond the
skill level of those involved. If they are redoing the electrical,
it's kind of scary that they would be asking that question.
If that's the case, probably time to call a pro. Better to do it
right now while the kitchen work is being done, then have to deal
with a mess later.






Using a water pipe as a ground in a situation where you're replacing a two wire receptacle with a grounding type receptacle *used* to be an accepted method, but is no longer code compliant. That would have only applied when there was no ground present however, and a continuous run of metal conduit back to the panel counts as a ground.



You will probably need new (deeper) boxes in the wall as well to comply with current box fill requirements. You definitely will if you are using 12AWG.



Finally, check your *local* codes for what you have to do for any new work; sometimes they are more restrictive than the NEC.



One thing that you may want to do, if you are concerned about grounding (not a bad thing to worry about) more bang for your buck and code legal is making sure that your water service is bonded to the ground/neutral bus at the panel, and if you don't have ground rods or a Ufer ground (I doubt it in a house that old) consider driving some ground rods. Also since you're upgrading, a surge protector at the panel can be helpful if you're in a storm prone area.



good luck



nate


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 27
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?




If they are adding outlets, etc, which

is certainly typical of many kitchen renovation, particularly in

that age houe, I agree there are a whole lot of issues beyond

the question asked.




No outlets are being added. You couldn't add them if you wanted to--all of the electrical is buried in concrete (the house is solid reinforced concrete) . The new kitchen is merely taking the place of the old kitchen. Same footprint.
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Thursday, February 6, 2014 4:14:36 PM UTC-5, Jon Danniken wrote:
On 02/06/2014 12:51 PM, wrote:

During a kitchen remodel in my mom's circa 1948 house (post WWII made


out of reinforced concrete!) with 2-wire electrical and metal


conduit, I mentioned to my brother and nephew that, since it was


exposed, it probably wouldn't be a bad idea to ground the wiring


conduit to a cold water pipe, thereby grounding the entire conduit


run and at the very least making grounded outlets work properly.




They reacted in horror saying it could cause a fire or even worse. I


said that at least you'd know if you had a short circuit because the


breaker would trip and touching something metal wouldn't kill you.




Ok, who's right here?




The main caveat is that you have absolute certainty that the water pipe

is metal all the way to the water meter, and doesn't transition into

PVC. You also have to make a solid connection to the pipe that will not

be compromised due to corrosion if the pipe is steel.



If you can accomplish these two issues, it would technically work, but

I'm guessssing it's probably not going to be code compliant (should the

incoming pipe be replaced by PVC in the future, the ground would end up

being non functional).



Jon


That about sums it up. It would work, but it's not code compliant.
Nor should it be necessary because the conduit should be grounded
back at the panel.


  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 460
Default Anything wrong with grounding metal conduit to a cold water pipe in a 2-wire house?

yrag,

With the recent popularity of plastic pipe, it may be unwise to.trust in
a cold water pipe as a ground. A bit of plastic pipe used for a repair may
disconnect the pipe from the ground.

Dave M.


  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,644
Default Anything wrong with grounding metal conduit to a cold water pipein a 2-wire house?

On Friday, February 7, 2014 1:29:47 AM UTC-5, wrote:
There are some testers that will verify the quality of the ground

SureTest is one. It is not the $5 3 light tester. A sure test actually

puts a load on the ground.


Just try the ground poweing a 60 watt incandescent lamp, if the light burns brite your all set.

  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default Anything wrong with grounding metal conduit to a cold water pipe in a 2-wire house?

posted for all of us...

And I know how to SNIP


There are some testers that will verify the quality of the ground
SureTest is one. It is not the $5 3 light tester. A sure test actually
puts a load on the ground.


Greg, wouldn't this also be an issue of bonding vs grounding?

--
Tekkie


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Grounding wire from panel to gas pipe??? blueman Home Repair 63 August 7th 19 07:26 PM
Water heater wire - conduit or romex? Jon Danniken[_2_] Home Repair 52 November 19th 09 09:57 PM
why does my basement cold water pipe only rattle during cold weather? Joe Home Repair 7 November 7th 07 02:26 AM
Cold water grounding coustanis Home Repair 12 February 10th 07 11:12 AM
grounding water pipe William Deans Home Repair 50 February 19th 05 04:09 AM


All times are GMT +1. The time now is 04:27 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"