Hi all,

I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?

Thank you in advance.

  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Cold water grounding

Open your main service panel and look for large, possibly bare wires
attached to the neutral/ground buss, that are not connected to any cable and
leave the panel as individual conductors. If they have insulation on them,
it should be marked with green tape. Depending upon the size of your
service, they could be #8,6, or 4, or larger for larger than 200 amp
services. If you follow these wires, one should go to a ground rod(s) and
the other clamped to the cold water pipe



"coustanis" wrote in message
ups.com...
Hi all,

I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?

Thank you in advance.



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 766
Default Cold water grounding

coustanis wrote:
Hi all,

I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?

Thank you in advance.



Likely the box has a independent ground to ground wires outside. There
should also be a ground coming from the service and one going to any metal
water pipes you have. Relying on water pipes to provide ground is no longer
code.

--
Joseph Meehan

Dia 's Muire duit



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,743
Default Cold water grounding

coustanis wrote:
Hi all,

I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?

Thank you in advance.


Re-think time. It is not the electrical service that is grounded through the
water pipes, it is the water pipes that are grounded through the electrical
service.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Cold water grounding

On Feb 9, 9:01 am, "HeyBub" wrote:
coustanis wrote:
Hi all,


I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?


Thank you in advance.


Re-think time. It is not the electrical service that is grounded through the
water pipes, it is the water pipes that are grounded through the electrical
service.


Really? I thought it was the other way around. What would electrify
the water pipes to
require this?
I'll try to follow the larger, bare wires from the buss and see if I
can trace them to a proper ground.
Hopefully they won't go hidden on me.

Thanks folks.



  #6   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Cold water grounding

If your underground water supply pipes were copper, they would indeed be
grounding the electrical system, but in your situation, the system is
grounded by the rods, and bonded to the internal piping to protect you in
the event that an internal pipe contacted something live. If the piping
wasn't bonded to the system, nothing would cause the circuit breaker to trip
if this occurred



"coustanis" wrote in message
oups.com...
On Feb 9, 9:01 am, "HeyBub" wrote:
coustanis wrote:
Hi all,


I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?


Thank you in advance.


Re-think time. It is not the electrical service that is grounded through
the
water pipes, it is the water pipes that are grounded through the
electrical
service.


Really? I thought it was the other way around. What would electrify
the water pipes to
require this?
I'll try to follow the larger, bare wires from the buss and see if I
can trace them to a proper ground.
Hopefully they won't go hidden on me.

Thanks folks.



  #7   Report Post  
Posted to alt.home.repair
N8N N8N is offline
external usenet poster
 
Posts: 1,192
Default Cold water grounding

On Feb 9, 9:08 am, "coustanis" wrote:
On Feb 9, 9:01 am, "HeyBub" wrote:





coustanis wrote:
Hi all,


I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?


Thank you in advance.


Re-think time. It is not the electrical service that is grounded through the
water pipes, it is the water pipes that are grounded through the electrical
service.


Really? I thought it was the other way around. What would electrify
the water pipes to
require this?


Hopefully, nothing. But, there's always the possibility that, say,
you'll drop your electric razor in the sink with the water running,
etc - better to have the juice short to ground through the water pipe
than through you.

I'll try to follow the larger, bare wires from the buss and see if I
can trace them to a proper ground.
Hopefully they won't go hidden on me.

Thanks folks.


Yup, if you have a big bare copper wire going back outside and then
disappearing underground, you're probably OK. If not, you may want to
consider driving some grounding rods.

nate

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Cold water grounding

On Feb 9, 9:28 am, "N8N" wrote:
On Feb 9, 9:08 am, "coustanis" wrote:



On Feb 9, 9:01 am, "HeyBub" wrote:


coustanis wrote:
Hi all,


I think I have a problem. I was doing some stuff in my basement and I
noticed that the
ground wire from the service panel was strapped to a copper cold water
pipe. The problem is
that the copper pipe with the ground then is then attached to a CPVC
pipe so the copper just ends.
Is it the copper pipe itself that carries the grounding or is it the
water inside the pipe that does it. I have this bad feeling that my
service panel is not grounded. What do you think?
To take it a step further, what method can I use to test the service
panel to see if it is, in fact grounded?


Thank you in advance.


Re-think time. It is not the electrical service that is grounded through the
water pipes, it is the water pipes that are grounded through the electrical
service.


Really? I thought it was the other way around. What would electrify
the water pipes to
require this?


Hopefully, nothing. But, there's always the possibility that, say,
you'll drop your electric razor in the sink with the water running,
etc - better to have the juice short to ground through the water pipe
than through you.

I'll try to follow the larger, bare wires from the buss and see if I
can trace them to a proper ground.
Hopefully they won't go hidden on me.


Thanks folks.


Yup, if you have a big bare copper wire going back outside and then
disappearing underground, you're probably OK. If not, you may want to
consider driving some grounding rods.

nate


The pipes coming into the house from the well are indeed black
plastic, not metal.
There is so much goofy stuff going on with this house it could easily
have been changed incorrectly before I bought it.
I'll look for that ground. An ohm meter would be useful here when I
find it to ensure connection.


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 458
Default Cold water grounding

N8N wrote:
....
Re-think time. It is not the electrical service that is grounded
through the water pipes, it is the water pipes that are grounded
through the electrical service.


Really? I thought it was the other way around. What would electrify
the water pipes to
require this?


Hopefully, nothing. But, there's always the possibility that, say,
you'll drop your electric razor in the sink with the water running,
etc - better to have the juice short to ground through the water pipe
than through you.

I'll try to follow the larger, bare wires from the buss and see if I
can trace them to a proper ground.
Hopefully they won't go hidden on me.

Thanks folks.


Yup, if you have a big bare copper wire going back outside and then
disappearing underground, you're probably OK. If not, you may want to
consider driving some grounding rods.

nate


Where the heck are you coming from, and what's your background enabling you
to make such a statement? A wet human body is MUCH MORE conductive than
water! If you complete a path, it'll go through you much faster than into
the pipes, or at least on its way to the pipes. Is there actually anything
in writing to substantiate your comments that might shed more accurate light
on this situation? I'm not familiar with grounding water pipe requirements
for these reasons and would like more info if it's true. Heck, if it's
true, I could rip out a few GFCIs, in fact. NOT!

Pop`





  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,743
Default Cold water grounding

Pop` wrote:
Where the heck are you coming from, and what's your background
enabling you to make such a statement? A wet human body is MUCH MORE
conductive than water! If you complete a path, it'll go through you
much faster than into the pipes, or at least on its way to the pipes.
Is there actually anything in writing to substantiate your comments
that might shed more accurate light on this situation? I'm not
familiar with grounding water pipe requirements for these reasons and
would like more info if it's true. Heck, if it's true, I could rip
out a few GFCIs, in fact. NOT!


Whatever. The water does taste better, though.




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Cold water grounding

On Feb 9, 12:22�pm, "Pop`" wrote:
N8N wrote:

...





Re-think time. It is not the electrical service that is grounded
through the water pipes, it is the water pipes that are grounded
through the electrical service.


Really? *I thought it was the other way around. *What would electrify
the water pipes to
require this?


Hopefully, nothing. *But, there's always the possibility that, say,
you'll drop your electric razor in the sink with the water running,
etc - better to have the juice short to ground through the water pipe
than through you.


I'll try to follow the larger, bare wires from the buss and see if I
can trace them to a proper ground.
Hopefully they won't go hidden on me.


Thanks folks.


Yup, if you have a big bare copper wire going back outside and then
disappearing underground, you're probably OK. *If not, you may want to
consider driving some grounding rods.


nate


Where the heck are you coming from, and what's your background enabling you
to make such a statement? *A wet human body is MUCH MORE conductive than
water! *If you complete a path, it'll go through you much faster than into
the pipes, or at least on its way to the pipes. * Is there actually anything
in writing to substantiate your comments that might shed more accurate light
on this situation? *I'm not familiar with grounding water pipe requirements
for these reasons and would like more info if it's true. *Heck, if it's
true, I could rip out a few GFCIs, in fact. *NOT!

Pop`- Hide quoted text -

- Show quoted text -


Actually all grounds MUST BE BONDED!

The more the salt in water the more conductive it is! Human bodies are
part saline salt....


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 330
Default Cold water grounding




Likely the box has a independent ground to ground wires outside.

There
should also be a ground coming from the service and one going to any metal
water pipes you have. Relying on water pipes to provide ground is no

longer
code.


Older homes that originally had fuse boxes were routinely "grounded" with
the water pipe. The ground wire went to where the water pipe entered the
house. That would preserve the ground in cases where plastic pipe was
installed inside the home. Problem is that if the water utility decides to
"upgrade" their service the odds are that they will go to PLASTIC mains (up
to 10").

They are doing that in the more built up areas "around here." The "drops"
(from the street line to the house) seem to be copper. I suspect that was
done mainly to not have to pay the customer to put in ground rods.

But everything seems to be plastic whenever possible today. The low
pressure gas lines (up to 8" by my directly observation) are plastic. The
drops are plastic. They protect the plastic above ground with a metal
sleeve when it enters the meter.

Grounding can be a serious concern. We have an unusual situation with a
400' run from our house to the transformer but we "lost" the neutral once.
If the neutral to the transformer is intact, the ground rods or water pipe
just don't make any difference. If the neutral is broken it's not obvious
that a two un-tested ground rods could keep you from getting a shock.


--
Joseph Meehan

Dia 's Muire duit





  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Cold water grounding

Here in Florida, there are some restrictions as to using bare copper
that comes in contact with sandy soil -- seems that the salts become
conductive and can lead to accelerated corrosion.
Does anyone have any experience with this?


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water main going plastic: questions about electricity grounding Chris Mear UK diy 10 September 29th 06 09:27 AM
Grounding straps on water meters tomkanpa Home Repair 24 October 12th 05 04:39 AM
grounding water pipe William Deans Home Repair 50 February 19th 05 04:09 AM
[Fwd: Self-grounding outlets vs. grounding wire] Phil Munro Home Repair 0 December 1st 04 07:52 PM
Doulble Receptacle Grounding Question/ Switch Grounding Michael Roback Home Repair 1 September 7th 03 07:37 AM


All times are GMT +1. The time now is 02:52 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"