Twayne wrote:
In ,
bud-- typed:
Twayne wrote:
A "Class 2" xfmr is simply a double-insulated transformer
without an earth ground on its plug, nor a polarized plug.
A "Class 1" xfmr requires a third wire, the earth ground
pin on its plug. The "Class of xfmr is a UL/CSA et al
classification which approves the xfmr and nothing else as
safety approved.

The primary characteristic of class 1, 2, and 3 power
sources is that they are power limited. There is a
specified maximum voltage, current and power you can get
from the source. For a class 2 24V transformer the max
current is 8A - the maximum current you get if you short
circuit the transformer.


I think you're confused between class definitions for Safety and what the
NEC defines; they are different.


I think you're confused about nearly everything.

Class 1, 2, and 3 CIRCUITS are classified as remote-control, signaling, and
power-limited circuits in the National Electrical Code (NEC).


Limiting the discussion to class 2, which many people are familiar with
(thermostat, doorbell):

Class 2 circuits are class 2 because they are _powered by a class 2
power supply_.

Class 1 and 2 Power Supplies determines the insulation PROPERTIES of a power
supply and there is no Class 3. To the layman, they either need the third
ground wire or not (1 & 2 respectively).


So if I buy a UL listed class 2 transformer, according to you, it is not
power limited and can not be used to power a class 2 circuit. What a
bizarre idea. Make that a stupid idea.

No class 3? UL category XOKV - "TRANSFORMERS, CLASS 2 AND CLASS 3".

The 8 Amp limitation IN NEC has nothing to do with UL/CSA et al
classifications. A transformer can output any current it can be designed for
as long as it meets the insulation and overvoltage/current test
specifications and meet the safety requirements.


That will surprise UL.

Class 1, 2, 3 as used in the NEC as you can see above is quite different.
While saftey is of course a concern, simply limiting an output to 8 amps
would not deem it to be "safe". The NEC is concerned with wiring, and the
Safety is concerned with safety. Two different worlds. A google for UL
1459 might be enlightening for you.


It might be a lot more enlightening for you.

UL 1459 is "Telephone power supplies" (and has probably been withdrawn).
You are probably the only person that thinks we are talking about
telephones.

Class 2 transformers are listed under UL 1585, "Class 2 and Class 3
Transformers." (There is that pesky "class 3" again.) They are power
limited "in accordance with ANSI/NFPA 70, ‘National Electrical Code’ (NEC)"

Some other standards may be applicable such as UL 1310, "Class 2 Power
Units" which also comply "with Class 2 voltage, current and volt-ampere
limits as specified in ANSI/NFPA 70, 'National Electrical Code'."

Note the reference to the power limits in the NEC.

Information is from the UL White Book.

Again you are posting nonsense.

Four months ago, in a thread about utility PF correction caps, you told
HeyBub "next time I'll be a lot more careful."
Obviously not.
Again.
G

--
bud--
  #42   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 198
Default Suggestion for 24V/120V relay to control new outlet?

You're right, I cited the wrong spec; it's probably actually something like
one of the 5085's. But I'm not tempted to refute anything you say because
you are still getting things terribly mixed up. Perhaps you should brush up
on how to read these specs too. Like, parts 1 & 2 apply unless excepted by 3
and so forth.
Sorry; I don't have the time to mess with your refusal to get the proper
information assembled for the project at hand.

HTH,

Twayne`


n ,
bud-- typed:
Twayne wrote:
In ,
bud-- typed:
Twayne wrote:
A "Class 2" xfmr is simply a double-insulated transformer
without an earth ground on its plug, nor a polarized
plug. A "Class 1" xfmr requires a third wire, the earth
ground pin on its plug. The "Class of xfmr is a UL/CSA
et al classification which approves the xfmr and nothing
else as safety approved.
The primary characteristic of class 1, 2, and 3 power
sources is that they are power limited. There is a
specified maximum voltage, current and power you can get
from the source. For a class 2 24V transformer the max
current is 8A - the maximum current you get if you short
circuit the transformer.


I think you're confused between class definitions for
Safety and what the NEC defines; they are different.


I think you're confused about nearly everything.

Class 1, 2, and 3 CIRCUITS are classified as
remote-control, signaling, and power-limited circuits in
the National Electrical Code (NEC).


Limiting the discussion to class 2, which many people are
familiar with (thermostat, doorbell):

Class 2 circuits are class 2 because they are _powered by a
class 2 power supply_.

Class 1 and 2 Power Supplies determines the insulation
PROPERTIES of a power supply and there is no Class 3. To
the layman, they either need the third ground wire or not
(1 & 2 respectively).


So if I buy a UL listed class 2 transformer, according to
you, it is not power limited and can not be used to power a
class 2 circuit. What a bizarre idea. Make that a stupid
idea.
No class 3? UL category XOKV - "TRANSFORMERS, CLASS 2 AND
CLASS 3".
The 8 Amp limitation IN NEC has nothing to do with UL/CSA
et al classifications. A transformer can output any
current it can be designed for as long as it meets the
insulation and overvoltage/current test specifications and
meet the safety requirements.


That will surprise UL.

Class 1, 2, 3 as used in the NEC as you can see above
is quite different. While saftey is of course a concern,
simply limiting an output to 8 amps would not deem it to
be "safe". The NEC is concerned with wiring, and the
Safety is concerned with safety. Two different worlds. A
google for UL 1459 might be enlightening for
you.


It might be a lot more enlightening for you.

UL 1459 is "Telephone power supplies" (and has probably
been withdrawn). You are probably the only person that
thinks we are talking about telephones.

Class 2 transformers are listed under UL 1585, "Class 2 and
Class 3 Transformers." (There is that pesky "class 3"
again.) They are power limited "in accordance with
ANSI/NFPA 70, National Electrical Code (NEC)"
Some other standards may be applicable such as UL 1310,
"Class 2 Power Units" which also comply "with Class 2
voltage, current and volt-ampere limits as specified in
ANSI/NFPA 70, 'National Electrical Code'."
Note the reference to the power limits in the NEC.

Information is from the UL White Book.

Again you are posting nonsense.

Four months ago, in a thread about utility PF correction
caps, you told HeyBub "next time I'll be a lot more
careful." Obviously not.
Again.
G




  #43   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Suggestion for 24V/120V relay to control new outlet?

Twayne wrote:
You're right, I cited the wrong spec; it's probably actually something like
one of the 5085's. But I'm not tempted to refute anything you say because
you are still getting things terribly mixed up.


Translation: you are wrong but won't admit it.

At least you admitted when you were wrong about utility PF correction caps.

Perhaps you should brush up
on how to read these specs too. Like, parts 1 & 2 apply unless excepted by 3
and so forth.


I have no problem reading specs.

Like - from UL:
Class 2 transformers are listed under UL 1585, "Class 2 and Class 3
Transformers." They are power limited "in accordance with ANSI/NFPA 70,
‘National Electrical Code’ (NEC)"

Repeating again - from UL: The transformers are power limited "in
accordance with ANSI/NFPA 70, ‘National Electrical Code’ (NEC)"

Perhaps you should brush up on the English language.

Explain what makes a class 2 door bell circuit class 2.

Sorry; I don't have the time to mess with your refusal to get the proper
information assembled for the project at hand.


Describe your "project at hand". I want to make sure I never get
anywhere near it.

bud--


n ,
bud-- typed:
Twayne wrote:
In ,
bud-- typed:
Twayne wrote:
A "Class 2" xfmr is simply a double-insulated transformer
without an earth ground on its plug, nor a polarized
plug. A "Class 1" xfmr requires a third wire, the earth
ground pin on its plug. The "Class of xfmr is a UL/CSA
et al classification which approves the xfmr and nothing
else as safety approved.
The primary characteristic of class 1, 2, and 3 power
sources is that they are power limited. There is a
specified maximum voltage, current and power you can get
from the source. For a class 2 24V transformer the max
current is 8A - the maximum current you get if you short
circuit the transformer.
I think you're confused between class definitions for
Safety and what the NEC defines; they are different.

I think you're confused about nearly everything.

Class 1, 2, and 3 CIRCUITS are classified as
remote-control, signaling, and power-limited circuits in
the National Electrical Code (NEC).

Limiting the discussion to class 2, which many people are
familiar with (thermostat, doorbell):

Class 2 circuits are class 2 because they are _powered by a
class 2 power supply_.

Class 1 and 2 Power Supplies determines the insulation
PROPERTIES of a power supply and there is no Class 3. To
the layman, they either need the third ground wire or not
(1 & 2 respectively).

So if I buy a UL listed class 2 transformer, according to
you, it is not power limited and can not be used to power a
class 2 circuit. What a bizarre idea. Make that a stupid
idea.
No class 3? UL category XOKV - "TRANSFORMERS, CLASS 2 AND
CLASS 3".
The 8 Amp limitation IN NEC has nothing to do with UL/CSA
et al classifications. A transformer can output any
current it can be designed for as long as it meets the
insulation and overvoltage/current test specifications and
meet the safety requirements.

That will surprise UL.

Class 1, 2, 3 as used in the NEC as you can see above
is quite different. While saftey is of course a concern,
simply limiting an output to 8 amps would not deem it to
be "safe". The NEC is concerned with wiring, and the
Safety is concerned with safety. Two different worlds. A
google for UL 1459 might be enlightening for
you.

It might be a lot more enlightening for you.

UL 1459 is "Telephone power supplies" (and has probably
been withdrawn). You are probably the only person that
thinks we are talking about telephones.

Class 2 transformers are listed under UL 1585, "Class 2 and
Class 3 Transformers." (There is that pesky "class 3"
again.) They are power limited "in accordance with
ANSI/NFPA 70, National Electrical Code (NEC)"
Some other standards may be applicable such as UL 1310,
"Class 2 Power Units" which also comply "with Class 2
voltage, current and volt-ampere limits as specified in
ANSI/NFPA 70, 'National Electrical Code'."
Note the reference to the power limits in the NEC.

Information is from the UL White Book.

Again you are posting nonsense.

Four months ago, in a thread about utility PF correction
caps, you told HeyBub "next time I'll be a lot more
careful." Obviously not.
Again.
G


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Timed relay control Tom Gardner Metalworking 14 November 17th 07 06:44 AM
After Electrical panel install one 120V outlet now has 104 Volts jetskifast Home Repair 9 October 22nd 06 10:52 PM
Reconditioning Chattering Well Water Pump Control Box Relay? [email protected] Electronics Repair 2 August 27th 05 03:54 AM
Reconditioning Chattering Well Water Pump Control Box Relay? [email protected] Electronics Repair 0 August 26th 05 01:28 AM
Can I do this? Outlet with cable and 120v in it? Steve Home Repair 39 November 29th 04 04:46 PM


All times are GMT +1. The time now is 03:48 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"