Happy New Year to everyone! I have an electical probem that's a little
bit of a mystery to me. We moved into our house 2 years ago and just
recently the electrical outlet for the washer started to drop voltage
under load. I have seemed to fix the problem but am not sure of the
exact cause.

The outlet will start out at 120v AC and then when the washer is
started, the voltage drops to 40-60v. If I reset the breaker, the
voltage will return to 120v until load is placed on the circuit again.
This is a recent problem that has occurred without any changes to the
wiring, electrical load, etc. For two years, the outlet on the washer
worked fine.

In tracing this problem, I found that the receptacle was a 15A, but the
breaker and wiring was 20A. When I replaced the 15A receptacle with
another 15A receptacle, the problem persisted. When I replaced the
receptacle with a 20A one and also replaced the breaker it seems to be
working now. Any ideas to what the problem is and why it has only
shown up recently?

Thanks in advance,

Herb

  #3   Report Post  
toller
 
Posts: n/a
Default


wrote in message
oups.com...
Happy New Year to everyone! I have an electical probem that's a little
bit of a mystery to me. We moved into our house 2 years ago and just
recently the electrical outlet for the washer started to drop voltage
under load. I have seemed to fix the problem but am not sure of the
exact cause.

The outlet will start out at 120v AC and then when the washer is
started, the voltage drops to 40-60v. If I reset the breaker, the
voltage will return to 120v until load is placed on the circuit again.
This is a recent problem that has occurred without any changes to the
wiring, electrical load, etc. For two years, the outlet on the washer
worked fine.


What do you mean "if I reset the breaker"? Did the breaker trip? If not,
why would you reset it?

Where did you measure the voltage?

In tracing this problem, I found that the receptacle was a 15A, but the
breaker and wiring was 20A. When I replaced the 15A receptacle with
another 15A receptacle, the problem persisted. When I replaced the
receptacle with a 20A one and also replaced the breaker it seems to be
working now. Any ideas to what the problem is and why it has only
shown up recently?


There is no difference between a 15a receptacle and a 20a receptacle except
for the holes; so if a new 15a didn't help, a new 20a wouldn't either.
If replacing the breaker fixed it, then it must have been a bad breaker or a
poor connection.

Thanks in advance,

Herb



  #4   Report Post  
 
Posts: n/a
Default

What do you mean "if I reset the breaker"? Did the breaker trip? If
not,
why would you reset it?

The breaker didn't trip. I reset it (switched off then on) to see what
would happen.

Where did you measure the voltage?

At the receptacle. The voltage is 120V after I reset the breaker.
When I plug in the washer, I initially hear it startup then it stops.
When it stops, I measure about 60V. The receptacle remains at about
60V until the breaker is reset. Note that when I test the voltage
(both times with 120V and 60V) there was no load (the washer was
unplugged).

Thanks, Herb

  #5   Report Post  
 
Posts: n/a
Default

Before replacing the breaker, did the breaker or the area around it feel
warm/hot? If so, it is most likely a loose connection where the wire is
terminated at the breaker - or burnt contacts in the breaker - unlikely if
the breaker was not tripping.

I would suggest tightening all of the breaker connections.

Does your house have aluminum wire. If so, tightening is especially
important as is ensuring that the right "gunk" has been used on the
terminals.


On 1 Jan 2005 17:46:27 -0800, wrote:

What do you mean "if I reset the breaker"? Did the breaker trip? If

not,
why would you reset it?

The breaker didn't trip. I reset it (switched off then on) to see what
would happen.

Where did you measure the voltage?

At the receptacle. The voltage is 120V after I reset the breaker.
When I plug in the washer, I initially hear it startup then it stops.
When it stops, I measure about 60V. The receptacle remains at about
60V until the breaker is reset. Note that when I test the voltage
(both times with 120V and 60V) there was no load (the washer was
unplugged).

Thanks, Herb




  #8   Report Post  
Dave in Lake Villa
 
Posts: n/a
Default

I would tighten all of your breaker connections PLUS all of your neutral
connections in the electric panel as well. For safetys sake, do it with
the Main Breaker 'off' and use a flashlight.

  #10   Report Post  
TURTLE
 
Posts: n/a
Default


wrote in message
oups.com...
Happy New Year to everyone! I have an electical probem that's a little
bit of a mystery to me. We moved into our house 2 years ago and just
recently the electrical outlet for the washer started to drop voltage
under load. I have seemed to fix the problem but am not sure of the
exact cause.

The outlet will start out at 120v AC and then when the washer is
started, the voltage drops to 40-60v. If I reset the breaker, the
voltage will return to 120v until load is placed on the circuit again.
This is a recent problem that has occurred without any changes to the
wiring, electrical load, etc. For two years, the outlet on the washer
worked fine.

In tracing this problem, I found that the receptacle was a 15A, but the
breaker and wiring was 20A. When I replaced the 15A receptacle with
another 15A receptacle, the problem persisted. When I replaced the
receptacle with a 20A one and also replaced the breaker it seems to be
working now. Any ideas to what the problem is and why it has only
shown up recently?

Thanks in advance,

Herb


This is Turtle.

Look at the spades where the breaker would tie on to the buss bar and you will
see the spades on the old breaker burnt somewhat if this was the problem. It
sure sounds like it.

TURTLE




  #11   Report Post  
Don Young
 
Posts: n/a
Default

I suspect that your "60volts" readings are actually zero power readings
caused by use of a high impedance digital voltmeter. With the load
disconnected, stray leakage and capacitance can cause this effect. Plug a
small load such as a lamp into one side of the receptacle while you measure.
Otherwise, the suggestions about bad connections or a bad breaker are good.
I believe your trouble was caused by a bad breaker.
Best Regards, Don Young

"Larry Caldwell" wrote in message
k.net...
In article .com,
) says...

Where did you measure the voltage?

At the receptacle. The voltage is 120V after I reset the breaker.
When I plug in the washer, I initially hear it startup then it stops.
When it stops, I measure about 60V. The receptacle remains at about
60V until the breaker is reset. Note that when I test the voltage
(both times with 120V and 60V) there was no load (the washer was
unplugged).


Bad breaker or not, you should either have measured 110-120v or nothing
with no load. There is a fairly serious problem with your electrical
service. The only way you could get a 60v. reading at a receptacle is
if there is a substantial voltage on the neutral. Usually that is
caused by the failure of the neutral connection to the power
transformer.

The problem will appear to be transient, depending on how well balanced
your household load happens to be. You might notice some lights getting
brighter than normal, or your garbage disposal suddenly slowing down or
running like a bandit.

If you don't feel confident that you can troubleshoot this, call an
electrician. A bad service neutral is a very dangerous condition.

--
http://home.teleport.com/~larryc



  #12   Report Post  
 
Posts: n/a
Default

Thanks everyone for the great answers and feedback!

After doing some additional searching, I also was wondering if the 60v
reading came from my cheap multi-meter (high impedance/inductive
pickup). Whenver I got this reading, it was always without any load on
the circuit and I would only notice this condition because the washing
machine would stop running. In retrospect, if it was really at 60v,
the washing machine may have at least gurgled (shouldn't the motor
still run at 60v, albeit much hotter)? If it occurs again, I'll try
plugging a lamp in and taking a reading with my analog multi-meter to
see it if is really 60v.

The other interesting thing is that the neutral wire snapped at the
terminal when I switched the receptacle so it may have been the bad
connection. The hot wire was warm.

Also, I only notice this problem on one receptacle that is serviced by
a single breaker -- so I assume this problem isn't systemic.
Thanks, Herb

  #13   Report Post  
Playintennis5274
 
Posts: n/a
Default

REMOTELY the motor may be partially burnt out drawing too
much current.


no, it's not the moter, check every connection from the panel to the plug.
start up machine like you have been when it shuts down stick yer meter on hot
and ground and see if you still get 60v , if you do get 60 then you know it's
the hot if you get 120 bad nuetral
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage drop switching relays? Joe in Bendigo Electronics 10 June 13th 04 06:59 AM
*** How to Filter out the Crap *** 017 David F. Eisan Woodworking 2 April 19th 04 03:09 PM
*** How to filter out the Crap! *** 007 David F. Eisan Woodworking 0 October 27th 03 12:29 PM
Better nfilter Bill Thomas Woodworking 2 October 21st 03 07:11 PM


All times are GMT +1. The time now is 05:17 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"