Default What type of wire for 50A overhead service from house to garage?

What type of wire should I use to make a 50 foot over head run from the
house to the garage? This will be a 50A 240V circuit from the main house
panel. Right now we have separate service from the electric company to
the garage with a separate meter (1 meter for the house 1 for the
garage). The electric company now wants to charge a 30 dollar per month
service charge for the garage. We can't afford that. To go below ground
would we would have to deal with a 4 foot across driveway and a gas
line, that's why we want to go overhead. Do we need 4 conductor wire
that being 2 hots a neutral and a ground? What about 3 conductor (2 hots
and a neutral) and a ground rod at garage panel? Do we need to enclose
the wire in a pipe to run up the house then leave it open till it
reaches the garage then more pipe down to the garage entrance?
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default What type of wire for 50A overhead service from house to garage?


"gorehound" wrote in message
...
What type of wire should I use to make a 50 foot over head run from the
house to the garage? This will be a 50A 240V circuit from the main house
panel. Right now we have separate service from the electric company to the
garage with a separate meter (1 meter for the house 1 for the garage). The
electric company now wants to charge a 30 dollar per month service charge
for the garage. We can't afford that. To go below ground would we would
have to deal with a 4 foot across driveway and a gas line, that's why we
want to go overhead. Do we need 4 conductor wire that being 2 hots a
neutral and a ground? What about 3 conductor (2 hots and a neutral) and a
ground rod at garage panel? Do we need to enclose the wire in a pipe to
run up the house then leave it open till it reaches the garage then more
pipe down to the garage entrance?



I think you'd be better off going underground. You can bang a pipe under the
driveway. To go overhead, you'll need to run a conduit or ser cable from the
panel in the house up the side of the house to a service head. You'll need 4
conductor messenger cable to go from the house to the garage. Three
insulated and one bare. Then you need more conduit or SER cable at the
garage, from the second service head to it's panel, and you do need ground
rods


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default What type of wire for 50A overhead service from house to garage?


"gorehound" wrote in message
...
What type of wire should I use to make a 50 foot over head run from the
house to the garage? This will be a 50A 240V circuit from the main house
panel. Right now we have separate service from the electric company to the
garage with a separate meter (1 meter for the house 1 for the garage). The
electric company now wants to charge a 30 dollar per month service charge
for the garage. We can't afford that. To go below ground would we would
have to deal with a 4 foot across driveway and a gas line, that's why we
want to go overhead. Do we need 4 conductor wire that being 2 hots a
neutral and a ground? What about 3 conductor (2 hots and a neutral) and a
ground rod at garage panel? Do we need to enclose the wire in a pipe to
run up the house then leave it open till it reaches the garage then more
pipe down to the garage entrance?



*As RBM noted you will need to make two service entrances; one at each
building. You will not need a meter socket or disconnect outside since you
will have over current protection in each circuit breaker panel. For
overhead you can run multiplex wire which has the neutral as the support and
you would splice that at each end to the wire coming out of your service
head. You can use SE cable or conduit for the service entrance on each
building and you will need strong hooks to carry the weight of the overhead
wire. The overhead wire needs to be at least 12' high and cannot pass over
a pool. You will need 4 conductors and at least one ground rod at the
garage.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,331
Default What type of wire for 50A overhead service from house to garage?

John Grabowski wrote:
For overhead you can run multiplex wire which has the neutral as the
support


(not saying you are incorrect, just adding some info)

I just had a 200 amp service run to my garage and a pole moved. I asked
if the bare wire was aluminum (it looked like it was but I thought it
would stretch). He said it is aluminum with the center strand steel so
it holds the weight of all three wires.

To avoid having 2 meters and being charged a monthly service charge plus
a higher business rate for the garage, they installed what they call a
"current transformer" and put one meter out on the pole with the
transformer and jumpers and a blank where the old meter was. It cost me
a hundred or so dollars for the new service and even more for the
current transformer hook up, but it's cost will be made up in less than
1 year without the surcharge.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default What type of wire for 50A overhead service from house to garage?


"Tony" wrote in message
...
John Grabowski wrote:
For overhead you can run multiplex wire which has the neutral as the
support


(not saying you are incorrect, just adding some info)

I just had a 200 amp service run to my garage and a pole moved. I asked
if the bare wire was aluminum (it looked like it was but I thought it
would stretch). He said it is aluminum with the center strand steel so it
holds the weight of all three wires.

To avoid having 2 meters and being charged a monthly service charge plus a
higher business rate for the garage, they installed what they call a
"current transformer" and put one meter out on the pole with the
transformer and jumpers and a blank where the old meter was. It cost me a
hundred or so dollars for the new service and even more for the current
transformer hook up, but it's cost will be made up in less than 1 year
without the surcharge.



I think what you have is sometimes called a farm service. One meter on a
privately owned pole, and multiple overhead drops to different buildings. It
may be possible for the OP to do something like that, but typically this
stuff is determined by the serving utility company.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,331
Default What type of wire for 50A overhead service from house to garage?

RBM wrote:
"Tony" wrote in message
...
John Grabowski wrote:
For overhead you can run multiplex wire which has the neutral as the
support

(not saying you are incorrect, just adding some info)

I just had a 200 amp service run to my garage and a pole moved. I asked
if the bare wire was aluminum (it looked like it was but I thought it
would stretch). He said it is aluminum with the center strand steel so it
holds the weight of all three wires.

To avoid having 2 meters and being charged a monthly service charge plus a
higher business rate for the garage, they installed what they call a
"current transformer" and put one meter out on the pole with the
transformer and jumpers and a blank where the old meter was. It cost me a
hundred or so dollars for the new service and even more for the current
transformer hook up, but it's cost will be made up in less than 1 year
without the surcharge.



I think what you have is sometimes called a farm service. One meter on a
privately owned pole, and multiple overhead drops to different buildings. It
may be possible for the OP to do something like that, but typically this
stuff is determined by the serving utility company.


Possibly the same thing. The key difference is that the actual power I
use doesn't go through the meter. Just a small percentage from the
"current transformer" feeds the meter. If I pulled the meter I would
still have power. Re-reading your post I'll mention that I do not own
the pole.

The rules about the poles and wires here. Any trees before the
transformer the power co. will cut themselves (to avoid people like me
felling a tree onto the high voltage 17Kv lines). Any trees after the
transformer and meter pole, I am responsible for... sort of. If I cut a
tree and it downs my lines, I am responsible for the damage. But if I
first call the power co., they will comes and disconnect the lines, I
cut the tree, then they hook up the lines again, no charge. However if
a storm knocks down a tree which takes out the low voltage lines, then
they will repair no charge.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default What type of wire for 50A overhead service from house to garage?

John Grabowski wrote:

You will need 4 conductors and at
least one ground rod at the garage.


As both RBM and John said, starting with the 2008 NEC you need 4 wires,
one of which is a ground wire. When you run a ground wire you need to
remove the neutral-ground bond that should be in your existing garage
panel. Sometimes it is an easily seen strap from the neutral bar to the
enclosure. Often it is a hard to distinguish screw that looks like a
mounting screw for the neutral bar. The neutral bar should be isolated
from the enclosure/ground.

You should already have a ground rod at the garage - verify it is there.

--
bud--
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default What type of wire for 50A overhead service from house to garage?


"Tony" wrote in message
...
RBM wrote:
"Tony" wrote in message
...
John Grabowski wrote:
For overhead you can run multiplex wire which has the neutral as the
support
(not saying you are incorrect, just adding some info)

I just had a 200 amp service run to my garage and a pole moved. I asked
if the bare wire was aluminum (it looked like it was but I thought it
would stretch). He said it is aluminum with the center strand steel so
it holds the weight of all three wires.

To avoid having 2 meters and being charged a monthly service charge plus
a higher business rate for the garage, they installed what they call a
"current transformer" and put one meter out on the pole with the
transformer and jumpers and a blank where the old meter was. It cost me
a hundred or so dollars for the new service and even more for the
current transformer hook up, but it's cost will be made up in less than
1 year without the surcharge.



I think what you have is sometimes called a farm service. One meter on a
privately owned pole, and multiple overhead drops to different buildings.
It may be possible for the OP to do something like that, but typically
this stuff is determined by the serving utility company.


Possibly the same thing. The key difference is that the actual power I
use doesn't go through the meter. Just a small percentage from the
"current transformer" feeds the meter. If I pulled the meter I would
still have power. Re-reading your post I'll mention that I do not own the
pole.

The rules about the poles and wires here. Any trees before the
transformer the power co. will cut themselves (to avoid people like me
felling a tree onto the high voltage 17Kv lines). Any trees after the
transformer and meter pole, I am responsible for... sort of. If I cut a
tree and it downs my lines, I am responsible for the damage. But if I
first call the power co., they will comes and disconnect the lines, I cut
the tree, then they hook up the lines again, no charge. However if a
storm knocks down a tree which takes out the low voltage lines, then they
will repair no charge.


That all makes perfect sense. Usually if the service is over 200 amp, they
use current transformers, as you describe, with a bypass meter socket. In my
area in NY, the customer pays for everything, materials and labor, with the
exception of the current transformers and the actual meter. The utility
company won't even install the pole. I mean, you can't even pay them to do
it, it has to be done privately.


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default What type of wire for 50A overhead service from house to garage?


"Tony" wrote in message
...
RBM wrote:
"Tony" wrote in message
...
John Grabowski wrote:
For overhead you can run multiplex wire which has the neutral as the
support
(not saying you are incorrect, just adding some info)

I just had a 200 amp service run to my garage and a pole moved. I asked
if the bare wire was aluminum (it looked like it was but I thought it
would stretch). He said it is aluminum with the center strand steel so
it holds the weight of all three wires.

To avoid having 2 meters and being charged a monthly service charge plus
a higher business rate for the garage, they installed what they call a
"current transformer" and put one meter out on the pole with the
transformer and jumpers and a blank where the old meter was. It cost me
a hundred or so dollars for the new service and even more for the
current transformer hook up, but it's cost will be made up in less than
1 year without the surcharge.



I think what you have is sometimes called a farm service. One meter on a
privately owned pole, and multiple overhead drops to different buildings.
It may be possible for the OP to do something like that, but typically
this stuff is determined by the serving utility company.


Possibly the same thing. The key difference is that the actual power I
use doesn't go through the meter. Just a small percentage from the
"current transformer" feeds the meter. If I pulled the meter I would
still have power. Re-reading your post I'll mention that I do not own the
pole.

The rules about the poles and wires here. Any trees before the
transformer the power co. will cut themselves (to avoid people like me
felling a tree onto the high voltage 17Kv lines). Any trees after the
transformer and meter pole, I am responsible for... sort of. If I cut a
tree and it downs my lines, I am responsible for the damage. But if I
first call the power co., they will comes and disconnect the lines, I cut
the tree, then they hook up the lines again, no charge. However if a
storm knocks down a tree which takes out the low voltage lines, then they
will repair no charge.


That all makes perfect sense. Usually if the service is over 200 amp, they
use current transformers, as you describe, with a bypass meter socket. In my
area in NY, the customer pays for everything, materials and labor, with the
exception of the current transformers and the actual meter. The utility
company won't even install the pole. I mean, you can't even pay them to do
it, it has to be done privately.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default What type of wire for 50A overhead service from house to garage?

gorehound wrote:
What type of wire should I use to make a 50 foot over head run from the
house to the garage? This will be a 50A 240V circuit from the main house
panel. Right now we have separate service from the electric company to
the garage with a separate meter (1 meter for the house 1 for the
garage). The electric company now wants to charge a 30 dollar per month
service charge for the garage. We can't afford that. To go below ground
would we would have to deal with a 4 foot across driveway and a gas
line, that's why we want to go overhead. Do we need 4 conductor wire
that being 2 hots a neutral and a ground? What about 3 conductor (2 hots
and a neutral) and a ground rod at garage panel? Do we need to enclose
the wire in a pipe to run up the house then leave it open till it
reaches the garage then more pipe down to the garage entrance?


Update! Turns out the run was about 100'. We rented a trencher to do the
long run, and we used it to dig a trench beside the drive (unfortunately
not quite long enough) so we could lay the pie in to beat it under the
driveway. What we didn't think about was the swing factor for the
sledge, and had to dig back a few feet using the maddock because we
already took the trencher back. Pounding that pipe under the driveway
was not easy, but it worked. We used 6/3 UF to get from the house to the
garage. Tomorrow we will finish up and hopefully no fires!

Thanks for all of the suggestions!


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 82
Default What type of wire for 50A overhead service from house to garage?

#8 will handle 45 amps. #6 wil handle 60 amps.

"gorehound" wrote in message
...
gorehound wrote:
What type of wire should I use to make a 50 foot over head run from the
house to the garage? This will be a 50A 240V circuit from the main house
panel. Right now we have separate service from the electric company to
the garage with a separate meter (1 meter for the house 1 for the
garage). The electric company now wants to charge a 30 dollar per month
service charge for the garage. We can't afford that. To go below ground
would we would have to deal with a 4 foot across driveway and a gas line,
that's why we want to go overhead. Do we need 4 conductor wire that being
2 hots a neutral and a ground? What about 3 conductor (2 hots and a
neutral) and a ground rod at garage panel? Do we need to enclose the wire
in a pipe to run up the house then leave it open till it reaches the
garage then more pipe down to the garage entrance?


Update! Turns out the run was about 100'. We rented a trencher to do the
long run, and we used it to dig a trench beside the drive (unfortunately
not quite long enough) so we could lay the pie in to beat it under the
driveway. What we didn't think about was the swing factor for the sledge,
and had to dig back a few feet using the maddock because we already took
the trencher back. Pounding that pipe under the driveway was not easy, but
it worked. We used 6/3 UF to get from the house to the garage. Tomorrow we
will finish up and hopefully no fires!

Thanks for all of the suggestions!



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Low overhead garage door opener Steve Manes Home Repair 10 March 16th 17 05:14 PM
Running service from house to garage [email protected] Home Repair 23 March 19th 07 11:24 AM
Problems with Type J Halogen bulb in overhead light Petrel Home Repair 1 January 15th 07 09:52 PM
wiring a detached garage - bringing it into the house/service panel [email protected] Home Repair 6 October 28th 05 01:30 AM
Overhead electrical service to a storage shed Timothy J. Trace Home Repair 3 December 3rd 03 04:21 AM


All times are GMT +1. The time now is 10:40 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"