I have a Leviton GFI in my bathroom which I happened to test today
with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... |
#2
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
blueman writes:
I have a Leviton GFI in my bathroom which I happened to test today with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. CORRECTION, when I hold down the test button the lights show: off, yellow, red which in a normal situation would be signalling a Hot/Neutral reverse but is probably just an artifact of the test button shunting current. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... |
#3
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
In article on Thu, 23 Jul 2009
23:32:52 -0400, blueman wrote: Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? Your GFIs, both old and new, are fine. On a GFI, the tester built-in to the receptacle works by shunting some current from hot to neutral. Your hand held tester works a little differently - it shunts some current from hot to ground. Either there is a grounding problem on that circuit, or the hand held tester itself is faulty. -- Seth Goodman |
#4
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Fri, 24 Jul 2009 05:24:09 -0400, Seth Goodman
wrote: In article on Thu, 23 Jul 2009 23:32:52 -0400, blueman wrote: Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? Your GFIs, both old and new, are fine. On a GFI, the tester built-in to the receptacle works by shunting some current from hot to neutral. Less incompletely, hot on the LOAD side to neutral on the LINE side. Your hand held tester works a little differently - it shunts some current from hot to ground. Either there is a grounding problem on that circuit, or the hand held tester itself is faulty. |
#5
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "blueman" wrote in message ... I have a Leviton GFI in my bathroom which I happened to test today with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... *Pull out the GFI and use a pigtail socket and bulb to confirm that you have a functional ground. |
#6
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Jul 24, 9:36*am, "John Grabowski" wrote:
"blueman" wrote in message ... I have a Leviton GFI in my bathroom which I happened to test today with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. *But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... *Pull out the GFI and use a pigtail socket and bulb to confirm that you have a functional ground.- Hide quoted text - - Show quoted text - Suggestion/question?????. GFIs trip when there is a certain amount of (milliamps) unbalance between current flowing in the live and neutral conductors; true? If the tester itself use say LEDs which take a very small amounts of current maybe there is not enough (total) current flowing to unbalance the GFI? Not familiar with the circuit arrangement of the tester. Or as suggested the ground is imperfect. |
#7
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
*Pull out the GFI and use a pigtail socket and bulb to confirm that you have
a functional ground.- Hide quoted text - - Show quoted text - A GFI's operation has nothing to do with the ground. It monitors the current flowing throught the hot and neutral. |
#8
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
In article , Mike rock wrote:
*Pull out the GFI and use a pigtail socket and bulb to confirm that you have a functional ground. A GFI's operation has nothing to do with the ground. It monitors the current flowing throught the hot and neutral. If you'd read the entire thread, you would have seen that the OP stated that the GFCI trips normally when he presses the test button on the GFCI, but fails to trip when he presses the test button on his plug-in tester -- and you would have also seen an explanation of why this is so: the plug-in tester shunts current to *ground*, and *cannot* trip the GFCI unless there is a functional ground at the outlet. |
#9
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() |
#10
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 2009-07-24, blueman wrote:
But how does the GFI test button work? Does it really just test if the breaker works or does it have a way of testing that the current monitoring part works? The GFI uses a current transformer to detect a downstream imbalance between hot and neutral current. The test button has access to the hot and neutral both before and after this current transformer. So it shunts a small amount of current from the hot after the transformer to the neutral before the transformer (or vice versa, I don't know), which creates an imbalance in the current transformer. Cheers, Wayne |
#11
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
"John Grabowski" writes:
"blueman" wrote in message ... I have a Leviton GFI in my bathroom which I happened to test today with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... *Pull out the GFI and use a pigtail socket and bulb to confirm that you have a functional ground. BINGO - no *functional* ground. Though not clear why the gfi tester didn't read it as an open ground unless there was some "inducted" current flow from ground to neutral in the cable sheathing. Also, interestingly, a digital (not analog) ohmeter read 120v between hot and ground again maybe consistent with inducted current. But as always resistive loads (i.e. bulb on a pigtail) tell the truth. This all does make me worry though about the accuracy of the low-end GFI tester I have -- i.e., how many open grounds are there lurking somewhere in the house that the tester has failed to detect... I fixed the problem by tracing upstream where I found that the ground wire had broken off in the box. Problem solved & thanks for the help. |
#12
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
blueman writes:
"John Grabowski" writes: "blueman" wrote in message ... I have a Leviton GFI in my bathroom which I happened to test today with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... *Pull out the GFI and use a pigtail socket and bulb to confirm that you have a functional ground. BINGO - no *functional* ground. Though not clear why the gfi tester didn't read it as an open ground unless there was some "inducted" current flow from ground to neutral in the cable sheathing. Also, interestingly, a digital (not analog) ohmeter read 120v between hot and ground again maybe consistent with inducted current. But as always resistive loads (i.e. bulb on a pigtail) tell the truth. This all does make me worry though about the accuracy of the low-end GFI tester I have -- i.e., how many open grounds are there lurking somewhere in the house that the tester has failed to detect... Actually it is kind of ironic that while the GFI tester didn't detect a floating ground in its normal mode, it (indirectly) signalled a bad ground by failing to trip the GFI when the test button was pressed. Do better quality GFI testers do a better job of testing for *functional* grounds? Also this led me to experiment and I noticed that if the ground and neutral pin on the GFI tester are both wired to neutral then the GFI tests ok which in some ways is electrically understandable since ultimately the neutral and hots are bonded at the service entrance. However, it is not a code ground. Do better quality GFI testers have a way of testing for functional ground vs. neutral used as ground? (perhaps as a proxy they could measure resistance between neutral and ground???) |
#13
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Much safer, now. Good job.
-- Christopher A. Young Learn more about Jesus www.lds.org .. "blueman" wrote in message ... I fixed the problem by tracing upstream where I found that the ground wire had broken off in the box. Problem solved & thanks for the help. |
#14
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Jul 24, 4:01*pm, "Stormin Mormon"
wrote: Much safer, now. Good job. -- Christopher A. Young Learn more about Jesus *www.lds.org . "blueman" wrote in message ... I fixed the problem by tracing upstream where I found that the ground wire had broken off in the box. Problem solved & thanks for the help. Thanks for posting the outcome. A broken ground; glad the OP found it. BTW: I agree with the person who posted; Quote: "If you'd read the entire thread, you would have seen that the OP stated that the GFCI trips normally when he presses the test button on the GFCI, but fails to trip when he presses the test button on his plug-in tester -- and you would have also seen an explanation of why this is so: the plug-in tester shunts current to *ground*, and *cannot* trip the GFCI unless there is a functional ground at the outlet.". It seemed obvious the question was why didn't the 'test' feature of the 'tester' work as expected! Interesting thread and as often makes one think (and learn!). Thanks for posting the original question. |
#15
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
stan writes:
On Jul 24, 4:01*pm, "Stormin Mormon" wrote: Much safer, now. Good job. -- Christopher A. Young Learn more about Jesus *www.lds.org . "blueman" wrote in message ... I fixed the problem by tracing upstream where I found that the ground wire had broken off in the box. Problem solved & thanks for the help. Thanks for posting the outcome. A broken ground; glad the OP found it. BTW: I agree with the person who posted; Quote: "If you'd read the entire thread, you would have seen that the OP stated that the GFCI trips normally when he presses the test button on the GFCI, but fails to trip when he presses the test button on his plug-in tester -- and you would have also seen an explanation of why this is so: the plug-in tester shunts current to *ground*, and *cannot* trip the GFCI unless there is a functional ground at the outlet.". It seemed obvious the question was why didn't the 'test' feature of the 'tester' work as expected! Interesting thread and as often makes one think (and learn!). Thanks for posting the original question. Your welcome ![]() And I learned a lot too -- it is always sobering to learn the limitations of your test equipment (or any other limitations). I wonder how many professionals (e.g., electricians, home inspectors, city inspectors) let alone DIY'ers realize that: 1. A GFI tester can show the circuit being fine even though there is no functional ground. Similarly a (digital) multimeter can read the full 120V hot-to-ground. Both presumably due to induced currents. 2. The test button on a GFI can work also without a functional ground. It all makes sense retrospectively, but probably not something that most people think about... |
#16
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
blueman wrote:
I have a Leviton GFI in my bathroom which I happened to test today with my little 3 prong/3 lamp tester. The socket shows as being wired correctly (2 yellow lights, no red) but pressing the 'trip' button on my tester failed to trip the GFI (note when the trip button is depressed all 3 lights (yellow-yellow-red) light up on the tester). The test button on the GFI works fine though. Still figuring that something must be wrong with the GFI, I replaced it with a new one. The physical wiring is correct and again the tester shows it is wired correctly. Also, the little green LED on the GFI is lit presumably showing it is working. But again the trip button failed to trigger the GFI even though again the manual test button on the GFI worked. My GFI tester worked fine triggering the other 13 or so GFI's in my house. Any idea what could be happening here? Why would both the old and new GFI show as being wired correctly and yet fail to trip? I am stumped... Hmm, I'd measure Ohmage between ground and neutral with a meter on that outlet. Reading should be very close to zero Ohm. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
RCD tripping problem | UK diy | |||
house wired without separate ground - problem? | Home Repair | |||
problem with newly wired lights | UK diy | |||
Problem with TV not powering up correctly | Electronics Repair | |||
Weird problem with RCD tripping | UK diy |