I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Generic electrical question Do volts drop when a load is on the circuit


"hombrewdude" wrote in message
oups.com...
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?

It is called voltage drop. Your cable has resistance, so it uses up some of
the energy.


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default Generic electrical question Do volts drop when a load is on thecircuit

Toller wrote:
"hombrewdude" wrote in message
oups.com...
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?

It is called voltage drop. Your cable has resistance, so it uses up some of
the energy.




The reason why I bothered to check...

We are having storms high wind in my area now.
The lights flickered like the power was off.
But this one particular circuit was actually off (my fish tank)

Could I have had a voltage drop in my entire house, then compounded with
the fish tank draw cause it to go out?
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Generic electrical question Do volts drop when a load is on thecircuit

hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?


is this a very long run?

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default Generic electrical question Do volts drop when a load is on thecircuit

Not really..

I ran 20 amp service about 50 feet



Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?


is this a very long run?

nate



  #6   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Generic electrical question Do volts drop when a load is on thecircuit

homebrewdude wrote:
....[top posting repaired]... Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?


is this a very long run?


Not really..

I ran 20 amp service about 50 feet


What size wire?

--
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default Generic electrical question Do volts drop when a load is on thecircuit

12 gage



dpb wrote:
homebrewdude wrote:
...[top posting repaired]... Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?


is this a very long run?


Not really..

I ran 20 amp service about 50 feet


What size wire?

--

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default Generic electrical question Do volts drop when a load is on thecircuit

I really messed that up...

I ran 20 amp on another project.

My basement and garage were on the same breaker.
I ran wire to isolate the basement from the garage.
Now they are on their own 15 breaker.

The basement service with the fish tank is probably pulling 10 amp at
full load.
Fish tank, lights and TV



homebrewdude wrote:
12 gage



dpb wrote:
homebrewdude wrote:
...[top posting repaired]... Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?


is this a very long run?


Not really..

I ran 20 amp service about 50 feet


What size wire?

--

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Generic electrical question Do volts drop when a load is on the circuit


"homebrewdude" wrote in message
news
Toller wrote:
"hombrewdude" wrote in message
oups.com...
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?

It is called voltage drop. Your cable has resistance, so it uses up some
of the energy.



The reason why I bothered to check...

We are having storms high wind in my area now.
The lights flickered like the power was off.
But this one particular circuit was actually off (my fish tank)

Could I have had a voltage drop in my entire house, then compounded with
the fish tank draw cause it to go out?


Most unlikely. The voltage drop is pretty constant, unless you have a large
motor go on and it spikes. But it can't trip a circuit breaker or damage a
circuit. (it can damage a motor, but that's another story.) More likely
you had some voltage transients hit you with the storm. They could easily
trip a GFCI or less likely a circuit breaker. I would look around for GFCIs
that have to be reset.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default Generic electrical question Do volts drop when a load is on the circuit

I don't think the distance had anything to do with the breaker
tripping. If it only happened once I would not sweat it.

I can't think of a scenario where a storm could trip an individual
breaker unless lightning directly hit something on the circuit.

A 5 amp load can cause that much drop over a long distance, but it is
within range. 12 gage wire on a 15 amp circuit gives you plenty of
breathing room.

On Mon, 10 Sep 2007 20:28:27 -0500, homebrewdude
wrote:

I really messed that up...

I ran 20 amp on another project.

My basement and garage were on the same breaker.
I ran wire to isolate the basement from the garage.
Now they are on their own 15 breaker.

The basement service with the fish tank is probably pulling 10 amp at
full load.
Fish tank, lights and TV



homebrewdude wrote:
12 gage



dpb wrote:
homebrewdude wrote:
...[top posting repaired]... Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?


is this a very long run?


Not really..

I ran 20 amp service about 50 feet

What size wire?

--



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default Generic electrical question Do volts drop when a load is on thecircuit

The breaker never tripped.

The power dropped and lights went out, pumps turned off.

But all the other lights and TV stayed on.

All on one breaker, which did not trip.




Terry wrote:
I don't think the distance had anything to do with the breaker
tripping. If it only happened once I would not sweat it.

I can't think of a scenario where a storm could trip an individual
breaker unless lightning directly hit something on the circuit.

A 5 amp load can cause that much drop over a long distance, but it is
within range. 12 gage wire on a 15 amp circuit gives you plenty of
breathing room.

On Mon, 10 Sep 2007 20:28:27 -0500, homebrewdude
wrote:

I really messed that up...

I ran 20 amp on another project.

My basement and garage were on the same breaker.
I ran wire to isolate the basement from the garage.
Now they are on their own 15 breaker.

The basement service with the fish tank is probably pulling 10 amp at
full load.
Fish tank, lights and TV



homebrewdude wrote:
12 gage



dpb wrote:
homebrewdude wrote:
...[top posting repaired]... Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the volts
should drop to 118?

Does this make sense?

is this a very long run?

Not really..

I ran 20 amp service about 50 feet
What size wire?

--

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 109
Default Generic electrical question Do volts drop when a load is on the circuit

On Mon, 10 Sep 2007 23:00:19 -0500, homebrewdude
wrote:

The breaker never tripped.

The power dropped and lights went out, pumps turned off.

But all the other lights and TV stayed on.

All on one breaker, which did not trip.

Voltage drop means the whole overall circuit will be drawing less
current , not more (due to the added resistance). If the voltage gets
too low, you might have problems with dim bulbs and a slow-to-heat
fish tank, but it sounds like you are not there yet.

If you continue to add load, you will be drawing more current and may
reach the tripping point of the breaker. (It may not be exactly 15
amps). The reason it trips can be a complex function involving time,
thermal delay, and factors like surge intensity. Residential circuits
are usually derated to 80% of the breaker rating for maximum
continuous load.

If the breaker is a GFCI breaker, it might trip for apparently no
reason at all. Usually, though it is caused by actual leakage to the
ground circuit. I've also had several trips due to nearby lightning
strikes, but the new GFCI's are supposed to be better for this.



  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Generic electrical question Do volts drop when a load is on thecircuit

homebrewdude wrote:
I really messed that up...

I ran 20 amp on another project.

My basement and garage were on the same breaker.
I ran wire to isolate the basement from the garage.
Now they are on their own 15 breaker.

The basement service with the fish tank is probably pulling 10 amp at
full load.
Fish tank, lights and TV


Voltage drop on a 15A circuit (#14 wire), 50 feet of Romex, is 3 volts.

--
bud--



homebrewdude wrote:
12 gage



dpb wrote:
homebrewdude wrote:
...[top posting repaired]... Nate Nagel wrote:
hombrewdude wrote:
I have one of these Kill A Watt meters.

In the socket it is showing 120volts
I put a load on it, that is about 5 amps. I would not think the
volts
should drop to 118?

Does this make sense?


is this a very long run?


Not really..

I ran 20 amp service about 50 feet

What size wire?

--

  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Generic electrical question Do volts drop when a load is on the circuit

On Sep 11, 12:00?am, homebrewdude
wrote:
The breaker never tripped.

The power dropped and lights went out, pumps turned off.

But all the other lights and TV stayed on.

All on one breaker, which did not trip.

'


simple most homes are 220 volt breakers are fed from both sides of
power line.

A supply transformer up the street fried once knocking out one side of
the line, while the other side continued to work fine.

thats probably what happened to you, power company breaker on
transformner tripped knocking out that outlet and others you hadnt
noticed, then reset.......

its happened here once and can be very confusing

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Question and request for circuit diagram Brian_SouthJersey Home Repair 7 February 27th 07 02:27 PM
Looking to drop 6 volts dc to 4.5 volts dc .D.E Electronics 19 October 7th 06 06:37 AM
Replacing a circuit breaker 110 Volts CGB Home Repair 21 December 24th 05 06:35 AM
Small electrical motor question. 12 volts 230 Watts on Peg-Perego power wheel jeep rutman Electronics Repair 13 May 1st 05 10:28 PM
Voltage Drop Under Load [email protected] Home Repair 12 January 12th 05 10:08 PM


All times are GMT +1. The time now is 09:52 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"