This is a code question more than anything, but I thought it might be
worth looking at.

I recently had a 240V electrical heating circuit added. #12 wire, 20A
breaker. Max load is 3840W, but I want to drive 4500W.
Unfortunately, 25A breakers aren't available for my panel (this would
fix the problem) and I have no additional circuits left in my panel.

One other solution is to use 30A breakers and switch to #10 wire.
Problem is that one heater was already in-place (and on a different
floor) so I'd have to demolish the house to re-wire it. Is it
acceptable to run #10 wire from the panel to the first thermostat
(3000W), and keep the existing #12 wire for the remaining 1500W (which
is branched from the first thermostat)?

Under normal conditions, current will never exceed wire maximums.
However, if the 1500W heater had a fault, current through that section
could potentially exceed the #12 capacity (30A) before tripping.
Doesn't sound safe to me, but I wonder if there is anything in the
code that would allow it.

FWIW, I have an alternate solution that will balance loads between
heating circuits..it just isn't pretty because I need to create (and
maintain access to) a junction in an existing circuit.
  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Electrical Breaker 'cheat'?

Borrall Wonnell wrote:
....

I recently had a 240V electrical heating circuit added. #12 wire, 20A
breaker. ...

....
... Is it
acceptable to run #10 wire from the panel to the first thermostat
(3000W), and keep the existing #12 wire for the remaining 1500W (which
is branched from the first thermostat)?


....

In a word, "No" (assuming you're intending to switch to a 30A breaker
which your posting doesn't explicitly state but I infer is the reason
for posing the question).

--
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,228
Default Electrical Breaker 'cheat'?


wrote in message
...
On Thu, 9 Dec 2010 10:27:58 -0800 (PST), Borrall Wonnell
What you suggest is probably safe (#10 to the stat #12 to a 1500w
heater) but it is not legal.
Arguing on the safety side I can say the 1500w load is well within the
ampacity of the 12ga wire and a short will still safely be cleared by
a 30a breaker.


A short circuit will trip breakes with much smaller wire than the code
requires. That is only part of the problem. If there is a wiring problem
that causes the smaller wire to draw more current, but not enough to trip
the larger breaker, the wire can over heat and causes a fire.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,567
Default Electrical Breaker 'cheat'?

On Dec 9, 1:27*pm, Borrall Wonnell wrote:
Hi all,

This is a code question more than anything, but I thought it might be
worth looking at.

I recently had a 240V electrical heating circuit added. *#12 wire, 20A
breaker. *Max load is 3840W, but I want to drive 4500W.
Unfortunately, 25A breakers aren't available for my panel (this would
fix the problem) and I have no additional circuits left in my panel.

One other solution is to use 30A breakers and switch to #10 wire.
Problem is that one heater was already in-place (and on a different
floor) so I'd have to demolish the house to re-wire it. *Is it
acceptable to run #10 wire from the panel to the first thermostat
(3000W), and keep the existing #12 wire for the remaining 1500W (which
is branched from the first thermostat)?

Under normal conditions, current will never exceed wire maximums.
However, if the 1500W heater had a fault, current through that section
could potentially exceed the #12 capacity (30A) before tripping.
Doesn't sound safe to me, but I wonder if there is anything in the
code that would allow it.

FWIW, I have an alternate solution that will balance loads between
heating circuits..it just isn't pretty because I need to create (and
maintain access to) a junction in an existing circuit.


Have you looked at possibly swapping out some of your other breakers
with a few of those single slot, double breakers to create some more
room in your box.

http://cdn.oneprojectcloser.com/wp-c...aker-panel.jpg
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 44
Default Electrical Breaker 'cheat'?

On Dec 13, 1:29*am, wrote:
On Thu, 9 Dec 2010 10:27:58 -0800 (PST), Borrall Wonnell
I recently had a 240V electrical heating circuit added. *#12 wire, 20A
breaker. *Max load is 3840W, but I want to drive 4500W.
Unfortunately, 25A breakers aren't available for my panel (this would
fix the problem) and I have no additional circuits left in my panel.



According to the code, this is NOT legal. *It's also a fire hazzard.


Update:
I went with the cheapest solution. I swapped two of my 500W heaters
for 300W units and transferred one of them to another heating
circuit. Both circuits are now loaded at 3800W, just below the 80%
limit. This required one extra junction box and 30' of wire, but the
heaters were a couple of bucks cheaper. On the downside, I have
absolutely no headroom for future expansion. If the next owner wants
to put in that hottub (or whatever), he'll have to pay dearly for
it

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical question-240V breaker. Charles Bishop[_2_] Home Repair 5 April 19th 09 02:33 AM
Electrical Breaker and dust collector question jtpr Home Repair 26 March 11th 09 03:43 PM
Electrical Query (Metal Breaker Box) Doug White Metalworking 26 January 29th 08 06:57 AM
Gas furnace electrical plug, What size breaker? Aaron Home Repair 5 November 30th 05 05:54 PM
electrical breaker comparison badgolferman Home Repair 3 June 6th 05 07:16 PM


All times are GMT +1. The time now is 01:42 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"