Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#41
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 14, 12:20*am, w_tom wrote:
On Jul 13, 2:00 pm, Caesar Romano wrote: I have a Delta LA302R lightning arrestor http://www.deltala.com/prod01.htm#LA302R installed at my meter. How effective can I expect that to be? * *LA302R is called a single phaseprotector. *That means it connects one AC hot wire to earth. *The other phase would not have protection. However it also uses the number 125/250 *and phrase 'per pole' implying this is really a two phaseprotector. did they teach you that at big mac school? |
#42
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 15, 11:58*am, bud-- wrote:
The required religious mantra. The IEEE guide explains, for anyone who can think, that plug-in suppressors work primarily by CLAMPING the voltage on all wires (power and signal) to the common ground at the suppressor. They do not work primarily by earthing. The guide explains that earthing occurs elsewhere in the system. The guide also explains that if that energy is not earthed, then energy will find earth destructively via household appliances. Plug- in protectors without a properly earthed 'whole house' protector can even contribute to damage of adjacent appliances. But that knowledge would harm profits. Bud is a sales promoter for plug-in protectors. Bud again posts insults to protect those profit margins. ‘Clamping to nothing’, according to Bud, makes that surge energy just magically disappear. Energy does not disappear. Surge current must find earth ground. If not properly earthed at the service entrance, then that surge current will find many paths to earth inside the building. Page 42 Figure 8 - surge obtained earth ground 8000 volts destructively through a TV. Protector did nothing but make that possible. Protector was too close to appliances AND did not have the ‘always necessary’ short connection to earth. Bud calls that 8000 volt damage “effective protection”. If Bud was honest, then Bud would post manufacturer numeric specs that claim protection. Bud refuses. Bud cannot post what even the manufacturer will not claim. It does not have that short connection to earth. It cannot clamp surges harmlessly into earth. It does not even claim to provide that protection. It ‘clamps to nothing’. Bud even ignores demands for those numeric specifications. Bud cannot post was does not exist - effective protection. Profits are at risk. Bud is a sales promoter. Obscene profits are at risk if consumers got informed. Buy and earth one 'whole house' protector. Waste no money on plug-in protectors. Have protection that is massively superior to what $3000 of plug-in protectors might accomplish. Bud would have you spend tens or 100 times more money for his product - that does not even claim to provide that protection. A protector is only as effective as its earth ground. No earth ground means no effective protection. From the IEEE Standards - only place that IEEE makes recommendations in 'Static and Lightning Protection Grounding': Lightning cannot be prevented; it can only be intercepted or diverted to a path which will, if well designed and constructed, not result in damage. Even this means is not positive, providing only 99.5-99.9% protection. ... Still, a 99.5% protection level will reduce the incidence of direct strokes from one stroke per 30 years ... to one stroke per 6000 years ... Somehow by posting insults and providing no numeric specifications, Bud proves 'clamping to nothing' works? IEEE says otherwise. But popular myths are easily believed just like Saddam's WMDs. Which does the lurker believe? The facts - such as where does that energy get dissipated? Of half truth and insults from a plug-in protector sales promoter? Provides elsewhere in this discussion is an answer to the OP’s question about what is and is not sufficient earthing. Earthing provides protection which is why so many professionals discuss earthing (not plug-in protectors) extensively. Earth is where the surge gets dissipated harmlessly rather than inside household appliances. A protector is only as effective as its earth ground which is why all high reliability facilities put their protectors close to earth ground and separated from better protected electronics. Plug-in protectors do not make that energy magically disappear. Effective protection earths before a surge can enter the building. Protection inside all appliances is not overwhelmed. Protection that is 99+% effective. Where does the plug-in protector even claim that protection? Nothing claimed. No earth ground means no effective protection. Reality does not use insults as proof. An honest Bud would have posted those manufacturer specs that claim protection. He cannot post what does not exist. |
#43
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
On Jul 15, 11:58 am, bud-- wrote: The required religious mantra. The IEEE guide explains, for anyone who can think, that plug-in suppressors work primarily by CLAMPING the voltage on all wires (power and signal) to the common ground at the suppressor. They do not work primarily by earthing. The guide explains that earthing occurs elsewhere in the system. Bud is a sales promoter for plug-in protectors. .. Complete bullcrap. Lacking valid technical arguments poor w_ has to try to discredit anyone who exposes his drivel. .. Bud again posts insults to protect those profit .. Poor w_ is insulted by reality. .. If Bud was honest, then Bud would post manufacturer numeric specs that claim protection. Bud refuses. .. Posted often and ignored. For example a few months ago on this newsgroup: http://tinyurl.com/6alnza .. A protector is only as effective as its earth ground. No earth ground means no effective protection. .. The required statement of religious belief in earthing. Ho-hum - read the quote at the top. .. From the IEEE Standards - only place that IEEE makes recommendations in 'Static and Lightning Protection Grounding': .. The IEEE Emerald book ("IEEE Recommended Practice for Powering and Grounding Sensitive Electronic Equipment"), an IEEE standard, recognizes plug-in suppressors as an effective protection device. This is the most appropriate IEEE standard for protecting electronics. Poor w_’s religious blinders prevent him from seeing anything that conflicts with his religious belief in earthing. And the IEEE guide, which was published by the IEEE, says plug-in suppressors are effective. .. IEEE says otherwise. .. Never explained: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? .. But popular myths are easily believed just like Saddam's WMDs. .. w_ was chief advisor to W on Wmds. Note the corresponding complete lack of sources that agree with w_ that plug-in suppressors are NOT effective. .. Which does the lurker believe? .. I would believe the IEEE and NIST guides. Both say plug-in suppressors are effective. Then look at w_’s sources that say plug-in suppressors are NOT effective. Oops - there are none. And never answers to embarrassing questions: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? - Why does the NIST guide says plug-in suppressors are "the easiest solution"? – Why does SquareD say "electronic equipment may need additional protection by installing plug-in [suppressors] at the point of use." - Why does the IEEE guide says in its example "the only effective way of protecting the equipment is to use a multiport protector"? - How would a service panel suppressor provide any protection in the IEEE guide example? - Why does the IEEE Emerald book recognize plug-in suppressors as effective? -- bud-- |
#44
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 16, 1:26 pm, bud-- wrote:
Poor w_ is insulted by reality. ... The required statement of religious belief in earthing. Ho-hum - read the quote at the top. .... The IEEE Emerald book ("IEEE Recommended Practice for Powering and Grounding Sensitive Electronic Equipment"), an IEEE standard, recognizes plug-in suppressors as an effective protection device. This is the most appropriate IEEE standard for protecting electronics. Poor w_’s religious blinders prevent him from seeing anything that conflicts with his religious belief in earthing. The IEEE says more than Bud's half truths. Amazing how a salesman will say anything to promote a product. One type of surge typically causes no damage. This surge made irrelevant by protection inside all appliances (and by a 'whole house' protector). A surge that creates, at most, hundreds of volts. Industry standards even in 1970 required electronics to withstand even 600 volts without damage. Some will install a plug-in protector for this surge anyway. A typically destructive surge arrives on any or all incoming wires - seeking earth ground. Shunt some wires together with a plug-in protector. That thousands of volts are shunted (clamped) on more or all wires and still seeking earth ground. Surge current on any one or all wires still must find a conductive path to earth. 8000 volt damage to an adjacent TV resulted. Same surge made irrelevant – does not overwhelm protection inside all appliances - when using only ‘whole house’ protector. Earthing where a typically destructive surge would enter a building - the service entrance – means tens of thousand of amps gets harmlessly earthed either by a direct wire connection (cable TV, satellite dish, TV antenna), or via a 'whole house' protector (telephone, AC electric). A surge not inside the building does not overwhelm protection inside appliances - does not cause surge damage. Every responsible source says surge energy must be dissipated harmlessly in earth. Well proven principles for the past 100 years define a single point earth ground and short connection to that electrode. Every Bud's citation even says what an effective protector does: divert (clamp, connect, shunt) surge energy to earth. But Bud is a salesman. He must twist anything - quote out of context - post insults - say anything to promote obscenely profitable plug-in protectors. Bud will say anything to avoid what even his NIST citation says: You cannot really suppress a surge altogether, nor "arrest" it. What these protective devices do is neither suppress nor arrest a surge, but simply divert it to ground, where it can do no harm. How does surge energy just disappear? Bud says 'clamping to nothing' will somehow stop, absorb, or make imaginary what even three miles of sky could not stop. Wow. Bud knows magic. Professional papers say that is impossible. What Bud also ignores. A 'whole house' protector is secondary protection. Homeowners are encouraged to inspect their primary protection system: http://www.tvtower.com/fpl.html If Bud admitted that, then Bud must admit what provides surge protection: earth ground. Bud again refused to provide a manufacturer spec that claims protection. Why? No plug-in protector claims such protection. None. Bud refuses to provide protection specs because those specs just don't exist. Just another fact that Bud forgot to mention while so busy posting insults. OP asked for information on earthing. Easy. Many industry professionals who install effective surge protection were cited. Bud could not quote them. Bud claims surge protection happens without earthing - 'clamping to nothing'. Professionals define what makes surges irrelevant and what makes protectors more effective. Install and connect protectors to a single point earth ground. Learn principles of earthing from numerous industry professionals in a reply to Caesar Romano - the OP. A protector is only as effective as its earth ground; where surge energy must be dissipated. A fact that does not require supporting insults. |
#45
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
On Jul 16, 1:26 pm, bud-- wrote: Poor w_ is insulted by reality. ... The required statement of religious belief in earthing. Ho-hum - read the quote at the top. .... The IEEE Emerald book ("IEEE Recommended Practice for Powering and Grounding Sensitive Electronic Equipment"), an IEEE standard, recognizes plug-in suppressors as an effective protection device. This is the most appropriate IEEE standard for protecting electronics. Poor w_’s religious blinders prevent him from seeing anything that conflicts with his religious belief in earthing. The IEEE says more than Bud's half truths. .. Never explained: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? - Why does the IEEE guide says in its example "the only effective way of protecting the equipment is to use a multiport protector"? - How would a service panel suppressor provide any protection in the IEEE guide example? - Why does the IEEE Emerald book recognize plug-in suppressors as effective? .. Bud will say anything to avoid what even his NIST citation says: .. What does the NIST guide really say about plug-in supprssors? "One effective solution is to have the consumer install" a multiport plug-in suppressor. .. Bud again refused to provide a manufacturer spec that claims protection. .. Ho-hum. Provided and ignored, as usual. .. A protector is only as effective as its earth ground .. The required statement of religious belief in earthing. Still never seen - a source that say plug-in suppressors are NOT effective. Poor w_ can’t even find anyone who agrees with him on the internet. Still never answered - embarrassing questions: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? - Why does the NIST guide says plug-in suppressors are "the easiest solution"? – Why does SquareD say "electronic equipment may need additional protection by installing plug-in [suppressors] at the point of use." - Why does the IEEE guide says in its example "the only effective way of protecting the equipment is to use a multiport protector"? - How would a service panel suppressor provide any protection in the IEEE guide example? - Why does the IEEE Emerald book recognize plug-in suppressors as effective? – Why does the NIST guide say "One effective solution is to have the consumer install" a multiport plug-in suppressor. For real science read the NIST and IEEE guides. Both say plug-in suppressors are effective. -- bud-- |
#46
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 17, 6:35*am, wrote:
Bud is not a sales promoter for anything. He's doing a thankless job pointing out to unsupecting casual readers here that you are a demented loon who spouts endless falsehoods, and potentially dangerous advice that you can't substantiate. And your technical proof is where? Cited was professional after professional. Numerous factilities where surge damage cannot and does not happen were exampled. How factilities are corrected when surge damage does happen demonstrated. Provided were pinciples used for 100 years to make surge damage - even direct lightning strike - irrelevant. Requested are numeric specs from any plug-in manufacturer that claims protection from each type of surge. Oh. No plug-in protector manufacturer claims such protection? So what does post? Over the years, repeatedly posts insults. Yes, a majority also believed Saddam had WMDs using logic. Where does salty post any facts, citations, or personal design experience? Some (ie salty) will blindly believe the first thing said: Saddam has WMDs and the miracle of plug-in protectors. . A protector is only as effective as its earth ground. Each layer of protection is defined by the one always required component - earthing electrode. Surge energy must be earthed before entering a building. Plug-in protectors may even provide surges with destructive paths to earth - Page 42 Figure 8. Facts posted without insults and that contradict half truths from a sales promoter. A protector is only as effective as its earth ground. How to identify ineffective (and highly profitable) protectors? 1) No dedicated earthing wire. 2) Manufacturer avoids all discussion about earthng. No wonder cannot provide those numeric spec numbers. Plug-in protectors don't claim protection AND do meet every indicator of ineffective protection. The OP asked for and obtained information on earthing. Numerous surge protector professional were quoted. Why do professionals discuss earthing extensively? Earth ground is where surge energy must be harmlessly dissipated. was too busy insulting rather than learn the science. http://www.harvardrepeater.org/news/lightning.html Well I assert, from personal and broadcast experience spanning 30 years, that you can design a system that will handle *direct lightning strikes* on a routine basis. It takes some planning and careful layout, but it's not hard, nor is it overly expensive. At WXIA-TV, my other job, we take direct lightning strikes nearly every time there's a thunderstorm. Our downtime from such strikes is almost non-existant. The last time we went down from a strike, it was due to a strike on the power company's lines knocking *them* out, ... Since my disasterous strike, I've been campaigning vigorously to educate amateurs that you *can* avoid damage from direct strikes. The belief that there's no protection from direct strike damage is *myth*. ... The keys to effective lightning protection are surprisingly simple, and surprisingly less than obvious. Of course you *must* have a single point ground system that eliminates all ground loops. And you must present a low *impedance* path for the energy to go. That's most generally a low *inductance* path rather than just a low ohm DC path. Just another professional who learned how to make surge damage irrelevant and who must insult. |
#47
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 17, 10:59*am, w_tom wrote:
On Jul 17, 6:35*am, wrote: Bud is not a sales promoter for anything. He's doing a thankless job pointing out to unsupecting casual readers here that you are a demented loon who spouts endless falsehoods, and potentially dangerous advice that you can't substantiate. * And your technical proof is where? The IEEE is good enough for everyone here but W_. They show plug-in surge protectors being used. As for technical proof, where is W_'s that says plug-in surger protectors offer no protection and actually cause damage. But has asked for that about 20 times now, but W_ hasn't provided a single source that says plug-ins are useless and destructive. Aside from exchanging specific points which go nowhere, I think W_'s whole approach to facts and how to choose facts to support his arguments leaves one questioning his basic reasoning and judgement. Case in point, W_ posts a list of many "responsible" surge protection companies that offer whole house protectors, while disparaging other companies that offer plug-ins as selling ineffective and damaging products that don't work. The obvious point W_ is attempting to make is that these responsible companies know about surge protection and only make whole house type protectors. Yet I pointed out months ago that every one of the companies on W_'s list of "responsible" companies, except one, ALSO MAKES AND SELLS PLUG-IN surge protectors. I even provided links to the plug-in products. Now, with that attempt at separating "responsible" from supposedly irresponsible companies selling fraudulent products so thoroughly demolished, any reasonably logical person would never try to bring it up again to support their position. But W_ continues to do it, rattling of the same list of supposedly responsible companies, ignoring the fact that they also make plug-ins. One can only question the logic and reasoning processes used by such a person. *Cited was professional after professional. *Numerous factilities where surge damage cannot and does not happen were exampled. *How factilities are corrected when surge damage does happen demonstrated. Provided were pinciples used for 100 years to make surge damage - even direct lightning strike - irrelevant. * Requested are numeric specs from any plug-in manufacturer that claims protection from each type of surge. *Oh. *No plug-in protector manufacturer claims such protection? *So what does post? *Over the years, repeatedly posts insults. Yes, a majority also believed Saddam had WMDs using logic. Where does salty post any facts, citations, or personal design experience? *Some (ie salty) will blindly believe the first thing said: Saddam has WMDs and the miracle of plug-in protectors. . * A protector is only as effective as its earth ground. Each layer of protection is defined by the one always required component - earthing electrode. *Surge energy must be earthed before entering a building. Plug-in protectors may even provide surges with destructive paths to earth - Page 42 Figure 8. *Facts posted without insults and that contradict half truths from a sales promoter. * A protector is only as effective as its earth ground. * How to identify ineffective (and highly profitable) protectors? *1) No dedicated earthing wire. *2) Manufacturer avoids all discussion about earthng. *No wonder cannot provide those numeric spec numbers. *Plug-in protectors don't claim protection AND do meet every indicator of ineffective protection. * The OP asked for and obtained information on earthing. *Numerous surge protector professional were quoted. *Why do professionals discuss earthing extensively? *Earth ground is where surge energy must be harmlessly dissipated. was too busy insulting rather than learn the science. http://www.harvardrepeater.org/news/lightning.html Well I assert, from personal and broadcast experience spanning 30 years, that you can design a system that will handle *direct lightning strikes* on a routine basis. It takes some planning and careful layout, but it's not hard, nor is it overly expensive. At WXIA-TV, my other job, we take direct lightning strikes nearly every time there's a thunderstorm. Our downtime from such strikes is almost non-existant. *The last time we went down from a strike, it was due to a strike on the power company's lines knocking *them* out, ... Since my disasterous strike, I've been campaigning vigorously to educate amateurs that you *can* avoid damage from direct strikes. The belief that there's no protection from direct strike damage is *myth*. ... The keys to effective lightning protection are surprisingly simple, and surprisingly less than obvious. Of course you *must* have a single point ground system that eliminates all ground loops. And you must present a low *impedance* path for the energy to go. That's most generally a low *inductance* path rather than just a low ohm DC path. * Just another professional who learned how to make surge damage irrelevant and who must insult.- Hide quoted text - - Show quoted text - |
#48
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 17, 1:32 pm, wrote:
The IEEE is good enough for everyone here but W_. They show plug-in surge protectors being used. As for technical proof, where is W_'s that says plug-in surger protectors offer no protection and actually cause damage. We discovered two plug-in protectors earthing lightning destructively into two powered off, networked computers. A hot (black) wire surge that probably would have been made irrelevant by the power supply, instead, was shunted around both supplies, into motherboard, out network, and to earth ground destructively via a third computer. But that is obvious. Any surge permitted inside the building means surges can find destructive path to earth via appliances. Other examples have also been observed. Meanwhile Page 42 Figure 8 shows same. Surge energy was permitted inside a building because only plug-in protectors were used. Plug-in protector does not even claim to protect from a typically destructive surge. Plug-in protectors did not stop, block, absorb or make the surge disappear. 'Clamping to nothing' only permitted surge damage. Instead, that surge energy was earthed 8000 volts destructively via the adjacent TV. What kind of protection is that? Ineffective protection that trader must ignore. But again, trader misrepresents the facts. Nobody said "plug-in surge protectors offer no protection". That is trader again reading only what he wants to see – what he must read only to argue. Plug-in protectors protect from surges that typically do no damage. Plug-in protectors protect from surges made irrelevant by protection already inside appliances AND made irrelevant by one 'whole house' protector. Why spend $3000 in plug-in protectors (as Bud says is necessary) when one 'whole house' protector provides the same protection – and other protection? Obtain same protection for tens or 100 times less money. Meanwhile a 'whole house' protector also protects from surges that typically do cause damage. Where is that spec for ANY plug-in protector that claims to protect from a type of surge that typically causes damage? No such numeric spec exists because no plug-in protector claims to protect from the typically destructive surge. How do we know? Every responsible source including IEEE Standards (where IEEE makes recommendations) state what the effective protector must do. Plug-in protectors do not do what effective protectors do. Of course, trader is too emotional to read these facts. These facts are posted for others who would learn science - who do not worship what is promoted by retail salesman. From IEEE Std 141 (Red Book):: In actual practice, lightning protection is achieve by the process of interception of lightning produced surges, diverting them to ground, and by altering their associated wave shapes. From IEEE Emerald Book: It is important to ensure that low-impedance grounding and bonding connections exist among the telephone and data equipment, the ac power system's electrical safety-grounding system, and the building grounding electrode system. ... Failure to observe any part of this grounding requirement may result in hazardous potential being developed between the telephone (data) equipment and other grounded items that personnel may be near or might simultaneously contact. IEEE Green Book (IEEE 142) entitled 'Static and Lightning Protection Grounding': Lightning cannot be prevented; it can only be intercepted or diverted to a path which will, if well designed and constructed, not result in damage. Even this means is not positive, providing only 99.5-99.9% protection. ... Still, a 99.5% protection level will reduce the incidence of direct strokes from one stroke per 30 years ... to one stroke per 6000 years ... Yes, IEEE says you can use plug-in protectors. But to protect from surges that typically do damage. IEEE lists what is necessary to provide that protection. Only 'whole house' protectors provide that earthing. No plug-in protector meets those IEEE requirements. Yes you can also install equipment to protect from gamma rays or nuclear electromagnetic pulses. IEEE even says how that works. trader says that provide gamma ray protection is also surge protection? That is trader's reasoning. The IEEE says what protection systems must do for effective surge protection. No plug-in protector does that. No plug- in protector claims to do that. Only protectors that earth surge energy harmless in earth: 'whole house' protectors. Only protectors always used when surge damage is not acceptable - 'whole house' protector. What is always required when using plug-in protectors? A properly earthed 'whole house' protector. What does what any plug-in protector might do? A properly earthed 'whole house' protector. What makes all plug-in protector functions redundant - wasted money? A 'whole house' protector. What does Sun Microsystems, the IEEE, NIST, US Air Force, QST (the ARRL), Dr Kenneth Schneider, Electrical Engineering Times, Schmidt Consulting, Polyphaser's highly regarded application notes, a station engineer from WXIA-TV, engineers who eliminated damage to Orange County FL emergency response facilities, every telephone company, commercial broadcasters, nuclear hardened radio stations, etc all require for surge protection? Plug-in protectors do not provide sufficient protection. All require earthing and protectors that shunt (connect, divert, clamp) to earth ground. In every case, plug- in protectors do not provide that protection. Meanwhile another highly regarded IEEE author notes the problem with plug-in (point of connection) protectors. In his 1995 IEEE paper, Martzloff stated as his very first conclusion: Conclusion: 1) Quantitative measurements in the Upside-Down house clearly show objectionable difference in reference voltages. These occur even when or perhaps because, surge protective devices are present at the point of connection of appliances. How many sources does trader ignore? Plug-in protectors can contribute to electronics damage. Plug-in protectors do not even claim to protect from typically destructive surges. Surges that a plug-in protector does protect from are 1) typically not destructive, 2) made irrelevant by protection inside all appliances, and 3) made irrelevant by one 'whole house' protector. Yes, even IEEE says you can buy plug-in protectors. IEEE then shows why plug-in protectors do not provide protection required by all consumers. IEEE even shows how plug-in protectors can contribute to appliance damage. Meanwhile, if plug-in protectors provide protection, then trader posted numeric specifications provided by that manufacturer. Why do no plug-in protectors list protection from each type of surge? No provided by a plug-in protector is protection from surges that typically are destructive. How many IEEE and other sources say this? Thousands that trader must ignore. One 'whole house' protector, without or without plug-in protectors, is the 99% protection defined by IEEE. But effective protectors do have the massive profit margin and are not recommended by the naive. Trader - why do you recommend consumers waste tens or 100 times more money on a solution that does not even claim to provide protection. Oh. Trader - where are those plug-in protector specs that even claim to provide effective protection? Oh. Trader knows that protection must exist. Trader need not first learn engineering facts? Just because IEEE recommends band pass filters for RFI also proves that RFI filters provide surge protection? That also is trader's reasoning. Plug-in protector that cost tens or 100 times more money do not have and cannot provide what the IEEE requires for effective protection – a low impedance connection to single point earth ground. Naysayers instead want to hype what protects from irrelevant surges and does not protect from destructive surges The OP asked what any informed consumer would ask. How do we install, upgrade, or inspect what provides surge protection - earth ground? How to obtain effective earthing for protection was posted in reply to the OP - Caesar Romano. Effective surge protection means surge energy is not inside a building - is instead dissipated harmlessly in earth. Where is the plug-in protector that claims to do that? No – not one – plug-in protectors makes such claims in its specifications. No earth ground means no effective protection. |
#49
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
On Jul 17, 1:32 pm, wrote: The IEEE is good enough for everyone here but W_. They show plug-in surge protectors being used. As for technical proof, where is W_'s that says plug-in surger protectors offer no protection and actually cause damage. Nobody said "plug-in surge protectors offer no protection". .. "No earth ground means no effective protection." .. Why spend $3000 in plug-in protectors (as Bud says is necessary) one 'whole house' protector provides the same protection .. bud does not say that is what is necessary. (w_ is sooo dumb.) And repeating: What does the NIST guide say? "Q - Will a surge protector installed at the service entrance be sufficient for the whole house? A - There are two answers to than question: Yes for one-link appliances [electronic equipment], No for two-link appliances [equipment connected to power AND phone or cable or....]. Since most homes today have some kind of two-link appliances, the prudent answer to the question would be NO - but that does not mean that a surge protector installed at the service entrance is useless." .. Where is that spec for ANY plug-in protector that claims to protect from a type of surge that typically causes damage? .. Specs provided often and ignored - including in this thread. .. From IEEE Emerald Book: .. Poor w_. Religious fanaticism can be so debilitating. From the Emerald Book: Multiport surge suppressor: "A surge-protective device used for connecting equipment to external systems whereby all conductors connected to the protected loads are routed, physically and electrically, through a single enclosure with a shared reference point between the input and output ports of each system." .. Meanwhile another highly regarded IEEE author notes the problem with plug-in (point of connection) protectors. In his 1995 IEEE paper, Martzloff stated as his very first conclusion: .. The village idiot always forgets to mention that Martzloff said in the same document: "Mitigation of the threat can take many forms. One solution. illustrated in this paper, is the insertion of a properly designed [multiport plug-in surge suppressor]." In 2001 Martzloff wrote the NIST guide which also says plug-in suppressors are effective. .. How many IEEE and other sources say this? Thousands that trader must ignore. .. How many IEEE and other sources say this? Thousands that w_ must ignore. .. No earth ground means no effective protection. .. And the required religious mantra. But still never seen - a source that agrees with w_ that plug-in suppressors are NOT effective. Why doesn’t anyone agree with you w_??? I am beginning to have doubts about what you have been saying. And still never answered - embarrassing questions: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? - Why does the NIST guide says plug-in suppressors are "the easiest solution"? – Why does SquareD say "electronic equipment may need additional protection by installing plug-in [suppressors] at the point of use." - Why do your "responsible manufacturers" make plug-in suppressors? - Why does the IEEE guide says in its example "the only effective way of protecting the equipment is to use a multiport protector"? - How would a service panel suppressor provide any protection in the IEEE guide example? - Why does the IEEE Emerald book recognize plug-in suppressors as effective? – Why does the NIST guide say "One effective solution is to have the consumer install" a multiport plug-in suppressor. Why can’t you answer simple questions w_??? For real science read the NIST and IEEE guides. Both say plug-in suppressors are effective. -- bud-- |
#50
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
Requested are numeric specs from any plug-in manufacturer that claims protection from each type of surge. Please list the exact specifications you desire and an example of a protection claim that would satisfy you. Thanks, Doug |
#51
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
On Jul 12, 9:04Â*am, "CL \"dnoyeB\" Gilbert" wrote: I don't follow this example you keep giving. Â*Seems like your saying a device adjacent to a protected device got damaged!? IEEE example on Page 42 Figure 8 shows a protector too far from earth ground. A surge was not earthed (energy diverted into earth) before entering the building. So the surge arrived at a plug-in surge protector. What do surge protectors do? Shunt (distribute, connect, clamp) that energy on all other wires. Well, that surge still must find earth ground. Since the wire back to the breaker box is maybe 50 feet long, then that surge voltage is so high as to find another path to earth: 8000 volts destructively through the adjacent TV. In an obvious example, lightning incoming on AC electric was shunted to all other wires by two plug-in protectors. Surge on the black wire was shunted to the green wire, into two adjacent, powered off computers, out via NIC cards, into a third powered off computer, and to earth via modem and telephone line. We literally located and replaced every IC that conducted the surge to make all computers functional. Surge not earthed at a service entrance (no 'whole house' protector) means a surge is inside the building finding other paths to earth. In this case, surge found earth ground via three powered off computers because the plug-in protector connected an AC hot (black) wire surge directly into computer motherboards. If the computer was off then there should be no current path through it. You mean it was in soft-off mode. Furthermore, you gave your whole argument away when you introduced the phone line path to ground. most likely that is where it entered. A phone line does not provide a better path to ground than the house ground.. Sure the surge gets dumped from one wire (say black) into another wire in the suppressor. However, the other device is also connected to the black wire and it already has to deal with the surge with 0 protection. The devices are already parallel. So I fail to see how this adds anything to the other device being damaged. Since we have 3 phase power, lets say the surge came in on 1 source wire. Then the surge was attempted to be dumped into ground/neutral. Some of that current can pass into adjacent device if ground/neutral cant sink all the load. So we are back to the question of the quality of the main path to ground vs. other paths. And the 3 phases should only mix in the fuse panel or at 220 devices. I think you misinterpreted the example. Probably it was talking about surges entering on auxiliary lines like Cable and phone. I agree a cable/phone surge suppressor is going to potentially introduce components isolated from the phone/cable line to surges that came in on the phone/cable line. Again, to the degree the ground can't sink the load. |
#52
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
I had several components in my house protected by these local devices. One
day lightning struck near by. I saw a flash behind my computer upstairs. My wife saw one at the TV downstairs. Both had surge suppressors. Everything still worked, but internet was down. I checked later to see what happened. My cable modem was fried. My router was also fried. After I checked further I noticed the cable company did not ground the cable outside of my house. If it were today I would sue the for both the equipment and the hazard since I have pre-paid legal... The came out and properly grounded the cable. CL |
#53
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
A protector is only as effective as its earth ground. Each layer of protection is defined by the one always required component - earthing electrode. Every plug-in surge protector has at least one path to earth -- the neutral line which is bonded to ground at the panel. You're right when you say a better ground makes for better protection. You're flat wrong when you extend that to imply plug in protectors are ineffective. Surge energy must be earthed before entering a building. Indeed it is better to keep surge energy out of a building. But "must" is way too strong. Even a panel protector does not keep it out of the building if the panel is inside. Plug-in protectors may even provide surges with destructive paths to earth - Page 42 Figure 8. Facts posted without insults and that contradict half truths from a sales promoter. As I'm sure you have read, the first line of body text after the diagram says "Figure 8 shows a very common improper use of multiport protectors that does not fully protect against lightning damage because of this effect." So the article attributes the failure to user error, not a failure of the protector. -- Doug |
#54
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 18, 2:59 pm, Douglas Johnson wrote:
Please list the exact specifications you desire and an example of a protection claim that would satisfy you. Cited are what is required by numerous industry standards, publications and professional experience. For example, two 'top of the front page' articles in Electrical Engineering Times entitled "Protecting Electrical Devices from Lightning Transients" define what provides protection. Required is a low impedance connection to earth - to shunt and dissipate surge energy harmlessly: http://www.planetanalog.com/showArti...leID=201807830 The inductance of a wire is predominately related to its length and weakly related to its diameter. Why do plug-in protectors have all but no earth connection? Wire impedance. Whereas a plug-in protector may be connected less than 0.2 ohm resistance to earth; it may be 120 ohms impedance. Even a trivial 100 amp surge would put something less than 12,000 volts between protector and breaker box. AC electricity about wire resistance. Surges are about wire impedance - which is why EE Times discusses impedance - not resistance. An AC wall receptacle is only a safety (or equipment) ground; not earth ground. It has low resistance and excessively high impedance. Why do industry professionals discuss wire impedance whereas plug-in promoters do not? Well known for generations, every foot of wire increases wire impedance adversely. Even sharp wire bends increase wire impedance; compromise the earthing. How many sharp wire bends from a wall receptacle safety ground to breaker box? 50? Wall receptacle provides safety ground; not earth ground. An effective protector requires that short connection to earth. Even wire splices can unacceptably increase wire impedance - but not resistance. User error. User has installed a protector that is too far from earth ground (therefore all but no earthing) and too close to appliances. Plug-in protectors without a properly earthed 'whole house' protector means a protector may even earth surges 8000 volts destructively through adjacent appliances. How do we eliminate this failure? Properly earth one 'whole house' protector. Surge energy must be kept out of the building. Also necessary is the single point earth ground - what every incoming utility wire in every cable must connect to: Lightning is essentially a current impulse which is trying to return to earth. Why was lightning striking Ben Franklin's church steeples? Even wood and other household materials are electrical conductors. Just more reasons why protection inside the building is complicated and compromised; why surges must be earthed outside the building. Practical application of the connection and electrode. Low impedance demands a ground wire typically 'less than 10 feet from each utility wire (in every cable) to earth ground. Some of my best experiences involved a less than three foot connection to earth. Sharp wire bends, passing through metallic sheets or conduits, and splices will also compromise protection. So that wire does not induce surges on other wires, grounding wire is routed separated from other non-grounding wires (just another reason why Romex ground wire does not provide effective earthing). All is accomplished (often trivial) at the service entrance with proper planning. How good must an earthing electrode be? Locations with average lightning storms and conductive earth can be earthed by a 10 foot ground rod. Others who want an even batter protector expands that earthing electrode. Better conductivity and equipotential means better protection. To you, that means installing a best single point ground. Best solution in low conductive (ie sandy) soil for a high lightning area is why massive earthing electrodes are installed - ie Ufer or halo (perimeter) grounds. Better earthing means a more effective protector: http://members.aol.com/gfretwell/ufer.jpg http://scott-inc.com/html/ufer.htm http://www.psihq.com/iread/ufergrnd.htm What most determines protector effectiveness? Its earthing. When surge damage results, ask where earthing is inferior or compromised; as discussed on 14 Jul 2008 at: http://tinyurl.com/6bc2jw |
#55
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 18, 2:59 pm, Douglas Johnson wrote:
Please list the exact specifications you desire and an example of a protection claim that would satisfy you. In most cases, upgrading earthing to post 1990 National Electrical Code provides a massive improvement - over 90% of what might be best achieved. Earthing to a water pipe on the other side of the basement is woefully insufficient; all but no earthing. To achieve maybe a single digit percent improvement, massively expand an earthing system. Another reason to enhance that earthing system is to correct unexpected problems that might compromise the single point earth ground (again, see that 14 Jul discussion). Like a house foundation, earthing is the foundation of any protection system. Any wire that might carry a surge into the building must dump surge energy harmless into earth. If that connection is via a protector, then we want a protector that will earth direct lightning strikes without damage. Minimally sized 'whole house' protectors for AC electric start at 1000 joules and 50,000 amps. Don't let those numbers also on plug-in protectors fool you. A 'whole house' protector uses all joules during protection. Plug-in protectors do not. Since an average surge is 20,000 amps and since that surge will also be seeking other homes, then a 50,000 amp 'whole house' protector is minimally sufficient. Joules is a ballpark measurement for protector life expectancy. We expect a protector to last over ten years without ever failing. Properly sized (effective) protectors only degrade. Remain functional for 10+ years and do not fail catastrophically. More joules exponentially increase a protector's life expectancy. Whereas quality of and connection to earth ground determines a protector's effectiveness during those critical microseconds; joules determines whether the protector is functional for decades. |
#56
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
[Third of three posts]
On Jul 18, 2:59 pm, Douglas Johnson wrote: Please list the exact specifications you desire and an example of a protection claim that would satisfy you. When one says, "My protector sacrificed itself to save my computer". Reality: a protector abandoned the computer. Computer saved itself from a surge so trivial as to destroy the grossly undersized protector. Previously listed were more responsible manufacturers that offer 'whole house' protectors. The responsible list is long. Includes just about every major electrical equipment supplier including Leviton, Square D, Cutler-Hammer, Siemens, Keison, GE, etc. Some 'whole house' protectors selected randomly: http://www.deltala.com/prod01.htm#LA302R http://www.smarthome.com/4860.html http://www.keison.co.uk/furse/furse06.htm In that 14 July discussion, every incoming wire must be integrated into a secondary protection system. Even network wires between buildings. Even TV and satellite dish antenna wires are earthed before entering. The primary protection system also should be inspected. First Energy customers, in particular, should give special attention to their primary protection system. Surge protection to make direct lightning strike irrelevant means protection 'system' is sufficient for most every type of surge. Surge damage is routinely made irrelevant for less money if not using plug- in protectors. A direct lightning strike is the ultimate system test. No damage should ever result - even to protectors. If damage occurs, ask why that surge was not earthed; why it was permitted inside a building. |
#57
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
[Third of three posts]
On Jul 18, 2:59 pm, Douglas Johnson wrote: Please list the exact specifications you desire and an example of a protection claim that would satisfy you. When one says, "My protector sacrificed itself to save my computer". Reality: a protector abandoned the computer. Computer saved itself from a surge so trivial as to destroy the grossly undersized protector. Previously listed were more responsible manufacturers that offer 'whole house' protectors. The responsible list is long. Includes just about every major electrical equipment supplier including Leviton, Square D, Cutler-Hammer, Siemens, Keison, GE, etc. Some 'whole house' protectors selected randomly: http://www.deltala.com/prod01.htm#LA302R http://www.smarthome.com/4860.html http://www.keison.co.uk/furse/furse06.htm In that 14 July discussion, every incoming wire must be integrated into a secondary protection system. Even network wires between buildings. Even TV and satellite dish antenna wires are earthed before entering. The primary protection system also should be inspected. First Energy customers, in particular, should give special attention to their primary protection system. Surge protection to make direct lightning strike irrelevant means protection 'system' is sufficient for most every type of surge. Surge damage is routinely made irrelevant for less money if not using plug- in protectors. A direct lightning strike is the ultimate system test. No damage should ever result - even to protectors. If damage occurs, ask why that surge was not earthed; why it was permitted inside a building. |
#58
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 18, 11:44*am, bud-- wrote:
w_tom wrote: On Jul 17, 1:32 pm, wrote: The IEEE is good enough for everyone here but W_. * They show plug-in surge protectors being used. * *As for technical proof, where is W_'s that says plug-in surger protectors offer no protection and actually cause damage. Nobody said "plug-in surge protectors offer no protection". . "No earth ground means no effective protection." . * Why spend $3000 in plug-in protectors (as Bud says is necessary) one 'whole house' protector provides the same protection Yeah, there you have it folks. Another classic. W_ rants on about how plug-ins offer no protection, then proceeds to deny he ever said that. W_ has not only made it quite clear that he believes they offer no protection, but has done everything he can to try to make it look like they burn houses down, complete with pics from 20 years ago. LOL. See what I mean about his failure at any kind of logical reasoning? |
#59
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 18, 3:18*pm, Douglas Johnson wrote:
w_tom wrote: *A protector is only as effective as its earth ground. Each layer of protection is defined by the one always required component - earthing electrode. * Every plug-in surge protector has at least one path to earth -- the neutral line which is bonded to ground at the panel. *You're right when you say a better ground makes for better protection. *You're flat wrong when you extend that to imply plug in protectors are ineffective. * Yes, seems everyone here agrees with that, except W_. Surge energy must be earthed before entering a building. Indeed it is better to keep surge energy out of a building. *But "must" is way too strong. *Even a panel protector does not keep it out of the building if the panel is inside. * Also true. Plug-in protectors may even provide surges with destructive paths to earth - Page 42 Figure 8. *Facts posted without insults and that contradict half truths from a sales promoter. As I'm sure you have read, the first line of body text after the diagram says "Figure 8 shows a very common improper use of multiport protectors that does not fully protect against lightning damage because of this effect." * So the article attributes the failure to user error, not a failure of the protector. -- Doug Yes, and another W_ argument shot down by his own reference. Did you catch the posts where he lists the "responsible" manufacturers who make and sell whole house protectors and then disparages other companies that make and sell plug-ins? I showed him links months ago that showed that all but one of these same "responsible" manufacturers also sell plug-ins. The remaining one on his list talks about using them as part of effective protection. Yet, he continues to post this list, trying to imply there is a difference between resonsible companies and those that sell plug-ins. Totally bizarre. |
#61
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 19, 10:50*am, w_tom wrote:
[Third of three posts] On Jul 18, 2:59 pm, Douglas Johnson wrote: Please list the exact specifications you desire and an example of a protection claim that would satisfy you. * When one says, "My protector sacrificed itself to save my computer". Reality: *a protector abandoned the computer. *Computer saved itself from a surge so trivial as to destroy the grossly undersized protector. * Previously listed were more responsible manufacturers that offer 'whole house' protectors. *The responsible list is long. *Includes just about every major electrical equipment supplier including Leviton, Square D, Cutler-Hammer, Siemens, Keison, GE, etc. *Some 'whole house' protectors selected randomly: *http://www.deltala.com/prod01.htm#LA302R *http://www.smarthome.com/4860.html *http://www.keison.co.uk/furse/furse06.htm It's quite amazing that W_ can't grasp that continuing to post this list doesn't advance his argument against plug-in surge protectors. It demolishes it, because every one of these "responsible" companies, except one, ALSO SELL PLUG-IN/POINT OF USE SURGE PROTECTORS. I think Keison is a new addition to the list. Let's look at what Keison says about surge protection: http://keison.co.uk/bowthorpe/docs/A...on%20Guide.pdf Take a look at page 10, which clearly shows plug-in protectors being used in an overall and complete protection example. And then there is Siemens, the one company on that list that does not sell plug-in surge protectors. Siemens makes a huge array of electrical equipment, residential, commericial, transmission, generation, communication, etc., so they should know a bit about surge protection. Here is what Simens says: http://www2.sea.siemens.com/Products...ge-Protection/ "Protection at the point of use The second line of defense is the point of use. Here, homeowners can reinforce point-of-entry protection by installing plug-in surge protectors (strips) into grounded wall receptacles where sensitive electronic equipment is located. These plug-in protectors, which generally have much lower limiting voltages than entry protectors, defend against externally and internally generated surges that travel through power, phone, data, and coaxial lines. Plug-in power strips should minimally include AC power protection and appropriate signal line protection and should protect against both catastrophic and small surges. These devices should be installed wherever expensive or sensitive electronic equipment like computers, VCRs, fax machines, PCs with modems, satellite systems, stereo systems, copiers and scanners are located. All types of equipment with signal lines, such as phones, cable TV, and satellites should be equipped with multi-port protectors, which protect signal and AC lines." * In that 14 July discussion, every incoming wire must be integrated into a secondary protection system. Even network wires between buildings. Even TV and satellite dish antenna wires are earthed before entering. *The primary protection system also should be inspected. First *Energy customers, in particular, should give special attention to their primary protection system. * Surge protection to make direct lightning strike irrelevant means protection 'system' is sufficient for most every type of surge. Surge damage is routinely made irrelevant for less money if not using plug- in protectors. * A direct lightning strike is the ultimate system test. *No damage should ever result - even to protectors. This is another statement of religious belief that is easily dismissed by anyone who has seen the effects of a direct lightning strike. To expect that a properly installed typical whole house surge protector means that a direct strike by a major bolt of lightning at the service mast entrance is not going to cause any damage at all is just ludicrous. There are plenty of photos around of what a direct lightning strike can do, including vaporizing conductors bigger than those used in home grounding systems. *If damage occurs, ask why that surge was not earthed; why it was permitted inside a building. And then attribute any damage that does occur to the use of a plug-in surge protector somewhere in the house, right? |
#62
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
[Third of three posts] On Jul 18, 2:59 pm, Douglas Johnson wrote: Please list the exact specifications you desire and an example of a protection claim that would satisfy you. When one says, etc,etc,etc Notice that w_ can't answer the question in 4 posts. -- bud-- |
#64
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 20, 6:28 am, wrote:
It's quite amazing that W_ can't grasp that continuing to post this list doesn't advance his argument against plug-in surge protectors. It demolishes it, because every one of these "responsible" companies, except one, ALSO SELL PLUG-IN/POINT OF USE SURGE PROTECTORS. I think Keison is a new addition to the list. Keison is but another of maybe 100 manufacturers that make effective 'whole house' protectors. With technical knowledge, trader would have known the list of responsible manufacturers is long AND that Keison has long been on that list. Yes, a plug-in protector does protect from surges that typically cause no damage - as w_tom has said repeatedly. Complete protection means also installing protection from surges that don’t cause damage or do not exist. Protection inside appliances makes some types of surges redundant - irrelevant. A complete solution means we buy everything - even protect from things that do not cause damage. Complete protection also means lightning rods, massive line filters, Early Streamer Emission devices, etc. Even telcos do not need or install complete protection. They need effective protection – do not enrich scammer such as ESE manufacturers. No responsible facility would waste money on complete protection. How about a psychic? Also necessary for ‘complete’ protection? High reliability facilities don't waste money on plug-in protectors. How curious. Only manufactures that provide devices for effective solutions are also responsible electrical equipment manufacturers such as GE, Intermatic, etc. That was the point that trader completely ignored to post attacks and accusations. Companies such as APC, Belkin, Tripplite, and Monster Cable - companies that sell no effective solutions - take a $3 power strip, some fancy paint, some ten cents parts, and sell it for an obscene $25 or $150. Why not sell 'whole house' protectors? 'Whole house' protectors do not have massive profit margins. What is promoted by trader and Bud? Profits or protection? If selling plug-in protection as effective (plug-in protector promoters say a ‘whole house’ protector is not necessary), then where does any plug-in protector even claim such protection? None. No plug- in protector - Bud's only solution - does not even claim protection from each type surge. trader also does not answer the #1 question. He cannot answer what requires electrical knowledge. If plug-in protectors were so effective, then why does lightning cause protector failure and some computers are damaged while connected to that protector? Effective solutions mean even the protector is not destroyed during a direct lightning strike. High reliability facilities don't use the 'complete' solution. Instead, they divert surge energy to be harmlessly dissipated in earth - an effective solution that also costs less money. A protector (available from responsible companies) is only as effective as its earth ground. Responsible companies sell ‘whole house’ protectors. APC, Belkin, Tripplite, Monster Cable, et al only sell the most obscenely profitable protectors that also do not even claim to provide protection. However even I would sell trader the ineffective protector. If he wants to remain so naïve as to enrich me, then fine. But I would also do what any responsible company does. I would sell ‘whole house’ protectors with the connection that makes protection possible – earthing. Posted above are concepts that provide a 99% effective solution. Those solutions only come from more responsible companies. Where does trader answer the OP's questions? Only a fool would recommend protectors that do not even claim to provide that protection. Well the complete protection includes $hundreds for plug- in protectors to protect from a surge that almost never exists - and no protection from the surge that typically does cause damage. trader recommends protectors that do not even claim to provide protection. trader ignores an effective product only sold by more responsible manufacturers. |
#65
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
Why do plug-in protectors have all but no earth connection? Wire impedance. Whereas a plug-in protector may be connected less than 0.2 ohm resistance to earth; it may be 120 ohms impedance. Even a trivial 100 amp surge would put something less than 12,000 volts between protector and breaker box. AC electricity about wire resistance. Surges are about wire impedance - which is why EE Times discusses impedance - not resistance. An AC wall receptacle is only a safety (or equipment) ground; not earth ground. It has low resistance and excessively high impedance. Unless the surge originates at the outlet, wire impendence works in your favor because inbound impendence is roughly the same as the outbound. Thus the surge voltage and rise time will be limited before it reaches the outlet. While we're at it, you've mentioned that all appliances have built in surge protection that exceeds the effective protection of plug in protectors. Could you please pick an appliance such as flat screen TV or computer and show us the manufacturer's specifications for surge protection? Thanks, Doug |
#66
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
On Jul 20, 6:28 am, wrote: It's quite amazing that W_ can't grasp that continuing to post this list doesn't advance his argument against plug-in surge protectors. It demolishes it, because every one of these "responsible" companies, except one, ALSO SELL PLUG-IN/POINT OF USE SURGE PROTECTORS. think Keison is a new addition to the list. How curious. Only manufactures that provide devices for effective solutions are also responsible electrical equipment manufacturers such as GE, Intermatic, etc. .. How curious. As has been pointed out several times, all w_'s responsible manufacturers make plug-in suppressors (except SquareD). They must not be responsible at all. SquareD says "electronic equipment may need additional protection by installing plug-in [suppressors] at the point of use." .. No plug- in protector - Bud's only solution - does not even claim protection from each type surge. .. Poor w_. Repeating: "Service panel suppressors are a good idea." Why does SquareD NOT claim protection from "each type of surge". [I have not looked at other manufacturers.] It is bullcrap. Still missing, of course, a source that agrees with w_ that plug-in suppressors are NOT effective. And still never answered - embarrassing questions: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? - Why does the NIST guide says plug-in suppressors are "the easiest solution"? – Why does SquareD say "electronic equipment may need additional protection by installing plug-in [suppressors] at the point of use." - Why do your "responsible manufacturers" make plug-in suppressors? - Why does the IEEE guide says in its example "the only effective way of protecting the equipment is to use a multiport protector"? - How would a service panel suppressor provide any protection in the IEEE guide example? - Why does the IEEE Emerald book recognize plug-in suppressors as effective? – Why does the NIST guide say "One effective solution is to have the consumer install" a multiport plug-in suppressor. For real science read the NIST and IEEE guides. Both say plug-in suppressors are effective. -- bud-- |
#67
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 10, 4:21 pm, w_tom wrote:
What does your telco do to have better protection from about 100 surges during every thunderstorm? They don't use any plug-in protectors adjacent to equipment. They put every 'whole house'protector where each wire enters the building, as close to earth ground as is practicable, and protectors up to 50 meters distant from electronics. Why 50 meters? Because separation increases protection. "Power surges on telephone exchange equipment meanwhile, affected a third of the Island. At 10.50 p.m. the surges resulted in a "main power failure" at Bermuda Telephone Company (BTC's) Paget Telephone Exchange, causing interruptions to 22,000 business and residential lines from Smiths to Dockyard. Last night, 2,000 customers in the West End were still without service. A BTC spokeswoman said: "The BTC staff will work very hard through the night to get everyone back on line. There are approximately 2,500 customers in the Devonshire South and Smiths South areas, feeding directly out of the Paget Exchange, who also continue to experience a service interruption." Guess they should have paid attention to the expert. |
#68
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
On Jul 19, 1:04 pm, Caesar Romano wrote:
I assume then that those plug-in surge protectors that have *more* than one path to earth have both the neutral line and the ground (green) line. Is that correct? Impedance is why that wire is not a connection to earth. To claim plug-in protectors are effective, others must ignore impedance or (more often) have no idea what impedance is. Impedance is why a surge protector on Page 42 Figure 8 does not divert surge current via white (neutral) and green (safety ground) wires. If the plug-in protector was earthed via those wires, then 8000 volts could not exist to destroy the adjacent TV. But the surge instead imposed 8000 volts destructively on an adjacent TV. How could these 8000 volts exist IF protector was earthed by neutral and safety ground wires? No such earthing existed. Wire impedance was excessive. Provided were typical numbers for 50 feet of Romex. Whereas that wire is well less than 0.2 ohms resistance, that same wire is maybe 120 ohms impedance. Even a trivial 100 amp surge would put wall receptacle (and surge protector) at something like 12,000 volts. Bud pretends wire impedance does not exist. And yet every professional citation (including Bud's) requires low impedance (not low resistance) earthing connections. Earthing for surge protection must be short to earth ('less than 10 feet', no sharp bends, no splices, etc). A wall receptacle is not called earth ground. It is called safety ground or equipment ground. No accident. Wall receptacles are not earth grounds. Why does Bud avoid discussing "What these protective devices do is ... simply divert it to ground, where it can do no harm." Because no plug-in protector claims (in numeric specs) to achieve that earthing and does not claim to protect from that type of surge. Bud would have you assume all surges are same. Sales are at risk. Front page article in Electrical Engineering Times entitled "Protecting Electrical Devices From Lightning Transients" discusses wire impedance because 50 foot of interior AC electric wiring is woefully too long to provide earthing. Since the article is about protecting electrical devices, then it does not discuss plug-in protectors and it does discuss how to make earthing better. But then EE Times is for engineers; not for a majority who know only what is taught on retail store shelves. That propaganda is powerful stuff. Assume a safety ground wire is earthing a surge. Since that wire is bundled with other wires, then surges are induced on those other wires. Now more surges on other wires - more surges inside the building. Just another reason why plug-in protectors do not properly earth the destructive surge AND why surges must be kept out of the building. One requirement for effective surge protection: those earthing wires must be separated from other non-grounding wires. No technically accurate answer is determined from majority conclusions. After all, Saddam had all those WMDs? The majority said so by ignoring facts and numbers that engineers saw. It was also obvious in those 2002 numbers that Saddam’s WMDs did not exist. So what did the majority say? Propaganda from retail store shelves is the source of most recommendations. With obscene profit margins, a plug-in protector gets promoted everywhere; 'whole house' protectors only sell on the science. If you don't grasp this simple science, then spend tens or 100 times more money on plug-in protectors. Propaganda is that effective. How does Monster Cable sell a $3 power strip with fancy paint and ten cent protector parts for $150? Obscene profits make propaganda easy. A surge will travel to earth via that Romex wire and not induce surges on all other wires? Of course not. Even sharp bends inside every junction box means that wire does not provide effective earthing. What is found only in responsible (professional) citations? Even references to no sharp bends. Why? A sharp bends only increase 8000 volts destructively through the adjacent TV - Page 42 Figure 8. No earth ground means no effective protection. Why does Polyphaser make a protector with no earth ground connection? For even better protection (Polyphaser is an industry benchmark), that protector makes a zero foot connection to earth. One who even designed and built this stuff (who learned after direct lightning strikes from surprising successes and by making these mistakes) is the minority. Therefore he is wrong? Why does your telco not use plug-in protectors? Why do all telcos use ‘whole house’ protectors? Retail store salesmen or angry others cannot answer that. A protector is only as effective as its earth ground. Demonstrated by numbers and citations is a wall receptacle does not provide earthing. Those who promote plug-in protectors also avoid all discussion about impedance – an engineering concept not taught on retail store shelves. A concept so essential to protection as to be discussed by engineers in a magazine only for electrical engineers. An article entitled “Protecting Electrical Devices From Lightning Transients" devotes a large part to impedance – and why that wire connection to earth must be so short; no sharp bends, etc. What does that article and most every professional source note? That neutral and safety ground wire cannot earth surges. It will easily conduct 60 Hz AC electricity. But surges have completely different characteristics make wire impedance relevant. People such as trader do not do this stuff. What did every professional citation define? Resistance? Of course not. Trader is only discussing resistance. It is what he understands. But every citation also talks about wire *impedance* when discussing surges. An electrical concept that is little taught in tech school but is well taught to engineers. How much current can a lamp cord (18 AWG) conduct? That wire typically rated for 10 amps may conduct approaching 60,000 amps of surge current – can even conduct a majority of direct lightning strikes without damage. A majority without engineering training would not know this; may even deny it. Which one is an engineer and has experience? A protector is only as effective as its earth ground - which is why a plug-in protector has all but no earthing. |
#69
Posted to alt.home.repair
|
|||
|
|||
"chain" surge suppressers?
w_tom wrote:
Even a trivial 100 amp surge would put wall receptacle (and surge protector) at something like 12,000 volts. Bud pretends wire impedance does not exist. .. w_ is fond of inventing opinions and attributing them to others. w_ is going to have trouble getting 12,000V past a receptacle, which will arc-over at 6.000V. After arc-over there will be hundreds of volts. The same thing happens at service panels. But w_ is not encumbered by reality. The 6,000V arc–over at service panels combined with the impedance of branch circuits greatly limits the current, and thus energy, that can reach a plug-in suppressor. .. Why does your telco not use plug-in protectors? .. Geez, thats a tough one. Umm, maybe because it is high amp direct wired. And wouldn’t all 683,297 telephone circuits have to go through a multiport suppressor? And appropriateness of devices for different uses? .. Trader is only discussing resistance. .. Nope. Poor w_ can’t figure out what trader said. Might be the religious blinders. .. A protector is only as effective as its earth ground , w_’s religious mantra will save him from confusing thoughts. Such as from the IEEE guide - plug-in suppressors work primarily by clamping, not earthing. The guide says earthing occurs elsewhere. And surprise - still missing, a source that agrees with w_ that plug-in suppressors are NOT effective. And still never answered - embarrassing questions: - Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors? - Why does the NIST guide says plug-in suppressors are "the easiest solution"? – Why does SquareD say "electronic equipment may need additional protection by installing plug-in [suppressors] at the point of use." - Why do your "responsible manufacturers" make plug-in suppressors? - Why does the IEEE guide says in its example "the only effective way of protecting the equipment is to use a multiport protector"? - How would a service panel suppressor provide any protection in the IEEE guide example? - Why does the IEEE Emerald book recognize plug-in suppressors as effective? – Why does the NIST guide say "One effective solution is to have the consumer install" a multiport plug-in suppressor. For real science read the NIST and IEEE guides. Both say plug-in suppressors are effective. -- bud-- |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Poulan pro 44cc 20" chain saw - chain oil not feeding | Home Repair | |||
Initial current surge with "ramp up" dimmer modules | UK diy | |||
For women who desire the traditional 12-marker dials, the "Faceto,""Juro" and "Rilati" all add a little more functionality, without sacrificingthe diamonds. | Woodworking | |||