Default Voltage when Switch is Off

I just replaced a 3-way switch, and when I was testing, I noticed that there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and tube
wiring. Should I worry that something nasty is going on?

Thanks,
Michael


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,447
Default Voltage when Switch is Off

On Jul 7, 3:43 pm, "M PRESSMAN" wrote:
I just replaced a 3-way switch, and when I was testing, I noticed that there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and tube
wiring. Should I worry that something nasty is going on?

Thanks,
Michael


An analog meter even though not as sensitive as digital/electronic
one, might pick up such an induced voltage.
Such a meter with a fairly typical one milliamp full scale deflection,
on its 30 volt scale will have a resistance of 30,000 ohms.
On a 100 volt scale perhaps 100,000 ohms.
No experience with K and T wiring but those wires tend to be
seaparated; not twisted or close together as with modern wiring. Would
that not make induction from an adajcent live wire more likely?
You could put a bulb in series with the feed wire from the fuse,
leaving the bulb out of the fixture, just to make sure there is no
current leaking through?

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 47
Default Voltage when Switch is Off

Me, I'd check your load bearing neutral. [Could be floating - causing you
slight voltage reading.]

--
Zyp

"terry" wrote in message
oups.com...
On Jul 7, 3:43 pm, "M PRESSMAN" wrote:
I just replaced a 3-way switch, and when I was testing, I noticed that

there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that

glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and

tube
wiring. Should I worry that something nasty is going on?

Thanks,
Michael


An analog meter even though not as sensitive as digital/electronic
one, might pick up such an induced voltage.
Such a meter with a fairly typical one milliamp full scale deflection,
on its 30 volt scale will have a resistance of 30,000 ohms.
On a 100 volt scale perhaps 100,000 ohms.
No experience with K and T wiring but those wires tend to be
seaparated; not twisted or close together as with modern wiring. Would
that not make induction from an adajcent live wire more likely?
You could put a bulb in series with the feed wire from the fuse,
leaving the bulb out of the fixture, just to make sure there is no
current leaking through?



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Voltage when Switch is Off

thanks.. what do you mean by a floating load bearing neutral?

Michael

"Zephyr" wrote in message
news:rvydnUFKy4FNYBLbnZ2dnUVZ_j6dnZ2d@championbroa dband.com...
Me, I'd check your load bearing neutral. [Could be floating - causing you
slight voltage reading.]

--
Zyp

"terry" wrote in message
oups.com...
On Jul 7, 3:43 pm, "M PRESSMAN" wrote:
I just replaced a 3-way switch, and when I was testing, I noticed that

there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that

glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and

tube
wiring. Should I worry that something nasty is going on?

Thanks,
Michael


An analog meter even though not as sensitive as digital/electronic
one, might pick up such an induced voltage.
Such a meter with a fairly typical one milliamp full scale deflection,
on its 30 volt scale will have a resistance of 30,000 ohms.
On a 100 volt scale perhaps 100,000 ohms.
No experience with K and T wiring but those wires tend to be
seaparated; not twisted or close together as with modern wiring. Would
that not make induction from an adajcent live wire more likely?
You could put a bulb in series with the feed wire from the fuse,
leaving the bulb out of the fixture, just to make sure there is no
current leaking through?





  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Voltage when Switch is Off

On Jul 7, 1:43 pm, "M PRESSMAN" wrote:
I just replaced a 3-way switch, and when I was testing, I noticed that there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and tube
wiring. Should I worry that something nasty is going on?

Thanks,
Michael


You could have a shared neutral. I have one in my house and I have to
turn off the breakers for both circuits to avoid a situation like you
describe. The breakers should in fact be ganged. (It's on my list!)

See this site: http://www.thecircuitdetective.com/twocircuit.htm



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,431
Default Voltage when Switch is Off

In article JgQji.228$z64.139@trnddc07, M PRESSMAN wrote:
I just replaced a 3-way switch, and when I was testing, I noticed that there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and tube
wiring. Should I worry that something nasty is going on?


Since it takes at least about 50 volts AC to light a neon lamp, and even
more for the NE-2H, A1C and similar ones in testers but the meter reads
only 30 volts, what you have is a situation with low, highly limited
current.

I suspect you have a switch at the end of a run of wire, and capacitance
between the two wires is allowing a small amount of AC current to flow.

If the switch in question is at the end of a run of wire, this is
perfectly normal.

- Don Klipstein )
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default Voltage when Switch is Off

DerbyDad03 wrote:

On Jul 7, 1:43 pm, "M PRESSMAN" wrote:

I just replaced a 3-way switch, and when I was testing, I noticed that there
was 30 volts (Radio Shack analog meter) at the light socket when the
switches were off. I tried using one of the little idiot lights that glow
with voltage, and indeed, it glowed weakly. The light and the 2 3-way
switches work perfectly though. This circuit is fed by old knob and tube
wiring. Should I worry that something nasty is going on?

Thanks,
Michael



You could have a shared neutral. I have one in my house and I have to
turn off the breakers for both circuits to avoid a situation like you
describe. The breakers should in fact be ganged. (It's on my list!)

See this site: http://www.thecircuitdetective.com/twocircuit.htm


C'mon, 30 VOLTS due to a shared neutral?

That would take more than just a "shared" neutral, it'd take a very
poorly connected or high resistance neutral, in which case it's unlikely
that as the OP said, the light and the switches work perfectly.

More likely slight resistive or capacitive leakage currents tweaking the
test meter, as several others have said already.

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
The speed of light is 1.98*10^14 fathoms per fortnight.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Voltage when Switch is Off

replying to Don Klipstein, Bruce wrote:
don wrote:

Since it takes at least about 50 volts AC to light a neon lamp, and even
more for the NE-2H, A1C and similar ones in testers but the meter reads
only 30 volts, what you have is a situation with low, highly limited
current.
I suspect you have a switch at the end of a run of wire, and capacitance
between the two wires is allowing a small amount of AC current to flow.
If the switch in question is at the end of a run of wire, this is
perfectly normal.
- Don Klipstein )




I have the exact same situation in the house addition I'm building, two
new 3-way circuits wired as in the photo at the end of a wire run. With
the switches in the off position, one circuit read 29 volts across the
load wires, and the other read 31 volts. So I hooked up a temporary
single light bulb thinking I'd see a very faint glow in the filament.
Nothing doing. No glow, and then with the light off, when I read across
the terminals of the bulb socket, I read zero volts.



--


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8,582
Default Voltage when Switch is Off

On Tue, 17 Nov 2015 19:44:02 +0000, Bruce
wrote:

replying to Don Klipstein, Bruce wrote:
don wrote:

Since it takes at least about 50 volts AC to light a neon lamp, and even
more for the NE-2H, A1C and similar ones in testers but the meter reads
only 30 volts, what you have is a situation with low, highly limited
current.
I suspect you have a switch at the end of a run of wire, and capacitance
between the two wires is allowing a small amount of AC current to flow.
If the switch in question is at the end of a run of wire, this is
perfectly normal.
- Don Klipstein )




I have the exact same situation in the house addition I'm building, two
new 3-way circuits wired as in the photo at the end of a wire run. With
the switches in the off position, one circuit read 29 volts across the
load wires, and the other read 31 volts. So I hooked up a temporary
single light bulb thinking I'd see a very faint glow in the filament.
Nothing doing. No glow, and then with the light off, when I read across
the terminals of the bulb socket, I read zero volts.


You probably need a low impedence meter to measure the voltage,
instead of high impedance that puts no load on the circuit. Usually
that means analog, with a needle, rather than digital.

And stop posting urls with [img] in front of or behind them. Each
real user of usenet has to edit them out. It's better that you edit
them once, than everyone of us having to do so.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Voltage when Switch is Off

On Tuesday, November 17, 2015 at 3:11:19 PM UTC-5, Micky wrote:
On Tue, 17 Nov 2015 19:44:02 +0000, Bruce
wrote:

replying to Don Klipstein, Bruce wrote:
don wrote:

Since it takes at least about 50 volts AC to light a neon lamp, and even
more for the NE-2H, A1C and similar ones in testers but the meter reads
only 30 volts, what you have is a situation with low, highly limited
current.
I suspect you have a switch at the end of a run of wire, and capacitance
between the two wires is allowing a small amount of AC current to flow.
If the switch in question is at the end of a run of wire, this is
perfectly normal.
- Don Klipstein )




I have the exact same situation in the house addition I'm building, two
new 3-way circuits wired as in the photo at the end of a wire run. With
the switches in the off position, one circuit read 29 volts across the
load wires, and the other read 31 volts. So I hooked up a temporary
single light bulb thinking I'd see a very faint glow in the filament.
Nothing doing. No glow, and then with the light off, when I read across
the terminals of the bulb socket, I read zero volts.


You probably need a low impedence meter to measure the voltage,
instead of high impedance that puts no load on the circuit. Usually
that means analog, with a needle, rather than digital.


That would account for why he had 30 volt with no bulb and 0
volts with it. A high impedance meter can read what amounts
to stray voltage. With even a small load, it disappears.

As to whether he has some real problem, who knows, because all
we know are the two voltage readings. Does the light work?


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 273
Default Voltage when Switch is Off

Bruce: Neon bulbs are low voltage I don,t what is max. voltage before it
burns,
however there are built in their fixture with Resistor in series and there
some
that resistor is built into fixture in most cases not visible that is why
some NE-2
are built as bayonet plug in, like flashlight so that could be easily
replace.

"Bruce" wrote in message
oups.com...

replying to Don Klipstein, Bruce wrote:
don wrote:

Since it takes at least about 50 volts AC to light a neon lamp, and even
more for the NE-2H, A1C and similar ones in testers but the meter reads
only 30 volts, what you have is a situation with low, highly limited
current.
I suspect you have a switch at the end of a run of wire, and capacitance
between the two wires is allowing a small amount of AC current to flow.
If the switch in question is at the end of a run of wire, this is
perfectly normal.
- Don Klipstein )




I have the exact same situation in the house addition I'm building, two
new 3-way circuits wired as in the photo at the end of a wire run. With
the switches in the off position, one circuit read 29 volts across the
load wires, and the other read 31 volts. So I hooked up a temporary
single light bulb thinking I'd see a very faint glow in the filament.
Nothing doing. No glow, and then with the light off, when I read across
the terminals of the bulb socket, I read zero volts.



--

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 420
Default Voltage when Switch is Off

Capacitive coupling from a hot wire into an ungrounded wire will give exactly the results the OP mentioned, If there is a third wire associated with the first two wires, and that wire is ungrounded at either end, it will also pick up a signal triggering a sensitive voltage tester. But, if that third wire is grounded at either end, there should be no voltage induced/capacitively in the ungrounded second wire. If the third wire is gounded at the near end, nothing should be measured. If the third wire is grounded at the far end and at the near end, and carries some return current, there can be magnetic coupling to the third wire and some voltage may be measured.
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,980
Default Voltage when Switch is Off

On 11/17/2015 02:11 PM, Micky wrote:

[snip]



You probably need a low impedence meter to measure the voltage,
instead of high impedance that puts no load on the circuit. Usually
that means analog, with a needle, rather than digital.


It's a high source impedance (what causes voltage drop). It doesn't take
much load to drop the voltage to 0. A LED with appropriate resistor my
light.

I have the same situation with solid-state relays (used for holiday
light control), "off" isn't quite off and a LED load will light (dimly).
Any non-LED load drops the voltage to 0.

And stop posting urls with [img] in front of or behind them. Each
real user of usenet has to edit them out. It's better that you edit
them once, than everyone of us having to do so.


I see no purpose to the [IMG] (perhaps some web forum thing?), but don't
have to edit them to click on the URL (which my newsreader, Thunderbird,
recognized).

--
37 days until the winter celebration (Friday December 25, 2015 12:00:00
AM for 1 day).

Mark Lloyd
http://notstupid.us/

"Never react emotionally to criticism. Analyze yourself to determine
whether it is justified. If it is, correct yourself. Otherwise, go on
about your business." -- Norman Vincent Peale
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help: low voltage in circuit, switch off Steve Home Repair 8 June 12th 06 05:08 AM
Strange voltage reading at unknown switch Max Home Repair 7 April 2nd 06 05:54 AM
Strange voltage reading at unknown switch Max Home Repair 0 April 1st 06 06:12 PM
voltage at ceiling fixture with switch off Mike Ballard Home Repair 3 August 17th 05 04:14 AM
Low voltage on switch John1 Home Repair 8 February 15th 05 01:06 AM


All times are GMT +1. The time now is 10:43 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"