I recently got a Champion 4000wpeak/3500w continuous generator that has a 120v 30a output.
I hooked up my elec panel with a 30a breaker with an interlock, ran a 10/4 and a generator inlet box outside. I made up my own extension SJ cord with a standard generator female plug at one end to plug in the inlet box, and on the generator side is a 30A 120v plug that has both red and black bonded together inside the plug to make both sides of elec panel live.
Now the only 220 device I have is my CAC, which I would not run anyway, but I was just curious, what would happen if you accidentally fed a 220v device with 2 hots of the same phase? Would anything happen? I'm thinking nothing would happen, it would just be dead, and no damage would be done since no current would flow.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,377
Default What happens if you connect 240 device with 2 of same phase?

On 11/06/2013 06:38 PM, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w continuous generator that has a 120v 30a output.
I hooked up my elec panel with a 30a breaker with an interlock, ran a 10/4 and a generator inlet box outside. I made up my own extension SJ cord with a standard generator female plug at one end to plug in the inlet box, and on the generator side is a 30A 120v plug that has both red and black bonded together inside the plug to make both sides of elec panel live.
Now the only 220 device I have is my CAC, which I would not run anyway, but I was just curious, what would happen if you accidentally fed a 220v device with 2 hots of the same phase? Would anything happen? I'm thinking nothing would happen, it would just be dead, and no damage would be done since no current would flow.


correct
  #3   Report Post  
Senior Member
 
Posts: 2,498
Default

Quote:
Originally Posted by philo*[_2_] View Post
On 11/06/2013 06:38 PM, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w continuous generator that has a 120v 30a output.
I hooked up my elec panel with a 30a breaker with an interlock, ran a 10/4 and a generator inlet box outside. I made up my own extension SJ cord with a standard generator female plug at one end to plug in the inlet box, and on the generator side is a 30A 120v plug that has both red and black bonded together inside the plug to make both sides of elec panel live.
Now the only 220 device I have is my CAC, which I would not run anyway, but I was just curious, what would happen if you accidentally fed a 220v device with 2 hots of the same phase? Would anything happen? I'm thinking nothing would happen, it would just be dead, and no damage would be done since no current would flow.


correct
That's what I think too. All of the 120 volt circuits in the appliance would operate properly, such as the oven light bulb in an oven or the 120V indicator lights on the stoves console, but none of the heating elements would work because you've got the same voltage at each end of the heating element, and therefore no current flow.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,526
Default What happens if you connect 240 device with 2 of same phase?

On Wednesday, November 6, 2013 7:38:37 PM UTC-5, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w continuous generator that has a 120v what would happen if you accidentally fed a 220v device with 2 hots of the same phase? Would anything happen? I'm thinking nothing would happen, it would just be dead, and no damage would be done since no current would flow.


I'm thinking you already did this and are wondering if you did some damage.

No, you didn't.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,644
Default What happens if you connect 240 device with 2 of same phase?

my neighbor installed a 240 volt compressor and it didnt work, i took a quick look, and said move the breaker one space. instant fix since i had done the same thing years before......

the whatever wuldnt work but it cant damage the device


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,228
Default What happens if you connect 240 device with 2 of same phase?


"Mikepier" wrote in message
...
I recently got a Champion 4000wpeak/3500w continuous generator that has a
120v 30a output.

I hooked up my elec panel with a 30a breaker with an interlock, ran a 10/4
and a generator inlet box outside. I made up my own extension SJ cord with a
standard generator female plug at one end to plug in the inlet box, and on
the generator side is a 30A 120v plug that has both red and black bonded
together inside the plug to make both sides of elec panel live.
Now the only 220 device I have is my CAC, which I would not run anyway, but
I was just curious, what would happen if you accidentally fed a 220v device
with 2 hots of the same phase? Would anything happen? I'm thinking nothing
would happen, it would just be dead, and no damage would be done since no
current would flow.

If it is pure 220 volt device, nothing would hapen. If you have some
control circuits involved that internally operate on 120 , they may or may
not come on. Even then I doubt there would be any damage done.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,029
Default What happens if you connect 240 device with 2 of same phase?

What everyone else has said, you are right on.
  #8   Report Post  
Posted to alt.home.repair
Bob Bob is offline
external usenet poster
 
Posts: 99
Default What happens if you connect 240 device with 2 of same phase?

On 11/6/2013 16:38, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w continuous generator that has a 120v 30a output.
I hooked up my elec panel with a 30a breaker with an interlock, ran a 10/4 and a generator inlet box outside. I made up my own extension SJ cord with a standard generator female plug at one end to plug in the inlet box, and on the generator side is a 30A 120v plug that has both red and black bonded together inside the plug to make both sides of elec panel live.


There would be no damage to (or performance of) 240 volt devices with
such a setup. But if you have two 120 volt circuits using a shared
neutral, as is often the case with kitchen appliance circuits, a danger
exists of overloading the neutral wire.


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default What happens if you connect 240 device with 2 of same phase?

On 11/06/2013 07:38 PM, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w continuous generator that has a 120v 30a output.
I hooked up my elec panel with a 30a breaker with an interlock, ran a 10/4 and a generator inlet box outside. I made up my own extension SJ cord with a standard generator female plug at one end to plug in the inlet box, and on the generator side is a 30A 120v plug that has both red and black bonded together inside the plug to make both sides of elec panel live.
Now the only 220 device I have is my CAC, which I would not run anyway, but I was just curious, what would happen if you accidentally fed a 220v device with 2 hots of the same phase? Would anything happen? I'm thinking nothing would happen, it would just be dead, and no damage would be done since no current would flow.



--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default What happens if you connect 240 device with 2 of same phase?

On 11/06/2013 07:38 PM, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w continuous generator that
has a 120v 30a output. I hooked up my elec panel with a 30a breaker
with an interlock, ran a 10/4 and a generator inlet box outside. I
made up my own extension SJ cord with a standard generator female
plug at one end to plug in the inlet box, and on the generator side
is a 30A 120v plug that has both red and black bonded together inside
the plug to make both sides of elec panel live. Now the only 220
device I have is my CAC, which I would not run anyway, but I was just
curious, what would happen if you accidentally fed a 220v device with
2 hots of the same phase? Would anything happen? I'm thinking nothing
would happen, it would just be dead, and no damage would be done
since no current would flow.



The potential between the to "phases" to the 240V circuits will be 0V,
so those simply won't work. The potential between those conductors and
ground will still be 120V, so there is a shock hazard of disassembling
the appliances while they're plugged in even though they're apparently
not working...

If you're powering your whole house panel with the generator however,
make sure that there are no "Edison" or shared-neutral 120VAC circuits
powered up by a single phase - that can result in the neutral conductor
of those circuits carrying up to twice the current that it's rated for.
(a good argument for a generator subpanel)

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,730
Default What happens if you connect 240 device with 2 of same phase?

On 11/6/2013 7:38 PM, Mikepier wrote:
I recently got a Champion 4000wpeak/3500w

continuous generator that has a 120v 30a output.
I hooked up my elec panel with a 30a breaker

with an interlock, ran a 10/4 and a generator
inlet box outside. I made up my own extension
SJ cord with a standard generator female plug at
one end to plug in the inlet box, and on the
generator side is a 30A 120v plug that has both
red and black bonded together inside the plug to
make both sides of elec panel live.
Now the only 220 device I have is my CAC, which

I would not run anyway, but I was just curious,
what would happen if you accidentally fed a 220v
device with 2 hots of the same phase? Would any
thing happen? I'm thinking nothing would happen,
it would just be dead, and no damage would be done
since no current would flow.


Agree. Nothing would happen. It's an interesting
question.

Q: When I was a teen, we had a central vacuum
cleaner system in the wood shop room at school.
This was hosed and piped to the various machines,
to remove the sawdust from saws, planers, etc.
We could also run flexible hose, to act like a
shop vac, if we had to clean around a machine.
One of the boys asked what happens, if you take
the end of one flex hose, and use it to vacuum
the end of another flex hose?

--
..
Christopher A. Young
Learn about Jesus
www.lds.org
..
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default What happens if you connect 240 device with 2 of same phase?

Thanks. No I actually have not done it to my CAC accidentally, but I was just curious what would happen if I did.
I have no Edison circuits, so no worries about overloading .

  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default What happens if you connect 240 device with 2 of same phase?

On Thursday, November 7, 2013 6:26:40 AM UTC-5, Nate Nagel wrote:
On 11/06/2013 07:38 PM, Mikepier wrote:

I recently got a Champion 4000wpeak/3500w continuous generator that


has a 120v 30a output. I hooked up my elec panel with a 30a breaker


with an interlock, ran a 10/4 and a generator inlet box outside. I


made up my own extension SJ cord with a standard generator female


plug at one end to plug in the inlet box, and on the generator side


is a 30A 120v plug that has both red and black bonded together inside


the plug to make both sides of elec panel live. Now the only 220


device I have is my CAC, which I would not run anyway, but I was just


curious, what would happen if you accidentally fed a 220v device with


2 hots of the same phase? Would anything happen? I'm thinking nothing


would happen, it would just be dead, and no damage would be done


since no current would flow.








The potential between the to "phases" to the 240V circuits will be 0V,

so those simply won't work. The potential between those conductors and

ground will still be 120V, so there is a shock hazard of disassembling

the appliances while they're plugged in even though they're apparently

not working...



If you're powering your whole house panel with the generator however,

make sure that there are no "Edison" or shared-neutral 120VAC circuits

powered up by a single phase - that can result in the neutral conductor

of those circuits carrying up to twice the current that it's rated for.

(a good argument for a generator subpanel)



nate



One good reason to use a generator with a 240V output.
It avoids that problem. I'm assuming Mike's doesn't
have 240V.
  #15   Report Post  
Senior Member
 
Posts: 2,498
Default

Quote:
Originally Posted by Bob View Post
There would be no damage to (or performance of) 240 volt devices with
such a setup. But if you have two 120 volt circuits using a shared
neutral, as is often the case with kitchen appliance circuits, a danger
exists of overloading the neutral wire.
I took a look at the wiring diagrams of the stoves in my building, and so far as I can see, the only heating element that connects to the neutral is the broil element. The bake element and all surface elements don't involve the neutral at all; the heating element is connected between L1 and L2 in all cases.

But, the OP's central air conditioner may be quite different, and burning out the neutral wire might be a risk there.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to connect weird AC 3 phase motor with a electric break _Req_motor.zip 569 (1/1) jo Electronic Schematics 1 April 7th 08 04:28 AM
Rotary phase converter versus trying to run a VMC straight from single phase Jeffrey Lebowski[_2_] Metalworking 0 February 21st 08 06:44 AM
profit-motive question: single phase adapter for 3-phase motor drives gwes Metalworking 8 October 5th 07 08:33 PM
Is it possible to convert an USB wire device to a bluetooth device? Frank Electronics Repair 2 December 2nd 06 02:20 AM
3-phase used for 1-phase (split-phase) power SRK Home Repair 9 July 22nd 06 11:01 AM


All times are GMT +1. The time now is 08:07 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"